Skip to main content
Install and maintain

Replace the caching module - FAS8200

Contributors

You must replace the caching module in the controller module when your system registers a single AutoSupport (ASUP) message that the module has gone offline; failure to do so results in performance degradation.

You might want to erase the contents of your caching module before replacing it.

  • Although data on the caching module is encrypted, you might want to erase any data from the impaired caching module and verify that the caching module has no data:

    • Erase the data on the caching module: system controller flash-cache secure-erase run -node node name localhost -device-id device_number

      Note Run the system controller flash-cache show command if you don't know the flashcache device ID.
    • Verify that the data has been erased from the caching module: system controller flash-cache secure-erase show

  • You must replace the failed component with a replacement FRU component you received from your provider.

Step 1: Shut down the impaired controller

You can shut down or take over the impaired controller using different procedures, depending on the storage system hardware configuration.

Option 1: Most configurations

To shut down the impaired controller, you must determine the status of the controller and, if necessary, take over the controller so that the healthy controller continues to serve data from the impaired controller storage.

About this task
  • If you are using NetApp Storage Encryption, you must have reset the MSID using the instructions in the Returning SEDs to unprotected mode.

  • If you have a SAN system, you must have checked event messages (cluster kernel-service show) for impaired controller SCSI blade. The cluster kernel-service show command displays the node name, quorum status of that node, availability status of that node, and operational status of that node.

    Each SCSI-blade process should be in quorum with the other nodes in the cluster. Any issues must be resolved before you proceed with the replacement.

  • If you have a cluster with more than two nodes, it must be in quorum. If the cluster is not in quorum or a healthy controller shows false for eligibility and health, you must correct the issue before shutting down the impaired controller; see Synchronize a node with the cluster.

Steps
  1. If AutoSupport is enabled, suppress automatic case creation by invoking an AutoSupport message: system node autosupport invoke -node * -type all -message MAINT=number_of_hours_downh

    The following AutoSupport message suppresses automatic case creation for two hours: cluster1:> system node autosupport invoke -node * -type all -message MAINT=2h

  2. Disable automatic giveback from the console of the healthy controller: storage failover modify –node local -auto-giveback false

    Note When you see Do you want to disable auto-giveback?, enter y.
  3. Take the impaired controller to the LOADER prompt:

    If the impaired controller is displaying…​ Then…​

    The LOADER prompt

    Go to the next step.

    Waiting for giveback…​

    Press Ctrl-C, and then respond y when prompted.

    System prompt or password prompt

    Take over or halt the impaired controller from the healthy controller: storage failover takeover -ofnode impaired_node_name

    When the impaired controller shows Waiting for giveback…​, press Ctrl-C, and then respond y.

Option 2: Controller is in a two-node MetroCluster

To shut down the impaired controller, you must determine the status of the controller and, if necessary, switch over the controller so that the healthy controller continues to serve data from the impaired controller storage.

About this task
  • If you are using NetApp Storage Encryption, you must have reset the MSID using the instructions in the "Return a FIPS drive or SED to unprotected mode" section of NetApp Encryption overview with the CLI.

  • You must leave the power supplies turned on at the end of this procedure to provide power to the healthy controller.

Steps
  1. Check the MetroCluster status to determine whether the impaired controller has automatically switched over to the healthy controller: metrocluster show

  2. Depending on whether an automatic switchover has occurred, proceed according to the following table:

    If the impaired controller…​ Then…​

    Has automatically switched over

    Proceed to the next step.

    Has not automatically switched over

    Perform a planned switchover operation from the healthy controller: metrocluster switchover

    Has not automatically switched over, you attempted switchover with the metrocluster switchover command, and the switchover was vetoed

    Review the veto messages and, if possible, resolve the issue and try again. If you are unable to resolve the issue, contact technical support.

  3. Resynchronize the data aggregates by running the metrocluster heal -phase aggregates command from the surviving cluster.

    controller_A_1::> metrocluster heal -phase aggregates
    [Job 130] Job succeeded: Heal Aggregates is successful.

    If the healing is vetoed, you have the option of reissuing the metrocluster heal command with the -override-vetoes parameter. If you use this optional parameter, the system overrides any soft vetoes that prevent the healing operation.

  4. Verify that the operation has been completed by using the metrocluster operation show command.

    controller_A_1::> metrocluster operation show
        Operation: heal-aggregates
          State: successful
    Start Time: 7/25/2016 18:45:55
       End Time: 7/25/2016 18:45:56
         Errors: -
  5. Check the state of the aggregates by using the storage aggregate show command.

    controller_A_1::> storage aggregate show
    Aggregate     Size Available Used% State   #Vols  Nodes            RAID Status
    --------- -------- --------- ----- ------- ------ ---------------- ------------
    ...
    aggr_b2    227.1GB   227.1GB    0% online       0 mcc1-a2          raid_dp, mirrored, normal...
  6. Heal the root aggregates by using the metrocluster heal -phase root-aggregates command.

    mcc1A::> metrocluster heal -phase root-aggregates
    [Job 137] Job succeeded: Heal Root Aggregates is successful

    If the healing is vetoed, you have the option of reissuing the metrocluster heal command with the -override-vetoes parameter. If you use this optional parameter, the system overrides any soft vetoes that prevent the healing operation.

  7. Verify that the heal operation is complete by using the metrocluster operation show command on the destination cluster:

    mcc1A::> metrocluster operation show
      Operation: heal-root-aggregates
          State: successful
     Start Time: 7/29/2016 20:54:41
       End Time: 7/29/2016 20:54:42
         Errors: -
  8. On the impaired controller module, disconnect the power supplies.

Step 2: Open the controller module

To access components inside the controller, you must first remove the controller module from the system and then remove the cover on the controller module.

  1. If you are not already grounded, properly ground yourself.

  2. Loosen the hook and loop strap binding the cables to the cable management device, and then unplug the system cables and SFPs (if needed) from the controller module, keeping track of where the cables were connected.

    Leave the cables in the cable management device so that when you reinstall the cable management device, the cables are organized.

  3. Remove and set aside the cable management devices from the left and right sides of the controller module.

    drw 32xx cbl mgmt arm
  4. Loosen the thumbscrew on the cam handle on the controller module.

    drw 8020 cam handle thumbscrew

    Callout number 1

    Thumbscrew

    Callout number 2

    Cam handle

  5. Pull the cam handle downward and begin to slide the controller module out of the chassis.

    Make sure that you support the bottom of the controller module as you slide it out of the chassis.

Step 3: Replace or add a caching module

To replace or add a caching module referred to as the M.2 PCIe card on the label on your controller, locate the slots inside the controller and follow the specific sequence of steps.

Your storage system must meet certain criteria depending on your situation:

  • It must have the appropriate operating system for the caching module you are installing.

  • It must support the caching capacity.

  • All other components in the storage system must be functioning properly; if not, you must contact technical support.

    1. Locate the caching module at the rear of the controller module and remove it.

      1. Press the release tab.

      2. Remove the heatsink.

        The storage system comes with two slots available for the caching module and only one slot is occupied, by default.

        drw rxl fcache
    2. If you are adding a caching module, go to the next step; if you are replacing the caching module, gently pull it straight out of the housing.

    3. Align the edges of the caching module with the socket in the housing, and then gently push it into the socket.

    4. Verify that the caching module is seated squarely and completely in the socket.

      If necessary, remove the caching module and reseat it into the socket.

    5. Reseat and push the heatsink down to engage the locking button on the caching module housing.

    6. Repeat the steps if you have a second caching module. Close the controller module cover, as needed.

Step 4: Reinstall the controller

After you replace a component within the controller module, you must reinstall the controller module in the system chassis.

  1. Align the end of the controller module with the opening in the chassis, and then gently push the controller module halfway into the system.

    Note Do not completely insert the controller module in the chassis until instructed to do so.
  2. Recable the system, as needed.

    If you removed the media converters (QSFPs or SFPs), remember to reinstall them if you are using fiber optic cables.

  3. Complete the reinstallation of the controller module:

    The controller module begins to boot as soon as it is fully seated in the chassis

    1. With the cam handle in the open position, firmly push the controller module in until it meets the midplane and is fully seated, and then close the cam handle to the locked position.

      Note Do not use excessive force when sliding the controller module into the chassis to avoid damaging the connectors.
    2. Tighten the thumbscrew on the cam handle on back of the controller module.

    3. If you have not already done so, reinstall the cable management device.

    4. Bind the cables to the cable management device with the hook and loop strap.

Step 5: Switch back aggregates in a two-node MetroCluster configuration

After you have completed the FRU replacement in a two-node MetroCluster configuration, you can perform the MetroCluster switchback operation. This returns the configuration to its normal operating state, with the sync-source storage virtual machines (SVMs) on the formerly impaired site now active and serving data from the local disk pools.

This task only applies to two-node MetroCluster configurations.

Steps
  1. Verify that all nodes are in the enabled state: metrocluster node show

    cluster_B::>  metrocluster node show
    
    DR                           Configuration  DR
    Group Cluster Node           State          Mirroring Mode
    ----- ------- -------------- -------------- --------- --------------------
    1     cluster_A
                  controller_A_1 configured     enabled   heal roots completed
          cluster_B
                  controller_B_1 configured     enabled   waiting for switchback recovery
    2 entries were displayed.
  2. Verify that resynchronization is complete on all SVMs: metrocluster vserver show

  3. Verify that any automatic LIF migrations being performed by the healing operations were completed successfully: metrocluster check lif show

  4. Perform the switchback by using the metrocluster switchback command from any node in the surviving cluster.

  5. Verify that the switchback operation has completed: metrocluster show

    The switchback operation is still running when a cluster is in the waiting-for-switchback state:

    cluster_B::> metrocluster show
    Cluster              Configuration State    Mode
    --------------------	------------------- 	---------
     Local: cluster_B configured       	switchover
    Remote: cluster_A configured       	waiting-for-switchback

    The switchback operation is complete when the clusters are in the normal state.:

    cluster_B::> metrocluster show
    Cluster              Configuration State    Mode
    --------------------	------------------- 	---------
     Local: cluster_B configured      		normal
    Remote: cluster_A configured      		normal

    If a switchback is taking a long time to finish, you can check on the status of in-progress baselines by using the metrocluster config-replication resync-status show command.

  6. Reestablish any SnapMirror or SnapVault configurations.

Step 6: Complete the replacement process

Return the failed part to NetApp, as described in the RMA instructions shipped with the kit. See the Part Return & Replacements page for further information.