Prepare to replace drive drawer (60-drive)

You prepare to replace a drive drawer by determining if you can perform the replacement procedure while the drive shelf is online or if you need to stop host I/O activity and power off any of the shelves that are powered on. If you are replacing a drawer in a shelf with Drawer Loss Protection, there is no need to stop host I/O activity and power off any of the shelves.

Before you begin

Steps

  1. Determine if the drive shelf is powered on.
    • If the power is off, you do not need to issue the CLI command. Go to Remove cable chains.
    • If the power is on, go to the next step.
  2. Type this command on the command line, and press Enter:
    SMcli <ctlr_IP1> -p "array_password" -c "set tray [trayID] drawer [drawerID]
    serviceAllowedIndicator=on;"
    
    where:
    • <ctlr_IP1> is the identifier of the controller.
    • array_password is the password for the storage array. You must enclose the value for array_password in double quotation marks ("").
    • [trayID] is the identifier of the drive shelf that contains the drive drawer that you want to replace. Drive shelf ID values are 0 to 99. You must enclose the value for trayID in square brackets.
    • [drawerID] is the identifier of the drive drawer that you want to replace. Drawer ID values are 1 (top drawer) to 5 (bottom drawer). You must enclose the value for drawerID in square brackets.
    Example

    This command ensures you can remove the top-most drawer in drive shelf 10:

    SMcli <ctlr_IP1> -p "safety-1" -c "set tray [10] drawer [1]
    serviceAllowedIndicator=forceOnWarning;"
    
  3. Determine if you need to stop host I/O activity, as follows:
    • If the command succeeds, you do not need to stop host I/O activity. All drives in the drawer are in pools or volume groups with Drawer Loss Protection. Go to Remove cable chains.

      Attention: Possible damage to drives – Wait 30 seconds after the command completes before you open the drive drawer. Waiting 30 seconds allows the drives to spin down, which prevents possible damage to the hardware.
    • If a warning is displayed indicating that this command could not be completed, you must stop host I/O activity before removing the drawer. The warning is displayed because one or more drives in the affected drawer are in pools or volume groups without Drawer Loss Protection. To avoid losing data, you must complete the next steps to stop host I/O activity and to power off the drive shelf and the controller shelf.

  4. Ensure that no I/O operations are occurring between the storage array and all connected hosts. For example, you can perform these steps:
    • Stop all processes that involve the LUNs mapped from the storage to the hosts.
    • Ensure that no applications are writing data to any LUNs mapped from the storage to the hosts.
    • Unmount all file systems associated with volumes on the array.
    Note: The exact steps to stop host I/O operations depend on the host operating system and the configuration, which are beyond the scope of these instructions. If you are not sure how to stop host I/O operations in your environment, consider shutting down the host.
  5. If the storage array participates in a mirroring relationship, stop all host I/O operations on the secondary storage array.
    Attention: Possible data loss – If you continue this procedure while I/O operations are occurring, the host application might lose data because the storage array will not be accessible.
  6. Wait for any data in cache memory to be written to the drives.
    The green Cache Active LED on the back of each controller is on when cached data needs to be written to the drives. You must wait for this LED to turn off.

    Cache Active LED

  7. From the Home page of SANtricity System Manager, select View Operations in Progress.
  8. Wait for all operations to complete before continuing with the next step.
  9. Power off the shelves as follows:

    There is NO need to power off any of the shelves.

    1. Turn off both power switches on the controller shelf.
    1. Turn off both power switches on the controller shelf.
    2. Wait for all LEDs on the controller shelf to go dark.
    3. Turn off both power switches on the drive shelf.

After you finish