Replacing the E2800 controller

You might need to replace the E2800 controller if it is not functioning optimally or if it has failed.

Before you begin

About this task

You can determine if you have a failed controller canister in two ways:
  • The Recovery Guru in SANtricity System Manager directs you to replace the controller.
  • The amber Attention LED on the controller is on, indicating that the controller has a fault.

The appliance Storage Node will not be accessible when you replace the controller. If the E2800 controller is functioning sufficiently, you can place the E5700SG controller into maintenance mode. Putting a StorageGRID appliance into maintenance mode might make the appliance unavailable for remote access.

When you replace a controller, you must remove the battery from the original controller and install it in the replacement controller.

Note: The E2800 controller in the appliance does not include a host interface card (HIC).

Steps

  1. Follow the instructions in the E2800 controller replacement procedure to prepare to remove the controller.
    You use SANtricity System Manager to perform these steps.
    1. Make a note of which version of SANtricity OS software is currently installed on the controller.
    2. Make a note of which version of NVSRAM is currently installed.
    3. If the Drive Security feature is enabled, be sure a saved key exists and that you know the pass phrase required to install it.
      Attention: Possible loss of data access – If all drives in the appliance are security enabled, the new controller will not be able to access the appliance until you unlock the secured drives using the Enterprise Management Window in SANtricity Storage Manager.
    4. Back up the configuration database.
      If a problem occurs when you remove a controller, you can use the saved file to restore your configuration.
    5. Collect support data for the appliance.
      Note: Collecting support data before and after replacing a component ensures you can send a full set of logs to technical support in case the replacement does not resolve the problem.
  2. If the StorageGRID appliance is running in a StorageGRID system, place the E5700SG controller into maintenance mode.
    1. From the Grid Manager, select Nodes.
    2. Select the appliance Storage Node.
    3. Select the Tasks tab.

      Maintenance Mode button for appliance
    4. Click Maintenance Mode.
      A confirmation dialog appears.
      Maintenance Mode confirmation dialog
    5. Enter the provisioning passphrase, and click OK.
      A confirmation message lists the URLs you can use to access the StorageGRID Appliance Installer while the controller is in maintenance mode.
      screenshot for Maintenance Mode confirmation message
    6. Wait a few minutes for the controller to reboot into maintenance mode. Then, browse to any of the URLs displayed.
      Note: If possible, use the URL containing the IP address of the appliance's Admin Network port.
      Note: Accessing https://169.254.0.1:8443 requires a direct connection to the local management port.
    7. Confirm that the appliance is in maintenance mode by noting the maintenance mode message on the StorageGRID Appliance Installer home page.

      maintenance mode message
  3. If the E2800 controller is functioning sufficiently to allow for a controlled shutdown, confirm that all operations have completed.
    1. From the home page of SANtricity System Manager, select View Operations in Progress.
    2. Confirm that all operations have completed.
  4. Remove the controller from the appliance:
    1. Put on an ESD wristband or take other antistatic precautions.
    2. Label the cables and then disconnect the cables and SFPs.
      Attention: To prevent degraded performance, do not twist, fold, pinch, or step on the cables.
    3. Release the controller from the appliance by squeezing the latch on the cam handle until it releases, and then open the cam handle to the right.
    4. Using two hands and the cam handle, slide the controller out of the appliance.
      Attention: Always use two hands to support the weight of the controller.
    5. Place the controller on a flat, static-free surface with the removable cover facing up.
    6. Remove the cover by pressing down on the button and sliding the cover off.
  5. Remove the battery from the failed controller, and install it into the replacement controller:
    1. Confirm that the green LED inside the controller (between the battery and the DIMMs) is off.
      If this green LED is on, the controller is still using battery power. You must wait for this LED to go off before removing any components.
      Green LED on E2800
      Item Description

      number 1 icon
      Internal Cache Active LED

      number 2 icon
      Battery
    2. Locate the blue release latch for the battery.
    3. Unlatch the battery by pushing the release latch down and away from the controller.

      Battery Latch
      Item Description

      number 1 icon
      Battery release latch

      number 2 icon
      Battery
    4. Lift up on the battery, and slide it out of the controller.
    5. Remove the cover from the replacement controller.
    6. Orient the replacement controller so that the slot for the battery faces toward you.
    7. Insert the battery into the controller at a slight downward angle.
      You must insert the metal flange at the front of the battery into the slot on the bottom of the controller, and slide the top of the battery beneath the small alignment pin on the left side of the controller.
    8. Move the battery latch up to secure the battery.
      When the latch clicks into place, the bottom of the latch hooks into a metal slot on the chassis.
    9. Turn the controller over to confirm that the battery is installed correctly.
      Attention: Possible hardware damage – The metal flange at the front of the battery must be completely inserted into the slot on the controller (as shown in the first figure). If the battery is not installed correctly (as shown in the second figure), the metal flange might contact the controller board, causing damage.
      • Correct – The battery's metal flange is completely inserted in the slot on the controller:
        Battery Flange Correct

      • Incorrect – The battery's metal flange is not inserted into the slot on the controller:
        Battery Flange Incorrect

    10. Replace the controller cover.
  6. Install the replacement controller into the appliance.
    1. Turn the controller over, so that the removable cover faces down.
    2. With the cam handle in the open position, slide the controller all the way into the appliance.
    3. Move the cam handle to the left to lock the controller in place.
    4. Replace the cables and SFPs.
    5. Wait for the E2800 controller to reboot. Verify that the seven-segment display shows a state of 99.
    6. Determine how you will assign an IP address to the replacement controller.
      Note: The steps for assigning an IP address to the replacement controller depend on whether you connected management port 1 to a network with a DHCP server and on whether all drives are secured.
      • If management port 1 is connected to a network with a DHCP server, the new controller will obtain its IP address from the DHCP server. This value might be different than the original controller's IP address.
      • If all drives are secured, you must use the Enterprise Management Window (EMW) in SANtricity Storage Manager to unlock the secured drives. You cannot access the new controller until you unlock the drives with the saved key. See the E-Series instructions for replacing a simplex E2800 controller.
  7. If the appliance uses secured drives, follow the instructions in the E2800 controller replacement procedure to import the drive security key.
  8. Return the appliance to normal operating mode:
    1. From the StorageGRID Appliance Installer, select Advanced > Reboot Controller.

      reboot controller
    2. Click Reboot Controller.
      The appliance reboots and rejoins the grid. This process can take up to 20 minutes.
    3. From the Grid Manager, monitor the status of the upgraded appliance Storage Node.
      Verify that the Storage Node returns to the expected status.
  9. From SANtricity System Manager, confirm that the new controller is Optimal, and collect support data.