How to migrate a two-node switched cluster with Cisco Nexus 3132Q-V cluster switches
If you have a two-node switchless cluster, you can migrate nondisruptively to a two-node switched cluster that includes Cisco Nexus 3132Q-V cluster network switches.
The configurations must be properly set up and functioning.
The nodes must be running ONTAP 9.4 or later.
All cluster ports must be in the
up
state. -
The Cisco Nexus 3132Q-V cluster switch must be supported.
The existing cluster network configuration must have:
The Nexus 3132 cluster infrastructure that is redundant and fully functional on both switches.
The latest RCF and NX-OS versions on your switches.
Management connectivity on both switches.
Console access to both switches.
All cluster logical interfaces (LIFs) in the
up
state without being migrated. -
Initial customization of the switch.
All the ISL ports enabled and cabled.
The examples in this procedure use the following switch and node nomenclature:
Nexus 3132Q-V cluster switches, C1 and C2.
The nodes are n1 and n2.
The examples in this procedure use two nodes, each utilizing two 40/100 GbE cluster interconnect ports e4a and e4e. The Hardware Universe has details about the cluster ports on your platforms. |
n1_clus1 is the first cluster logical interface (LIF) to be connected to cluster switch C1 for node n1.
n1_clus2 is the first cluster LIF to be connected to cluster switch C2 for node n1.
n2_clus1 is the first cluster LIF to be connected to cluster switch C1 for node n2.
n2_clus2 is the second cluster LIF to be connected to cluster switch C2 for node n2.
The number of 10 GbE and 40/100 GbE ports are defined in the reference configuration files (RCFs) available on the Cisco ® Cluster Network Switch Reference Configuration File Download page.
The procedure requires the use of both ONTAP commands and Cisco Nexus 3000 Series Switches commands; ONTAP commands are used unless otherwise indicated. |
If AutoSupport is enabled on this cluster, suppress automatic case creation by invoking an AutoSupport message:
system node autosupport invoke -node * -type all - message MAINT=xh
x is the duration of the maintenance window in hours.
The AutoSupport message notifies technical support of this maintenance task so that automatic case creation is suppressed during the maintenance window.
Determine the administrative or operational status for each cluster interface:
Display the network port attributes:
network port show
cluster::*> network port show –role cluster (network port show) Node: n1 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e4a Cluster Cluster up 9000 auto/40000 - - e4e Cluster Cluster up 9000 auto/40000 - - Node: n2 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e4a Cluster Cluster up 9000 auto/40000 - - e4e Cluster Cluster up 9000 auto/40000 - - 4 entries were displayed.
Display information about the logical interfaces:
network interface show
cluster::*> network interface show -role cluster (network interface show) Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------------ ------------- ------- ---- Cluster n1_clus1 up/up 10.10.0.1/24 n1 e4a true n1_clus2 up/up 10.10.0.2/24 n1 e4e true n2_clus1 up/up 10.10.0.3/24 n2 e4a true n2_clus2 up/up 10.10.0.4/24 n2 e4e true 4 entries were displayed.
Verify that the appropriate RCFs and image are installed on the new 3132Q-V switches as necessary for your requirements, and make any essential site customizations, such as users and passwords, network addresses, and so on.
You must prepare both switches at this time. If you need to upgrade the RCF and image software, you must follow these steps:
Go to the Cisco Ethernet Switches page on the NetApp Support Site.
Note your switch and the required software versions in the table on that page.
Download the appropriate version of RCF.
Click CONTINUE on the Description page, accept the license agreement, and then follow the instructions on the Download page to download the RCF.
Download the appropriate version of the image software.
On Nexus 3132Q-V switches C1 and C2, disable all node-facing ports C1 and C2, but do not disable the ISL ports.
The following example shows ports 1 through 30 being disabled on Nexus 3132Q-V cluster switches C1 and C2 using a configuration supported in RCF
NX3132_RCF_v1.1_24p10g_26p40g.txt
:C1# copy running-config startup-config [########################################] 100% Copy complete. C1# configure C1(config)# int e1/1/1-4,e1/2/1-4,e1/3/1-4,e1/4/1-4,e1/5/1-4,e1/6/1-4,e1/7-30 C1(config-if-range)# shutdown C1(config-if-range)# exit C1(config)# exit C2# copy running-config startup-config [########################################] 100% Copy complete. C2# configure C2(config)# int e1/1/1-4,e1/2/1-4,e1/3/1-4,e1/4/1-4,e1/5/1-4,e1/6/1-4,e1/7-30 C2(config-if-range)# shutdown C2(config-if-range)# exit C2(config)# exit
Connect ports 1/31 and 1/32 on C1 to the same ports on C2 using supported cabling.
Verify that the ISL ports are operational on C1 and C2:
show port-channel summary
C1# show port-channel summary Flags: D - Down P - Up in port-channel (members) I - Individual H - Hot-standby (LACP only) s - Suspended r - Module-removed S - Switched R - Routed U - Up (port-channel) M - Not in use. Min-links not met -------------------------------------------------------------------------------- Group Port- Type Protocol Member Ports Channel -------------------------------------------------------------------------------- 1 Po1(SU) Eth LACP Eth1/31(P) Eth1/32(P) C2# show port-channel summary Flags: D - Down P - Up in port-channel (members) I - Individual H - Hot-standby (LACP only) s - Suspended r - Module-removed S - Switched R - Routed U - Up (port-channel) M - Not in use. Min-links not met -------------------------------------------------------------------------------- Group Port- Type Protocol Member Ports Channel -------------------------------------------------------------------------------- 1 Po1(SU) Eth LACP Eth1/31(P) Eth1/32(P)
Display the list of neighboring devices on the switch:
show cdp neighbors
C1# show cdp neighbors Capability Codes: R - Router, T - Trans-Bridge, B - Source-Route-Bridge S - Switch, H - Host, I - IGMP, r - Repeater, V - VoIP-Phone, D - Remotely-Managed-Device, s - Supports-STP-Dispute Device-ID Local Intrfce Hldtme Capability Platform Port ID C2 Eth1/31 174 R S I s N3K-C3132Q-V Eth1/31 C2 Eth1/32 174 R S I s N3K-C3132Q-V Eth1/32 Total entries displayed: 2 C2# show cdp neighbors Capability Codes: R - Router, T - Trans-Bridge, B - Source-Route-Bridge S - Switch, H - Host, I - IGMP, r - Repeater, V - VoIP-Phone, D - Remotely-Managed-Device, s - Supports-STP-Dispute Device-ID Local Intrfce Hldtme Capability Platform Port ID C1 Eth1/31 178 R S I s N3K-C3132Q-V Eth1/31 C1 Eth1/32 178 R S I s N3K-C3132Q-V Eth1/32 Total entries displayed: 2
Display the cluster port connectivity on each node:
network device-discovery show
The following example shows a two-node switchless cluster configuration.
cluster::*> network device-discovery show Local Discovered Node Port Device Interface Platform ----------- ------ ------------------- ---------------- ---------------- n1 /cdp e4a n2 e4a FAS9000 e4e n2 e4e FAS9000 n2 /cdp e4a n1 e4a FAS9000 e4e n1 e4e FAS9000
Migrate the clus1 interface to the physical port hosting clus2:
network interface migrate
Execute this command from each local node.
cluster::*> network interface migrate -vserver Cluster -lif n1_clus1 -source-node n1 –destination-node n1 -destination-port e4e cluster::*> network interface migrate -vserver Cluster -lif n2_clus1 -source-node n2 –destination-node n2 -destination-port e4e
Verify the cluster interfaces migration:
cluster::*> network interface show -role cluster (network interface show) Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------------ ------------- ------- ---- Cluster n1_clus1 up/up 10.10.0.1/24 n1 e4e false n1_clus2 up/up 10.10.0.2/24 n1 e4e true n2_clus1 up/up 10.10.0.3/24 n2 e4e false n2_clus2 up/up 10.10.0.4/24 n2 e4e true 4 entries were displayed.
Shut down cluster ports clus1 LIF on both nodes:
network port modify
cluster::*> network port modify -node n1 -port e4a -up-admin false cluster::*> network port modify -node n2 -port e4a -up-admin false
Ping the remote cluster interfaces and perform an RPC server check:
cluster ping-cluster
cluster::*> cluster ping-cluster -node n1 Host is n1 Getting addresses from network interface table... Cluster n1_clus1 n1 e4a 10.10.0.1 Cluster n1_clus2 n1 e4e 10.10.0.2 Cluster n2_clus1 n2 e4a 10.10.0.3 Cluster n2_clus2 n2 e4e 10.10.0.4 Local = 10.10.0.1 10.10.0.2 Remote = 10.10.0.3 10.10.0.4 Cluster Vserver Id = 4294967293 Ping status: .... Basic connectivity succeeds on 4 path(s) Basic connectivity fails on 0 path(s) ................ Detected 1500 byte MTU on 32 path(s): Local 10.10.0.1 to Remote 10.10.0.3 Local 10.10.0.1 to Remote 10.10.0.4 Local 10.10.0.2 to Remote 10.10.0.3 Local 10.10.0.2 to Remote 10.10.0.4 Larger than PMTU communication succeeds on 4 path(s) RPC status: 1 paths up, 0 paths down (tcp check) 1 paths up, 0 paths down (ucp check)
Disconnect the cable from e4a on node n1.
You can refer to the running configuration and connect the first 40 GbE port on the switch C1 (port 1/7 in this example) to e4a on n1 using supported cabling on Nexus 3132Q-V.
When reconnecting any cables to a new Cisco cluster switch, the cables used must be either fiber or cabling supported by Cisco. -
Disconnect the cable from e4a on node n2.
You can refer to the running configuration and connect e4a to the next available 40 GbE port on C1, port 1/8, using supported cabling.
Enable all node-facing ports on C1.
The following example shows ports 1 through 30 being enabled on Nexus 3132Q-V cluster switches C1 and C2 using the configuration supported in RCF
:C1# configure C1(config)# int e1/1/1-4,e1/2/1-4,e1/3/1-4,e1/4/1-4,e1/5/1-4,e1/6/1-4,e1/7-30 C1(config-if-range)# no shutdown C1(config-if-range)# exit C1(config)# exit
Enable the first cluster port, e4a, on each node:
network port modify
cluster::*> network port modify -node n1 -port e4a -up-admin true cluster::*> network port modify -node n2 -port e4a -up-admin true
Verify that the clusters are up on both nodes:
network port show
For each node, revert all of the migrated cluster interconnect LIFs:
network interface revert
The following example shows the migrated LIFs being reverted to their home ports.
cluster::*> network interface revert -vserver Cluster -lif n1_clus1 cluster::*> network interface revert -vserver Cluster -lif n2_clus1
Verify that all of the cluster interconnect ports are now reverted to their home ports:
The
Is Home
column should display a value oftrue
for all of the ports listed in theCurrent Port
column. If the displayed value isfalse
, the port has not been reverted.cluster::*> network interface show -role cluster (network interface show) Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------------ ------------- ------- ---- Cluster n1_clus1 up/up 10.10.0.1/24 n1 e4a true n1_clus2 up/up 10.10.0.2/24 n1 e4e true n2_clus1 up/up 10.10.0.3/24 n2 e4a true n2_clus2 up/up 10.10.0.4/24 n2 e4e true 4 entries were displayed.
cluster::*> network device-discovery show Local Discovered Node Port Device Interface Platform ----------- ------ ------------------- ---------------- ---------------- n1 /cdp e4a C1 Ethernet1/7 N3K-C3132Q-V e4e n2 e4e FAS9000 n2 /cdp e4a C1 Ethernet1/8 N3K-C3132Q-V e4e n1 e4e FAS9000
On the console of each node, migrate clus2 to port e4a:
cluster::*> network interface migrate -vserver Cluster -lif n1_clus2 -source-node n1 –destination-node n1 -destination-port e4a cluster::*> network interface migrate -vserver Cluster -lif n2_clus2 -source-node n2 –destination-node n2 -destination-port e4a
Shut down cluster ports clus2 LIF on both nodes:
network port modify
The following example shows the specified ports being shut down on both nodes:
cluster::*> network port modify -node n1 -port e4e -up-admin false cluster::*> network port modify -node n2 -port e4e -up-admin false
Verify the cluster LIF status:
cluster::*> network interface show -role cluster (network interface show) Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------------ ------------- ------- ---- Cluster n1_clus1 up/up 10.10.0.1/24 n1 e4a true n1_clus2 up/up 10.10.0.2/24 n1 e4a false n2_clus1 up/up 10.10.0.3/24 n2 e4a true n2_clus2 up/up 10.10.0.4/24 n2 e4a false 4 entries were displayed.
Disconnect the cable from e4e on node n1.
You can refer to the running configuration and connect the first 40 GbE port on the switch C2 (port 1/7 in this example) to e4e on n1 using supported cabling on Nexus 3132Q-V.
Disconnect the cable from e4e on node n2.
You can refer to the running configuration and connect e4e to the next available 40 GbE port on C2, port 1/8, using supported cabling.
Enable all node-facing ports on C2.
The following example shows ports 1 through 30 being enabled on Nexus 3132Q-V cluster switches C1 and C2 using a configuration supported in RCF
:C2# configure C2(config)# int e1/1/1-4,e1/2/1-4,e1/3/1-4,e1/4/1-4,e1/5/1-4,e1/6/1-4,e1/7-30 C2(config-if-range)# no shutdown C2(config-if-range)# exit C2(config)# exit
Enable the second cluster port, e4e, on each node:
network port modify
The following example shows the specified ports being brought up:
cluster::*> network port modify -node n1 -port e4e -up-admin true cluster::*> network port modify -node n2 -port e4e -up-admin true
cluster::*> network interface revert -vserver Cluster -lif n1_clus2 cluster::*> network interface revert -vserver Cluster -lif n2_clus2
The
Is Home
Verify that all of the cluster interconnect ports are in the
up
state.cluster::*> network port show –role cluster (network port show) Node: n1 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e4a Cluster Cluster up 9000 auto/40000 - - e4e Cluster Cluster up 9000 auto/40000 - - Node: n2 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e4a Cluster Cluster up 9000 auto/40000 - - e4e Cluster Cluster up 9000 auto/40000 - - 4 entries were displayed.
Display the cluster switch port numbers each cluster port is connected to on each node:
cluster::*> network device-discovery show Local Discovered Node Port Device Interface Platform ----------- ------ ------------------- ---------------- ---------------- n1 /cdp e4a C1 Ethernet1/7 N3K-C3132Q-V e4e C2 Ethernet1/7 N3K-C3132Q-V n2 /cdp e4a C1 Ethernet1/8 N3K-C3132Q-V e4e C2 Ethernet1/8 N3K-C3132Q-V
Display discovered and monitored cluster switches:
system cluster-switch show
cluster::*> system cluster-switch show Switch Type Address Model --------------------------- ------------------ ---------------- --------------- C1 cluster-network 10.10.1.101 NX3132V Serial Number: FOX000001 Is Monitored: true Reason: Software Version: Cisco Nexus Operating System (NX-OS) Software, Version 7.0(3)I4(1) Version Source: CDP C2 cluster-network 10.10.1.102 NX3132V Serial Number: FOX000002 Is Monitored: true Reason: Software Version: Cisco Nexus Operating System (NX-OS) Software, Version 7.0(3)I4(1) Version Source: CDP 2 entries were displayed.
Disable the two-node switchless configuration settings on any node:
network options switchless-cluster
network options switchless-cluster modify -enabled false
Verify that the
switchless-cluster
option has been disabled.network options switchless-cluster show
Enable the cluster switch health monitor log collection feature for collecting switch-related log files:
system cluster-switch log setup-password
system cluster-switch log enable-collection
cluster::*> **system cluster-switch log setup-password** Enter the switch name: <return> The switch name entered is not recognized. Choose from the following list: C1 C2 cluster::*> system cluster-switch log setup-password Enter the switch name: C1 RSA key fingerprint is e5:8b:c6:dc:e2:18:18:09:36:63:d9:63:dd:03:d9:cc Do you want to continue? {y|n}::[n] y Enter the password: <enter switch password> Enter the password again: <enter switch password> cluster::*> system cluster-switch log setup-password Enter the switch name: C2 RSA key fingerprint is 57:49:86:a1:b9:80:6a:61:9a:86:8e:3c:e3:b7:1f:b1 Do you want to continue? {y|n}:: [n] y Enter the password: <enter switch password> Enter the password again: <enter switch password> cluster::*> system cluster-switch log enable-collection Do you want to enable cluster log collection for all nodes in the cluster? {y|n}: [n] y Enabling cluster switch log collection. cluster::*>
If any of these commands return an error, contact NetApp support. -
If you suppressed automatic case creation, re-enable it by invoking an AutoSupport message: