Prepare the nodes for upgrade
Contributors netapp-thomi Download PDF of this page
Before you can replace the original nodes, you must ensure that they are in an HA pair, have no missing or failed disks, can access each other’s storage, and do not own data LIFs assigned to the other nodes in the cluster. You also need to collect information about the original nodes and, if the cluster is in a SAN environment, ensure that all the nodes in the cluster are in quorum.
Steps
  1. Ensure that each of the original nodes has enough resources to adequately support the workload of both nodes during takeover mode.
    Refer to References to link to ONTAP 9 High-Availability Configuration Guide and follow the Best practices for HA pairs section. Neither of the original nodes should be running at more than 50 percent utilization; if a node is running at less than 50 percent utilization, it can handle the loads for both nodes during the controller upgrade.
  2. Complete the following substeps to create a performance baseline for the original nodes:
    1. Make sure that the diagnostic user account is unlocked.
      Important: The diagnostic user account is intended only for low-level diagnostic purposes and should be used only with guidance from technical support.
      Important: For information about unlocking the user accounts, refer to References to link to the System Administration Reference.
    2. Refer to References to link to the NetApp Support Site and download the Performance and Statistics Collector (Perfstat Converged).
      The Perfstat Converged tool lets you establish a performance baseline for comparison after the upgrade.
    3. Create a performance baseline, following the instructions on the NetApp Support Site.
  3. Refer to References to link to the NetApp Support Site and open a support case on the NetApp Support Site.
    You can use the case to report any issues that might arise during the upgrade.
  4. Verify that NVMEM or NVRAM batteries of node3 and node4 are charged, and charge them if they are not.
    You need to physically check node3 and node4 to see if the NVMEM or NVRAM batteries are charged. For information about the LEDs for the model of node3 and node4, refer to References to link to the Hardware Universe.
    Attention Do not try to clear the NVRAM contents. If there is a need to clear the contents of NVRAM, contact NetApp technical support.
  5. Check the version of ONTAP on node3 and node4.
    The new nodes must have the same version of ONTAP 9.x installed on them that is installed on the original nodes. If the new nodes have a different version of ONTAP installed, you need to netboot the new controllers after you install them. For instructions on how to upgrade ONTAP, refer to References to link to the ONTAP 9 Upgrade and Revert/Downgrade Guide.
    Information about the version of ONTAP on node3 and node4 should be included in the shipping boxes. The ONTAP version is displayed when the node boots up or you can boot the node to maintenance mode and run the command:
    version
  6. Check whether you have two or four cluster LIFs on node1 and node 2:
    network interface show -role cluster
    The system displays any cluster LIFs, as shown in the following example:
    cluster::> network interface show -role cluster
            Logical    Status     Network          Current  Current Is
    Vserver Interface  Admin/Oper Address/Mask     Node     Port    Home
    node1
            clus1      up/up      172.17.177.2/24  node1    e0c     true
            clus2      up/up      172.17.177.6/24  node1    e0e     true
    node2
            clus1      up/up      172.17.177.3/24  node2    e0c     true
            clus2      up/up      172.17.177.7/24  node2    e0e     true
  7. If you have two or four cluster LIFs on node1 or node2, make sure that you can ping both cluster LIFs across all the available paths by completing the following substeps:
    1. Enter the advanced privilege level:
      set -privilege advanced
      The system displays the following message:
      Warning: These advanced commands are potentially dangerous; use them only when directed to do so by NetApp personnel.
      Do you wish to continue? (y or n):
    2. Enter y.
    3. Ping the nodes and test the connectivity:
      cluster ping-cluster -node node_name
      The system displays a message similar to the following example:
      cluster::*> cluster ping-cluster -node node1
      Host is node1
      Getting addresses from network interface table...
      Local = 10.254.231.102 10.254.91.42
      Remote = 10.254.42.25 10.254.16.228
      Ping status:
      Basic connectivity succeeds on 4 path(s) Basic connectivity fails on 0 path(s)
      Detected 1500 byte MTU on 4 path(s):
      Local 10.254.231.102 to Remote 10.254.16.228
      Local 10.254.231.102 to Remote 10.254.42.25
      Local 10.254.91.42 to Remote 10.254.16.228
      Local 10.254.91.42 to Remote 10.254.42.25
      Larger than PMTU communication succeeds on 4 path(s)
      RPC status:
      2 paths up, 0 paths down (tcp check)
      2 paths up, 0 paths down (udp check)
      If the node uses two cluster ports, you should see that it is able to communicate on four paths, as shown in the example.
    4. Return to the administrative level privilege:
      set -privilege admin
  8. Ensure that node1 and node2 are in an HA pair and verify that the nodes are connected to each other, and that takeover is possible:
    storage failover show
    The following example shows the output when the nodes are connected to each other and
    cluster::> storage failover show
                                  Takeover
    Node           Partner        Possible State Description
    node1          node2          true     Connected to node2
    node2          node1          true     Connected to node1
    Neither node should be in partial giveback. The following example shows that node1 is in partial giveback:
                                  Takeover
    node1          node2          true     Connected to node2, Partial giveback
    If either node is in partial giveback, use the storage failover giveback command to perform the giveback, and then use the storage failover show-giveback command to make sure that no aggregates still need to be given back. For detailed information about the commands, refer to References to link to the ONTAP 9 High-Availability Configuration Guide.
  9. Ensure that neither node1 nor node2 owns the aggregates for which it is the current owner (but not the home owner):
    storage aggregate show -node <node_name> -is-home false -fields owner-name,homename,state
    If neither node1 nor node2 owns aggregates for which it is the current owner (but not the home owner), the system will return a message similar to the following example:
    cluster::> storage aggregate show -node node2 -is-home false -fields owner-name,homename,state
    There are no entries matching your query.
    The following example shows the output of the command for a node named node2 that is the home owner, but not the current owner, of four aggregates:
                   -fields owner-name,home-name,state
    aggregate     home-name    owner-name   state
    aggr1         node1        node2        online
    aggr2         node1        node2        online
    aggr3         node1        node2        online
    aggr4         node1        node2        online
    4 entries were displayed.
  10. Take one of the following actions:
    If the command in Step 9…​ Then…​
    Had blank output
    Skip Step 11 and go to Step 12.
    Had output
    Go to Step 11.
  11. If either node1 or node2 owns aggregates for which it is the current owner but not the home owner, complete the following substeps:
    1. Return the aggregates currently owned by the partner node to the home owner node:
      storage failover giveback -ofnode <home_node_name>
    2. Verify that neither node1 nor node2 still owns aggregates for which it is the current owner (but not the home owner):
      storage aggregate show -nodes <node_name> -is-home false -fields owner-name,home-name,state
      The following example shows the output of the command when a node is both the current owner and home owner of aggregates:
      cluster::> storage aggregate show -nodes node1
                -is-home true -fields owner-name,home-name,state
      aggr1         node1        node1        online
      aggr2         node1        node1        online
      aggr3         node1        node1        online
      aggr4         node1        node1        online
  12. Ensure that node1 and node2 can access each other’s storage and verify that no disks are missing:
    storage failover show -fields local-missing-disks,partner-missing-disks
    The following example shows the output when no disks are missing:
    cluster::> storage failover show -fields local-missing-disks,partner-missing-disks
    node     local-missing-disks partner-missing-disks
    node1    None                None
    node2    None                None
    If any disks are missing, refer to References to link to the ONTAP 9 Disks and Aggregates Power Guide, the ONTAP 9 Logical Storage Management Guide, and the ONTAP 9 High-Availability Configuration Guide to configure storage for the HA pair.
  13. Ensure that node1 and node2 are healthy and eligible to participate in the cluster:
    cluster show
    The following example shows the output when both nodes are eligible and healthy:
    cluster::> cluster show
    Node                  Health  Eligibility
    node1                 true    true
    node2                 true    true
  14. Set the privilege level to advanced:
  15. Ensure that node1 and node2 are running the same ONTAP release:
    system node image show -node <node1,node2> -iscurrent true
    The following example shows the output of the command:
    cluster::*> system node image show -node node1,node2 -iscurrent true
                     Is      Is                Install
    Node     Image   Default Current Version   Date
    node1
             image1  true    true    9.1         2/7/2017 20:22:06
    node2
             image1  true    true    9.1         2/7/2017 20:20:48
    2 entries were displayed.
  16. Verify that neither node1 nor node2 owns any data LIFs that belong to other nodes in the cluster and check the Current Node and Is Home columns in the output:
    network interface show -role data -is-home false -curr-node <node_name>
    The following example shows the output when node1 has no LIFs that are home-owned by other nodes in the cluster:
    cluster::> network interface show -role data -is-home false -curr-node node1
    The following example shows the output when node1 owns data LIFs home-owned by the other node:
    vs0
                data1      up/up      172.18.103.137/24  node1         e0d     false
                data2      up/up      172.18.103.143/24  node1         e0f     false
  17. If the output in Step 15 shows that either node1 or node2 owns any data LIFs home-owned by other nodes in the cluster, migrate the data LIFs away from node1 or node2:
    network interface revert -vserver * -lif *
    For detailed information about the network interface revert command, refer to References to link to the ONTAP 9 Commands: Manual Page Reference.
  18. Check whether node1 or node2 owns any failed disks:
    storage disk show -nodelist <node1,node2> -broken
    If any of the disks have failed, remove them, following instructions in the ONTAP 9 Disks and Aggregates Power Guide. (Refer to References to link to the ONTAP 9 Disks and Aggregates Power Guide.)
  19. Collect information about node1 and node2 by completing the following substeps and recording the output of each command:
    You will use this information later in the procedure.
    1. Record the model, system ID, and serial number of both nodes:
      system node show -node <node1,node2> -instance
      You will use the information to reassign disks and decommission the original nodes.
    2. Enter the following command on both node1 and node2 and record information about the shelves, number of disks in each shelf, flash storage details, memory, NVRAM, and network cards from the output:
      run -node <node_name> sysconfig
      You can use the information to identify parts or accessories that you might want to transfer to node3 or node4. If you do not know if the nodes are V-Series systems or have FlexArray Virtualization software, you can learn that also from the output.
    3. Enter the following command on both node1 and node2 and record the aggregates that are online on both nodes:
      storage aggregate show -node <node_name> -state online
      You can use this information and the information in the following substep to verify that the aggregates and volumes remain online throughout the procedure, except for the brief period when they are offline during relocation.
    4. Enter the following command on both node1 and node2 and record the volumes that are offline on both nodes:
      volume show -node <node_name> -state offline
      After the upgrade, you will run the command again and compare the output with the output in this step to see if any other volumes have gone offline.
  20. Enter the following commands to see if any interface groups or VLANs are configured on node1 or node2:
    network port ifgrp show
    network port vlan show
    Make note of whether interface groups or VLANs are configured on node1 or node2; you need that information in the next step and later in the procedure.
  21. Complete the following substeps on both node1 and node2 to ensure that physical ports can be mapped correctly later in the procedure:
    1. Enter the following command to see if there are failover groups on the node other than clusterwide:
      network interface failover-groups show
      Failover groups are sets of network ports present on the system. Because upgrading the controller hardware can change the location of physical ports, failover groups can be inadvertently changed during the upgrade.
      The system displays failover groups on the node, as shown in the following example:
      cluster::> network interface failover-groups show
      Vserver             Group             Targets
      Cluster             Cluster           node1:e0a, node1:e0b
                                            node2:e0a, node2:e0b
      fg_6210_e0c         Default           node1:e0c, node1:e0d
                                            node1:e0e, node2:e0c
                                            node2:e0d, node2:e0e
    2. If there are failover groups present other than clusterwide, record the failover group names and the ports that belong to the failover groups.
    3. Enter the following command to see if there are any VLANs configured on the node:
      network port vlan show -node <node_name>
      VLANs are configured over physical ports. If the physical ports change, then the VLANs will need to be re-created later in the procedure.
      The system displays VLANs configured on the node, as shown in the following example:
      cluster::> network port vlan show
      Network Network
      Node    VLAN Name Port    VLAN ID MAC Address
      node1   e1b-70    e1b     70      00:15:17:76:7b:69
    4. If there are VLANs configured on the node, take note of each network port and VLAN ID pairing.
  22. Take one of the following actions:
    If interface groups or VLANS are…​ Then…​
    On node1 or node2
    Complete Step 23 and Step 24.
    Not on node1 or node2
    Go to Step 24.
  23. If you do not know if node1 and node2 are in a SAN or non-SAN environment, enter the following command and examine its output:
    network interface show -vserver <vserver_name> -data-protocol iscsi|fcp
    If neither iSCSI nor FC is configured for the SVM, the command will display a message similar to the following example:
    cluster::> network interface show -vserver Vserver8970 -data-protocol iscsi|fcp
    You can confirm that the node is in a NAS environment by using the network interface show command with the -data-protocol nfs|cifs parameters.
    If either iSCSI or FC is configured for the SVM, the command will display a message similar to the following example:
    cluster::> network interface show -vserver vs1 -data-protocol iscsi|fcp
    vs1      vs1_lif1   up/down    172.17.176.20/24   node1    0d      true
  24. Verify that all the nodes in the cluster are in quorum by completing the following substeps:
    2. Enter y.
    3. Verify the cluster service state in the kernel, once for each node:
      cluster kernel-service show
      cluster::*> cluster kernel-service show
      Master        Cluster       Quorum        Availability  Operational
      Node          Node          Status        Status        Status
      node1         node1         in-quorum     true          operational
                    node2         in-quorum     true          operational
      Nodes in a cluster are in quorum when a simple majority of nodes are healthy and can communicate with each other. For more information, refer to References to link to the System Administration Reference.
    4. Return to the administrative privilege level:
  25. Take one of the following actions:
    If the cluster…​ Then…​
    Has SAN configured
    Go to Step 26.
    Does not have SAN configured
    Go to Step 29.
  26. Verify that there are SAN LIFs on node1 and node2 for each SVM that has either SAN iSCSI or FC service enabled by entering the following command and examining its output:
    network interface show -data-protocol iscsi|fcp -home-node <node_name>
    The command displays SAN LIF information for node1 and node2. The following examples show the status in the Status Admin/Oper column as up/up, indicating that SAN iSCSI and FC service are enabled:
    cluster::> network interface show -data-protocol iscsi|fcp
    a_vs_iscsi  data1      up/up      10.228.32.190/21         node1     e0a     true
                data2      up/up      10.228.32.192/21         node2     e0a     true
    b_vs_fcp    data1      up/up      20:09:00:a0:98:19:9f:b0  node1     0c      true
                data2      up/up      20:0a:00:a0:98:19:9f:b0  node2     0c      true
    c_vs_iscsi_fcp data1   up/up      20:0d:00:a0:98:19:9f:b0  node2     0c      true
                data2      up/up      20:0e:00:a0:98:19:9f:b0  node2     0c      true
                data3      up/up      10.228.34.190/21         node2     e0b     true
                data4      up/up      10.228.34.192/21         node2     e0b     true
    Alternatively, you can view more detailed LIF information by entering the following
    command:
    network interface show -instance -data-protocol iscsi|fcp
  27. Capture the default configuration of any FC ports on the original nodes by entering the following command and recording the output for your systems:
    ucadmin show
    The command displays information about all FC ports in the cluster, as shown in the following example:
    cluster::> ucadmin show
                    Current Current   Pending Pending   Admin
    Node    Adapter Mode    Type      Mode    Type      Status
    node1   0a      fc      initiator -       -         online
    node1   0b      fc      initiator -       -         online
    node1   0c      fc      initiator -       -         online
    node1   0d      fc      initiator -       -         online
    node2   0a      fc      initiator -       -         online
    node2   0b      fc      initiator -       -         online
    node2   0c      fc      initiator -       -         online
    node2   0d      fc      initiator -       -         online
    8 entries were displayed.
    You can use the information after the upgrade to set the configuration of FC ports on the new nodes.
  28. If you are upgrading a V-Series system or a system with FlexArray Virtualization software, capture information about the topology of the original nodes by entering the following command and recording the output:
    storage array config show -switch
    The system displays topology information, as show in the following example:
    cluster::> storage array config show -switch
          LUN LUN                                  Target Side Initiator Side Initi-
    Node  Grp Cnt Array Name    Array Target Port  Switch Port Switch Port    ator
    node1 0   50  I_1818FAStT_1
                                205700a0b84772da   vgbr6510a:5  vgbr6510s164:3  0d
                                206700a0b84772da   vgbr6510a:6  vgbr6510s164:4  2b
                                207600a0b84772da   vgbr6510b:6  vgbr6510s163:1  0c
    node2 0   50  I_1818FAStT_1
                                205700a0b84772da   vgbr6510a:5  vgbr6510s164:1  0d
                                206700a0b84772da   vgbr6510a:6  vgbr6510s164:2  2b
                                207600a0b84772da   vgbr6510b:6  vgbr6510s163:3  0c
                                208600a0b84772da   vgbr6510b:5  vgbr6510s163:4  2a
    7 entries were displayed.
  29. Complete the following substeps:
    1. Enter the following command on one of the original nodes and record the output:
      service-processor show -node * -instance
      The system displays detailed information about the SP on both nodes.
    2. Ensure that the SP status is online.
    3. Ensure that the SP network is configured.
    4. Record the IP address and other information about the SP.
    You might want to reuse the network parameters of the remote management devices, in this case the SPs, from the original system for the SPs on the new nodes.
    For detailed information about the SP, refer to References to link to the System Administration Reference and the ONTAP 9 Commands: Manual Page Reference.
  30. If you want the new nodes to have the same licensed functionality as the original nodes, enter the following command to see the cluster licenses on the original system:
    system license show -owner *
    The following example shows the site licenses for cluster1:
    Serial Number: 1-80-000013
    Owner: cluster1
    Package           Type    Description           Expiration
    Base              site    Cluster Base License  -
    NFS               site    NFS License           -
    CIFS              site    CIFS License          -
    SnapMirror        site    SnapMirror License    -
    FlexClone         site    FlexClone License     -
    SnapVault         site    SnapVault License     -
    6 entries were displayed.
  31. Obtain new license keys for the new nodes at the NetApp Support Site. Refer to References to link to NetApp Support Site.
    If the site does not have the license keys you need, contact your NetApp sales representative.
  32. Check whether the original system has AutoSupport enabled by entering the following command on each node and examining its output:
    system node autosupport show -node <node1,node2>
    The command output shows whether AutoSupport is enabled, as shown in the following example:
    cluster::> system node autosupport show -node node1,node2
    Node             State     From          To                Mail Hosts
    node1            enable    Postmaster    admin@netapp.com  mailhost
    node2            enable    Postmaster    -                 mailhost
  33. Take one of the following actions:
    If the original system…​ Then…​
    Has AutoSupport enabled…​
    Does not have AutoSupport enabled…​
    1. Enable AutoSupport by following the instructions in the System Administration Reference. (Refer to References to link to the System Administration Reference.)
      Note: AutoSupport is enabled by default when you configure your storage system for the first time. Although you can disable AutoSupport at any time, you should leave it enabled. Enabling AutoSupport can significantly help identify problems and solutions should a problem occur on your storage system.
    2. Go to the Get an IP address of an external key management server for Storage Encryption section.
  34. Verify that AutoSupport is configured with the correct mailhost details and recipient e-mail IDs by entering the following command on both of the original nodes and examining the output:
    system node autosupport show -node node_name -instance
    For detailed information about AutoSupport, refer to References to link to the System Administration Reference and the ONTAP 9 Commands: Manual Page Reference.
  35. Send an AutoSupport message to NetApp for node1 by entering the following command:
    system node autosupport invoke -node node1 -type all -message "Upgrading node1 from platform_old to platform_new"
    Do not send an AutoSupport message to NetApp for node2 at this point; you do so later in the procedure.
  36. Verify that the AutoSupport message was sent by entering the following command and examining its output:
    system node autosupport show -node <node1> -instance
    The fields Last Subject Sent: and Last Time Sent: contain the message title of the last message sent and the time the message was sent.