Replace a DIMM - ASA C400
You must replace a DIMM in the controller module when your system registers an increasing number of correctable error correction codes (ECC); failure to do so causes a system panic.
All other components in the system must be functioning properly; if not, you must contact technical support.
You must replace the failed component with a replacement FRU component you received from your provider.
Step 1: Shut down the impaired controller
Shut down or take over the impaired controller using the appropriate procedure for your configuration.
To shut down the impaired controller, you must determine the status of the controller and, if necessary, take over the controller so that the healthy controller continues to serve data from the impaired controller storage.
If you have a SAN system, you must have checked event messages (
cluster kernel-service show
) for impaired controller SCSI blade. Thecluster kernel-service show
command displays the node name, quorum status of that node, availability status of that node, and operational status of that node.Each SCSI-blade process should be in quorum with the other nodes in the cluster. Any issues must be resolved before you proceed with the replacement.
If you have a cluster with more than two nodes, it must be in quorum. If the cluster is not in quorum or a healthy controller shows false for eligibility and health, you must correct the issue before shutting down the impaired controller; see Synchronize a node with the cluster.
If AutoSupport is enabled, suppress automatic case creation by invoking an AutoSupport message:
system node autosupport invoke -node * -type all -message MAINT=number_of_hours_downh
The following AutoSupport message suppresses automatic case creation for two hours:
Disable automatic giveback from the console of the healthy controller:
storage failover modify –node local -auto-giveback false
When you see Do you want to disable auto-giveback?, enter y
Take the impaired controller to the LOADER prompt:
If the impaired controller is displaying… Then… The LOADER prompt
Go to the next step.
Waiting for giveback…
Press Ctrl-C, and then respond
y
when prompted.System prompt or password prompt
Take over or halt the impaired controller from the healthy controller:
storage failover takeover -ofnode impaired_node_name
When the impaired controller shows Waiting for giveback…, press Ctrl-C, and then respond
y
To shut down the impaired controller, you must determine the status of the controller and, if necessary, switch over the controller so that the healthy controller continues to serve data from the impaired controller storage.
If you are using NetApp Storage Encryption, you must have reset the MSID using the instructions in the "Return a FIPS drive or SED to unprotected mode" section of NetApp Encryption overview with the CLI.
You must leave the power supplies turned on at the end of this procedure to provide power to the healthy controller.
Check the MetroCluster status to determine whether the impaired controller has automatically switched over to the healthy controller:
metrocluster show
Depending on whether an automatic switchover has occurred, proceed according to the following table:
If the impaired controller… Then… Has automatically switched over
Proceed to the next step.
Has not automatically switched over
Perform a planned switchover operation from the healthy controller:
metrocluster switchover
Has not automatically switched over, you attempted switchover with the
command, and the switchover was vetoedReview the veto messages and, if possible, resolve the issue and try again. If you are unable to resolve the issue, contact technical support.
Resynchronize the data aggregates by running the
metrocluster heal -phase aggregates
command from the surviving cluster.controller_A_1::> metrocluster heal -phase aggregates [Job 130] Job succeeded: Heal Aggregates is successful.
If the healing is vetoed, you have the option of reissuing the
metrocluster heal
command with the-override-vetoes
parameter. If you use this optional parameter, the system overrides any soft vetoes that prevent the healing operation. -
Verify that the operation has been completed by using the metrocluster operation show command.
controller_A_1::> metrocluster operation show Operation: heal-aggregates State: successful Start Time: 7/25/2016 18:45:55 End Time: 7/25/2016 18:45:56 Errors: -
Check the state of the aggregates by using the
storage aggregate show
command.controller_A_1::> storage aggregate show Aggregate Size Available Used% State #Vols Nodes RAID Status --------- -------- --------- ----- ------- ------ ---------------- ------------ ... aggr_b2 227.1GB 227.1GB 0% online 0 mcc1-a2 raid_dp, mirrored, normal...
Heal the root aggregates by using the
metrocluster heal -phase root-aggregates
command.mcc1A::> metrocluster heal -phase root-aggregates [Job 137] Job succeeded: Heal Root Aggregates is successful
metrocluster heal
command with the -override-vetoes parameter. If you use this optional parameter, the system overrides any soft vetoes that prevent the healing operation. -
Verify that the heal operation is complete by using the
command on the destination cluster:mcc1A::> metrocluster operation show Operation: heal-root-aggregates State: successful Start Time: 7/29/2016 20:54:41 End Time: 7/29/2016 20:54:42 Errors: -
On the impaired controller module, disconnect the power supplies.
Step 2: Remove the controller module
To access components inside the controller module, you must remove the controller module from the chassis.
If you are not already grounded, properly ground yourself.
Release the power cable retainers, and then unplug the cables from the power supplies.
Loosen the hook and loop strap binding the cables to the cable management device, and then unplug the system cables and SFPs (if needed) from the controller module, keeping track of where the cables were connected.
Leave the cables in the cable management device so that when you reinstall the cable management device, the cables are organized.
Remove the cable management device from the controller module and set it aside.
Press down on both of the locking latches, and then rotate both latches downward at the same time.
The controller module moves slightly out of the chassis.
Locking latches
Controller moves slightly out of chassis
Slide the controller module out of the chassis.
Make sure that you support the bottom of the controller module as you slide it out of the chassis.
Place the controller module on a stable, flat surface.
Step 3: Replace system DIMMs
Replacing a system DIMM involves identifying the target DIMM through the associated error message, locating the target DIMM using the FRU map on the air duct, and then replacing the DIMM.
You can use the following animation, illustration, or the written steps to replace a system DIMM.
The animation and illustration show empty slots for sockets without DIMMs. These empty sockets are populated with blanks. |
DIMM locking tabs |
DIMM |
DIMM socket |
The DIMMs are located in sockets 2, 4, 13, and 15. The NVDIMM is located in slot 11.
Open the air duct:
Press the locking tabs on the sides of the air duct in toward the middle of the controller module.
Slide the air duct toward the back of the controller module, and then rotate it upward to its completely open position.
Locate the DIMMs on your controller module.
Note the orientation of the DIMM in the socket so that you can insert the replacement DIMM in the proper orientation.
Eject the DIMM from its socket by slowly pushing apart the two DIMM ejector tabs on either side of the DIMM, and then slide the DIMM out of the socket.
Carefully hold the DIMM by the edges to avoid pressure on the components on the DIMM circuit board. -
Remove the replacement DIMM from the antistatic shipping bag, hold the DIMM by the corners, and align it to the slot.
The notch among the pins on the DIMM should line up with the tab in the socket.
Make sure that the DIMM ejector tabs on the connector are in the open position, and then insert the DIMM squarely into the slot.
The DIMM fits tightly in the slot, but should go in easily. If not, realign the DIMM with the slot and reinsert it.
Visually inspect the DIMM to verify that it is evenly aligned and fully inserted into the slot. -
Push carefully, but firmly, on the top edge of the DIMM until the ejector tabs snap into place over the notches at the ends of the DIMM.
Close the air duct.
Step 4: Install the controller module
After you have replaced the component in the controller module, you must reinstall the controller module into the chassis, and then boot it to Maintenance mode.
Controller module |
Controller locking latches |
If you have not already done so, close the air duct.
Align the end of the controller module with the opening in the chassis, and then gently push the controller module halfway into the system.
Do not completely insert the controller module in the chassis until instructed to do so. -
Cable the management and console ports only, so that you can access the system to perform the tasks in the following sections.
You will connect the rest of the cables to the controller module later in this procedure. -
Complete the installation of the controller module:
Plug the power cord into the power supply, reinstall the power cable locking collar, and then connect the power supply to the power source.
Using the locking latches, firmly push the controller module into the chassis until the locking latches begin to rise.
Do not use excessive force when sliding the controller module into the chassis to avoid damaging the connectors. -
Fully seat the controller module in the chassis by rotating the locking latches upward, tilting them so that they clear the locking pins, gently push the controller all the way in, and then lower the locking latches into the locked position.
The controller module begins to boot as soon as it is fully seated in the chassis. Be prepared to interrupt the boot process.
If you have not already done so, reinstall the cable management device.
Interrupt the normal boot process and boot to LOADER by pressing
Ctrl-C
.If your system stops at the boot menu, select the option to boot to LOADER. -
At the LOADER prompt, enter
bye
to reinitialize the PCIe cards and other components. -
Interrupt the boot process and boot to the LOADER prompt by pressing
Ctrl-C
Step 5: Restore the controller module to operation
You must recable the system, give back the controller module, and then reenable automatic giveback.
Recable the system, as needed.
If you removed the media converters (QSFPs or SFPs), remember to reinstall them if you are using fiber optic cables.
Return the controller to normal operation by giving back its storage:
storage failover giveback -ofnode impaired_node_name
If automatic giveback was disabled, reenable it:
Step 6: Switch back aggregates in a two-node MetroCluster configuration
After you have completed the FRU replacement in a two-node MetroCluster configuration, you can perform the MetroCluster switchback operation. This returns the configuration to its normal operating state, with the sync-source storage virtual machines (SVMs) on the formerly impaired site now active and serving data from the local disk pools.
This task only applies to two-node MetroCluster configurations.
Verify that all nodes are in the
enabled
state:metrocluster node show
cluster_B::> metrocluster node show DR Configuration DR Group Cluster Node State Mirroring Mode ----- ------- -------------- -------------- --------- -------------------- 1 cluster_A controller_A_1 configured enabled heal roots completed cluster_B controller_B_1 configured enabled waiting for switchback recovery 2 entries were displayed.
Verify that resynchronization is complete on all SVMs:
metrocluster vserver show
Verify that any automatic LIF migrations being performed by the healing operations were completed successfully:
metrocluster check lif show
Perform the switchback by using the
metrocluster switchback
command from any node in the surviving cluster. -
Verify that the switchback operation has completed:
metrocluster show
The switchback operation is still running when a cluster is in the
waiting-for-switchback
state:cluster_B::> metrocluster show Cluster Configuration State Mode -------------------- ------------------- --------- Local: cluster_B configured switchover Remote: cluster_A configured waiting-for-switchback
The switchback operation is complete when the clusters are in the
normal
state.:cluster_B::> metrocluster show Cluster Configuration State Mode -------------------- ------------------- --------- Local: cluster_B configured normal Remote: cluster_A configured normal
If a switchback is taking a long time to finish, you can check on the status of in-progress baselines by using the
metrocluster config-replication resync-status show
command. -
Reestablish any SnapMirror or SnapVault configurations.
Step 7: Return the failed part to NetApp
Return the failed part to NetApp, as described in the RMA instructions shipped with the kit. See the Part Return & Replacements page for further information.