Install and maintain
Replace an NVDIMM - ASA C400
Contributors netapp-jsnyder
You must replace the NVDIMM in the controller module when your system registers that the flash lifetime is almost at an end or that the identified NVDIMM is not healthy in general; failure to do so causes a system panic.
All other components in the system must be functioning properly; if not, you must contact technical support.
You must replace the failed component with a replacement FRU component you received from your provider.
Step 1: Shut down the impaired controller
Shut down or take over the impaired controller using the appropriate procedure for your configuration.
Option 1: Most configurations
To shut down the impaired controller, you must determine the status of the controller and, if necessary, take over the controller so that the healthy controller continues to serve data from the impaired controller storage.
About this task
  • If you have a SAN system, you must have checked event messages (cluster kernel-service show) for impaired controller SCSI blade. The cluster kernel-service show command displays the node name, quorum status of that node, availability status of that node, and operational status of that node.
    Each SCSI-blade process should be in quorum with the other nodes in the cluster. Any issues must be resolved before you proceed with the replacement.
  • If you have a cluster with more than two nodes, it must be in quorum. If the cluster is not in quorum or a healthy controller shows false for eligibility and health, you must correct the issue before shutting down the impaired controller; see Synchronize a node with the cluster.
Steps
  1. If AutoSupport is enabled, suppress automatic case creation by invoking an AutoSupport message: system node autosupport invoke -node * -type all -message MAINT=number_of_hours_downh
    The following AutoSupport message suppresses automatic case creation for two hours: cluster1:> system node autosupport invoke -node * -type all -message MAINT=2h
  2. Disable automatic giveback from the console of the healthy controller: storage failover modify –node local -auto-giveback false
    Note When you see Do you want to disable auto-giveback?, enter y.
  3. Take the impaired controller to the LOADER prompt:
    If the impaired controller is displaying…​ Then…​
    The LOADER prompt
    Go to the next step.
    Waiting for giveback…​
    Press Ctrl-C, and then respond y when prompted.
    System prompt or password prompt
    Take over or halt the impaired controller from the healthy controller: storage failover takeover -ofnode impaired_node_name
    When the impaired controller shows Waiting for giveback…​, press Ctrl-C, and then respond y.
Option 2: Controller is in a two-node MetroCluster
To shut down the impaired controller, you must determine the status of the controller and, if necessary, switch over the controller so that the healthy controller continues to serve data from the impaired controller storage.
About this task
  • If you are using NetApp Storage Encryption, you must have reset the MSID using the instructions in the "Return a FIPS drive or SED to unprotected mode" section of NetApp Encryption overview with the CLI.
  • You must leave the power supplies turned on at the end of this procedure to provide power to the healthy controller.
Steps
  1. Check the MetroCluster status to determine whether the impaired controller has automatically switched over to the healthy controller: metrocluster show
  2. Depending on whether an automatic switchover has occurred, proceed according to the following table:
    If the impaired controller…​ Then…​
    Has automatically switched over
    Proceed to the next step.
    Has not automatically switched over
    Perform a planned switchover operation from the healthy controller: metrocluster switchover
    Has not automatically switched over, you attempted switchover with the metrocluster switchover command, and the switchover was vetoed
    Review the veto messages and, if possible, resolve the issue and try again. If you are unable to resolve the issue, contact technical support.
  3. Resynchronize the data aggregates by running the metrocluster heal -phase aggregates command from the surviving cluster.
    controller_A_1::> metrocluster heal -phase aggregates
    [Job 130] Job succeeded: Heal Aggregates is successful.
    If the healing is vetoed, you have the option of reissuing the metrocluster heal command with the -override-vetoes parameter. If you use this optional parameter, the system overrides any soft vetoes that prevent the healing operation.
  4. Verify that the operation has been completed by using the metrocluster operation show command.
    controller_A_1::> metrocluster operation show
        Operation: heal-aggregates
          State: successful
    Start Time: 7/25/2016 18:45:55
       End Time: 7/25/2016 18:45:56
         Errors: -
  5. Check the state of the aggregates by using the storage aggregate show command.
    controller_A_1::> storage aggregate show
    Aggregate     Size Available Used% State   #Vols  Nodes            RAID Status
    aggr_b2    227.1GB   227.1GB    0% online       0 mcc1-a2          raid_dp, mirrored, normal...
  6. Heal the root aggregates by using the metrocluster heal -phase root-aggregates command.
    mcc1A::> metrocluster heal -phase root-aggregates
    [Job 137] Job succeeded: Heal Root Aggregates is successful
  7. Verify that the heal operation is complete by using the metrocluster operation show command on the destination cluster:
    mcc1A::> metrocluster operation show
      Operation: heal-root-aggregates
          State: successful
     Start Time: 7/29/2016 20:54:41
       End Time: 7/29/2016 20:54:42
         Errors: -
  8. On the impaired controller module, disconnect the power supplies.
Step 2: Remove the controller module
To access components inside the controller module, you must remove the controller module from the chassis.
  1. If you are not already grounded, properly ground yourself.
  2. Release the power cable retainers, and then unplug the cables from the power supplies.
  3. Loosen the hook and loop strap binding the cables to the cable management device, and then unplug the system cables and SFPs (if needed) from the controller module, keeping track of where the cables were connected.
    Leave the cables in the cable management device so that when you reinstall the cable management device, the cables are organized.
  4. Remove the cable management device from the controller module and set it aside.
  5. Press down on both of the locking latches, and then rotate both latches downward at the same time.
    The controller module moves slightly out of the chassis.
    drw c400 remove controller IEOPS 1216
    legend icon 01
    Locking latches
    legend icon 02
    Controller moves slightly out of chassis
  6. Slide the controller module out of the chassis.
    Make sure that you support the bottom of the controller module as you slide it out of the chassis.
  7. Place the controller module on a stable, flat surface.
Step 3: Replace the NVDIMM
To replace the NVDIMM, you must locate it in the controller module using the FRU map on top of the air duct or the FRU Map on the top of the slot 1 riser.
  • The NVDIMM LED blinks while destaging contents when you halt the system. After the destage is complete, the LED turns off.
  • Although the contents of the NVDIMM is encrypted, it is a best practice to erase the contents of the NVDIMM before replacing it. For more information, see the Statement of Volatility on the NetApp Support Site.
    Note You must log into the NetApp Support Site to display the Statement of Volatility for your system.
You can use the following animation, illustration, or the written steps to replace the NVDIMM.
Note The animation shows empty slots for sockets without DIMMs. These empty sockets are populated with blanks.
Animation - Replace the NVDIMM
drw A400 Replace NVDIMM DIMM IEOPS 1009
Callout number 1
DIMM locking tabs
Callout number 2
DIMM
Callout number 3
DIMM socket
  1. Open the air duct and then locate the NVDIMM in slot 11 on your controller module.
    Note The NVDIMM looks significantly different than system DIMMs.
  2. Eject the NVDIMM from its slot by slowly pushing apart the two NVDIMM ejector tabs on either side of the NVDIMM, and then slide the NVDIMM out of the socket and set it aside.
    Note Carefully hold the NVDIMM by the edges to avoid pressure on the components on the NVDIMM circuit board.
  3. Remove the replacement NVDIMM from the antistatic shipping bag, hold the NVDIMM by the corners, and then align it to the slot.
    The notch among the pins on the NVDIMM should line up with the tab in the socket.
  4. Locate the slot where you are installing the NVDIMM.
  5. Insert the NVDIMM squarely into the slot.
    The NVDIMM fits tightly in the slot, but should go in easily. If not, realign the NVDIMM with the slot and reinsert it.
    Note Visually inspect the NVDIMM to verify that it is evenly aligned and fully inserted into the slot.
  6. Push carefully, but firmly, on the top edge of the NVDIMM until the ejector tabs snap into place over the notches at the ends of the NVDIMM.
  7. Close the air duct.
Step 4: Install the controller module
After you have replaced the component in the controller module, you must reinstall the controller module into the chassis, and then boot it to Maintenance mode.
  1. If you have not already done so, close the air duct.
  2. Align the end of the controller module with the opening in the chassis, and then gently push the controller module halfway into the system.
    Note Do not completely insert the controller module in the chassis until instructed to do so.
  3. Cable the management and console ports only, so that you can access the system to perform the tasks in the following sections.
    Note You will connect the rest of the cables to the controller module later in this procedure.
  4. Complete the installation of the controller module:
    1. Plug the power cord into the power supply, reinstall the power cable locking collar, and then connect the power supply to the power source.
    2. Using the locking latches, firmly push the controller module into the chassis until the locking latches begin to rise.
      Note Do not use excessive force when sliding the controller module into the chassis to avoid damaging the connectors.
    3. Fully seat the controller module in the chassis by rotating the locking latches upward, tilting them so that they clear the locking pins, gently push the controller all the way in, and then lower the locking latches into the locked position.
      The controller module begins to boot as soon as it is fully seated in the chassis. Be prepared to interrupt the boot process.
    4. If you have not already done so, reinstall the cable management device.
    5. Interrupt the normal boot process and boot to LOADER by pressing Ctrl-C.
      Note If your system stops at the boot menu, select the option to boot to LOADER.
    6. At the LOADER prompt, enter bye to reinitialize the PCIe cards and other components.
    7. Interrupt the boot process and boot to the LOADER prompt by pressing Ctrl-C.
Step 5: Restore the controller module to operation
You must recable the system, give back the controller module, and then reenable automatic giveback.
  1. Recable the system, as needed.
    If you removed the media converters (QSFPs or SFPs), remember to reinstall them if you are using fiber optic cables.
  2. Return the controller to normal operation by giving back its storage: storage failover giveback -ofnode impaired_node_name
  3. If automatic giveback was disabled, reenable it: storage failover modify -node local -auto-giveback true
Step 6: Switch back aggregates in a two-node MetroCluster configuration
After you have completed the FRU replacement in a two-node MetroCluster configuration, you can perform the MetroCluster switchback operation. This returns the configuration to its normal operating state, with the sync-source storage virtual machines (SVMs) on the formerly impaired site now active and serving data from the local disk pools.
This task only applies to two-node MetroCluster configurations.
Steps
  1. Verify that all nodes are in the enabled state: metrocluster node show
    cluster_B::>  metrocluster node show
    DR                           Configuration  DR
    Group Cluster Node           State          Mirroring Mode
    1     cluster_A
                  controller_A_1 configured     enabled   heal roots completed
          cluster_B
                  controller_B_1 configured     enabled   waiting for switchback recovery
    2 entries were displayed.
  2. Verify that resynchronization is complete on all SVMs: metrocluster vserver show
  3. Verify that any automatic LIF migrations being performed by the healing operations were completed successfully: metrocluster check lif show
  4. Perform the switchback by using the metrocluster switchback command from any node in the surviving cluster.
  5. Verify that the switchback operation has completed: metrocluster show
    The switchback operation is still running when a cluster is in the waiting-for-switchback state:
    cluster_B::> metrocluster show
    Cluster              Configuration State    Mode
     Local: cluster_B configured       	switchover
    Remote: cluster_A configured       	waiting-for-switchback
    The switchback operation is complete when the clusters are in the normal state.:
     Local: cluster_B configured      		normal
    Remote: cluster_A configured      		normal
    If a switchback is taking a long time to finish, you can check on the status of in-progress baselines by using the metrocluster config-replication resync-status show command.
  6. Reestablish any SnapMirror or SnapVault configurations.
Step 7: Return the failed part to NetApp
Return the failed part to NetApp, as described in the RMA instructions shipped with the kit. See the Part Return & Replacements page for further information.
