Considerations for using MetroCluster compliant switches

MetroCluster IP switches provided by NetApp are NetApp validated. Beginning with ONTAP 9.7, MetroCluster IP configurations can support switches that are not NetApp validated provided that they are compliant with NetApp specifications.

General requirements

The requirements show how to configure MetroCluster compliant switches without using reference configuration (RCF) files.

Platform-specific network speeds for MetroCluster compliant switches

The following table provides platform-specific network speeds for MetroCluster compliant switches.

Note: Missing values indicate that the platform is not supported.
Platform Network Speed (Gbps)
AFF A800 40 or 80
AFF A700 40
AFF A320 100
AFF A300 25
AFF A220 -
FAS9000 40
FAS8200 25
FAS2750 -

Assumptions for the examples

The examples provided are valid for Cisco NX31xx and NX32xx switches. If other switches are used, these commands can be used as guidance, but the commands might be different. If a feature shown in the examples is not available on the switch, this means that the switch does not meet the minimum requirements and cannot be used to deploy a MetroCluster configuration. This is true for any switch that is connecting a MetroCluster configuration and for all switches on the path between those switches.

Generic switch configuration

A VLAN in each network must be configured. The example shows how to configure a VLAN in network 10.

Example:

# vlan 10

The load balancing policy should be set so that order is preserved.

Example:

# port-channel load-balance src-dst ip-l4port-vlan

You must configure the access and class maps, which map the RDMA and iSCSI traffic to the appropriate classes.

All TCP traffic to and from the port 65200 is mapped to the storage (iSCSI) class. All TCP traffic to and from the port 10006 is mapped to the RDMA class.

Example:

ip access-list storage
  10 permit tcp any eq 65200 any
  20 permit tcp any any eq 65200
ip access-list rdma
  10 permit tcp any eq 10006 any
  20 permit tcp any any eq 10006 

class-map type qos match-all storage
  match access-group name storage
class-map type qos match-all rdma 
  match access-group name rdma

You must configure the ingress policy. The ingress policy maps the traffic as classified to the different COS groups. In this example, the RDMA traffic is mapped to COS group 5 and iSCSI traffic is mapped to COS group 4.

Example:

policy-map type qos MetroClusterIP_Ingress
class rdma
  set dscp 40
  set cos 5
  set qos-group 5
class storage
  set dscp 32
  set cos 4
  set qos-group 4

You must configure the egress policy on the switch. The egress policy maps the traffic to the egress queues. In this example, RDMA traffic is mapped to queue 5 and iSCSI traffic is mapped to queue 4.

Example:

policy-map type queuing MetroClusterIP_Egress
class type queuing c-out-8q-q7
  priority level 1
class type queuing c-out-8q-q6
  priority level 2
class type queuing c-out-8q-q5
  priority level 3
  random-detect threshold burst-optimized ecn
class type queuing c-out-8q-q4
  priority level 4
  random-detect threshold burst-optimized ecn
class type queuing c-out-8q-q3
  priority level 5
class type queuing c-out-8q-q2
  priority level 6
class type queuing c-out-8q-q1
  priority level 7
class type queuing c-out-8q-q-default
  bandwidth remaining percent 100
  random-detect threshold burst-optimized ecn

You need to configure a switch that has MetroCluster traffic on an ISL but does not connect to any MetroCluster interfaces. In this case, the traffic is already classified and only needs to be mapped to the appropriate queue. In the following example, all of the COS5 traffic is mapped to the class RDMA, and all of the COS4 traffic is mapped to the class iSCSI. Note that this will affect all of the COS5 and COS4 traffic, not only the MetroCluster traffic. If you only want to map the MetroCluster traffic, then you must use the above class maps to identify the traffic using the access groups.

Example:

class-map type qos match-all rdma
  match cos 5
class-map type qos match-all storage
  match cos 4

Configuring the ISLs

You can configure a 'trunk' mode port when setting an allowed VLAN.

There are two commands, one to set the allowed VLAN list, and one to add to the existing allowed VLAN list.

You can set the allowed VLANs as shown in the example.

Example:

switchport trunk allowed vlan 10

You can add a VLAN to the allowed list as shown in the example.

Example:

switchport trunk allowed vlan add 10

In the example, port-channel 10 is configured for VLAN 10.

Example:

interface port-channel10
switchport mode trunk
switchport trunk allowed vlan 10
mtu 9216
service-policy type queuing output MetroClusterIP_Egress

The ISL ports should be configured as part of a port-channel and be assigned the egress queues as shown in the example.

Example:

interface eth1/15-16
switchport mode trunk
switchport trunk allowed vlan 10
no lldp transmit
no lldp receive
mtu 9216
channel-group 10 mode active
service-policy type queuing output MetroClusterIP_Egress
no shutdown

Configuring the node ports

You might need to configure the node port in breakout mode. In this example, ports 25 and 26 are configured in 4 x 25 Gbps breakout mode.

Example:

interface breakout module 1 port 25-26 map 25g-4x

You might need to configure the MetroCluster interface port speed. The example shows how to configure the speed to "auto".

Example:

speed auto

The following example shows how to fix the speed at 40 Gbps.

Example:

speed 40000

You might need to configure the interface. In the following example, the interface speed is set to "auto".

The port is in access mode in VLAN 10, MTU is set to 9216 and the MetroCluster ingress policy is assigned.

Example:

interface eth1/9
description MetroCluster-IP Node Port
speed auto
switchport access vlan 10
spanning-tree port type edge
spanning-tree bpduguard enable
mtu 9216
flowcontrol receive on
flowcontrol send on
service-policy type qos input MetroClusterIP_Ingress
no shutdown

On 25-Gbps ports, the FEC setting might need to be set to "off" as shown in the example.

Example:

fec off