NetApp solutions for SAP
Storage controller setup
Contributors netapp-mschoen kevin-hoke
This section describes the configuration of the NetApp storage system. You must complete the primary installation and setup according to the corresponding ONTAP setup and configuration guides.
Storage efficiency
Inline deduplication, cross- volume inline deduplication, inline compression, and inline compaction are supported with SAP HANA in an SSD configuration.
Enabling storage efficiency features in an HDD-based configuration is not supported.
NetApp FlexGroup Volumes
The usage of NetApp FlexGroup Volumes is not supported for SAP HANA. Due to the architecture of SAP HANA the usage of FlexGroup Volumes does not provide any benefit and may results in performance issues.
NetApp volume and aggregate encryption
The use of NetApp Volume Encryption (NVE) and NetApp Aggregate Encryption (NAE) are supported with SAP HANA.
ONTAP Autonomous Ransomware Protection
The Snapshots created by ONTAP Autonomous Ransomware Protection can't be used for forward recovery of the SAP HANA database. Therefore it is not recommended to use it for SAP HANA data and log volumes and should be disabled for these volumes. Use SnapCenter based data protection with Tamperproof Snapshots instead for ransomware protection:
SAP HANA backup and recovery with SnapCenter.
ONTAP Autonomous Ransomware Protection might be beneficial for other volumes such as /hana/shared.
It is possible to disable the automatically activation of this feature during volume creation for an ONTAP Cluster, however it is recommended to keep the default setting and disable it for volumes where this functionality is not needed.
Quality of service
QoS can be used to limit the storage throughput for specific SAP HANA systems or other applications on a shared-use controller. One use case would be to limit the throughput of development and test systems so that they cannot influence production systems in a mixed setup.
During the sizing process, you should determine the performance requirements of a nonproduction system. Development and test systems can be sized with lower performance values, typically in the range of 20% to 50% of a production-system KPI as defined by SAP.
Starting with ONTAP 9, QoS is configured on the storage volume level and uses maximum values for throughput (MBps) and the amount of I/O (IOPS).
Large write I/O has the biggest performance effect on the storage system. Therefore, the QoS throughput limit should be set to a percentage of the corresponding write SAP HANA storage performance KPI values in the data and log volumes.
NetApp FabricPool
NetApp FabricPool technology must not be used for active primary file systems in SAP HANA systems. This includes the file systems for the data and log area as well as the /hana/shared file system. Doing so results in unpredictable performance, especially during the startup of an SAP HANA system.
Using the “snapshot-only” tiering policy is possible as well as using FabricPool in general at a backup target such as a SnapVault or SnapMirror destination.
Note Using FabricPool for tiering Snapshot copies at primary storage or using FabricPool at a backup target changes the required time for the restore and recovery of a database or other tasks such as creating system clones or repair systems. Take this into consideration for planning your overall lifecycle- management strategy and check to make sure that your SLAs are still being met while using this function.
FabricPool is a good option for moving log backups to another storage tier. Moving backups affects the time needed to recover an SAP HANA database. Therefore, the option “tiering-minimum-cooling-days” should be set to a value that places log backups, which are routinely needed for recovery, on the local fast storage tier.
Storage configuration
The following overview summarizes the required storage configuration steps. Each step is covered in detail in the subsequent sections. In this section, we assume that the storage hardware is set up and that the ONTAP software is already installed. Also, the connections between the storage ports (10GbE or faster) and the network must already be in place.
  1. Check the correct SAS stack configuration as described in Disk shelf connection.
  2. Create and configure the required aggregates as described in Aggregate configuration.
  3. Create a storage virtual machine (SVM) as described in Storage virtual machine configuration.
  4. Create LIFs as described in Logical interface configuration.
  5. Create volumes within the aggregates as described in Volume configuration for SAP HANA single-host systems and Volume configuration for SAP HANA multiple-host systems.
  6. Set the required volume options as described in Volume options.
  7. Set the required options for NFSv3 as described in NFS configuration for NFSv3 or for NFSv4 as described in NFS configuration for NFSv4.
  8. Mount the volumes to namespace and set export policies as described in Mount volumes to namespace and set export policies.
With HDDs, a maximum of two DS2246 disk shelves or four DS224C disk shelves can be connected to one SAS stack to provide the required performance for the SAP HANA hosts, as shown in the following figure. The disks within each shelf must be distributed equally to both controllers of the HA pair.
Figure showing input/output dialog or representing written content
With SSDs, a maximum of one disk shelf can be connected to one SAS stack to provide the required performance for the SAP HANA hosts, as shown in the following figure. The disks within each shelf must be distributed equally to both controllers of the HA pair. With the DS224C disk shelf, quad- path SAS cabling can also be used, but is not required.
NVMe (100GbE) disk shelves
Each NS224 NVMe disk shelf is connected with two 100GbE ports per controller, as shown in the following figure. The disks within each shelf must be distributed equally to both controllers of the HA pair.
MVMe disk shelf connections
In general, you must configure two aggregates per controller, independent of the disk shelf or drive technology (SSD or HDD) that is used. For FAS2000 series systems, one data aggregate is enough.
Aggregate configuration with HDDs
The following figure shows a configuration for eight SAP HANA hosts. Four SAP HANA hosts are attached to each storage controller. Two separate aggregates, one at each storage controller, are configured. Each aggregate is configured with 4 × 10 = 40 data disks (HDDs).
Aggregate configuration with SDD-only systems
In general, you must configure two aggregates per controller, independent of which disk shelf or disk technology (SSDs or HDDs) is used. For FAS2000 series systems, one data aggregate is enough.
The following figure shows a configuration of 12 SAP HANA hosts running on a 12Gb SAS shelf configured with ADPv2. Six SAP HANA hosts are attached to each storage controller. Four separate aggregates, two at each storage controller, are configured. Each aggregate is configured with 11 disks with nine data and two parity disk partitions. For each controller, two spare partitions are available.
Multiple SAP landscapes with SAP HANA databases can use a single SVM. An SVM can also be assigned to each SAP landscape, if necessary, in case they are managed by different teams within a company.
If a QoS profile was automatically created and assigned during new SVM creation, remove the automatically created profile from the SVM to provide the required performance for SAP HANA:
vserver modify -vserver <svm-name> -qos-policy-group none
For SAP HANA production systems, you must use different LIFs for mounting the data volume and the log volume from the SAP HANA host. Therefore at least two LIFs are required.
The data and log volume mounts of different SAP HANA hosts can share a physical storage network port by using either the same LIFs or by using individual LIFs for each mount.
The maximum number of data and log volume mounts per physical interface are shown in the following table.
Ethernet port speed 10GbE 25GbE 40GbE 100GeE
Maximum number of log or data volume mounts per physical port
3
8
12
30
Note Sharing one LIF between different SAP HANA hosts might require a remount of data or log volumes to a different LIF. This change avoids performance penalties if a volume is moved to a different storage controller.
Development and test systems can use more data and volume mounts or LIFs on a physical network interface.
For production, development, and test systems, the /hana/shared file system can use the same LIF as the data or log volume.
The following figure shows the volume configuration of four single-host SAP HANA systems. The data and log volumes of each SAP HANA system are distributed to different storage controllers. For example, volume SID1_data_mnt00001 is configured on controller A, and volume SID1_log_mnt00001 is configured on controller B.
Note If only one storage controller of an HA pair is used for the SAP HANA systems, data and log volumes can also be stored on the same storage controller.
Note If the data and log volumes are stored on the same controller, access from the server to the storage must be performed with two different LIFs: one LIF to access the data volume and one to access the log volume.
For each SAP HANA DB host, a data volume, a log volume, and a volume for /hana/shared are configured. The following table shows an example configuration for single-host SAP HANA systems.
Purpose Aggregate 1 at Controller A Aggregate 2 at Controller A Aggregate 1 at Controller B Aggregate 2 at Controller b
Data, log, and shared volumes for system SID1
Data volume: SID1_data_mnt00001
Shared volume: SID1_shared
Log volume: SID1_log_mnt00001
Data, log, and shared volumes for system SID2
Log volume: SID2_log_mnt00001
Data volume: SID2_data_mnt00001
Shared volume: SID2_shared
Data, log, and shared volumes for system SID3
Shared volume: SID3_shared
Data volume: SID3_data_mnt00001
Log volume: SID3_log_mnt00001
Data, log, and shared volumes for system SID4
Log volume: SID4_log_mnt00001
Shared volume: SID4_shared
Data volume: SID4_data_mnt00001
The following table shows an example of the mount point configuration for a single-host system. To place the home directory of the sidadm user on the central storage, the /usr/sap/SID file system should be mounted from the SID_shared volume.
Note If SAP Local Secure Store service (LSS) is used, the /lss/shared/SID directory, the default installation directory of LSS is on the local disk. In a disaster recovery setup with disk-based replication, NetApp recommends creating a directory within the SID_shared volume for the /lss/shared/SID directory so that all file systems are on the central storage.
Junction Path Directory Mount point at HANA host
SID_data_mnt00001
/hana/data/SID/mnt00001
SID_log_mnt00001
/hana/log/SID/mnt00001
SID-shared
usr-sap
shared
lss-shared
/usr/sap/SID
/hana/shared
/lss/shared/SID
The following figure shows the volume configuration of a 4+1 SAP HANA system. The data and log volumes of each SAP HANA host are distributed to different storage controllers. For example, volume SID1_data1_mnt00001 is configured on controller A, and volume SID1_log1_mnt00001 is configured on controller B.
Note If only one storage controller of an HA pair is used for the SAP HANA system, the data and log volumes can also be stored on the same storage controller.
Note If the data and log volumes are stored on the same controller, access from the server to the storage must be performed with two different LIFs: one to access the data volume and one to access the log volume.
For each SAP HANA host, a data volume and a log volume are created. The /hana/shared volume is used by all hosts of the SAP HANA system. The following table shows an example configuration for a multiple-host SAP HANA system with four active hosts.
Purpose Aggregate 1 at Controller A Aggregate 2 at Controller A Aggregate 1 at Controller B Aggregate 2 at Controller B
Data and log volumes for node 1
Data volume: SID_data_mnt00001
Log volume: SID_log_mnt00001
Data and log volumes for node 2
Log volume: SID_log_mnt00002
Data volume: SID_data_mnt00002
Data and log volumes for node 3
Data volume: SID_data_mnt00003
Log volume: SID_log_mnt00003
Data and log volumes for node 4
Log volume: SID_log_mnt00004
Data volume: SID_data_mnt00004
Shared volume for all hosts
Shared volume: SID_shared
The following table shows the configuration and the mount points of a multiple-host system with four active SAP HANA hosts. To place the home directories of the sidadm user of each host on the central storage, the /usr/sap/SID file systems are mounted from the SID_shared volume.
Note If SAP Local Secure Store service (LSS) is used, the /lss/shared/SID directory must be accessible at all hosts. NetApp recommends creating a directory within the SID_shared volume for the /lss/shared/SID directory.
Junction path Directory Mount point at SAP HANA host Note
SID_data_mnt00001
Mounted at all hosts
SID_log_mnt00001
SID_data_mnt00002
/hana/data/SID/mnt00002
SID_log_mnt00002
/hana/log/SID/mnt00002
SID_data_mnt00003
/hana/data/SID/mnt00003
SID_log_mnt00003
/hana/log/SID/mnt00003
SID_data_mnt00004
/hana/data/SID/mnt00004
SID_log_mnt00004
/hana/log/SID/mnt00004
SID_shared
shared
/hana/shared/
SID_shared
lss-shared
/lss/shared/
SID_shared
usr-sap-host1
/usr/sap/SID
Mounted at host 1
SID_shared
usr-sap-host2
/usr/sap/SID
Mounted at host 2
SID_shared
usr-sap-host3
/usr/sap/SID
Mounted at host 3
SID_shared
usr-sap-host4
/usr/sap/SID
Mounted at host 4
SID_shared
usr-sap-host5
/usr/sap/SID
Mounted at host 5
Volume options
You must verify and set the volume options listed in the following table on all SVMs. For some of the commands, you must switch to the advanced privilege mode within ONTAP.
Action Command
Disable visibility of Snapshot directory
vol modify -vserver <vserver-name> -volume <volname> -snapdir-access false
Disable automatic Snapshot copies
vol modify -vserver <vserver-name> -volume <volname> -snapshot-policy none
Disable ransomware protection, except of the SID_shared volume
vol modify -vserver <vserver-name> -volume <volname> -anti-ransomware-state disabled
Disable access time update except of the SID_shared volume
set advanced
vol modify -vserver <vserver-name> -volume <volname> -atime-update false
set admin
The NFS options listed in the following table must be verified and set on all storage controllers.
For some of the commands shown, you must switch to the advanced privilege mode within ONTAP.
Action Command
Enable NFSv3
nfs modify -vserver <vserver-name> v3.0 enabled
Set NFS TCP maximum transfer size to 1MB
set advanced
nfs modify -vserver <vserver_name> -tcp-max-xfer-size 1048576
set admin
Note In shared environments with different workloads set the max NFS TCP transfer size to 262144
The NFS options listed in the following table must be verified and set on all SVMs.
Action Command
Enable NFSv4
nfs modify -vserver <vserver-name> -v4.1
enabled
set advanced
set admin
Disable NFSv4 access control lists (ACLs)
nfs modify -vserver <vserver_name> -v4.1-acl disabled
Set NFSv4 domain ID
nfs modify -vserver <vserver_name> -v4-id-domain <domain-name>
Disable NFSv4 read delegation
nfs modify -vserver <vserver_name> -v4.1-read-delegation disabled
Disable NFSv4 write delegation
nfs modify -vserver <vserver_name> -v4.1-write-delegation disabled
Disable NFSv4 numeric ids
nfs modify -vserver <vserver_name> -v4-numeric-ids disabled
Change amount of NFSv4.x session slots
optional
set advanced
nfs modify -vserver hana -v4.x-session-num-slots <value>
set admin
Note Please note that disabling numering ids requires user management as described in SAP HANA installation preparations for NFSv4.
Note The NFSv4 domain ID must be set to the same value on all Linux servers (/etc/idmapd.conf) and SVMs, as described in SAP HANA installation preparations for NFSv4.
Note pNFS can be enabled and used.
If SAP HANA multiple-host systems with host auto-failover are being used, the failover parameters need to be adjusted within nameserver.ini as shown in the following table. Keep the default retry interval of 10 seconds within these sections.
Section within nameserver.ini Parameter Value
failover
normal_retries
9
distributed_watchdog
deactivation_retries
11
takeover_retries
9
When a volume is created, the volume must be mounted to the namespace. In this document, we assume that the junction path name is the same as the volume name. By default, the volume is exported with the default policy. The export policy can be adapted if required.