Install and maintain
Upgrade the RCF on the Broadcom BES-53248 cluster switch
Contributors netapp-yvonneo netapp-jsnyder
Upgrade the reference configuration file (RCF) on the Broadcom BES-53248 cluster switch after upgrading the EFOS software and applying any required licenses.
Before you begin
Make sure you have the following:
  • A current backup of the switch configuration.
  • A fully functioning cluster (no errors in the logs or similar issues).
  • The current RCF file, available from the Broadcom Cluster Switches page.
  • A boot configuration in the RCF that reflects the desired boot images, required if you are installing only EFOS and keeping your current RCF version. If you need to change the boot configuration to reflect the current boot images, you must do so before reapplying the RCF so that the correct version is instantiated on future reboots.
  • A console connection to the switch, required when installing the RCF from a factory-default state.
Suggested documentation
  • Consult the switch compatibility table for the supported ONTAP and RCF versions. Refer to EFOS Software download. Note that there can be command dependencies between the command syntax in the RCF and that found in versions of EFOS.
  • Refer to the appropriate software and upgrade guides available on the Broadcom site for complete documentation on the BES-53248 switch upgrade and downgrade procedures.
About the examples
The examples in this procedure use the following switch and node nomenclature:
  • The names of the two BES-53248 switches are cs1 and cs2.
  • The node names are cluster1-01, cluster1-02, cluster1-03, and cluster1-04.
  • The cluster LIF names are cluster1-01_clus1, cluster1-01_clus2, cluster1-02_clus1, cluster1-02_clus2, cluster1-03_clus1, cluster1-03_clus2, cluster1-04_clus1, and cluster1-04_clus2.
  • The cluster1::*> prompt indicates the name of the cluster.
  • The examples in this procedure use four nodes. These nodes use two 10GbE cluster interconnect ports e0a and e0b. Refer to the Hardware Universe to verify the correct cluster ports on your platforms.
Note The command outputs might vary depending on different releases of ONTAP.
About this task
The procedure requires the use of both ONTAP commands and Broadcom switch commands; ONTAP commands are used unless otherwise indicated.
No operational inter-switch link (ISL) is needed during this procedure. This is by design because RCF version changes can affect ISL connectivity temporarily. To ensure non-disruptive cluster operations, the following procedure migrates all the cluster LIFs to the operational partner switch while performing the steps on the target switch.
Step 1: Prepare for upgrade
Using the ONTAP CLI for the following steps, prepare for the RCF upgrade by suppressing automatic case creation as needed, checking administrative and operational status on the ports, and disabling auto-revert on the cluster LIFs.
  1. If AutoSupport is enabled on this cluster, suppress automatic case creation by invoking an AutoSupport message:
    system node autosupport invoke -node * -type all -message MAINT=xh
    where x is the duration of the maintenance window in hours.
    Note The AutoSupport message notifies technical support of this maintenance task so that automatic case creation is suppressed during the maintenance window.
    The following command suppresses automatic case creation for two hours:
    system node autosupport invoke -node * -type all -message MAINT=2h
  2. Change the privilege level to advanced, entering y when prompted to continue:
    set -privilege advanced
    The advanced prompt (*>) appears.
  3. Display the cluster ports on each node that are connected to the cluster switches:
    network device-discovery show
    Show example
    cluster1::*> network device-discovery show
    Node/       Local  Discovered
    Protocol    Port   Device (LLDP: ChassisID)  Interface         Platform
    cluster1-01/cdp
                e0a    cs1                       0/2               BES-53248
                e0b    cs2                       0/2               BES-53248
    cluster1-02/cdp
                e0a    cs1                       0/1               BES-53248
                e0b    cs2                       0/1               BES-53248
    cluster1-03/cdp
                e0a    cs1                       0/4               BES-53248
                e0b    cs2                       0/4               BES-53248
    cluster1-04/cdp
                e0a    cs1                       0/3               BES-53248
                e0b    cs2                       0/3               BES-53248
    cluster1::*>
  4. Check the administrative and operational status of each cluster port.
    1. Verify that all the cluster ports are up with a healthy status:
      network port show -ipspace Cluster
      Show example
      cluster1::*> network port show -ipspace Cluster
      Node: cluster1-01
        Ignore
                                                        Speed(Mbps) Health   Health
      Port      IPspace      Broadcast Domain Link MTU  Admin/Oper  Status   Status
      e0a       Cluster      Cluster          up   9000  auto/100000 healthy false
      e0b       Cluster      Cluster          up   9000  auto/100000 healthy false
      Node: cluster1-02
        Ignore
      8 entries were displayed.
      Node: cluster1-03
         Ignore
      e0a       Cluster      Cluster          up   9000  auto/10000 healthy  false
      e0b       Cluster      Cluster          up   9000  auto/10000 healthy  false
      Node: cluster1-04
        Ignore
      cluster1::*>
    2. Verify that all the cluster interfaces (LIFs) are on the home port:
      network interface show -vserver Cluster
      Show example
      cluster1::*> network interface show -vserver Cluster
                  Logical            Status     Network           Current      Current Is
      Vserver     Interface          Admin/Oper Address/Mask      Node         Port    Home
      Cluster
                  cluster1-01_clus1  up/up     169.254.3.4/23     cluster1-01  e0a     true
                  cluster1-01_clus2  up/up     169.254.3.5/23     cluster1-01  e0b     true
                  cluster1-02_clus1  up/up     169.254.3.8/23     cluster1-02  e0a     true
                  cluster1-02_clus2  up/up     169.254.3.9/23     cluster1-02  e0b     true
                  cluster1-03_clus1  up/up     169.254.1.3/23     cluster1-03  e0a     true
                  cluster1-03_clus2  up/up     169.254.1.1/23     cluster1-03  e0b     true
                  cluster1-04_clus1  up/up     169.254.1.6/23     cluster1-04  e0a     true
                  cluster1-04_clus2  up/up     169.254.1.7/23     cluster1-04  e0b     true
  5. Verify that the cluster displays information for both cluster switches.
ONTAP 9.8 and later
Beginning with ONTAP 9.8, use the command:
system switch ethernet show -is-monitoring-enabled-operational true
cluster1::*> system switch ethernet show -is-monitoring-enabled-operational true
Switch                      Type               Address          Model
cs1                         cluster-network    10.228.143.200   BES-53248
           Serial Number: QTWCU22510008
            Is Monitored: true
                  Reason: None
        Software Version: 3.10.0.3
          Version Source: CDP/ISDP
cs2                         cluster-network    10.228.143.202   BES-53248
           Serial Number: QTWCU22510009
            Is Monitored: true
                  Reason: None
cluster1::*>
ONTAP 9.7 and earlier
For ONTAP 9.7 and earlier, use the command:
system cluster-switch show -is-monitoring-enabled-operational true
cluster1::*> system cluster-switch show -is-monitoring-enabled-operational true
            Is Monitored: true
                  Reason: None
            Is Monitored: true
                  Reason: None
cluster1::*>
  1. Disable auto-revert on the cluster LIFs.
    network interface modify -vserver Cluster -lif * -auto-revert false
Step 2: Configure ports
You use the switch CLI and the ONTAP CLI (as indicated in the following steps) for port configurations. You configure ports on the first switch (cs2) and then repeat these steps for the second switch (cs1).
  1. On switch cs2, confirm the list of ports that are connected to the nodes in the cluster.
    show isdp neighbor
  2. On switch cs2, shut down the ports connected to the cluster ports of the nodes. For example, if ports 0/1 to 0/16 are connected to ONTAP nodes:
    (cs2)> enable
    (cs2)# configure
    (cs2)(Config)# interface 0/1-0/16
    (cs2)(Interface 0/1-0/16)# shutdown
    (cs2)(Interface 0/1-0/16)# exit
    (cs2)(Config)# exit
    (cs2)#
  3. Verify that the cluster LIFs have migrated to the ports hosted on cluster switch cs1. This might take a few seconds.
    Show example
    Cluster
                cluster1-01_clus2 up/up      169.254.3.5/23     cluster1-01   e0a     false
                cluster1-02_clus2 up/up      169.254.3.9/23     cluster1-02   e0a     false
                cluster1-03_clus2 up/up      169.254.1.1/23     cluster1-03   e0a     false
                cluster1-04_clus2 up/up      169.254.1.7/23     cluster1-04   e0a     false
    cluster1::*>
  4. Verify that the cluster is healthy:
    cluster show
    Show example
    cluster1::*> cluster show
    Node                 Health  Eligibility   Epsilon
    cluster1-01          true    true          false
    cluster1-02          true    true          false
    cluster1-03          true    true          true
    cluster1-04          true    true          false
  5. If you have not already done so, save the current switch configuration by copying the output of the following command to a log file:
    show running-config
  6. Clean the configuration on switch cs2 and perform a basic setup.
    Caution When updating or applying a new RCF, you must erase the switch settings and perform basic configuration. You must be connected to the switch using the serial console to erase switch settings.
    Note Clearing the configuration does not delete licenses.
    1. SSH into the switch.
      Only proceed when all the cluster LIFs have been removed from the ports on the switch and the switch is prepared to have the configuration cleared.
    2. Enter privilege mode:
      (cs2)> *enable*
      (cs2)#
    3. Copy and paste the following commands to remove the previous RCF configuration (depending on the previous RCF version used, some commands might generate an error if a particular setting is not present):
      clear config interface 0/1-0/56
      y
      clear config interface lag 1
      y
      configure
      deleteport 1/1 all
      no policy-map CLUSTER
      no policy-map WRED_25G
      no policy-map WRED_100G
      no policy-map InShared
      no policy-map InMetroCluster
      no policy-map InCluster
      no policy-map InClusterRdma
      no class-map CLUSTER
      no class-map HA
      no class-map RDMA
      no class-map c5
      no class-map c4
      no class-map CLUSTER_RDMA
      no class-map StorageSrc
      no class-map StorageDst
      no class-map RdmaSrc
      no class-map RdmaDstA
      no classofservice dot1p-mapping
      no random-detect queue-parms 0
      no random-detect queue-parms 1
      no random-detect queue-parms 2
      no random-detect queue-parms 3
      no random-detect queue-parms 4
      no random-detect queue-parms 5
      no random-detect queue-parms 6
      no random-detect queue-parms 7
      no cos-queue min-bandwidth
      no cos-queue random-detect 0
      no cos-queue random-detect 1
      no cos-queue random-detect 2
      no cos-queue random-detect 3
      no cos-queue random-detect 4
      no cos-queue random-detect 5
      no cos-queue random-detect 6
      no cos-queue random-detect 7
      exit
      vlan database
      no vlan 17
      no vlan 18
      exit
      show running-config
    4. Save the running configuration to the startup configuration:
      write memory
      (cs2)# write memory
      This operation may take a few minutes.
      Management interfaces will not be available during this time.
      Are you sure you want to save? (y/n) y
      Config file 'startup-config' created successfully.
      Configuration Saved!
    5. Perform a reboot of the switch:
      reload
      (cs2)# reload
      Are you sure you would like to reset the system? (y/n) y
    6. Log in to the switch again using SSH to complete the RCF installation.
  7. Note the following:
    1. If additional port licenses have been installed on the switch, you must modify the RCF to configure the additional licensed ports. Refer to Activate newly licensed ports for details. However, when you upgrade to RCF 1.12 or later, the modifications are no longer needed because all interfaces are now pre-configured.
    2. Record any customizations that were made in the previous RCF and apply these to the new RCF. For example, setting port speeds or hard-coding FEC mode.
EFOS version 3.12.x and later
  1. Copy the RCF to the switch cs2 using one of the following transfer protocols: HTTP, HTTPS, FTP, SFTP, or SCP.
    This example shows SFTP being used to copy an RCF to the bootflash on switch cs2:
(cs2)# copy sftp://172.19.2.1/BES-53248_RCF_v1.9-Cluster-HA.txt nvram:reference-config
Remote Password:**
Mode........................................... SFTP
Set Server IP.................................. 172.19.2.1
Path........................................... /
Filename....................................... BES-53248_RCF_v1.9-Cluster-HA.txt
Data Type...................................... Config Script
Destination Filename........................... reference-config.scr
Management access will be blocked for the duration of the transfer
Are you sure you want to start? (y/n) y
SFTP Code transfer starting...
File transfer operation completed successfully.
  1. Verify that the script was downloaded and saved under the file name you gave it:
    script list
    (cs2)# script list
    Configuration Script Name                  Size(Bytes)  Date of Modification
    reference-config.scr                       2680         2024 05 31 21:54:22
    2 configuration script(s) found.
    2042 Kbytes free.
  2. Apply the script to the switch:
    script apply
    (cs2)# script apply reference-config.scr
    Are you sure you want to apply the configuration script? (y/n) y
    The system has unsaved changes.
    Would you like to save them now? (y/n) y
    Configuration script 'reference-config.scr' applied.
All other EFOS versions
(cs2)# copy sftp://172.19.2.1/tmp/BES-53248_RCF_v1.9-Cluster-HA.txt
nvram:script BES-53248_RCF_v1.9-Cluster-HA
Remote Password:**
Path........................................... //tmp/
Destination Filename........................... BES-53248_RCF_v1.9-Cluster-HA.scr
  1. Verify that the script was downloaded and saved to the file name you gave it:
    script list
    (cs2)# script list
    BES-53248_RCF_v1.9-Cluster-HA.scr          2241         2020 09 30 05:41:00
    1 configuration script(s) found.
    script apply
    (cs2)# script apply BES-53248_RCF_v1.9-Cluster-HA.scr
    Configuration script 'BES-53248_RCF_v1.9-Cluster-HA.scr' applied.
  1. Examine the banner output from the show clibanner command. You must read and follow these instructions to ensure the proper configuration and operation of the switch.
    show clibanner
    Show example
    (cs2)# show clibanner
    Banner Message configured :
    BES-53248 Reference Configuration File v1.9 for Cluster/HA/RDMA
    Switch   : BES-53248
    Filename : BES-53248-RCF-v1.9-Cluster.txt
    Date     : 10-26-2022
    Version  : v1.9
    Port Usage:
    Ports 01 - 16: 10/25GbE Cluster Node Ports, base config
    Ports 17 - 48: 10/25GbE Cluster Node Ports, with licenses
    Ports 49 - 54: 40/100GbE Cluster Node Ports, with licenses, added right to left
    Ports 55 - 56: 100GbE Cluster ISL Ports, base config
    NOTE:
    - The 48 SFP28/SFP+ ports are organized into 4-port groups in terms of port
    speed:
    Ports 1-4, 5-8, 9-12, 13-16, 17-20, 21-24, 25-28, 29-32, 33-36, 37-40, 41-44,
    45-48
    The port speed should be the same (10GbE or 25GbE) across all ports in a 4-port
    group
    - If additional licenses are purchased, follow the 'Additional Node Ports
    activated with Licenses' section for instructions
    - If SSH is active, it will have to be re-enabled manually after 'erase
    startup-config'
    command has been executed and the switch rebooted
  2. On the switch, verify that the additional licensed ports appear after the RCF is applied:
    show port all | exclude Detach
    Show example
    (cs2)# show port all | exclude Detach
                     Admin     Physical     Physical   Link   Link    LACP   Actor
    Intf      Type   Mode      Mode         Status     Status Trap    Mode   Timeout
    0/1              Enable    Auto                    Down   Enable  Enable long
    0/2              Enable    Auto                    Down   Enable  Enable long
    0/3              Enable    Auto                    Down   Enable  Enable long
    0/4              Enable    Auto                    Down   Enable  Enable long
    0/5              Enable    Auto                    Down   Enable  Enable long
    0/6              Enable    Auto                    Down   Enable  Enable long
    0/7              Enable    Auto                    Down   Enable  Enable long
    0/8              Enable    Auto                    Down   Enable  Enable long
    0/9              Enable    Auto                    Down   Enable  Enable long
    0/10             Enable    Auto                    Down   Enable  Enable long
    0/11             Enable    Auto                    Down   Enable  Enable long
    0/12             Enable    Auto                    Down   Enable  Enable long
    0/13             Enable    Auto                    Down   Enable  Enable long
    0/14             Enable    Auto                    Down   Enable  Enable long
    0/15             Enable    Auto                    Down   Enable  Enable long
    0/16             Enable    Auto                    Down   Enable  Enable long
    0/49             Enable    40G Full                Down   Enable  Enable long
    0/50             Enable    40G Full                Down   Enable  Enable long
    0/51             Enable    100G Full               Down   Enable  Enable long
    0/52             Enable    100G Full               Down   Enable  Enable long
    0/53             Enable    100G Full               Down   Enable  Enable long
    0/54             Enable    100G Full               Down   Enable  Enable long
    0/55             Enable    100G Full               Down   Enable  Enable long
    0/56             Enable    100G Full               Down   Enable  Enable long
  3. Verify on the switch that your changes have been made.
    show running-config
  4. Save the running configuration so that it becomes the startup configuration when you reboot the switch:
    write memory
    Show example
    (cs2)# write memory
  5. Reboot the switch and verify that the running configuration is correct.
    reload
    (cs2)# reload
    System will now restart!
  6. Save the running configuration to the startup configuration:
    write memory
    Show example
    (cs2)# write memory
  7. Verify the ports on switch cs2:
    show interfaces status all | exclude Detach
    Show example
    (cs1)# show interfaces status all | exclude Detach
                                    Link    Physical    Physical    Media       Flow
    Port       Name                 State   Mode        Status      Type        Control     VLAN
    0/16       10/25GbE Node Port   Down    Auto                                Inactive    Trunk
    0/17       10/25GbE Node Port   Down    Auto                                Inactive    Trunk
    0/18       10/25GbE Node Port   Up      25G Full    25G Full    25GBase-SR  Inactive    Trunk
    0/19       10/25GbE Node Port   Up      25G Full    25G Full    25GBase-SR  Inactive    Trunk
    0/50       40/100GbE Node Port  Down    Auto                                Inactive    Trunk
    0/51       40/100GbE Node Port  Down    Auto                                Inactive    Trunk
    0/52       40/100GbE Node Port  Down    Auto                                Inactive    Trunk
    0/53       40/100GbE Node Port  Down    Auto                                Inactive    Trunk
    0/54       40/100GbE Node Port  Down    Auto                                Inactive    Trunk
    0/55       Cluster   ISL Port   Up      Auto        100G Full   Copper      Inactive    Trunk
    0/56       Cluster   ISL Port   Up      Auto        100G Full   Copper      Inactive    Trunk
  8. Verify the health of cluster ports on the cluster.
    1. Verify that e0b ports are up and healthy across all nodes in the cluster:
      Show example
      Node: cluster1-01
        Ignore
      Node: cluster1-02
        Ignore
      Node: cluster1-03
        Ignore
      Node: cluster1-04
        Ignore
    2. Verify the switch health from the cluster:
      Show example
      cluster1::*> network device-discovery show -protocol cdp
      cluster1-01/cdp
      cluster01-2/cdp
      cluster01-3/cdp
      cluster1-04/cdp
  9. Verify that the cluster displays information for both cluster switches.
ONTAP 9.8 and later
            Is Monitored: true
                  Reason: None
            Is Monitored: true
                  Reason: None
cluster1::*>
            Is Monitored: true
                  Reason: None
            Is Monitored: true
                  Reason: None
cluster1::*>
  1. Repeat steps 1 to 19 on switch cs1.
  2. Enable auto-revert on the cluster LIFs:
    network interface modify -vserver Cluster -lif * -auto-revert true
  3. Verify that the cluster LIFs have reverted to their home port:
    For further details, refer to Revert a LIF to its home port.
Step 3: Verify the configuration
After the RCF is upgraded on both switches, verify the cluster network configuration and cluster health.
  1. On switch cs1, verify that the switch ports connected to the cluster ports are up:
    Show example
  2. Verify that the ISL between switches cs1 and cs2 is functional:
    show port-channel 1/1
    Show example
    (cs1)# show port-channel 1/1
    Local Interface................................ 1/1
    Channel Name................................... Cluster-ISL
    Link State..................................... Up
    Admin Mode..................................... Enabled
    Type........................................... Dynamic
    Port-channel Min-links......................... 1
    Load Balance Option............................ 7
    (Enhanced hashing mode)
    Mbr     Device/       Port      Port
    Ports   Timeout       Speed     Active
    0/55    actor/long    Auto      True
            partner/long
    0/56    actor/long    Auto      True
            partner/long
    Show example
    Cluster
    cluster show
    Show example
  5. Verify the connectivity of the remote cluster interfaces:
ONTAP 9.9.1 and later
You can use the network interface check cluster-connectivity command to start an accessibility check for cluster connectivity and then display the details:
network interface check cluster-connectivity start and network interface check cluster-connectivity show
cluster1::*> network interface check cluster-connectivity start
NOTE: Wait for a number of seconds before running the show command to display the details.
cluster1::*> network interface check cluster-connectivity show
                                  Source              Destination         Packet
Node   Date                       LIF                 LIF                 Loss
cluster1-01
       3/5/2022 19:21:18 -06:00   cluster1-01_clus2   cluster01-02_clus1  none
       3/5/2022 19:21:20 -06:00   cluster1-01_clus2   cluster01-02_clus2  none
cluster1-02
       3/5/2022 19:21:18 -06:00   cluster1-02_clus2   cluster1-02_clus1   none
       3/5/2022 19:21:20 -06:00   cluster1-02_clus2   cluster1-02_clus2   none
All ONTAP releases
For all ONTAP releases, you can also use the cluster ping-cluster -node <name> command to check the connectivity:
cluster1::*> cluster ping-cluster -node local
Host is cluster1-03
Getting addresses from network interface table...
Cluster cluster1-03_clus1 169.254.1.3 cluster1-03 e0a
Cluster cluster1-03_clus2 169.254.1.1 cluster1-03 e0b
Cluster cluster1-04_clus1 169.254.1.6 cluster1-04 e0a
Cluster cluster1-04_clus2 169.254.1.7 cluster1-04 e0b
Cluster cluster1-01_clus1 169.254.3.4 cluster1-01 e0a
Cluster cluster1-01_clus2 169.254.3.5 cluster1-01 e0b
Cluster cluster1-02_clus1 169.254.3.8 cluster1-02 e0a
Cluster cluster1-02_clus2 169.254.3.9 cluster1-02 e0b
Local = 169.254.1.3 169.254.1.1
Remote = 169.254.1.6 169.254.1.7 169.254.3.4 169.254.3.5 169.254.3.8
169.254.3.9
Cluster Vserver Id = 4294967293
Ping status:
Basic connectivity succeeds on 12 path(s)
Basic connectivity fails on 0 path(s)
Detected 9000 byte MTU on 12 path(s):
  Local 169.254.1.3 to Remote 169.254.1.6
  Local 169.254.1.3 to Remote 169.254.1.7
  Local 169.254.1.3 to Remote 169.254.3.4
  Local 169.254.1.3 to Remote 169.254.3.5
  Local 169.254.1.3 to Remote 169.254.3.8
  Local 169.254.1.3 to Remote 169.254.3.9
  Local 169.254.1.1 to Remote 169.254.1.6
  Local 169.254.1.1 to Remote 169.254.1.7
  Local 169.254.1.1 to Remote 169.254.3.4
  Local 169.254.1.1 to Remote 169.254.3.5
  Local 169.254.1.1 to Remote 169.254.3.8
  Local 169.254.1.1 to Remote 169.254.3.9
Larger than PMTU communication succeeds on 12 path(s)
RPC status:
6 paths up, 0 paths down (tcp check)
6 paths up, 0 paths down (udp check)
  1. Change the privilege level back to admin:
    set -privilege admin
  2. If you suppressed automatic case creation, re-enable it by invoking an AutoSupport message:
What's next?
After you've upgraded your RCF, you can enable SSH for log collection.