Migrate from a two-node switchless cluster to Cisco Nexus 3232C cluster switches
Migrate from a two-node switchless cluster to a switched cluster using Cisco Nexus 3232C cluster switches. This is a nondisruptive procedure.
Review requirements
Verify the following installations and connections:
Ports are available for node connections. The cluster switches use the Inter-Switch Link (ISL) ports e1/31-32.
You have appropriate cables for cluster connections:
The nodes with 10 GbE cluster connections require QSFP optical modules with breakout fiber cables or QSFP to SFP+ copper breakout cables.
The nodes with 40/100 GbE cluster connections require supportedQSFP/ QSFP28 optical modules with fiber cables or QSFP/QSFP28 copper direct-attach cables.
The cluster switches require the appropriate ISL cabling: 2x QSFP28 fiber or copper direct-attach cables.
The configurations are properly set up and functioning.
The two nodes must be connected and functioning in a two-node switchless cluster setting.
All cluster ports are in the up state.
The Cisco Nexus 3232C cluster switch are supported.
The existing cluster network configuration has the following:
A redundant and fully functional Nexus 3232C cluster infrastructure on both switches
The latest RCF and NX-OS versions on your switches
Management connectivity on both switches
Console access to both switches
All cluster logical interfaces (LIFs) in the up state without having been migrated
Initial customization of the switch
All ISL ports enabled and cabled
The examples in this procedure use the following switch and node nomenclature:
Nexus 3232C cluster switches, C1 and C2.
The nodes are n1 and n2.
The examples in this procedure use two nodes, each utilizing two 40 GbE cluster interconnect ports e4a and e4e. The Hardware Universe has details about the cluster ports on your platforms.
n1_clus1 is the first cluster logical interface (LIF) to be connected to cluster switch C1 for node n1.
n1_clus2 is the first cluster LIF to be connected to cluster switch C2 for node n1.
n2_clus1 is the first cluster LIF to be connected to cluster switch C1 for node n2.
n2_clus2 is the second cluster LIF to be connected to cluster switch C2 for node n2.
The number of 10 GbE and 40/100 GbE ports are defined in the reference configuration files (RCFs) available at Cisco® Cluster Network Switch Reference Configuration File Download.
The procedure requires the use of both ONTAP commands and Cisco Nexus 3000 Series Switches commands; ONTAP commands are used unless otherwise indicated. |
Step 1: Display and migrate physical and logical ports
If AutoSupport is enabled on this cluster, suppress automatic case creation by invoking an AutoSupport message:
system node autosupport invoke -node * -type all - message MAINT=xhx is the duration of the maintenance window in hours.
The AutoSupport message notifies technical support of this maintenance task so that automatic case creation is suppressed during the maintenance window.
Determine the administrative or operational status for each cluster interface:
Display the network port attributes:
network port show -role clusterShow example
cluster::*> network port show -role cluster (network port show) Node: n1 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ----- e4a Cluster Cluster up 9000 auto/40000 - e4e Cluster Cluster up 9000 auto/40000 - - Node: n2 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ----- e4a Cluster Cluster up 9000 auto/40000 - e4e Cluster Cluster up 9000 auto/40000 - 4 entries were displayed. -
Display information about the logical interfaces and their designated home nodes:
network interface show -role clusterShow example
cluster::*> network interface show -role cluster (network interface show) Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------------ ------------- ------- --- Cluster n1_clus1 up/up 10.10.0.1/24 n1 e4a true n1_clus2 up/up 10.10.0.2/24 n1 e4e true n2_clus1 up/up 10.10.0.3/24 n2 e4a true n2_clus2 up/up 10.10.0.4/24 n2 e4e true 4 entries were displayed. -
Verify that switchless cluster detection is enabled using the advanced privilege command:
network options detect-switchless-cluster show`Show example
The output in the following example shows that switchless cluster detection is enabled:
cluster::*> network options detect-switchless-cluster show Enable Switchless Cluster Detection: true
Verify that the appropriate RCFs and image are installed on the new 3232C switches and make any necessary site customizations such as adding users, passwords, and network addresses.
You must prepare both switches at this time. If you need to upgrade the RCF and image software, you must follow these steps:
Go to the Cisco Ethernet Switches page on the NetApp Support Site.
Note your switch and the required software versions in the table on that page.
Download the appropriate version of RCF.
Click CONTINUE on the Description page, accept the license agreement, and then follow the instructions on the Download page to download the RCF.
Download the appropriate version of the image software.
On Nexus 3232C switches C1 and C2, disable all node-facing ports C1 and C2, but do not disable the ISL ports e1/31-32.
For more information on Cisco commands, refer to the guides listed in the Cisco Nexus 3000 Series NX-OS Command References.
Show example
The following example shows ports 1 through 30 being disabled on Nexus 3232C cluster switches C1 and C2 using a configuration supported in RCF
NX3232_RCF_v1.0_24p10g_24p100g.txt:C1# copy running-config startup-config [] 100% Copy complete. C1# configure C1(config)# int e1/1/1-4,e1/2/1-4,e1/3/1-4,e1/4/1-4,e1/5/1-4,e1/6/1-4,e1/7-30 C1(config-if-range)# shutdown C1(config-if-range)# exit C1(config)# exit C2# copy running-config startup-config [] 100% Copy complete. C2# configure C2(config)# int e1/1/1-4,e1/2/1-4,e1/3/1-4,e1/4/1-4,e1/5/1-4,e1/6/1-4,e1/7-30 C2(config-if-range)# shutdown C2(config-if-range)# exit C2(config)# exit
Connect ports 1/31 and 1/32 on C1 to the same ports on C2 using supported cabling.
Verify that the ISL ports are operational on C1 and C2:
show port-channel summaryFor more information on Cisco commands, refer to the guides listed in the Cisco Nexus 3000 Series NX-OS Command References.
Show example
The following example shows the Cisco
show port-channel summarycommand being used to verify the ISL ports are operational on C1 and C2:C1# show port-channel summary Flags: D - Down P - Up in port-channel (members) I - Individual H - Hot-standby (LACP only) s - Suspended r - Module-removed S - Switched R - Routed U - Up (port-channel) M - Not in use. Min-links not met -------------------------------------------------------------------------------- Port- Group Channel Type Protocol Member Ports ------------------------------------------------------------------------------- 1 Po1(SU) Eth LACP Eth1/31(P) Eth1/32(P) C2# show port-channel summary Flags: D - Down P - Up in port-channel (members) I - Individual H - Hot-standby (LACP only) s - Suspended r - Module-removed S - Switched R - Routed U - Up (port-channel) M - Not in use. Min-links not met -------------------------------------------------------------------------------- Group Port- Type Protocol Member Ports Channel -------------------------------------------------------------------------------- 1 Po1(SU) Eth LACP Eth1/31(P) Eth1/32(P) -
Display the list of neighboring devices on the switch.
Show example
The following example shows the Cisco command
show cdp neighborsbeing used to display the neighboring devices on the switch:C1# show cdp neighbors Capability Codes: R - Router, T - Trans-Bridge, B - Source-Route-Bridge S - Switch, H - Host, I - IGMP, r - Repeater, V - VoIP-Phone, D - Remotely-Managed-Device, s - Supports-STP-Dispute Device-ID Local Intrfce Hldtme Capability Platform Port ID C2 Eth1/31 174 R S I s N3K-C3232C Eth1/31 C2 Eth1/32 174 R S I s N3K-C3232C Eth1/32 Total entries displayed: 2 C2# show cdp neighbors Capability Codes: R - Router, T - Trans-Bridge, B - Source-Route-Bridge S - Switch, H - Host, I - IGMP, r - Repeater, V - VoIP-Phone, D - Remotely-Managed-Device, s - Supports-STP-Dispute Device-ID Local Intrfce Hldtme Capability Platform Port ID C1 Eth1/31 178 R S I s N3K-C3232C Eth1/31 C1 Eth1/32 178 R S I s N3K-C3232C Eth1/32 Total entries displayed: 2 -
Display the cluster port connectivity on each node:
network device-discovery showShow example
The following example shows the cluster port connectivity displayed for a two-node switchless cluster configuration:
cluster::*> network device-discovery show Local Discovered Node Port Device Interface Platform ----------- ------ ------------------- ---------------- ---------------- n1 /cdp e4a n2 e4a FAS9000 e4e n2 e4e FAS9000 n2 /cdp e4a n1 e4a FAS9000 e4e n1 e4e FAS9000 -
Migrate the n1_clus1 and n2_clus1 LIFs to the physical ports of their destination nodes:
network interface migrate -vserver vserver-name -lif lif-name source-node source-node-name -destination-port destination-port-nameShow example
You must execute the command for each local node as shown in the following example:
cluster::*> network interface migrate -vserver cluster -lif n1_clus1 -source-node n1 -destination-node n1 -destination-port e4e cluster::*> network interface migrate -vserver cluster -lif n2_clus1 -source-node n2 -destination-node n2 -destination-port e4e
Step 2: Shut down the reassigned LIFs and disconnect the cables
Verify the cluster interfaces have successfully migrated:
The following example shows the "Is Home" status for the n1_clus1 and n2_clus1 LIFs has become "false" after the migration is completed:
cluster::*> network interface show -role cluster (network interface show) Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------------ ------------- ------- ---- Cluster n1_clus1 up/up 10.10.0.1/24 n1 e4e false n1_clus2 up/up 10.10.0.2/24 n1 e4e true n2_clus1 up/up 10.10.0.3/24 n2 e4e false n2_clus2 up/up 10.10.0.4/24 n2 e4e true 4 entries were displayed. -
Shut down cluster ports for the n1_clus1 and n2_clus1 LIFs, which were migrated in step 9:
network port modify -node node-name -port port-name -up-admin falseShow example
You must execute the command for each port as shown in the following example:
cluster::*> network port modify -node n1 -port e4a -up-admin false cluster::*> network port modify -node n2 -port e4a -up-admin false
Verify the connectivity of the remote cluster interfaces:
You can use the network interface check cluster-connectivity command to start an accessibility check for cluster connectivity and then display the details:
network interface check cluster-connectivity start and network interface check cluster-connectivity show
cluster1::*> network interface check cluster-connectivity start
NOTE: Wait for a number of seconds before running the show command to display the details.
cluster1::*> network interface check cluster-connectivity show
Source Destination Packet
Node Date LIF LIF Loss
n1
3/5/2022 19:21:18 -06:00 n1_clus2 n2-clus1 none
3/5/2022 19:21:20 -06:00 n1_clus2 n2_clus2 none
n2
3/5/2022 19:21:18 -06:00 n2_clus2 n1_clus1 none
3/5/2022 19:21:20 -06:00 n2_clus2 n1_clus2 none
For all ONTAP releases, you can also use the cluster ping-cluster -node <name> command to check the connectivity:
cluster1::*> cluster ping-cluster -node local
Host is n1
Getting addresses from network interface table...
Cluster n1_clus1 n1 e4a 10.10.0.1
Cluster n1_clus2 n1 e4e 10.10.0.2
Cluster n2_clus1 n2 e4a 10.10.0.3
Cluster n2_clus2 n2 e4e 10.10.0.4
Local = 10.10.0.1 10.10.0.2
Remote = 10.10.0.3 10.10.0.4
Cluster Vserver Id = 4294967293 Ping status:
Basic connectivity succeeds on 4 path(s)
Basic connectivity fails on 0 path(s) ................
Detected 9000 byte MTU on 32 path(s):
Local 10.10.0.1 to Remote 10.10.0.3
Local 10.10.0.1 to Remote 10.10.0.4
Local 10.10.0.2 to Remote 10.10.0.3
Local 10.10.0.2 to Remote 10.10.0.4
Larger than PMTU communication succeeds on 4 path(s) RPC status:
1 paths up, 0 paths down (tcp check)
1 paths up, 0 paths down (ucp check)
Step 3: Enable the cluster ports
Disconnect the cable from e4a on node n2.
You can refer to the running configuration and connect e4a to the next available 40 GbE port on C1, port 1/8, using supported cabling.
Enable all node-facing ports on C1.
Show example
The following example shows ports 1 through 30 being enabled on Nexus 3232C cluster switches C1 and C2 using the configuration supported in RCF
NX3232_RCF_v1.0_24p10g_26p100g.txt:C1# configure C1(config)# int e1/1/1-4,e1/2/1-4,e1/3/1-4,e1/4/1-4,e1/5/1-4,e1/6/1-4,e1/7-30 C1(config-if-range)# no shutdown C1(config-if-range)# exit C1(config)# exit
Enable the first cluster port, e4a, on each node:
network port modify -node node-name -port port-name -up-admin trueShow example
cluster::*> network port modify -node n1 -port e4a -up-admin true cluster::*> network port modify -node n2 -port e4a -up-admin true
Verify that the clusters are up on both nodes:
For each node, revert all of the migrated cluster interconnect LIFs:
network interface revert -vserver cluster -lif lif-nameShow example
You must revert each LIF to its home port individually as shown in the following example:
cluster::*> network interface revert -vserver cluster -lif n1_clus1 cluster::*> network interface revert -vserver cluster -lif n2_clus1
Verify that all the LIFs are now reverted to their home ports:
network interface show -role clusterThe
Is Homecolumn should display a value oftruefor all of the ports listed in theCurrent Portcolumn. If the displayed value isfalse, the port has not been reverted.Show example
cluster::*> network interface show -role cluster (network interface show) Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------------ ------------- ------- ---- Cluster n1_clus1 up/up 10.10.0.1/24 n1 e4a true n1_clus2 up/up 10.10.0.2/24 n1 e4e true n2_clus1 up/up 10.10.0.3/24 n2 e4a true n2_clus2 up/up 10.10.0.4/24 n2 e4e true 4 entries were displayed.
Step 4: Enable the reassigned LIFs
cluster::*> network device-discovery show Local Discovered Node Port Device Interface Platform ----------- ------ ------------------- ---------------- ---------------- n1 /cdp e4a C1 Ethernet1/7 N3K-C3232C e4e n2 e4e FAS9000 n2 /cdp e4a C1 Ethernet1/8 N3K-C3232C e4e n1 e4e FAS9000 -
Migrate clus2 to port e4a on the console of each node:
network interface migrate cluster -lif lif-name -source-node source-node-name -destination-node destination-node-name -destination-port destination-port-nameShow example
You must migrate each LIF to its home port individually as shown in the following example:
cluster::*> network interface migrate -vserver cluster -lif n1_clus2 -source-node n1 -destination-node n1 -destination-port e4a cluster::*> network interface migrate -vserver cluster -lif n2_clus2 -source-node n2 -destination-node n2 -destination-port e4a
Shut down cluster ports clus2 LIF on both nodes:
network port modifyShow example
The following example shows the specified ports being set to
false, shutting the ports down on both nodes:cluster::*> network port modify -node n1 -port e4e -up-admin false cluster::*> network port modify -node n2 -port e4e -up-admin false
Verify the cluster LIF status:
network interface showShow example
cluster::*> network interface show -role cluster (network interface show) Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------------ ------------- ------- ---- Cluster n1_clus1 up/up 10.10.0.1/24 n1 e4a true n1_clus2 up/up 10.10.0.2/24 n1 e4a false n2_clus1 up/up 10.10.0.3/24 n2 e4a true n2_clus2 up/up 10.10.0.4/24 n2 e4a false 4 entries were displayed. -
Disconnect the cable from e4e on node n1.
You can refer to the running configuration and connect the first 40 GbE port on switch C2 (port 1/7 in this example) to e4e on node n1, using the appropriate cabling for the Nexus 3232C switch model.
Disconnect the cable from e4e on node n2.
You can refer to the running configuration and connect e4e to the next available 40 GbE port on C2, port 1/8, using the appropriate cabling for the Nexus 3232C switch model.
Enable all node-facing ports on C2.
Show example
The following example shows ports 1 through 30 being enabled on Nexus 3132Q-V cluster switches C1 and C2 using a configuration supported in RCF
NX3232C_RCF_v1.0_24p10g_26p100g.txt:C2# configure C2(config)# int e1/1/1-4,e1/2/1-4,e1/3/1-4,e1/4/1-4,e1/5/1-4,e1/6/1-4,e1/7-30 C2(config-if-range)# no shutdown C2(config-if-range)# exit C2(config)# exit
Enable the second cluster port, e4e, on each node:
The following example shows the second cluster port e4e being brought up on each node:
cluster::*> network port modify -node n1 -port e4e -up-admin true cluster::*> *network port modify -node n2 -port e4e -up-admin true*s
network interface revertShow example
The following example shows the migrated LIFs being reverted to their home ports.
cluster::*> network interface revert -vserver Cluster -lif n1_clus2 cluster::*> network interface revert -vserver Cluster -lif n2_clus2
Verify that all of the cluster interconnect ports are now reverted to their home ports:
cluster::*> network interface show -role cluster (network interface show) Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------------ ------------- ------- ---- Cluster n1_clus1 up/up 10.10.0.1/24 n1 e4a true n1_clus2 up/up 10.10.0.2/24 n1 e4e true n2_clus1 up/up 10.10.0.3/24 n2 e4a true n2_clus2 up/up 10.10.0.4/24 n2 e4e true 4 entries were displayed. -
Verify that all of the cluster interconnect ports are in the
upstate:network port show -role cluster -
Display the cluster switch port numbers through which each cluster port is connected to each node:
cluster::*> network device-discovery show Local Discovered Node Port Device Interface Platform ----------- ------ ------------------- ---------------- ---------------- n1 /cdp e4a C1 Ethernet1/7 N3K-C3232C e4e C2 Ethernet1/7 N3K-C3232C n2 /cdp e4a C1 Ethernet1/8 N3K-C3232C e4e C2 Ethernet1/8 N3K-C3232C -
Display discovered and monitored cluster switches:
system cluster-switch showShow example
cluster::*> system cluster-switch show Switch Type Address Model --------------------------- ------------------ ---------------- --------------- C1 cluster-network 10.10.1.101 NX3232CV Serial Number: FOX000001 Is Monitored: true Reason: Software Version: Cisco Nexus Operating System (NX-OS) Software, Version 7.0(3)I6(1) Version Source: CDP C2 cluster-network 10.10.1.102 NX3232CV Serial Number: FOX000002 Is Monitored: true Reason: Software Version: Cisco Nexus Operating System (NX-OS) Software, Version 7.0(3)I6(1) Version Source: CDP 2 entries were displayed.
Verify that switchless cluster detection changed the switchless cluster option to disabled:
network options switchless-cluster show -
n1
n2
Host is n1
Ping status: