Upgrade the RCF on a Cisco Nexus 9336C-FX2 shared switch
Upgrade the reference configuration file (RCF) on a Cisco Nexus 9336C-FX2 shared switch when a newer version of the RCF is available.
Make sure you have the following:
A current backup of the switch configuration.
A fully functioning cluster (no errors in the logs or similar issues).
The current RCF.
If you are updating your RCF version, you need a boot configuration in the RCF that reflects the desired boot images.
If you need to change the boot configuration to reflect the current boot images, you must do so before reapplying the RCF so that the correct version is instantiated on future reboots.
No operational inter-switch link (ISL) is needed during this procedure. This is by design because RCF version changes can affect ISL connectivity temporarily. To ensure non-disruptive cluster operations, the following procedure migrates all of the cluster LIFs to the operational partner switch while performing the steps on the target switch. |
Before installing a new switch software version and RCFs, you must erase the switch settings and perform basic configuration. You must be connected to the switch using the serial console or have preserved basic configuration information before erasing the switch settings. |
Step 1: Prepare for the upgrade
Change the privilege level to advanced, entering y when prompted to continue:
set -privilege advancedThe advanced prompt (
*>) appears. -
Display the cluster ports on each node that are connected to the cluster switches:
network device-discovery showShow example
cluster1::*> network device-discovery show Node/ Local Discovered Protocol Port Device (LLDP: ChassisID) Interface Platform ----------- ------ ------------------------- ---------------- -------- cluster1-01/cdp e0a cs1 Ethernet1/7 N9K-C9336C e0d cs2 Ethernet1/7 N9K-C9336C cluster1-02/cdp e0a cs1 Ethernet1/8 N9K-C9336C e0d cs2 Ethernet1/8 N9K-C9336C cluster1-03/cdp e0a cs1 Ethernet1/1/1 N9K-C9336C e0b cs2 Ethernet1/1/1 N9K-C9336C cluster1-04/cdp e0a cs1 Ethernet1/1/2 N9K-C9336C e0b cs2 Ethernet1/1/2 N9K-C9336C -
Check the administrative and operational status of each cluster port, node storage port, and storage shelf port.
Verify that all the cluster ports are up with a healthy status:
network port show -ipspace ClusterShow example
cluster1::*> network port show -ipspace Cluster Node: cluster1-01 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/100000 healthy false e0d Cluster Cluster up 9000 auto/100000 healthy false Node: cluster1-02 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/100000 healthy false e0d Cluster Cluster up 9000 auto/100000 healthy false 8 entries were displayed. Node: cluster1-03 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/10000 healthy false e0b Cluster Cluster up 9000 auto/10000 healthy false Node: cluster1-04 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/10000 healthy false e0b Cluster Cluster up 9000 auto/10000 healthy false -
Verify that all the cluster interfaces (LIFs) are on the home port:
network interface show -vserver ClusterShow example
cluster1::*> network interface show -vserver Cluster Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ------------------ ---------- ----------------- ------------ ------- ---- Cluster cluster1-01_clus1 up/up 169.254.3.4/23 cluster1-01 e0a true cluster1-01_clus2 up/up 169.254.3.5/23 cluster1-01 e0d true cluster1-02_clus1 up/up 169.254.3.8/23 cluster1-02 e0a true cluster1-02_clus2 up/up 169.254.3.9/23 cluster1-02 e0d true cluster1-03_clus1 up/up 169.254.1.3/23 cluster1-03 e0a true cluster1-03_clus2 up/up 169.254.1.1/23 cluster1-03 e0b true cluster1-04_clus1 up/up 169.254.1.6/23 cluster1-04 e0a true cluster1-04_clus2 up/up 169.254.1.7/23 cluster1-04 e0b true -
Verify that all the node storage ports are up with a healthy status:
storage port show -port-type ENETShow example
cluster1::*> storage port show -port-type ENET Speed Node Port Type Mode (Gb/s) State Status ------------------ ---- ----- ------- ------ -------- ----------- cluster1-01 e5a ENET - 100 enabled online e3b ENET - 100 enabled online cluster1-02 e5a ENET - 100 enabled online e3b ENET - 100 enabled online . . -
Verify that all the storage shelf ports are up with a healthy status:
storage shelf port showShow example
cluster1::> storage shelf port show Shelf ID Module State Internal? ----- -- ------ ------------ --------- 1.4 0 A connected false 1 A connected false 2 B connected false 3 B connected false . . -
Verify that the switches are being monitored.
system switch ethernet showShow example
cluster1::*> system switch ethernet show Switch Type Address Model --------------------------- ------------------ ---------------- --------------- s1 storage-network 10.228.143.216 N9K-C9336C-FX2 Serial Number: FDOXXXXXXB Is Monitored: true Reason: None Software Version: Cisco Nexus Operating System (NX-OS) Software, Version 10.4(6) Version Source: CDP/ISDP s2 storage-network 10.228.143.219 N9K-C9336C-FX2 Serial Number: FDOXXXXXXC Is Monitored: true Reason: None Software Version: Cisco Nexus Operating System (NX-OS) Software, Version 10.6(2) Version Source: CDP/ISDP cs1 cluster-network 10.228.184.39 N9K-C9336C-FX2 Serial Number: FLMXXXXXXXJ Is Monitored: true Reason: None Software Version: Cisco Nexus Operating System (NX-OS) Software, Version 10.4(6) Version Source: CDP/ISDP cs2 cluster-network 10.228.184.40 N9K-C9336C-FX2 Serial Number: FLMXXXXXXXG Is Monitored: true Reason: None Software Version: Cisco Nexus Operating System (NX-OS) Software, Version 10.6(2) Version Source: CDP/ISDP
Disable auto-revert on the cluster LIFs.
cluster1::*> network interface modify -vserver Cluster -lif * -auto-revert false
Step 2: Configure ports
On cluster switch cs1, shut down the ports connected to the cluster ports of the nodes.
cs1(config)# interface eth1/1/1-2,eth1/7-8cs1(config-if-range)# shutdownMake sure to shutdown all connected cluster ports to avoid any network connection issues. Refer to the Knowledge Base article Node out of quorum when migrating cluster LIF during switch OS upgrade for further details. -
Verify that the cluster LIFs have failed over to the ports hosted on cluster switch cs1. This might take a few seconds.
cluster1::*> network interface show -vserver Cluster Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ----------------- ---------- ------------------ ------------- ------- ---- Cluster cluster1-01_clus1 up/up 169.254.3.4/23 cluster1-01 e0a true cluster1-01_clus2 up/up 169.254.3.5/23 cluster1-01 e0a false cluster1-02_clus1 up/up 169.254.3.8/23 cluster1-02 e0a true cluster1-02_clus2 up/up 169.254.3.9/23 cluster1-02 e0a false cluster1-03_clus1 up/up 169.254.1.3/23 cluster1-03 e0a true cluster1-03_clus2 up/up 169.254.1.1/23 cluster1-03 e0a false cluster1-04_clus1 up/up 169.254.1.6/23 cluster1-04 e0a true cluster1-04_clus2 up/up 169.254.1.7/23 cluster1-04 e0a false -
Verify that the cluster is healthy:
cluster showShow example
cluster1::*> cluster show Node Health Eligibility Epsilon -------------------- ------- ------------ ------- cluster1-01 true true false cluster1-02 true true false cluster1-03 true true true cluster1-04 true true false
If you have not already done so, save a copy of the current switch configuration by copying the output of the following command to a text file:
show running-config-
Record any custom additions between the current running-config and the RCF file in use (such as an SNMP configuration for your organization).
For NX-OS 10.2 and later, use the
show diff running-configcommand to compare with the saved RCF file in the bootflash. Otherwise, use a third party diff or compare tool.
Save basic configuration details to the
write_erase.cfgfile on the bootflash.cs1# show run | i "username admin password" > bootflash:write_erase.cfgcs1# show run | section "vrf context management" >> bootflash:write_erase.cfgcs1# show run | section "interface mgmt0" >> bootflash:write_erase.cfgcs1# show run | section "switchname" >> bootflash:write_erase.cfg -
For RCF version 1.12 and later, run the following commands:
cs1# echo "hardware access-list tcam region ing-racl 1024" >> bootflash:write_erase.cfgcs1# echo "hardware access-list tcam region egr-racl 1024" >> bootflash:write_erase.cfgcs1# echo "hardware access-list tcam region ing-l2-qos 1280" >> bootflash:write_erase.cfgRefer to the Knowledge Base article How to clear configuration on a Cisco interconnect switch while retaining remote connectivity for further details.
Verify that the
write_erase.cfgfile is populated as expected:show file bootflash:write_erase.cfg -
Issue the write erase command to erase the current saved configuration:
cs1# write eraseWarning: This command will erase the startup-configuration.Do you wish to proceed anyway? (y/n) [n] y -
Copy the previously saved basic configuration into the startup configuration.
cs1# copy bootflash:write_erase.cfg startup-config -
Perform a reboot of the switch:
switch# reloadThis command will reboot the system. (y/n)? [n] y -
After the management IP address is reachable again, log in to the switch through SSH.
You might need to update host file entries related to the SSH keys.
Copy the RCF to the bootflash of switch cs1 using one of the following transfer protocols: FTP, TFTP, SFTP, or SCP.
For more information on Cisco commands, refer to the appropriate guide in the Cisco Nexus 9000 Series NX-OS Command Reference.
Show example
This example shows TFTP being used to copy an RCF to the bootflash on switch cs1:
cs1# copy tftp: bootflash: vrf management Enter source filename: Nexus_9336C_RCF_v1.6-Cluster-HA-Breakout.txt Enter hostname for the tftp server: 172.22.201.50 Trying to connect to tftp server......Connection to Server Established. TFTP get operation was successful Copy complete, now saving to disk (please wait)...
Apply the RCF previously downloaded to the bootflash.
Show example
This example shows the RCF file
Nexus_9336C_RCF_v1.6-Cluster-HA-Breakout.txtbeing installed on switch cs1:cs1# copy Nexus_9336C_RCF_v1.6-Cluster-HA-Breakout.txt running-config echo-commands
Examine the banner output from the
show banner motdcommand. You must read and follow these instructions to ensure the proper configuration and operation of the switch.Show example
cs1# show banner motd ****************************************************************************** * NetApp Reference Configuration File (RCF) * * Switch : Nexus N9K-C9336C-FX2 * Filename : Nexus_9336C_RCF_v1.6-Cluster-HA-Breakout.txt * Date : 10-23-2020 * Version : v1.6 * * Port Usage: * Ports 1- 3: Breakout mode (4x10G) Intra-Cluster Ports, int e1/1/1-4, e1/2/1-4 , e1/3/1-4 * Ports 4- 6: Breakout mode (4x25G) Intra-Cluster/HA Ports, int e1/4/1-4, e1/5/ 1-4, e1/6/1-4 * Ports 7-34: 40/100GbE Intra-Cluster/HA Ports, int e1/7-34 * Ports 35-36: Intra-Cluster ISL Ports, int e1/35-36 * * Dynamic breakout commands: * 10G: interface breakout module 1 port <range> map 10g-4x * 25G: interface breakout module 1 port <range> map 25g-4x * * Undo breakout commands and return interfaces to 40/100G configuration in confi g mode: * no interface breakout module 1 port <range> map 10g-4x * no interface breakout module 1 port <range> map 25g-4x * interface Ethernet <interfaces taken out of breakout mode> * inherit port-profile 40-100G * priority-flow-control mode auto * service-policy input HA * exit * ******************************************************************************
Verify that the RCF file is the correct newer version:
show running-configWhen you check the output to verify you have the correct RCF, make sure that the following information is correct:
The RCF banner
The node and port settings
Customizations
The output varies according to your site configuration. Check the port settings and refer to the release notes for any changes specific to the RCF that you have installed.
Reapply any previous customizations to the switch configuration.
Refer to Review cabling and configuration considerations for details of any further changes required.
After you verify the RCF versions, custom additions, and switch settings are correct, copy the running-config file to the startup-config file.
cs1# copy running-config startup-config[] 100% Copy complete -
Reboot switch cs1. You can ignore the “cluster switch health monitor” alerts and “cluster ports down” events reported on the nodes while the switch reboots.
cs1# reloadThis command will reboot the system. (y/n)? [n] y -
Verify the health of all ports on the cluster.
Verify that cluster ports are up and healthy across all nodes in the cluster:
cluster1::*> network port show -ipspace Cluster Node: cluster1-01 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/10000 healthy false e0b Cluster Cluster up 9000 auto/10000 healthy false Node: cluster1-02 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/10000 healthy false e0b Cluster Cluster up 9000 auto/10000 healthy false Node: cluster1-03 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/100000 healthy false e0d Cluster Cluster up 9000 auto/100000 healthy false Node: cluster1-04 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/100000 healthy false e0d Cluster Cluster up 9000 auto/100000 healthy false 8 entries were displayed. -
Verify the switch health from the cluster.
network device-discovery show -protocol cdpShow example
cluster1::*> network device-discovery show -protocol cdp Node/ Local Discovered Protocol Port Device (LLDP: ChassisID) Interface Platform ----------- ------ ------------------------- ----------------- -------- cluster1-01/cdp e0a cs1 Ethernet1/7 N9K-C9336C e0d cs2 Ethernet1/7 N9K-C9336C cluster01-2/cdp e0a cs1 Ethernet1/8 N9K-C9336C e0d cs2 Ethernet1/8 N9K-C9336C cluster01-3/cdp e0a cs1 Ethernet1/1/1 N9K-C9336C e0b cs2 Ethernet1/1/1 N9K-C9336C cluster1-04/cdp e0a cs1 Ethernet1/1/2 N9K-C9336C e0b cs2 Ethernet1/1/2 N9K-C9336CYou might observe the following output on the cs1 switch console depending on the RCF version previously loaded on the switch:
2020 Nov 17 16:07:18 cs1 %$ VDC-1 %$ %STP-2-UNBLOCK_CONSIST_PORT: Unblocking port port-channel1 on VLAN0092. Port consistency restored. 2020 Nov 17 16:07:23 cs1 %$ VDC-1 %$ %STP-2-BLOCK_PVID_PEER: Blocking port-channel1 on VLAN0001. Inconsistent peer vlan. 2020 Nov 17 16:07:23 cs1 %$ VDC-1 %$ %STP-2-BLOCK_PVID_LOCAL: Blocking port-channel1 on VLAN0092. Inconsistent local vlan.
cluster1::*> cluster show Node Health Eligibility Epsilon -------------------- -------- ------------- ------- cluster1-01 true true false cluster1-02 true true false cluster1-03 true true true cluster1-04 true true false 4 entries were displayed. cluster1::*>
Repeat steps 1 to 21 on switch cs2.
Enable auto-revert on the cluster LIFs.
cluster1::*> network interface modify -vserver Cluster -lif * -auto-revert true
Step 3: Verify the cluster network configuration and cluster health
Verify that the switch ports connected to the cluster ports are up.
show interface briefShow example
cs1# show interface brief | grep up . . Eth1/1/1 1 eth access up none 10G(D) -- Eth1/1/2 1 eth access up none 10G(D) -- Eth1/7 1 eth trunk up none 100G(D) -- Eth1/8 1 eth trunk up none 100G(D) -- . .
Verify that the expected nodes are still connected:
show cdp neighborsShow example
cs1# show cdp neighbors Capability Codes: R - Router, T - Trans-Bridge, B - Source-Route-Bridge S - Switch, H - Host, I - IGMP, r - Repeater, V - VoIP-Phone, D - Remotely-Managed-Device, s - Supports-STP-Dispute Device-ID Local Intrfce Hldtme Capability Platform Port ID node1 Eth1/1 133 H FAS2980 e0a node2 Eth1/2 133 H FAS2980 e0a cs1 Eth1/35 175 R S I s N9K-C9336C Eth1/35 cs1 Eth1/36 175 R S I s N9K-C9336C Eth1/36 Total entries displayed: 4 -
Verify that the cluster nodes are in their correct cluster VLANs using the following commands:
show vlan briefshow interface trunkShow example
cs1# show vlan brief VLAN Name Status Ports ---- -------------------------------- --------- ------------------------------- 1 default active Po1, Eth1/1, Eth1/2, Eth1/3 Eth1/4, Eth1/5, Eth1/6, Eth1/7 Eth1/8, Eth1/35, Eth1/36 Eth1/9/1, Eth1/9/2, Eth1/9/3 Eth1/9/4, Eth1/10/1, Eth1/10/2 Eth1/10/3, Eth1/10/4 17 VLAN0017 active Eth1/1, Eth1/2, Eth1/3, Eth1/4 Eth1/5, Eth1/6, Eth1/7, Eth1/8 Eth1/9/1, Eth1/9/2, Eth1/9/3 Eth1/9/4, Eth1/10/1, Eth1/10/2 Eth1/10/3, Eth1/10/4 18 VLAN0018 active Eth1/1, Eth1/2, Eth1/3, Eth1/4 Eth1/5, Eth1/6, Eth1/7, Eth1/8 Eth1/9/1, Eth1/9/2, Eth1/9/3 Eth1/9/4, Eth1/10/1, Eth1/10/2 Eth1/10/3, Eth1/10/4 31 VLAN0031 active Eth1/11, Eth1/12, Eth1/13 Eth1/14, Eth1/15, Eth1/16 Eth1/17, Eth1/18, Eth1/19 Eth1/20, Eth1/21, Eth1/22 32 VLAN0032 active Eth1/23, Eth1/24, Eth1/25 Eth1/26, Eth1/27, Eth1/28 Eth1/29, Eth1/30, Eth1/31 Eth1/32, Eth1/33, Eth1/34 33 VLAN0033 active Eth1/11, Eth1/12, Eth1/13 Eth1/14, Eth1/15, Eth1/16 Eth1/17, Eth1/18, Eth1/19 Eth1/20, Eth1/21, Eth1/22 34 VLAN0034 active Eth1/23, Eth1/24, Eth1/25 Eth1/26, Eth1/27, Eth1/28 Eth1/29, Eth1/30, Eth1/31 Eth1/32, Eth1/33, Eth1/34 cs1# show interface trunk ----------------------------------------------------- Port Native Status Port Vlan Channel ----------------------------------------------------- Eth1/1 1 trunking -- Eth1/2 1 trunking -- Eth1/3 1 trunking -- Eth1/4 1 trunking -- Eth1/5 1 trunking -- Eth1/6 1 trunking -- Eth1/7 1 trunking -- Eth1/8 1 trunking -- Eth1/9/1 1 trunking -- Eth1/9/2 1 trunking -- Eth1/9/3 1 trunking -- Eth1/9/4 1 trunking -- Eth1/10/1 1 trunking -- Eth1/10/2 1 trunking -- Eth1/10/3 1 trunking -- Eth1/10/4 1 trunking -- Eth1/11 33 trunking -- Eth1/12 33 trunking -- Eth1/13 33 trunking -- Eth1/14 33 trunking -- Eth1/15 33 trunking -- Eth1/16 33 trunking -- Eth1/17 33 trunking -- Eth1/18 33 trunking -- Eth1/19 33 trunking -- Eth1/20 33 trunking -- Eth1/21 33 trunking -- Eth1/22 33 trunking -- Eth1/23 34 trunking -- Eth1/24 34 trunking -- Eth1/25 34 trunking -- Eth1/26 34 trunking -- Eth1/27 34 trunking -- Eth1/28 34 trunking -- Eth1/29 34 trunking -- Eth1/30 34 trunking -- Eth1/31 34 trunking -- Eth1/32 34 trunking -- Eth1/33 34 trunking -- Eth1/34 34 trunking -- Eth1/35 1 trnk-bndl Po1 Eth1/36 1 trnk-bndl Po1 Po1 1 trunking -- ------------------------------------------------------ Port Vlans Allowed on Trunk ------------------------------------------------------ Eth1/1 1,17-18 Eth1/2 1,17-18 Eth1/3 1,17-18 Eth1/4 1,17-18 Eth1/5 1,17-18 Eth1/6 1,17-18 Eth1/7 1,17-18 Eth1/8 1,17-18 Eth1/9/1 1,17-18 Eth1/9/2 1,17-18 Eth1/9/3 1,17-18 Eth1/9/4 1,17-18 Eth1/10/1 1,17-18 Eth1/10/2 1,17-18 Eth1/10/3 1,17-18 Eth1/10/4 1,17-18 Eth1/11 31,33 Eth1/12 31,33 Eth1/13 31,33 Eth1/14 31,33 Eth1/15 31,33 Eth1/16 31,33 Eth1/17 31,33 Eth1/18 31,33 Eth1/19 31,33 Eth1/20 31,33 Eth1/21 31,33 Eth1/22 31,33 Eth1/23 32,34 Eth1/24 32,34 Eth1/25 32,34 Eth1/26 32,34 Eth1/27 32,34 Eth1/28 32,34 Eth1/29 32,34 Eth1/30 32,34 Eth1/31 32,34 Eth1/32 32,34 Eth1/33 32,34 Eth1/34 32,34 Eth1/35 1 Eth1/36 1 Po1 1 .. .. .. .. ..For specific port and VLAN usage details, refer to the banner and important notes section in your RCF. -
Verify that the ISL between cs1 and cs2 is functional:
show port-channel summaryShow example
cs1# show port-channel summary Flags: D - Down P - Up in port-channel (members) I - Individual H - Hot-standby (LACP only) s - Suspended r - Module-removed b - BFD Session Wait S - Switched R - Routed U - Up (port-channel) p - Up in delay-lacp mode (member) M - Not in use. Min-links not met -------------------------------------------------------------------------------- Group Port- Type Protocol Member Ports Channel -------------------------------------------------------------------------------- 1 Po1(SU) Eth LACP Eth1/35(P) Eth1/36(P) cs1# -
Verify that the cluster LIFs have reverted to their home port:
cluster1::*> network interface show -vserver Cluster Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ------------------ ---------- ------------------ ------------------- ------- ---- Cluster cluster1-01_clus1 up/up 169.254.3.4/23 cluster1-01 e0d true cluster1-01_clus2 up/up 169.254.3.5/23 cluster1-01 e0d true cluster1-02_clus1 up/up 169.254.3.8/23 cluster1-02 e0d true cluster1-02_clus2 up/up 169.254.3.9/23 cluster1-02 e0d true cluster1-03_clus1 up/up 169.254.1.3/23 cluster1-03 e0b true cluster1-03_clus2 up/up 169.254.1.1/23 cluster1-03 e0b true cluster1-04_clus1 up/up 169.254.1.6/23 cluster1-04 e0b true cluster1-04_clus2 up/up 169.254.1.7/23 cluster1-04 e0b trueIf any cluster LIFs have not returned to their home ports, revert them manually from the local node:
network interface revert -vserver vserver_name -lif lif_name -
cluster1::*> cluster show Node Health Eligibility Epsilon -------------------- ------- ------------- ------- cluster1-01 true true false cluster1-02 true true false cluster1-03 true true true cluster1-04 true true false
Verify the connectivity of the remote cluster interfaces:
You can use the network interface check cluster-connectivity command to start an accessibility check for cluster connectivity and then display the details:
cluster1::*> network interface check cluster-connectivity start -node *
NOTE: Wait for a number of seconds before running the show command to display the details. Check the entries matching today's date.
cluster1::*> network interface check cluster-connectivity show
Source Destination Packet
Node Date LIF LIF Loss
node1
3/5/2022 19:21:18 -06:00 cluster1-01_clus2 cluster1-02-clus1 none
3/5/2022 19:21:20 -06:00 cluster1-01_clus2 cluster1-02_clus2 none
node2
3/5/2022 19:21:18 -06:00 cluster1-02_clus2 cluster1-01_clus1 none
3/5/2022 19:21:20 -06:00 cluster1-02_clus2 cluster1-01_clus2 none
For all ONTAP releases, you can also use the cluster ping-cluster -node <name> command to check the connectivity:
cluster1::*> cluster ping-cluster -node local
Host is cluster1-03
Getting addresses from network interface table...
Cluster cluster1-03_clus1 169.254.1.3 cluster1-03 e0a
Cluster cluster1-03_clus2 169.254.1.1 cluster1-03 e0b
Cluster cluster1-04_clus1 169.254.1.6 cluster1-04 e0a
Cluster cluster1-04_clus2 169.254.1.7 cluster1-04 e0b
Cluster cluster1-01_clus1 169.254.3.4 cluster1-01 e0a
Cluster cluster1-01_clus2 169.254.3.5 cluster1-01 e0d
Cluster cluster1-02_clus1 169.254.3.8 cluster1-02 e0a
Cluster cluster1-02_clus2 169.254.3.9 cluster1-02 e0d
Local = 169.254.1.3 169.254.1.1
Remote = 169.254.1.6 169.254.1.7 169.254.3.4 169.254.3.5 169.254.3.8 169.254.3.9
Cluster Vserver Id = 4294967293
Ping status:
Basic connectivity succeeds on 12 path(s)
Basic connectivity fails on 0 path(s)
Detected 9000 byte MTU on 12 path(s):
Local 169.254.1.3 to Remote 169.254.1.6
Local 169.254.1.3 to Remote 169.254.1.7
Local 169.254.1.3 to Remote 169.254.3.4
Local 169.254.1.3 to Remote 169.254.3.5
Local 169.254.1.3 to Remote 169.254.3.8
Local 169.254.1.3 to Remote 169.254.3.9
Local 169.254.1.1 to Remote 169.254.1.6
Local 169.254.1.1 to Remote 169.254.1.7
Local 169.254.1.1 to Remote 169.254.3.4
Local 169.254.1.1 to Remote 169.254.3.5
Local 169.254.1.1 to Remote 169.254.3.8
Local 169.254.1.1 to Remote 169.254.3.9
Larger than PMTU communication succeeds on 12 path(s)
RPC status:
6 paths up, 0 paths down (tcp check)
6 paths up, 0 paths down (udp check)
After you've upgraded the RCF, you can configure switch health monitoring.