Alerts reference
This reference lists the default alerts that appear in the Grid Manager. Recommended actions are in the alert message you receive.
As required, you can create custom alert rules to fit your system management approach.
Some of the default alerts use Prometheus metrics.
Appliance alerts
Alert name Description
Appliance battery expired
The battery in the appliance's storage controller has expired.
Appliance battery failed
The battery in the appliance's storage controller has failed.
Appliance battery has insufficient learned capacity
The battery in the appliance's storage controller has insufficient learned capacity.
Appliance battery near expiration
The battery in the appliance's storage controller is nearing expiration.
Appliance battery removed
The battery in the appliance's storage controller is missing.
Appliance battery too hot
The battery in the appliance's storage controller is overheated.
Appliance BMC communication error
Communication with the baseboard management controller (BMC) has been lost.
Appliance boot device fault detected
A problem was detected with the boot device in the appliance.
Appliance cache backup device failed
A persistent cache backup device has failed.
Appliance cache backup device insufficient capacity
There is insufficient cache backup device capacity.
Appliance cache backup device write-protected
A cache backup device is write-protected.
Appliance cache memory size mismatch
The two controllers in the appliance have different cache sizes.
Appliance CMOS battery fault
A problem was detected with the CMOS battery in the appliance.
Appliance compute controller chassis temperature too high
The temperature of the compute controller in a StorageGRID appliance has exceeded a nominal threshold.
Appliance compute controller CPU temperature too high
The temperature of the CPU in the compute controller in a StorageGRID appliance has exceeded a nominal threshold.
Appliance compute controller needs attention
A hardware fault has been detected in the compute controller of a StorageGRID appliance.
Appliance compute controller power supply A has a problem
Power supply A in the compute controller has a problem.
Appliance compute controller power supply B has a problem
Power supply B in the compute controller has a problem.
Appliance compute hardware monitor service stalled
The service that monitors storage hardware status has stalled.
Appliance DAS drive exceeding limit for data written per day
An excessive amount of data is being written to a drive each day, which might void its warranty.
Appliance DAS drive fault detected
A problem was detected with a direct-attached storage (DAS) drive in the appliance.
Appliance DAS drive locator light on
The drive locator light for one or more direct-attached storage (DAS) drives in an appliance Storage Node is on.
Appliance DAS drive rebuilding
A direct-attached storage (DAS) drive is rebuilding. This is expected if it was recently replaced or removed/reinserted.
Appliance fan fault detected
A problem with a fan unit in the appliance was detected.
Appliance Fibre Channel fault detected
A Fibre Channel link problem has been detected between the appliance storage controller and compute controller
Appliance Fibre Channel HBA port failure
A Fibre Channel HBA port is failing or has failed.
Appliance flash cache drives non-optimal
The drives used for the SSD cache are non-optimal.
Appliance interconnect/battery canister removed
The interconnect/battery canister is missing.
Appliance LACP port missing
A port on a StorageGRID appliance is not participating in the LACP bond.
Appliance NIC fault detected
A problem with a network interface card (NIC) in the appliance was detected.
Appliance overall power supply degraded
The power of a StorageGRID appliance has deviated from the recommended operating voltage.
Appliance SSD critical warning
An appliance SSD is reporting a critical warning.
Appliance storage controller A failure
Storage controller A in a StorageGRID appliance has failed.
Appliance storage controller B failure
Storage controller B in a StorageGRID appliance has failed.
Appliance storage controller drive failure
One or more drives in a StorageGRID appliance has failed or is not optimal.
Appliance storage controller hardware issue
SANtricity software is reporting "Needs attention" for a component in a StorageGRID appliance.
Appliance storage controller power supply A failure
Power supply A in a StorageGRID appliance has deviated from the recommended operating voltage.
Appliance storage controller power supply B failure
Power supply B in a StorageGRID appliance has deviated from the recommended operating voltage.
Appliance storage hardware monitor service stalled
Appliance storage shelves degraded
The status of one of the components in the storage shelf for a storage appliance is degraded.
Appliance temperature exceeded
The nominal or maximum temperature for the appliance's storage controller has been exceeded.
Appliance temperature sensor removed
A temperature sensor has been removed.
Appliance UEFI secure boot error
An appliance has not been booted securely.
Disk I/O is very slow
Very slow disk I/O might be impacting grid performance.
Storage appliance fan fault detected
A problem with a fan unit in the storage controller for an appliance was detected.
Storage appliance storage connectivity degraded
There is a problem with one or more connections between the compute controller and storage controller.
Storage device inaccessible
A storage device cannot be accessed.
Audit and syslog alerts
Audit logs are being added to the in-memory queue
Node cannot send logs to the local syslog server and the in-memory queue is filling up.
External syslog server forwarding error
Node cannot forward logs to the external syslog server.
Large audit queue
The disk queue for audit messages is full. If this condition is not addressed, S3 or Swift operations might fail.
Logs are being added to the on-disk queue
Node cannot forward logs to the external syslog server and the on-disk queue is filling up.
Bucket alerts
FabricPool bucket has unsupported bucket consistency setting
A FabricPool bucket uses the Available or Strong-site consistency level, which is not supported.
FabricPool bucket has unsupported versioning setting
A FabricPool bucket has versioning or S3 Object Lock enabled, which are not supported.
Cassandra alerts
Cassandra auto-compactor error
The Cassandra auto-compactor has experienced an error.
Cassandra auto-compactor metrics out of date
The metrics that describe the Cassandra auto-compactor are out of date.
Cassandra communication error
The nodes that run the Cassandra service are having trouble communicating with each other.
Cassandra compactions overloaded
The Cassandra compaction process is overloaded.
Cassandra oversize write error
An internal StorageGRID process sent a write request to Cassandra that was too large.
Cassandra repair metrics out of date
The metrics that describe Cassandra repair jobs are out of date.
Cassandra repair progress slow
The progress of Cassandra database repairs is slow.
Cassandra repair service not available
The Cassandra repair service is not available.
Cassandra table corruption
Cassandra has detected table corruption. Cassandra automatically restarts if it detects table corruption.
Cloud Storage Pool alerts
Cloud Storage Pool connectivity error
The health check for Cloud Storage Pools detected one or more new errors.
IAM Roles Anywhere end-entity certification expiration
IAM Roles Anywhere end-entity certificate is about to expire.
Cross-grid replication alerts
Cross-grid replication permanent failure
A cross-grid replication error occurred that requires user intervention to resolve.
Cross-grid replication resources unavailable
Cross-grid replication requests are pending because a resource is unavailable.
DHCP alerts
DHCP lease expired
The DHCP lease on a network interface has expired.
DHCP lease expiring soon
The DHCP lease on a network interface is expiring soon.
DHCP server unavailable
The DHCP server is unavailable.
Debug and trace alerts
Debug performance impact
When debug mode is enabled, system performance might be negatively impacted.
Trace configuration enabled
When trace configuration is enabled, system performance might be negatively impacted.
Email and AutoSupport alerts
AutoSupport message failed to send
The most recent AutoSupport message failed to send.
Domain name resolution failure
The StorageGRID node has been unable to resolve domain names.
Email notification failure
The email notification for an alert could not be sent.
SNMP inform errors
Errors sending SNMP inform notifications to a trap destination.
SSH or console login detected
In the past 24 hours, a user has logged in with Web Console or SSH.
Erasure coding (EC) alerts
EC rebalance failure
The EC rebalance procedure has failed or has been stopped.
EC repair failure
A repair job for EC data has failed or has been stopped.
EC repair stalled
A repair job for EC data has stalled.
Erasure-coded fragment verification error
Erasure-coded fragments can no longer be verified. Corrupt fragments might not be repaired.
Expiration of certificates alerts
Admin Proxy CA certificate expiration
One or more certificates in the admin proxy server CA bundle is about to expire.
Expiration of client certificate
One or more client certificates are about to expire.
Expiration of global server certificate for S3 and Swift
The global server certificate for S3 and Swift is about to expire.
Expiration of load balancer endpoint certificate
One or more load balancer endpoint certificates are about to expire.
Expiration of server certificate for Management interface
The server certificate used for the management interface is about to expire.
External syslog CA certificate expiration
The certificate authority (CA) certificate used to sign the external syslog server certificate is about to expire.
External syslog client certificate expiration
The client certificate for an external syslog server is about to expire.
External syslog server certificate expiration
The server certificate presented by the external syslog server is about to expire.
Grid Network alerts
Grid Network MTU mismatch
The MTU setting for the Grid Network interface (eth0) differs significantly across nodes in the grid.
Grid federation alerts
Expiration of grid federation certificate
One or more grid federation certificates are about to expire.
Grid federation connection failure
The grid federation connection between the local and remote grid is not working.
High usage or high latency alerts
High Java heap use
A high percentage of Java heap space is being used.
High latency for metadata queries
The average time for Cassandra metadata queries is too long.
Identity federation alerts
Identity federation synchronization failure
Unable to synchronize federated groups and users from the identity source.
Identity federation synchronization failure for a tenant
Unable to synchronize federated groups and users from the identity source configured by a tenant.
Information lifecycle management (ILM) alerts
ILM placement unachievable
A placement instruction in an ILM rule cannot be achieved for certain objects.
ILM scan rate low
The ILM scan rate is set to less than 100 objects/second.
Key management server (KMS) alerts
KMS CA certificate expiration
The certificate authority (CA) certificate used to sign the key management server (KMS) certificate is about to expire.
KMS client certificate expiration
The client certificate for a key management server is about to expire
KMS configuration failed to load
The configuration for the key management server exists but failed to load.
KMS connectivity error
An appliance node could not connect to the key management server for its site.
KMS encryption key name not found
The configured key management server does not have an encryption key that matches the name provided.
KMS encryption key rotation failed
All appliance volumes were successfully decrypted, but one or more volumes could not rotate to the latest key.
KMS is not configured
No key management server exists for this site.
KMS key failed to decrypt an appliance volume
One or more volumes on an appliance with node encryption enabled could not be decrypted with the current KMS key.
KMS server certificate expiration
The server certificate used by the key management server (KMS) is about to expire.
KMS server connectivity failure
An appliance node could not connect to one or more servers in the key management server cluster for its site.
Load balancer alerts
Elevated zero-request load balancer connections
An elevated percentage of connections to load balancer endpoints disconnected without performing requests.
Local clock offset alerts
Local clock large time offset
The offset between local clock and Network Time Protocol (NTP) time is too large.
Low memory or low space alerts
Low audit log disk capacity
The space available for audit logs is low. If this condition is not addressed, S3 or Swift operations might fail.
Low available node memory
The amount of RAM available on a node is low.
Low free space for storage pool
The space available for storing object data in the Storage Node is low.
Low installed node memory
The amount of installed memory on a node is low.
Low metadata storage
The space available for storing object metadata is low.
Low metrics disk capacity
The space available for the metrics database is low.
Low object data storage
The space available for storing object data is low.
Low read-only watermark override
The storage volume soft read-only watermark override is less than the minimum optimized watermark for a Storage Node.
Low root disk capacity
The space available on the root disk is low.
Low system data capacity
The space available for /var/local is low. If this condition is not addressed, S3 or Swift operations might fail.
Low tmp directory free space
The space available in the /tmp directory is low.
Node or node network alerts
Admin Network receive usage
The receive usage on the Admin Network is high.
Admin Network transmit usage
The transmit usage on the Admin Network is high.
Firewall configuration failure
Failed to apply firewall configuration.
Management interface endpoints in fallback mode
All management interface endpoints have been falling back to the default ports for too long.
Node network connectivity error
Errors have occurred while transferring data between nodes.
Node network reception frame error
A high percentage of the network frames received by a node had errors.
Node not in sync with NTP server
The node is not in sync with the network time protocol (NTP) server.
Node not locked with NTP server
The node is not locked to a network time protocol (NTP) server.
Non-appliance node network down
One or more network devices are down or disconnected.
Services appliance link down on Admin Network
The appliance interface to the Admin Network (eth1) is down or disconnected.
Services appliance link down on Admin Network port 1
The Admin Network port 1 on the appliance is down or disconnected.
Services appliance link down on Client Network
The appliance interface to the Client Network (eth2) is down or disconnected.
Services appliance link down on network port 1
Services appliance link down on network port 2
Network port 2 on the appliance is down or disconnected.
Services appliance link down on network port 3
Network port 3 on the appliance is down or disconnected.
Services appliance link down on network port 4
Network port 4 on the appliance is down or disconnected.
Storage appliance link down on Admin Network
Storage appliance link down on Admin Network port 1
Storage appliance link down on Client Network
Storage appliance link down on network port 1
Storage appliance link down on network port 2
Storage appliance link down on network port 3
Storage appliance link down on network port 4
Storage Node not in desired storage state
The LDR service on a Storage Node cannot transition to the desired state because of an internal error or volume related issue
TCP connection usage
The number of TCP connections on this node is approaching the maximum number that can be tracked.
Unable to communicate with node
One or more services are unresponsive, or the node cannot be reached.
Unexpected node reboot
A node rebooted unexpectedly within the last 24 hours.
Object alerts
Object existence check failed
The object existence check job has failed.
Object existence check stalled
The object existence check job has stalled.
Objects lost
One or more objects have been lost from the grid.
S3 PUT object size too large
A client is attempting a PUT Object operation that exceeds S3 size limits.
Unidentified corrupt object detected
A file was found in replicated object storage that could not be identified as a replicated object.
Platform services alerts
Platform Services pending request capacity low
The number of Platform Services pending requests is approaching capacity.
Platform services unavailable
Too few Storage Nodes with the RSM service are running or available at a site.
Storage volume alerts
Storage volume needs attention
A storage volume is offline and needs attention.
Storage volume needs to be restored
A storage volume has been recovered and needs to be restored.
Storage volume offline
A storage volume has been offline for more than 5 minutes.
Storage volume remount attempted
A storage volume was offline and triggered an automatic remount. This could indicate a drive issue or filesystem errors.
Volume Restoration failed to start replicated data repair
Replicated data repair for a repaired volume couldn't be started automatically.
StorageGRID services alerts
nginx service using backup configuration
The configuration of the nginx service is invalid. The previous configuration is now being used.
nginx-gw service using backup configuration
The configuration of the nginx-gw service is invalid. The previous configuration is now being used.
Reboot required to disable FIPS
The security policy does not require FIPS mode, but the NetApp Cryptographic Security Module is enabled.
Reboot required to enable FIPS
The security policy requires FIPS mode, but the NetApp Cryptographic Security Module is disabled.
SSH service using backup configuration
The configuration of the SSH service is invalid. The previous configuration is now being used.
Tenant alerts
Tenant quota usage high
A high percentage of quota space is being used. This rule is disabled by default because it might cause too many notifications.
