REST API reference
Update node information
Updates node information or perform shutdown and reboot actions on a node. Use this endpoint to modify node configurations or manage node power states efficiently.
HTTP method and endpoint
PATCH /cluster/nodes/{uuid}
Introduced in
ONTAP 9.6
Usage notes
Updates the node information or performs shutdown/reboot actions on a node.
  • cluster ha modify
  • storage failover modify
  • system node modify
  • system node reboot
  • system node power off
  • system node power on
  • system service-processor network modify
  • system service-processor reboot-sp
  • system service-processor image modify
  • system service-processor network auto-configuration enable
  • system service-processor network auto-configuration disable
uuid
string
path
True
  • format: uuid
action
string
query
False
The shutdown action shuts the node down and transfers storage control to its HA group if storage failover is enabled. The reboot action reboots the node and transfers storage control to its HA group if storage failover is enabled. The giveback action transfers storage control back to the owner from its HA group. The "power_off" action shuts the node down with the assistance of the service processor. The "power_on" action restores power to the node with the assistance of the service processor.
  • enum: ["shutdown", "reboot", "giveback", "power_off", "power_on"]
shutdown_reboot_reason
string
query
False
Indicates the reason for the reboot or shutdown. This only applies when an action of reboot or shutdown is provided.
allow_data_outage
boolean
query
False
This only applies when an action of reboot or shutdown is provided. It allows storage failover to be bypassed along with any failures related to mainintaing quorum in the cluster.
  • Default value:
service_processor.firmware_image
string
query
False
Service processor image to boot with after a reboot.
  • Introduced in: 9.10
  • enum: ["primary", "backup"]
service_processor.action
string
query
False
Action used to reboot the service processor (SP).
  • enum: ["reboot"]
allow_version_mismatch
boolean
query
False
Applies only when a reboot action is provided. It allows storage failover to be bypassed along with any failures related to software version mismatch.
  • Introduced in: 9.12
  • Default value:
override_vetoes
boolean
query
False
Applies only when a giveback action is provided. If giveback is vetoed, you must check the EMS messages to determine the cause. Depending on the reason or reasons, you can decide whether you can safely override the vetoes.
  • Introduced in: 9.13
  • Default value:
return_timeout
integer
query
False
  • Default value: 0
  • Max value: 120
  • Min value: 0
Request Body
Name Type Description
cluster_interfaces
array[cluster_interfaces]
controller
controller
Controller information
date
string
The current or "wall clock" time of the node in ISO-8601 date, time, and time zone format. The ISO-8601 date and time are localized based on the ONTAP cluster's timezone setting.
  • example: 2019-04-17 15:49:26 +0000
  • format: date-time
  • readOnly: 1
  • Introduced in: 9.6
  • x-nullable: true
ha
ha
is_spares_low
boolean
Specifies whether or not the node is in spares low condition.
location
string
management_interfaces
array[management_interfaces]
membership
string
Possible values:
  • available - A node is detected on the internal cluster network and can be added to the cluster. Nodes that have a membership of "available" are not returned when a GET request is called when the cluster exists. Provide a query on the "membership" property for available to scan for nodes on the cluster network. Nodes that have a membership of "available" are returned automatically before a cluster is created.
  • joining - Joining nodes are in the process of being added to the cluster. The node might be progressing through the steps to become a member or might have failed. The job to add the node or create the cluster provides details on the current progress of the node.
  • member - Nodes that are members have successfully joined the cluster.
metrocluster
metrocluster
Metrocluster
model
string
name
string
nvram
nvram
owner
string
Owner of the node.
serial_number
string
service_processor
service_processor
state
string
State of the node:
  • up - Node is up and operational.
  • booting - Node is booting up.
  • down - Node has stopped or is dumping core.
  • taken_over - Node has been taken over by its HA partner and is not yet waiting for giveback.
  • waiting_for_giveback - Node has been taken over by its HA partner and is waiting for the HA partner to giveback disks.
  • degraded - Node has one or more critical services offline.
  • unknown - Node or its HA partner cannot be contacted and there is no information on the node's state.
storage_configuration
string
The storage configuration in the system. Possible values:
  • mixed_path
  • single_path
  • multi_path
  • quad_path
  • mixed_path_ha
  • single_path_ha
  • multi_path_ha
  • quad_path_ha
  • unknown
system_id
string
system_machine_type
string
OEM system machine type.
uptime
integer
The total time, in seconds, that the node has been up.
uuid
string
vendor_serial_number
string
OEM vendor serial number.
vm
vm
Example request
  "cluster_interfaces": [
      "name": "lif1",
  "controller": {
    "board": "System Board XXVIII",
    "cpu": {
      "count": 20,
      "firmware_release": "string",
      "processor": "string"
    "failed_fan": {
      "count": 1,
      "message": {
        "code": "111411207",
        "message": "There are no failed fans."
    "failed_power_supply": {
      "count": 1,
      "message": {
        "code": "111411208",
        "message": "There are no failed power supplies."
    "flash_cache": [
        "capacity": 1024000000000,
        "device_id": 0,
        "firmware_file": "X9170_O000Z6300NVM",
        "firmware_version": "NA05",
        "hardware_revision": "A1",
        "model": "X1970A",
        "part_number": "119-00207",
        "serial_number": "A22P5061550000187",
        "slot": "6-1",
        "state": "string"
    "frus": [
        "id": "string",
        "state": "string",
        "type": "string"
    "memory_size": 1024000000,
    "over_temperature": "string"
  "date": "2019-04-17 15:49:26 +0000",
  "ha": {
    "giveback": {
      "failure": {
        "code": 852126,
        "message": "Failed to initiate giveback. Run the \"storage failover show-giveback\" command for more information."
      "state": "failed",
      "status": [
          "aggregate": {
            "name": "aggr1",
          "error": {
            "code": "852126",
            "message": "string"
          "state": "string"
    "interconnect": {
      "adapter": "MVIA-RDMA",
      "state": "string"
    "partners": [
        "name": "node1",
    "ports": [
        "number": 0,
        "state": "active"
    "takeover": {
      "failure": {
        "code": 852130,
        "message": "Failed to initiate takeover. Run the \"storage failover show-takeover\" command for more information."
      "state": "failed"
  "location": "rack 2 row 5",
  "management_interfaces": [
      "name": "lif1",
  "membership": "string",
  "metrocluster": {
    "ports": [
        "name": "e1b"
    "type": "string"
  "model": "FAS3070",
  "name": "node-01",
  "nvram": {
    "battery_state": "string",
    "id": 0
  "owner": "Example Corp",
  "serial_number": "4048820-60-9",
  "service_processor": {
    "api_service": {
      "port": 0
    "auto_config": {
      "ipv4_subnet": "ipv4_mgmt",
      "ipv6_subnet": "ipv6_mgmt"
    "backup": {
      "state": "string",
      "version": "11.6"
    "firmware_version": "string",
    "ipv4_interface": {
      "address": "10.10.10.7",
      "gateway": "10.1.1.1",
      "netmask": "24"
    "ipv6_interface": {
      "address": "fd20:8b1e:b255:5011:10:141:4:97",
      "gateway": "fd20:8b1e:b255:5011:10::1",
      "netmask": 64
    "last_update_state": "string",
    "link_status": "string",
    "mac_address": "string",
    "primary": {
      "state": "string",
      "version": "11.6"
    "ssh_info": {
      "allowed_addresses": [
        "10.10.10.7/24"
    "state": "string",
    "type": "string"
  "state": "string",
  "storage_configuration": "string",
  "system_id": 92027651,
  "system_machine_type": "7Y56-CTOWW1",
  "uptime": 300536,
  "uuid": "4ea7a442-86d1-11e0-ae1c-123478563412",
  "vendor_serial_number": 791603000068,
  "vm": {
    "provider_type": "string"
Status: 202, Accepted
job
job_link
  "job": {
    "uuid": "string"
Status: Default
ONTAP Error Response Codes
Error Code Description
852046
HA partner node
852115
The reboot/shutdown is prevented because LIFs cannot be moved away from the node
3604514
A reboot or shutdown request is already in progress.
3604515
Reboot or shutdown of all nodes results in data service failure and client disruption for the entire cluster. Use "allow-data-outage=true" to bypass this check.
9240606
The reboot/shutdown is prevented due to quorum warnings.
string
node_setup_ip
The IP configuration for cluster setup.
address
string
IPv4 or IPv6 address
cluster_interface
The cluster network IP address of the node to be added.
ip
IP information
cluster_interfaces
Network interface
ip
ip
IP information
name
string
The name of the interface. If only the name is provided, the SVM scope must be provided by the object this object is embedded in.
uuid
string
The UUID that uniquely identifies the interface.
cpu
CPU information.
count
integer
Number of CPUs on the node.
firmware_release
string
Firmware release number. Defined by the CPU manufacturer.
processor
string
CPU type on the node.
message
code
string
Error code describing the current condition of chassis fans.
message
string
Message describing the current condition of chassis fans. It is only of use when failed_fan.count is not zero.
failed_fan
count
integer
Specifies a count of the number of chassis fans that are not operating within the recommended RPM range.
message
message
message
code
string
Error code describing the current condition of power supply.
message
string
Message describing the state of any power supplies that are currently degraded. It is only of use when failed_power_supply.count is not zero.
failed_power_supply
count
integer
Number of failed power supply units.
message
message
flash_cache
capacity
integer
Size in bytes
device_id
integer
firmware_file
string
firmware_version
string
hardware_revision
string
model
string
part_number
string
serial_number
string
slot
string
state
string
frus
id
string
state
string
type
string
controller
board
string
Type of the system board. This is defined by vendor.
cpu
cpu
CPU information.
failed_fan
failed_fan
failed_power_supply
failed_power_supply
flash_cache
array[flash_cache]
A list of Flash-Cache devices. Only returned when requested by name.
frus
array[frus]
List of FRUs on the node. Only returned when requested by name.
memory_size
integer
Memory available on the node, in bytes.
over_temperature
string
Specifies whether the hardware is currently operating outside of its recommended temperature range. The hardware shuts down if the temperature exceeds critical thresholds.
external_cache
Cache used for buffer management.
failure
Indicates the failure code and message.
code
integer
Message code
message
string
Detailed message based on the state.
aggregate
Aggregate name and UUID.
_links
_links
name
string
uuid
string
error
Indicates the failed aggregate giveback code and message.
code
string
Message code.
message
string
status
aggregate
aggregate
error
error
state
string
Giveback state of the aggregate.
Possible values include no aggregates to giveback(nothing_to_giveback), failed to disable background disk firmware update(BDFU) on source node(failed_bdfu_source),
giveback delayed as disk firmware update is in progress on source node(delayed_bdfu_source), performing veto checks(running_checks).
giveback
Represents the state of the node that is giving storage back to its HA partner.
failure
failure
state
string
status
array[status]
Giveback status of each aggregate.
interconnect
adapter
string
HA interconnect device name.
state
string
Indicates the HA interconnect status.
partners
name
string
uuid
string
ports
number
integer
HA port number
state
string
HA port state:
  • down - Logical HA link is down.
  • initialized - Logical HA link is initialized. The physical link is up, but the subnet manager hasn't started to configure the port.
  • armed - Logical HA link is armed. The physical link is up and the subnet manager started but did not yet complete configuring the port.
  • active - Logical HA link is active.
  • reserved - Logical HA link is active, but the physical link is down.
takeover
This represents the state of the node that is taking over storage from its HA partner.
failure
failure
state
string
ha
auto_giveback
boolean
Specifies whether giveback is automatically initiated when the node that owns the storage is ready.
enabled
boolean
Specifies whether or not storage failover is enabled.
giveback
giveback
interconnect
interconnect
partners
array[partners]
Nodes in this node's High Availability (HA) group.
ports
array[ports]
takeover
takeover
local
ip
string
The hardware assist IP address.
port
integer
The hardware assist port.
state
string
The hardware assist monitor status.
partner
ip
string
port
integer
state
string
status
enabled
boolean
Indicates whether hardware assist is enabled on the node.
hw_assist
The hardware assist information.
The management interface of the node to be added. The subnet mask is set based on the management interface of the cluster or the management interfaces of other nodes.
Network interface
ip
ip
IP information
name
string
uuid
string
metric
CPU performance for the nodes.
duration
string
The duration over which this sample is calculated. The time durations are represented in the ISO-8601 standard format. Samples can be calculated over the following durations:
processor_utilization
integer
Average CPU Utilization for the node
status
string
Errors associated with the sample. For example, if the aggregation of data over multiple nodes fails, then any partial errors might return "ok" on success or "error" on an internal uncategorized failure. Whenever a sample collection is missed but done at a later time, it is back filled to the previous 15 second timestamp and tagged with "backfilled_data". "inconsistent_delta_time" is encountered when the time between two collections is not the same for all nodes. Therefore, the aggregated value might be over or under inflated. "Negative_delta" is returned when an expected monotonically increasing value has decreased in value. "inconsistent_old_data" is returned when one or more nodes do not have the latest data.
timestamp
string
The timestamp of the performance data.
uuid
string
ports
name
string
metrocluster
Metrocluster
custom_vlan_capable
boolean
Indicates whether the MetroCluster over IP platform supports custom VLAN IDs.
ports
array[ports]
MetroCluster over IP ports.
type
string
The Metrocluster configuration type
nvram
battery_state
string
Specifies status of the NVRAM battery. Possible values:
  • battery_ok
  • battery_partially_discharged
  • battery_fully_discharged
  • battery_not_present
  • battery_near_end_of_life
  • battery_at_end_of_life
  • battery_unknown
  • battery_over_charged
  • battery_fully_charged
id
integer
Vendor specific NVRAM ID of the node.
api_service
Provides the properties of the service processor API service.
enabled
boolean
Indicates whether the service processor API service is enabled.
limit_access
boolean
Indicates whether the service processor API service limit access is enabled.
port
integer
Indicates the port number of service processor API service.
auto_config
Provides the properties of the service processor auto configuration.
ipv4_subnet
string
Indicates the service processor auto configuration IPv4 subnet name. To enable IPv4 auto-config give the subnet name, give the value as null or an empty string "" to disable auto-config.
ipv6_subnet
string
Indicates the service processor auto configuration IPv6 subnet name. To enable IPv6 auto-config give the subnet name, give the value as null or an empty string "" to disable auto-config.
backup
Provides the properties of the service processor backup partition.
is_current
boolean
Indicates whether the service processor is currently booted from the backup partition.
state
string
Status of the backup partition.
version
string
Firmware version of the backup partition.
ipv4_interface
Object to setup an interface along with its default router.
address
string
gateway
string
The IPv4 or IPv6 address of the default router.
netmask
string
Input as netmask length (16) or IPv4 mask (255.255.0.0). For IPv6, the default value is 64 with a valid range of 1 to 127. Output is always netmask length.
ipv6_interface
address
string
IPv6 address
gateway
string
The IPv6 address of the default router.
netmask
integer
The IPv6 netmask/prefix length. The default value is 64 with a valid range of 1 to 127.
primary
Provides the properties of the service processor primary partition.
is_current
boolean
Indicates whether the service processor is currently booted from the primary partition.
state
string
Status of the primary partition.
version
string
Firmware version of the primary partition.
ssh_info
Service processor SSH allowed IP address configuration applied across the cluster.
allowed_addresses
array[string]
Allowed IP addresses
service_processor
api_service
api_service
auto_config
auto_config
autoupdate_enabled
boolean
Indicates whether the service processor can be automatically updated from ONTAP.
  • x-ntap-readModify: true
  • x-nullable: true
backup
backup
dhcp_enabled
boolean
Set to "true" to use DHCP to configure an IPv4 interface. Do not provide values for address, netmask and gateway when set to "true".
firmware_version
string
The version of firmware installed.
ipv4_interface
ipv4_interface
ipv6_interface
ipv6_interface
is_ip_configured
boolean
Indicates whether the service processor network is configured.
last_update_state
string
Provides the "update status" of the last service processor update.
link_status
string
mac_address
string
primary
primary
ssh_info
ssh_info
state
string
type
string
snaplock
SnapLock-related properties.
compliance_clock_time
string
SnapLock compliance clock time.
statistics
Raw CPU performance for the nodes.
processor_utilization_base
integer
Base counter for CPU Utilization.
processor_utilization_raw
integer
Raw CPU Utilization for the node. This should be divided by the processor_utilization_base to calculate the percentage CPU utilization for the node.
status
string
timestamp
string
version
This returns the cluster version information. When the cluster has more than one node, the cluster version is equivalent to the lowest of generation, major, and minor versions on all nodes.
full
string
The full cluster version string.
generation
integer
The generation portion of the version.
major
integer
The major portion of the version.
minor
integer
The minor portion of the version.
vm
provider_type
string
Cloud provider where the VM is hosted.
node
Complete node information
cluster_interfaces
controller
controller
date
string
  • format: date-time
  • readOnly: 1
  • x-nullable: true
ha
ha
is_spares_low
boolean
location
string
membership
string
Possible values:
metrocluster
metrocluster
Metrocluster
model
string
name
string
nvram
nvram
owner
string
Owner of the node.
serial_number
string
service_processor
service_processor
state
string
State of the node:
string
  • mixed_path
  • single_path
  • multi_path
  • quad_path
  • mixed_path_ha
  • single_path_ha
  • multi_path_ha
  • quad_path_ha
  • unknown
system_id
string
system_machine_type
string
uptime
integer
uuid
string
string
vm
vm
uuid
string
The UUID of the asynchronous job that is triggered by a POST, PATCH, or DELETE operation.
code
string
Argument code
message
string
Message argument
error
arguments
array[error_arguments]
Message arguments
code
string
Error code
message
string
Error message
target