Install and maintain
Migrate from CN1610 cluster switches to Cisco Nexus 3132Q-V cluster switches
Contributors netapp-yvonneo netapp-jolieg
Follow this procedure to replace the existing CN1610 cluster switches with Cisco Nexus 3132Q-V cluster switches.
Review requirements
Review the NetApp CN1610 requirements requirements in Requirements for replacing Cisco Nexus 3132Q-V cluster switches.
For more information, see:
Replace the switch
Switch and node nomenclature
The examples in this procedure use the following switch and node nomenclature:
  • The command outputs might vary depending on different releases of ONTAP software.
  • The CN1610 switches to be replaced are CL1 and CL2.
  • The Nexus 3132Q-V switches to replace the CN1610 switches are C1 and C2.
  • n1_clus1 is the first cluster logical interface (LIF) that is connected to cluster switch 1 (CL1 or C1) for node n1.
  • n1_clus2 is the first cluster LIF that is connected to cluster switch 2 (CL2 or C2) for node n1.
  • n1_clus3 is the second LIF that is connected to cluster switch 2 (CL2 or C2) for node n1.
  • n1_clus4 is the second LIF that is connected to cluster switch 1 (CL1 or C1) for node n1.
  • The nodes are n1, n2, n3, and n4.
  • The number of 10 GbE and 40 GbE ports are defined in the reference configuration files (RCFs) available at Cisco® Cluster Network Switch Reference Configuration File Download.
About the examples
The examples in this procedure use four nodes:
  • Two nodes use four 10 GbE cluster interconnect ports: e0a, e0b, e0c, and e0d.
  • The other two nodes use two 40 GbE cluster interconnect fiber cables: e4a and e4e.
The Hardware Universe has information about the cluster fiber cables on your platforms.
About this task
This procedure covers the following scenario:
  • The cluster starts with two nodes connected to two CN1610 cluster switches.
  • Cluster switch CL2 to be replaced by C2
    • Traffic on all cluster ports and LIFs on all nodes connected to CL2 are migrated onto the first cluster ports and LIFs connected to CL1.
    • Disconnect cabling from all cluster ports on all nodes connected to CL2, and then use supported breakout cabling to reconnect the ports to new cluster switch C2.
    • Disconnect cabling between ISL ports CL1 and CL2, and then use supported breakout cabling to reconnect the ports from CL1 to C2.
    • Traffic on all cluster ports and LIFs connected to C2 on all nodes is reverted.
  • Cluster switch CL1 to be replaced by C1
    • Traffic on all cluster ports and LIFs on all nodes connected to CL1 are migrated onto the second cluster ports and LIFs connected to C2.
    • Disconnect cabling from all cluster ports on all nodes connected to CL1, and then use supported breakout cabling to reconnect the ports to new cluster switch C1.
    • Disconnect cabling between ISL ports CL1 and C2, and then use supported breakout cabling to reconnect the ports from C1 to C2.
    • Traffic on all migrated cluster ports and LIFs connected to C1 on all nodes is reverted.
Note The procedure requires the use of both ONTAP commands and Cisco Nexus 3000 Series Switches commands; ONTAP commands are used unless otherwise indicated.
Step 1: Prepare for replacement
  1. If AutoSupport is enabled on this cluster, suppress automatic case creation by invoking an AutoSupport message:
    system node autosupport invoke -node * -type all - message MAINT=xh
    x is the duration of the maintenance window in hours.
    Note The AutoSupport message notifies technical support of this maintenance task so that automatic case creation is suppressed during the maintenance window.
  2. Display information about the devices in your configuration:
    network device-discovery show
    Show example
    The following example displays how many cluster interconnect interfaces have been configured in each node for each cluster interconnect switch:
    cluster::> network device-discovery show
           Local  Discovered
    Node   Port   Device       Interface   Platform
    n1     /cdp
            e0a   CL1          0/1         CN1610
            e0b   CL2          0/1         CN1610
            e0c   CL2          0/2         CN1610
            e0d   CL1          0/2         CN1610
    n2     /cdp
            e0a   CL1          0/3         CN1610
            e0b   CL2          0/3         CN1610
            e0c   CL2          0/4         CN1610
            e0d   CL1          0/4         CN1610
    8 entries were displayed.
  3. Determine the administrative or operational status for each cluster interface.
    1. Display the cluster network port attributes:
      network port show
      Show example
      The following example displays the network port attributes on a system:
      cluster::*> network port show -role Cluster
             (network port show)
      Node: n1
                      Broadcast              Speed (Mbps) Health Ignore
      Port  IPspace   Domain     Link  MTU   Admin/Open   Status Health Status
      e0a   cluster   cluster    up    9000  auto/10000     -        -
      e0b   cluster   cluster    up    9000  auto/10000     -        -
      e0c   cluster   cluster    up    9000  auto/10000     -        -
      e0d   cluster   cluster    up    9000  auto/10000     -        -
      Node: n2
    2. Display information about the logical interfaces: + network interface show
      Show example
      The following example displays the general information about all of the LIFs on your system:
      cluster::*> network interface show -role Cluster
             (network interface show)
               Logical    Status      Network        Current  Current  Is
      Vserver  Interface  Admin/Oper  Address/Mask   Node     Port     Home
      Cluster
               n1_clus1   up/up       10.10.0.1/24   n1       e0a      true
               n1_clus2   up/up       10.10.0.2/24   n1       e0b      true
               n1_clus3   up/up       10.10.0.3/24   n1       e0c      true
               n1_clus4   up/up       10.10.0.4/24   n1       e0d      true
               n2_clus1   up/up       10.10.0.5/24   n2       e0a      true
               n2_clus2   up/up       10.10.0.6/24   n2       e0b      true
               n2_clus3   up/up       10.10.0.7/24   n2       e0c      true
               n2_clus4   up/up       10.10.0.8/24   n2       e0d      true
    3. Display information about the discovered cluster switches:
      system cluster-switch show
      Show example
      The following example displays the cluster switches that are known to the cluster, along with their management IP addresses:
      cluster::> system cluster-switch show
      Switch                        Type             Address       Model
      CL1                           cluster-network  10.10.1.101   CN1610
           Serial Number: 01234567
            Is Monitored: true
                  Reason:
        Software Version: 1.2.0.7
          Version Source: ISDP
      CL2                           cluster-network  10.10.1.102   CN1610
           Serial Number: 01234568
            Is Monitored: true
                  Reason:
      2 entries were displayed.
  4. Set the -auto-revert parameter to false on cluster LIFs clus1 and clus4 on both nodes:
    network interface modify
    Show example
    cluster::*> network interface modify -vserver node1 -lif clus1 -auto-revert false
    cluster::*> network interface modify -vserver node1 -lif clus4 -auto-revert false
    cluster::*> network interface modify -vserver node2 -lif clus1 -auto-revert false
    cluster::*> network interface modify -vserver node2 -lif clus4 -auto-revert false
  5. Verify that the appropriate RCF and image are installed on the new 3132Q-V switches as necessary for your requirements, and make any essential site customizations, such as users and passwords, network addresses, and so on.
    You must prepare both switches at this time. If you need to upgrade the RCF and image, follow these steps:
    1. Refer to Cisco Ethernet Switches on the NetApp Support Site.
    2. Note your switch and the required software versions in the table on that page.
    3. Download the appropriate version of the RCF.
    4. Click CONTINUE on the Description page, accept the license agreement, and then follow the instructions on the Download page to download the RCF.
    5. Download the appropriate version of the image software.
  6. Migrate the LIFs associated with the second CN1610 switch to be replaced:
    network interface migrate
    Note
    You must migrate the cluster LIFs from a connection to the node, either through the service processor or node management interface, which owns the cluster LIF being migrated.
    Show example
    The following example shows n1 and n2, but LIF migration must be done on all the nodes:
    cluster::*> network interface migrate -vserver Cluster -lif n1_clus2 -destination-node  n1  -destination-port  e0a
    cluster::*> network interface migrate -vserver Cluster -lif n1_clus3 -destination-node  n1  -destination-port  e0d
    cluster::*> network interface migrate -vserver Cluster -lif n2_clus2 -destination-node  n2  -destination-port  e0a
    cluster::*> network interface migrate -vserver Cluster -lif n2_clus3 -destination-node  n2  -destination-port  e0d
  7. Verify the cluster's health:
    Show example
    The following example shows the result of the previous network interface migrate command:
    Cluster
             n1_clus2   up/up       10.10.0.2/24    n1       e0a      false
             n1_clus3   up/up       10.10.0.3/24    n1       e0d      false
             n2_clus2   up/up       10.10.0.6/24    n2       e0a      false
             n2_clus3   up/up       10.10.0.7/24    n2       e0d      false
  8. Shut down the cluster interconnect ports that are physically connected to switch CL2:
    network port modify
    Show example
    The following commands shut down the specified ports on n1 and n2, but the ports must be shut down on all nodes:
    cluster::*> network port modify -node n1 -port e0b -up-admin false
    cluster::*> network port modify -node n1 -port e0c -up-admin false
    cluster::*> network port modify -node n2 -port e0b -up-admin false
    cluster::*> network port modify -node n2 -port e0c -up-admin false
  9. Verify the connectivity of the remote cluster interfaces:
ONTAP 9.9.1 and later
You can use the network interface check cluster-connectivity command to start an accessibility check for cluster connectivity and then display the details:
network interface check cluster-connectivity start and network interface check cluster-connectivity show
cluster1::*> network interface check cluster-connectivity start
NOTE: Wait for a number of seconds before running the show command to display the details.
cluster1::*> network interface check cluster-connectivity show
                                  Source      Destination   Packet
Node   Date                       LIF         LIF           Loss
n1
       3/5/2022 19:21:18 -06:00   n1_clus2   n1_clus1       none
       3/5/2022 19:21:20 -06:00   n1_clus2   n2_clus2       none
n2
       3/5/2022 19:21:18 -06:00   n2_clus2   n1_clus1       none
       3/5/2022 19:21:20 -06:00   n2_clus2   n1_clus2       none
All ONTAP releases
For all ONTAP releases, you can also use the cluster ping-cluster -node <name> command to check the connectivity:
cluster::*> cluster ping-cluster -node n1
Host is n1
Getting addresses from network interface table...
Cluster n1_clus1 n1       e0a    10.10.0.1
Cluster n1_clus2 n1       e0b    10.10.0.2
Cluster n1_clus3 n1       e0c    10.10.0.3
Cluster n1_clus4 n1       e0d    10.10.0.4
Cluster n2_clus1 n2       e0a    10.10.0.5
Cluster n2_clus2 n2       e0b    10.10.0.6
Cluster n2_clus3 n2       e0c    10.10.0.7
Cluster n2_clus4 n2       e0d    10.10.0.8
Local = 10.10.0.1 10.10.0.2 10.10.0.3 10.10.0.4
Remote = 10.10.0.5 10.10.0.6 10.10.0.7 10.10.0.8
Cluster Vserver Id = 4294967293
Ping status:....
Basic connectivity succeeds on 16 path(s)
Basic connectivity fails on 0 path(s)
Detected 1500 byte MTU on 16 path(s):
    Local 10.10.0.1 to Remote 10.10.0.5
    Local 10.10.0.1 to Remote 10.10.0.6
    Local 10.10.0.1 to Remote 10.10.0.7
    Local 10.10.0.1 to Remote 10.10.0.8
    Local 10.10.0.2 to Remote 10.10.0.5
    Local 10.10.0.2 to Remote 10.10.0.6
    Local 10.10.0.2 to Remote 10.10.0.7
    Local 10.10.0.2 to Remote 10.10.0.8
    Local 10.10.0.3 to Remote 10.10.0.5
    Local 10.10.0.3 to Remote 10.10.0.6
    Local 10.10.0.3 to Remote 10.10.0.7
    Local 10.10.0.3 to Remote 10.10.0.8
    Local 10.10.0.4 to Remote 10.10.0.5
    Local 10.10.0.4 to Remote 10.10.0.6
    Local 10.10.0.4 to Remote 10.10.0.7
    Local 10.10.0.4 to Remote 10.10.0.8
Larger than PMTU communication succeeds on 16 path(s)
RPC status:
4 paths up, 0 paths down (tcp check)
4 paths up, 0 paths down (udp check)
  1. Shut down the ISL ports 13 through 16 on the active CN1610 switch CL1:
    shutdown
    Show example
    The following example shows how to shut down ISL ports 13 through 16 on the CN1610 switch CL1:
    (CL1)# configure
    (CL1)(Config)# interface 0/13-0/16
    (CL1)(Interface 0/13-0/16)# shutdown
    (CL1)(Interface 0/13-0/16)# exit
    (CL1)(Config)# exit
    (CL1)#
  2. Build a temporary ISL between CL1 and C2:
    Show example
    The following example builds a temporary ISL between CL1 (ports 13-16) and C2 (ports e1/24/1-4):
    C2# configure
    C2(config)# interface port-channel 2
    C2(config-if)# switchport mode trunk
    C2(config-if)# spanning-tree port type network
    C2(config-if)# mtu 9216
    C2(config-if)# interface breakout module 1 port 24 map 10g-4x
    C2(config)# interface e1/24/1-4
    C2(config-if-range)# switchport mode trunk
    C2(config-if-range)# mtu 9216
    C2(config-if-range)# channel-group 2 mode active
    C2(config-if-range)# exit
    C2(config-if)# exit
Step 2: Configure ports
  1. On all nodes, remove the cables that are attached to the CN1610 switch CL2.
    With supported cabling, you must reconnect the disconnected ports on all of the nodes to the Nexus 3132Q-V switch C2.
  2. Remove four ISL cables from ports 13 to 16 on the CN1610 switch CL1.
    You must attach appropriate Cisco QSFP to SFP+ breakout cables connecting port 1/24 on the new Cisco 3132Q-V switch C2, to ports 13 to 16 on existing CN1610 switch CL1.
    Note When reconnecting any cables to the new Cisco 3132Q-V switch, you must use either optical fiber or Cisco twinax cables.
  3. To make the ISL dynamic, configure the ISL interface 3/1 on the active CN1610 switch to disable the static mode: no port-channel static
    This configuration matches with the ISL configuration on the 3132Q-V switch C2 when the ISLs are brought up on both switches in step 11
    Show example
    The following example shows the configuration of the ISL interface 3/1 using the no port-channel static command to make the ISL dynamic:
    (CL1)# configure
    (CL1)(Config)# interface 3/1
    (CL1)(Interface 3/1)# no port-channel static
    (CL1)(Interface 3/1)# exit
    (CL1)(Config)# exit
    (CL1)#
  4. Bring up ISLs 13 through 16 on the active CN1610 switch CL1.
    Show example
    The following example illustrates the process of bringing up ISL ports 13 through 16 on the port-channel interface 3/1:
    (CL1)# configure
    (CL1)(Config)# interface 0/13-0/16,3/1
    (CL1)(Interface 0/13-0/16,3/1)# no shutdown
    (CL1)(Interface 0/13-0/16,3/1)# exit
    (CL1)(Config)# exit
    (CL1)#
  5. Verify that the ISLs are up on the CN1610 switch CL1:
    show port-channel
    The "Link State" should be Up, "Type" should be Dynamic, and the "Port Active" column should be True for ports 0/13 to 0/16:
    Show example
    (CL1)# show port-channel 3/1
    Local Interface................................ 3/1
    Channel Name................................... ISL-LAG
    Link State..................................... Up
    Admin Mode..................................... Enabled
    Type........................................... Dynamic
    Load Balance Option............................ 7
    (Enhanced hashing mode)
    Mbr    Device/       Port        Port
    Ports  Timeout       Speed       Active
    0/13   actor/long    10 Gb Full  True
           partner/long
    0/14   actor/long    10 Gb Full  True
           partner/long
    0/15   actor/long    10 Gb Full  True
           partner/long
    0/16   actor/long    10 Gb Full  True
           partner/long
  6. Verify that the ISLs are up on the 3132Q-V switch C2:
    show port-channel summary
    Show example
    Ports Eth1/24/1 through Eth1/24/4 should indicate (P), meaning that all four ISL ports are up in the port-channel. Eth1/31 and Eth1/32 should indicate (D) as they are not connected:
    C2# show port-channel summary
    Flags:  D - Down        P - Up in port-channel (members)
            I - Individual  H - Hot-standby (LACP only)
            s - Suspended   r - Module-removed
            S - Switched    R - Routed
            U - Up (port-channel)
            M - Not in use. Min-links not met
    Group Port-       Type     Protocol  Member Ports
          Channel
    1     Po1(SU)     Eth      LACP      Eth1/31(D)   Eth1/32(D)
    2     Po2(SU)     Eth      LACP      Eth1/24/1(P) Eth1/24/2(P) Eth1/24/3(P)
                                         Eth1/24/4(P)
  7. Bring up all of the cluster interconnect ports that are connected to the 3132Q-V switch C2 on all of the nodes:
    network port modify
    Show example
    The following example shows how to bring up the cluster interconnect ports connected to the 3132Q-V switch C2:
    cluster::*> network port modify -node n1 -port e0b -up-admin true
    cluster::*> network port modify -node n1 -port e0c -up-admin true
    cluster::*> network port modify -node n2 -port e0b -up-admin true
    cluster::*> network port modify -node n2 -port e0c -up-admin true
  8. Revert all of the migrated cluster interconnect LIFs that are connected to C2 on all of the nodes:
    network interface revert
    Show example
    cluster::*> network interface revert -vserver Cluster -lif n1_clus2
    cluster::*> network interface revert -vserver Cluster -lif n1_clus3
    cluster::*> network interface revert -vserver Cluster -lif n2_clus2
    cluster::*> network interface revert -vserver Cluster -lif n2_clus3
  9. Verify that all of the cluster interconnect ports are reverted to their home ports:
    Show example
    The following example shows that the LIFs on clus2 are reverted to their home ports, and shows that the LIFs are successfully reverted if the ports in the "Current Port" column have a status of true in the "Is Home" column. If the Is Home value is false, then the LIF is not reverted.
    cluster::*> network interface show -role cluster
    Cluster
  10. Verify that all of the cluster ports are connected:
    network port show
    Show example
    The following example shows the result of the previous network port modify command, verifying that all of the cluster interconnects are up:
           (network port show)
    Node: n1
    Node: n2
  11. Verify the connectivity of the remote cluster interfaces:
n1
n2
All ONTAP releases
Host is n1
Ping status:....
RPC status:
  1. On each node in the cluster, migrate the interfaces that are associated with the first CN1610 switch CL1, to be replaced:
    Show example
    The following example shows the ports or LIFs being migrated on nodes n1 and n2:
    cluster::*> network interface migrate -vserver Cluster -lif n1_clus1 -destination-node n1 -destination-port e0b
    cluster::*> network interface migrate -vserver Cluster -lif n1_clus4 -destination-node n1 -destination-port e0c
    cluster::*> network interface migrate -vserver Cluster -lif n2_clus1 -destination-node n2 -destination-port e0b
    cluster::*> network interface migrate -vserver Cluster -lif n2_clus4 -destination-node n2 -destination-port e0c
  2. Verify the cluster status:
    Show example
    The following example shows that the required cluster LIFs have been migrated to the appropriate cluster ports hosted on cluster switch C2:
    Cluster
             n1_clus1   up/up       10.10.0.1/24   n1       e0b      false
             n1_clus4   up/up       10.10.0.4/24   n1       e0c      false
             n2_clus1   up/up       10.10.0.5/24   n2       e0b      false
             n2_clus4   up/up       10.10.0.8/24   n2       e0c      false
  3. Shut down the node ports that are connected to CL1 on all of the nodes:
    network port modify
    Show example
    The following example shows how to shut down the specified ports on nodes n1 and n2:
    cluster::*> network port modify -node n1 -port e0a -up-admin false
    cluster::*> network port modify -node n1 -port e0d -up-admin false
    cluster::*> network port modify -node n2 -port e0a -up-admin false
    cluster::*> network port modify -node n2 -port e0d -up-admin false
  4. Shut down the ISL ports 24, 31, and 32 on the active 3132Q-V switch C2:
    shutdown
    Show example
    The following example shows how to shut down ISLs 24, 31, and 32 on the active 3132Q-V switch C2:
    C2# configure
    C2(config)# interface ethernet 1/24/1-4
    C2(config-if-range)# shutdown
    C2(config)# interface ethernet 1/31-32
    C2(config)# exit
    C2#
  5. Remove the cables that are attached to the CN1610 switch CL1 on all of the nodes.
    With supported cabling, you must reconnect the disconnected ports on all of the nodes to the Nexus 3132Q-V switch C1.
  6. Remove the QSFP cables from Nexus 3132Q-V C2 port e1/24.
    You must connect ports e1/31 and e1/32 on C1 to ports e1/31 and e1/32 on C2 using supported Cisco QSFP optical fiber or direct-attach cables.
  7. Restore the configuration on port 24 and remove the temporary port-channel 2 on C2, by copying the running-configuration file to the startup-configuration file.
    Show example
    The following example copies the running-configuration file to the startup-configuration file:
    C2# configure
    C2(config)# no interface breakout module 1 port 24 map 10g-4x
    C2(config)# no interface port-channel 2
    C2(config-if)# interface e1/24
    C2(config-if)# description 40GbE Node Port
    C2(config-if)# spanning-tree port type edge
    C2(config-if)# spanning-tree bpduguard enable
    C2(config)# exit
    C2# copy running-config startup-config
    [########################################] 100%
    Copy Complete.
  8. Bring up ISL ports 31 and 32 on C2, the active 3132Q-V switch:
    no shutdown
    Show example
    The following example shows how to bring up ISLs 31 and 32 on the 3132Q-V switch C2:
    C2# configure
    C2(config-if-range)# no shutdown
    C2(config)# exit
    Copy Complete.
Step 3: Verify the configuration
  1. Verify that the ISL connections are up on the 3132Q-V switch C2:
    Ports Eth1/31 and Eth1/32 should indicate (P), meaning that both the ISL ports are up in the port-channel.
    Show example
    C1# show port-channel summary
          Channel
    1     Po1(SU)     Eth      LACP      Eth1/31(P)   Eth1/32(P)
  2. Bring up all of the cluster interconnect ports connected to the new 3132Q-V switch C1 on all of the nodes:
    network port modify
    Show example
    The following example shows how to bring up all of the cluster interconnect ports connected to the new 3132Q-V switch C1:
    cluster::*> network port modify -node n1 -port e0a -up-admin true
    cluster::*> network port modify -node n1 -port e0d -up-admin true
    cluster::*> network port modify -node n2 -port e0a -up-admin true
    cluster::*> network port modify -node n2 -port e0d -up-admin true
  3. Verify the status of the cluster node port:
    network port show
    Show example
    The following example verifies that all of the cluster interconnect ports on n1 and n2 on the new 3132Q-V switch C1 are up:
           (network port show)
    Node: n1
    Node: n2
  4. Revert all of the migrated cluster interconnect LIFs that were originally connected to C1 on all of the nodes:
    Show example
    The following example shows how to revert the migrated cluster LIFs to their home ports:
    cluster::*> network interface revert -vserver Cluster -lif n1_clus1
    cluster::*> network interface revert -vserver Cluster -lif n1_clus4
    cluster::*> network interface revert -vserver Cluster -lif n2_clus1
    cluster::*> network interface revert -vserver Cluster -lif n2_clus4
  5. Verify that the interface is now home:
    Show example
    The following example shows the status of cluster interconnect interfaces is up and Is home for n1 and n2:
    Cluster
  6. Verify the connectivity of the remote cluster interfaces:
n1
n2
All ONTAP releases
Host is n1
Ping status:....
RPC status:
  1. Expand the cluster by adding nodes to the Nexus 3132Q-V cluster switches.
  2. Display the information about the devices in your configuration:
    • network device-discovery show
    • network port show -role cluster
    • network interface show -role cluster
    • system cluster-switch show
      Show example
      The following examples show nodes n3 and n4 with 40 GbE cluster ports connected to ports e1/7 and e1/8, respectively on both the Nexus 3132Q-V cluster switches, and both nodes have joined the cluster. The 40 GbE cluster interconnect ports used are e4a and e4e.
      cluster::*> network device-discovery show
             Local  Discovered
      n1     /cdp
              e0a   C1           Ethernet1/1/1   N3K-C3132Q-V
              e0b   C2           Ethernet1/1/1   N3K-C3132Q-V
              e0c   C2           Ethernet1/1/2   N3K-C3132Q-V
              e0d   C1           Ethernet1/1/2   N3K-C3132Q-V
      n2     /cdp
              e0a   C1           Ethernet1/1/3   N3K-C3132Q-V
              e0b   C2           Ethernet1/1/3   N3K-C3132Q-V
              e0c   C2           Ethernet1/1/4   N3K-C3132Q-V
              e0d   C1           Ethernet1/1/4   N3K-C3132Q-V
      n3     /cdp
              e4a   C1           Ethernet1/7     N3K-C3132Q-V
              e4e   C2           Ethernet1/7     N3K-C3132Q-V
      n4     /cdp
              e4a   C1           Ethernet1/8     N3K-C3132Q-V
              e4e   C2           Ethernet1/8     N3K-C3132Q-V
      12 entries were displayed.
      cluster::*> network port show -role cluster
             (network port show)
      Node: n1
      Node: n2
      Node: n3
      e4a   cluster   cluster    up    9000  auto/40000     -        -
      e4e   cluster   cluster    up    9000  auto/40000     -        -
      Node: n4
      Cluster
               n3_clus1   up/up       10.10.0.9/24   n3       e4a      true
               n3_clus2   up/up       10.10.0.10/24  n3       e4e      true
               n4_clus1   up/up       10.10.0.11/24  n4       e4a      true
               n4_clus2   up/up       10.10.0.12/24  n4       e4e      true
      C1                          cluster-network  10.10.1.103   NX3132V
           Serial Number: FOX000001
            Is Monitored: true
                  Reason:
        Software Version: Cisco Nexus Operating System (NX-OS) Software, Version
                          7.0(3)I4(1)
          Version Source: CDP
      C2                          cluster-network  10.10.1.104   NX3132V
           Serial Number: FOX000002
            Is Monitored: true
                  Reason:
                          7.0(3)I4(1)
          Version Source: CDP
            Is Monitored: true
                  Reason:
            Is Monitored: true
                  Reason:
      4 entries were displayed.
  3. Remove the replaced CN1610 switches if they are not automatically removed:
    system cluster-switch delete
    Show example
    The following example shows how to remove the CN1610 switches:
    cluster::> system cluster-switch delete -device CL1
    cluster::> system cluster-switch delete -device CL2
  4. Configure clusters clus1 and clus4 to -auto-revert on each node and confirm:
    Show example
    cluster::*> network interface modify -vserver node1 -lif clus1 -auto-revert true
    cluster::*> network interface modify -vserver node1 -lif clus4 -auto-revert true
    cluster::*> network interface modify -vserver node2 -lif clus1 -auto-revert true
    cluster::*> network interface modify -vserver node2 -lif clus4 -auto-revert true
  5. Verify that the proper cluster switches are monitored:
    Show example
          Is Monitored: true
                Reason:
                        7.0(3)I4(1)
        Version Source: CDP
          Is Monitored: true
                Reason:
                        7.0(3)I4(1)
        Version Source: CDP
  6. If you suppressed automatic case creation, reenable it by invoking an AutoSupport message: