Install and maintain
Migrate from a Cisco Nexus 5596 cluster switch to a Cisco Nexus 3232C cluster switch
Contributors netapp-yvonneo netapp-jolieg
Follow this procedure to migrate an existing Cisco Nexus 5596 cluster switches in a cluster with Nexus 3232C cluster switches.
Review requirements
Before migration, be sure to review Migration requirements.
Note
The procedure requires the use of both ONTAP commands and Cisco Nexus 3000 Series Switches commands; ONTAP commands are used unless otherwise indicated.
For more information, see:
Migrate the switch
About the examples
The examples in this procedure describe replacing Cisco Nexus 5596 switches with Cisco Nexus 3232C switches. You can use these steps (with modifications) for other older Cisco switches (for example, 3132Q-V).
The procedure also uses the following switch and node nomenclature:
  • The command outputs might vary depending on different releases of ONTAP.
  • The Nexus 5596 switches to be replaced are CL1 and CL2.
  • The Nexus 3232C switches to replace the Nexus 5596 switches are C1 and C2.
  • n1_clus1 is the first cluster logical interface (LIF) connected to cluster switch 1 (CL1 or C1) for node n1.
  • n1_clus2 is the first cluster LIF connected to cluster switch 2 (CL2 or C2) for node n1.
  • n1_clus3 is the second LIF connected to cluster switch 2 (CL2 or C2) for node n1.
  • n1_clus4 is the second LIF connected to cluster switch 1 (CL1 or C1) for node n1.-
  • The number of 10 GbE and 40/100 GbE ports are defined in the reference configuration files (RCFs) available at Cisco® Cluster Network Switch Reference Configuration File Download.
  • The nodes are n1, n2, n3, and n4.
The examples in this procedure use four nodes:
  • Two nodes use four 10 GbE cluster interconnect ports: e0a, e0b, e0c, and e0d.
  • The other two nodes use two 40 GbE cluster interconnect ports: e4a, e4e. The Hardware Universe lists the actual cluster ports on your platforms.
Scenarios
This procedure covers the following scenarios:
  • The cluster starts with two nodes connected and functioning in a two Nexus 5596 cluster switches.
  • The cluster switch CL2 to be replaced by C2 (steps 1 to 19):
    • Traffic on all cluster ports and LIFs on all nodes connected to CL2 are migrated onto the first cluster ports and LIFs connected to CL1.
    • Disconnect cabling from all cluster ports on all nodes connected to CL2, and then use supported break-out cabling to reconnect the ports to new cluster switch C2.
    • Disconnect cabling between ISL ports between CL1 and CL2, and then use supported break-out cabling to reconnect the ports from CL1 to C2.
    • Traffic on all cluster ports and LIFs connected to C2 on all nodes is reverted.
  • The cluster switch CL2 to be replaced by C2.
    • Traffic on all cluster ports or LIFs on all nodes connected to CL1 are migrated onto the second cluster ports or LIFs connected to C2.
    • Disconnect cabling from all cluster port on all nodes connected to CL1 and reconnect, using supported break-out cabling, to new cluster switch C1.
    • Disconnect cabling between ISL ports between CL1 and C2, and reconnect using supported cabling, from C1 to C2.
    • Traffic on all cluster ports or LIFs connected to C1 on all nodes is reverted.
  • Two FAS9000 nodes have been added to cluster with examples showing cluster details.
Step 1: Prepare for migration
  1. If AutoSupport is enabled on this cluster, suppress automatic case creation by invoking an AutoSupport message:
    system node autosupport invoke -node * -type all - message MAINT=xh
    x is the duration of the maintenance window in hours.
    Note
    The AutoSupport message notifies technical support of this maintenance task so that automatic case creation is suppressed during the maintenance window.
  2. Display information about the devices in your configuration:
    network device-discovery show
    Show example
    The following example shows how many cluster interconnect interfaces have been configured in each node for each cluster interconnect switch:
    cluster::> network device-discovery show
                Local  Discovered
    Node        Port   Device              Interface        Platform
    n1         /cdp
                e0a    CL1                 Ethernet1/1      N5K-C5596UP
                e0b    CL2                 Ethernet1/1      N5K-C5596UP
                e0c    CL2                 Ethernet1/2      N5K-C5596UP
                e0d    CL1                 Ethernet1/2      N5K-C5596UP
    n2         /cdp
                e0a    CL1                 Ethernet1/3      N5K-C5596UP
                e0b    CL2                 Ethernet1/3      N5K-C5596UP
                e0c    CL2                 Ethernet1/4      N5K-C5596UP
                e0d    CL1                 Ethernet1/4      N5K-C5596UP
    8 entries were displayed.
  3. Determine the administrative or operational status for each cluster interface.
    1. Display the network port attributes:
      network port show -role cluster
      Show example
      The following example displays the network port attributes on nodes n1 and n2:
      cluster::*> network port show –role cluster
        (network port show)
      Node: n1
        Ignore
                                                        Speed(Mbps) Health   Health
      Port      IPspace      Broadcast Domain Link MTU  Admin/Oper  Status   Status
      e0a       Cluster      Cluster          up   9000 auto/10000  -        -
      e0b       Cluster      Cluster          up   9000 auto/10000  -        -
      e0c       Cluster      Cluster          up   9000 auto/10000  -        -
      e0d       Cluster      Cluster          up   9000 auto/10000  -        -
      Node: n2
        Ignore
    2. Display information about the logical interfaces:
      network interface show -role cluster
      Show example
      The following example displays the general information about all of the LIFs on the cluster, including their current ports:
      cluster::*> network interface show -role cluster
       (network interface show)
                  Logical    Status     Network            Current       Current Is
      Vserver     Interface  Admin/Oper Address/Mask       Node          Port    Home
      Cluster
                  n1_clus1   up/up      10.10.0.1/24       n1            e0a     true
                  n1_clus2   up/up      10.10.0.2/24       n1            e0b     true
                  n1_clus3   up/up      10.10.0.3/24       n1            e0c     true
                  n1_clus4   up/up      10.10.0.4/24       n1            e0d     true
                  n2_clus1   up/up      10.10.0.5/24       n2            e0a     true
                  n2_clus2   up/up      10.10.0.6/24       n2            e0b     true
                  n2_clus3   up/up      10.10.0.7/24       n2            e0c     true
                  n2_clus4   up/up      10.10.0.8/24       n2            e0d     true
    3. Display information about the discovered cluster switches:
      system cluster-switch show
      Show example
      The following example shows the active cluster switches:
      cluster::*> system cluster-switch show
      Switch                        Type               Address         Model
      CL1                           cluster-network    10.10.1.101     NX5596
           Serial Number: 01234567
            Is Monitored: true
                  Reason:
        Software Version: Cisco Nexus Operating System (NX-OS) Software, Version
                          7.1(1)N1(1)
          Version Source: CDP
      CL2                           cluster-network    10.10.1.102     NX5596
           Serial Number: 01234568
            Is Monitored: true
                  Reason:
                          7.1(1)N1(1)
          Version Source: CDP
      2 entries were displayed.
  4. Verify that the appropriate RCF and image are installed on the new 3232C switches as necessary for your requirements, and make the essential site customizations, such as users and passwords, network addresses, and other customizations.
    Note
    You must prepare both switches at this time.
    If you need to upgrade the RCF and image, you must complete the following steps:
    1. Go to the Cisco Ethernet Switches page on the NetApp Support Site.
    2. Note your switch and the required software versions in the table on that page.
    3. Download the appropriate version of the RCF.
    4. Click CONTINUE on the Description page, accept the license agreement, and then follow the instructions on the Download page to download the RCF.
    5. Download the appropriate version of the image software.
      See the ONTAP 8.x or later Cluster and Management Network Switch Reference Configuration Files Download page, and then click the appropriate version.
      To find the correct version, see the ONTAP 8.x or later Cluster Network Switch Download page.
  5. Migrate the LIFs associated with the second Nexus 5596 switch to be replaced:
    network interface migrate -vserver vserver-name -lif lif-name -source-node source-node-name - destination-node node-name -destination-port destination-port-name
    Show example
    The following example shows the LIFs being migrated for nodes n1 and n2; LIF migration must be done on all of the nodes:
    cluster::*> network interface migrate -vserver Cluster -lif n1_clus2 -source-node n1 -
    destination-node n1 -destination-port e0a
    cluster::*> network interface migrate -vserver Cluster -lif n1_clus3 -source-node n1 -
    destination-node n1 -destination-port e0d
    cluster::*> network interface migrate -vserver Cluster -lif n2_clus2 -source-node n2 -
    destination-node n2 -destination-port e0a
    cluster::*> network interface migrate -vserver Cluster -lif n2_clus3 -source-node n2 -
    destination-node n2 -destination-port e0d
  6. Verify the cluster's health:
    Show example
    The following example shows the current status of each cluster:
    Cluster
                n1_clus2   up/up      10.10.0.2/24       n1            e0a     false
                n1_clus3   up/up      10.10.0.3/24       n1            e0d     false
                n2_clus2   up/up      10.10.0.6/24       n2            e0a     false
                n2_clus3   up/up      10.10.0.7/24       n2            e0d     false
Step 2: Configure ports
  1. Shut down the cluster interconnect ports that are physically connected to switch CL2:
    network port modify -node node-name -port port-name -up-admin false
    Show example
    The following commands shut down the specified ports on n1 and n2, but the ports must be shut down on all nodes:
    cluster::*> network port modify -node n1 -port e0b -up-admin false
    cluster::*> network port modify -node n1 -port e0c -up-admin false
    cluster::*> network port modify -node n2 -port e0b -up-admin false
    cluster::*> network port modify -node n2 -port e0c -up-admin false
  2. Verify the connectivity of the remote cluster interfaces:
ONTAP 9.9.1 and later
You can use the network interface check cluster-connectivity command to start an accessibility check for cluster connectivity and then display the details:
network interface check cluster-connectivity start and network interface check cluster-connectivity show
cluster1::*> network interface check cluster-connectivity start
NOTE: Wait for a number of seconds before running the show command to display the details.
cluster1::*> network interface check cluster-connectivity show
                                  Source           Destination      Packet
Node   Date                       LIF              LIF              Loss
n1
       3/5/2022 19:21:18 -06:00   n1_clus2         n2-clus1         none
       3/5/2022 19:21:20 -06:00   n1_clus2         n2_clus2         none
n2
       3/5/2022 19:21:18 -06:00   n2_clus2         n1_clus1         none
       3/5/2022 19:21:20 -06:00   n2_clus2         n1_clus2         none
All ONTAP releases
For all ONTAP releases, you can also use the cluster ping-cluster -node <name> command to check the connectivity:
cluster1::*> cluster ping-cluster -node local
Host is n1
Getting addresses from network interface table...
Cluster n1_clus1 n1       e0a    10.10.0.1
Cluster n1_clus2 n1       e0b    10.10.0.2
Cluster n1_clus3 n1       e0c    10.10.0.3
Cluster n1_clus4 n1       e0d    10.10.0.4
Cluster n2_clus1 n2       e0a    10.10.0.5
Cluster n2_clus2 n2       e0b    10.10.0.6
Cluster n2_clus3 n2       e0c    10.10.0.7
Cluster n2_clus4 n2       e0d    10.10.0.8
Local = 10.10.0.1 10.10.0.2 10.10.0.3 10.10.0.4
Remote = 10.10.0.5 10.10.0.6 10.10.0.7 10.10.0.8
Cluster Vserver Id = 4294967293
Ping status:....
Basic connectivity succeeds on 16 path(s)
Basic connectivity fails on 0 path(s)
Detected 9000 byte MTU on 16 path(s):
    Local 10.10.0.1 to Remote 10.10.0.5
    Local 10.10.0.1 to Remote 10.10.0.6
    Local 10.10.0.1 to Remote 10.10.0.7
    Local 10.10.0.1 to Remote 10.10.0.8
    Local 10.10.0.2 to Remote 10.10.0.5
    Local 10.10.0.2 to Remote 10.10.0.6
    Local 10.10.0.2 to Remote 10.10.0.7
    Local 10.10.0.2 to Remote 10.10.0.8
    Local 10.10.0.3 to Remote 10.10.0.5
    Local 10.10.0.3 to Remote 10.10.0.6
    Local 10.10.0.3 to Remote 10.10.0.7
    Local 10.10.0.3 to Remote 10.10.0.8
    Local 10.10.0.4 to Remote 10.10.0.5
    Local 10.10.0.4 to Remote 10.10.0.6
    Local 10.10.0.4 to Remote 10.10.0.7
    Local 10.10.0.4 to Remote 10.10.0.8
Larger than PMTU communication succeeds on 16 path(s)
RPC status:
4 paths up, 0 paths down (tcp check)
4 paths up, 0 paths down (udp check)
  1. Shut down ISLs 41 through 48 on CL1, the active Nexus 5596 switch, using the Cisco shutdown command.
    For more information on Cisco commands, see the appropriate guide in the Cisco Nexus 3000 Series NX-OS Command References.
    Show example
    The following example shows ISLs 41 through 48 being shut down on the Nexus 5596 switch CL1:
    (CL1)# configure
    (CL1)(Config)# interface e1/41-48
    (CL1)(config-if-range)# shutdown
    (CL1)(config-if-range)# exit
    (CL1)(Config)# exit
    (CL1)#
  2. Build a temporary ISL between CL1 and C2 using the appropriate Cisco commands.
    Show example
    The following example shows a temporary ISL being set up between CL1 and C2:
    C2# configure
    C2(config)# interface port-channel 2
    C2(config-if)# switchport mode trunk
    C2(config-if)# spanning-tree port type network
    C2(config-if)# mtu 9216
    C2(config-if)# interface breakout module 1 port 24 map 10g-4x
    C2(config)# interface e1/24/1-4
    C2(config-if-range)# switchport mode trunk
    C2(config-if-range)# mtu 9216
    C2(config-if-range)# channel-group 2 mode active
    C2(config-if-range)# exit
    C2(config-if)# exit
  3. On all nodes, remove all cables attached to the Nexus 5596 switch CL2.
    With supported cabling, reconnect disconnected ports on all nodes to the Nexus 3232C switch C2.
  4. Remove all the cables from the Nexus 5596 switch CL2.
    Attach the appropriate Cisco QSFP to SFP+ break-out cables connecting port 1/24 on the new Cisco 3232C switch, C2, to ports 45 to 48 on existing Nexus 5596, CL1.
  5. Bring up ISLs ports 45 through 48 on the active Nexus 5596 switch CL1.
    Show example
    The following example shows ISLs ports 45 through 48 being brought up:
    (CL1)# configure
    (CL1)(Config)# interface e1/45-48
    (CL1)(config-if-range)# no shutdown
    (CL1)(Config)# exit
    (CL1)#
  6. Verify that the ISLs are up on the Nexus 5596 switch CL1.
    Show example
    The following example shows Ports eth1/45 through eth1/48 indicating (P), meaning that the ISL ports are up in the port-channel.
    CL1# show port-channel summary
    Flags: D - Down         P - Up in port-channel (members)
           I - Individual   H - Hot-standby (LACP only)
           s - Suspended    r - Module-removed
           S - Switched     R - Routed
           U - Up (port-channel)
           M - Not in use. Min-links not met
    Group Port-        Type   Protocol  Member Ports
          Channel
    1     Po1(SU)      Eth    LACP      Eth1/41(D)   Eth1/42(D)   Eth1/43(D)
                                        Eth1/44(D)   Eth1/45(P)   Eth1/46(P)
                                        Eth1/47(P)   Eth1/48(P)
  7. Verify that interfaces eth1/45-48 already have `channel-group 1 mode active`in their running configuration.
  8. On all nodes, bring up all the cluster interconnect ports connected to the 3232C switch C2:
    network port modify -node node-name -port port-name -up-admin true
    Show example
    The following example shows the specified ports being brought up on nodes n1 and n2:
    cluster::*> network port modify -node n1 -port e0b -up-admin true
    cluster::*> network port modify -node n1 -port e0c -up-admin true
    cluster::*> network port modify -node n2 -port e0b -up-admin true
    cluster::*> network port modify -node n2 -port e0c -up-admin true
  9. On all nodes, revert all of the migrated cluster interconnect LIFs connected to C2:
    network interface revert -vserver Cluster -lif lif-name
    Show example
    The following example shows the migrated cluster LIFs being reverted to their home ports:
    cluster::*> network interface revert -vserver Cluster -lif n1_clus2
    cluster::*> network interface revert -vserver Cluster -lif n1_clus3
    cluster::*> network interface revert -vserver Cluster -lif n2_clus2
    cluster::*> network interface revert -vserver Cluster -lif n2_clus3
  10. Verify all the cluster interconnect ports are now reverted to their home:
    Show example
    The following example shows that the LIFs on clus2 reverted to their home ports and shows that the LIFs are successfully reverted if the ports in the Current Port column have a status of true in the Is Home column. If the Is Home value is false, the LIF has not been reverted.
    cluster::*> *network interface show -role cluster*
    Cluster
  11. Verify that the clustered ports are connected:
    Show example
    The following example shows the result of the previous network port modify command, verifying that all the cluster interconnects are up:
    cluster::*> network port show -role cluster
      (network port show)
    Node: n1
        Ignore
    Node: n2
        Ignore
  12. Verify the connectivity of the remote cluster interfaces:
n1
n2
All ONTAP releases
Host is n1
Ping status:....
RPC status:
  1. On each node in the cluster, migrate the interfaces associated with the first Nexus 5596 switch, CL1, to be replaced:
    network interface migrate -vserver vserver-name -lif lif-name -source-node source-node-name -destination-node destination-node-name -destination-port destination-port-name
    Show example
    The following example shows the ports or LIFs being migrated on nodes n1 and n2:
    cluster::*> network interface migrate -vserver Cluster -lif n1_clus1 -source-node n1 -
    destination-node n1 -destination-port e0b
    cluster::*> network interface migrate -vserver Cluster -lif n1_clus4 -source-node n1 -
    destination-node n1 -destination-port e0c
    cluster::*> network interface migrate -vserver Cluster -lif n2_clus1 -source-node n2 -
    destination-node n2 -destination-port e0b
    cluster::*> network interface migrate -vserver Cluster -lif n2_clus4 -source-node n2 -
    destination-node n2 -destination-port e0c
  2. Verify the cluster's status:
    Show example
    The following example shows that the required cluster LIFs have been migrated to appropriate cluster ports hosted on cluster switch, C2:
    Cluster
                n1_clus1   up/up      10.10.0.1/24       n1            e0b     false
                n1_clus4   up/up      10.10.0.4/24       n1            e0c     false
                n2_clus1   up/up      10.10.0.5/24       n2            e0b     false
                n2_clus4   up/up      10.10.0.8/24       n2            e0c     false
  3. On all the nodes, shut down the node ports that are connected to CL1:
    Show example
    The following example shows the specified ports being shut down on nodes n1 and n2:
    cluster::*> network port modify -node n1 -port e0a -up-admin false
    cluster::*> network port modify -node n1 -port e0d -up-admin false
    cluster::*> network port modify -node n2 -port e0a -up-admin false
    cluster::*> network port modify -node n2 -port e0d -up-admin false
  4. Shut down ISL 24, 31 and 32 on the active 3232C switch C2.
    Show example
    The following example shows ISLs being shutdown:
    C2# configure
    C2(Config)# interface e1/24/1-4
    C2(config-if-range)# shutdown
    C2(config)# interface 1/31-32
    C2(config-if)# exit
    C2#
  5. On all nodes, remove all cables attached to the Nexus 5596 switch CL1.
    With supported cabling, reconnect disconnected ports on all nodes to the Nexus 3232C switch C1.
  6. Remove the QSFP breakout cable from Nexus 3232C C2 ports e1/24.
    Connect ports e1/31 and e1/32 on C1 to ports e1/31 and e1/32 on C2 using supported Cisco QSFP optical fiber or direct-attach cables.
  7. Restore the configuration on port 24 and remove the temporary Port Channel 2 on C2.
    Show example
    The following example shows the configuration on port m24 being restored using the appropriate Cisco commands:
    C2# configure
    C2(config)# no interface breakout module 1 port 24 map 10g-4x
    C2(config)# no interface port-channel 2
    C2(config-if)# int e1/24
    C2(config-if)# description 40GbE Node Port
    C2(config-if)# spanning-tree port type edge
    C2(config-if)# spanning-tree bpduguard enable
    C2(config)# exit
    C2# copy running-config startup-config
    [] 100%
    Copy Complete.
  8. Bring up ISL ports 31 and 32 on C2, the active 3232C switch, by entering the following Cisco command: no shutdown
    Show example
    The following example shows the Cisco commands switchname configure brought up on the 3232C switch C2:
    C2# configure
    C2(config)# interface ethernet 1/31-32
    C2(config-if-range)# no shutdown
  9. Verify that the ISL connections are up on the 3232C switch C2.
    Ports eth1/31 and eth1/32 should indicate (P) meaning that both ISL ports up in the port-channel
    Show example
    C1# show port-channel summary
          Channel
    1     Po1(SU)      Eth    LACP      Eth1/31(P)   Eth1/32(P)
  10. On all nodes, bring up all the cluster interconnect ports connected to the new 3232C switch C1:
    network port modify
    Show example
    The following example shows all the cluster interconnect ports being brought up for n1 and n2 on the 3232C switch C1:
    cluster::*> network port modify -node n1 -port e0a -up-admin true
    cluster::*> network port modify -node n1 -port e0d -up-admin true
    cluster::*> network port modify -node n2 -port e0a -up-admin true
    cluster::*> network port modify -node n2 -port e0d -up-admin true
  11. Verify the status of the cluster node port:
    network port show
    Show example
    The following example shows verifies that all cluster interconnect ports on all nodes on the new 3232C switch C1 are up:
      (network port show)
    Node: n1
        Ignore
    Node: n2
        Ignore
  12. On all nodes, revert the specific cluster LIFs to their home ports:
    network interface revert -server Cluster -lif lif-name
    Show example
    The following example shows the specific cluster LIFs being reverted to their home ports on nodes n1 and n2:
    cluster::*> network interface revert -vserver Cluster -lif n1_clus1
    cluster::*> network interface revert -vserver Cluster -lif n1_clus4
    cluster::*> network interface revert -vserver Cluster -lif n2_clus1
    cluster::*> network interface revert -vserver Cluster -lif n2_clus4
  13. Verify that the interface is home:
    Show example
    The following example shows the status of cluster interconnect interfaces are up and Is Home for n1 and n2:
    Cluster
  14. Verify the connectivity of the remote cluster interfaces:
n1
n2
All ONTAP releases
Host is n1
Ping status:....
RPC status:
  1. Expand the cluster by adding nodes to the Nexus 3232C cluster switches.
    The following examples show nodes n3 and n4 have 40 GbE cluster ports connected to ports e1/7 and e1/8 respectively on both the Nexus 3232C cluster switches, and both nodes have joined the cluster. The 40 GbE cluster interconnect ports used are e4a and e4e.
    Display the information about the devices in your configuration:
    • network device-discovery show
    • network port show -role cluster
    • network interface show -role cluster
    • system cluster-switch show
    Show example
                Local  Discovered
    n1         /cdp
                e0a    C1                 Ethernet1/1/1    N3K-C3232C
                e0b    C2                 Ethernet1/1/1    N3K-C3232C
                e0c    C2                 Ethernet1/1/2    N3K-C3232C
                e0d    C1                 Ethernet1/1/2    N3K-C3232C
    n2         /cdp
                e0a    C1                 Ethernet1/1/3    N3K-C3232C
                e0b    C2                 Ethernet1/1/3    N3K-C3232C
                e0c    C2                 Ethernet1/1/4    N3K-C3232C
                e0d    C1                 Ethernet1/1/4    N3K-C3232C
    n3         /cdp
                e4a    C1                 Ethernet1/7      N3K-C3232C
                e4e    C2                 Ethernet1/7      N3K-C3232C
    n4         /cdp
                e4a    C1                 Ethernet1/8      N3K-C3232C
                e4e    C2                 Ethernet1/8      N3K-C3232C
    12 entries were displayed.
      (network port show)
    Node: n1
        Ignore
    Node: n2
        Ignore
    Node: n3
        Ignore
    e4a       Cluster      Cluster          up   9000 auto/40000  -        -
    e4e       Cluster      Cluster          up   9000 auto/40000  -        -
    Node: n4
        Ignore
    Cluster
                n3_clus1   up/up      10.10.0.9/24       n3            e4a     true
                n3_clus2   up/up      10.10.0.10/24      n3            e4e     true
                n4_clus1   up/up      10.10.0.11/24      n4            e4a     true
                n4_clus2   up/up      10.10.0.12/24      n4            e4e     true
    C1                          cluster-network    10.10.1.103      NX3232C
         Serial Number: FOX000001
          Is Monitored: true
                Reason:
                        7.0(3)I4(1)
        Version Source: CDP
    C2                          cluster-network     10.10.1.104      NX3232C
         Serial Number: FOX000002
          Is Monitored: true
                Reason:
                        7.0(3)I4(1)
        Version Source: CDP
          Is Monitored: true
                Reason:
                        7.1(1)N1(1)
        Version Source: CDP
          Is Monitored: true
                Reason:
                        7.1(1)N1(1)
        Version Source: CDP
    4 entries were displayed.
  2. Remove the replaced Nexus 5596 by using the system cluster-switch delete command, if it is not automatically removed:
    system cluster-switch delete -device switch-name
    Show example
    cluster::> system cluster-switch delete –device CL1
    cluster::> system cluster-switch delete –device CL2
Step 3: Complete the procedure
  1. Verify that the proper cluster switches are monitored:
    Show example
    cluster::> system cluster-switch show
          Is Monitored: true
                Reason:
                        7.0(3)I4(1)
        Version Source: CDP
          Is Monitored: true
                Reason:
                        7.0(3)I4(1)
        Version Source: CDP
  2. If you suppressed automatic case creation, re-enable it by invoking an AutoSupport message: