Migrate to a two-node switched cluster using Cisco Nexus 92300YC cluster switches
Migrate an existing two-node switchless cluster to a switched cluster environment using Cisco Nexus 92300YC cluster switches. This nondisruptive migration enables you to scale the cluster beyond two nodes.
The procedure you use depends on whether you have two dedicated cluster-network ports on each controller or a single cluster port on each controller. The process documented works for all nodes using optical or twinax ports, but is not supported on this switch if nodes are using onboard 10Gb BASE-T RJ45 ports for the cluster-network ports.
Most systems require two dedicated cluster-network ports on each controller.
After your migration completes, you might need to install the required configuration file to support the Cluster Switch Health Monitor (CSHM) for 92300YC cluster switches. Refer to Switch Health Monitoring (CSHM). |
Review requirements
Make sure you have the following:
For a two-node switchless configuration, ensure that:
The two-node switchless configuration is properly set up and functioning.
The nodes are running ONTAP 9.6 and later.
All cluster ports are in the up state.
All cluster logical interfaces (LIFs) are in the up state and on their home ports.
For the Cisco Nexus 92300YC switch configuration:
Both switches have management network connectivity.
There is console access to the cluster switches.
Nexus 92300YC node-to-node switch and switch-to-switch connections use twinax or fiber cables.
The Hardware Universe - Switches contains more information about cabling.
Inter-Switch Link (ISL) cables are connected to ports 1/65 and 1/66 on both 92300YC switches.
Initial customization of both the 92300YC switches are completed. So that the:
92300YC switches are running the latest version of software
Reference Configuration Files (RCFs) are applied to the switches Any site customization, such as SMTP, SNMP, and SSH is configured on the new switches.
Migrate the switch
The examples in this procedure use the following cluster switch and node nomenclature:
The names of the 92300YC switches are cs1 and cs2.
The names of the cluster SVMs are node1 and node2.
The names of the LIFs are node1_clus1 and node1_clus2 on node 1, and node2_clus1 and node2_clus2 on node 2 respectively.
The
cluster1::*>prompt indicates the name of the cluster. -
The cluster ports used in this procedure are e0a and e0b.
The Hardware Universe contains the latest information about the actual cluster ports for your platforms.
Step 1: Prepare for migration
Change the privilege level to advanced, entering
ywhen prompted to continue:set -privilege advancedThe advanced prompt (
*>) appears. -
If AutoSupport is enabled on this cluster, suppress automatic case creation by invoking an AutoSupport message:
system node autosupport invoke -node * -type all -message MAINT=xhwhere x is the duration of the maintenance window in hours.
The AutoSupport message notifies technical support of this maintenance task so that automatic case creation is suppressed during the maintenance window. Show example
The following command suppresses automatic case creation for two hours:
cluster1::*> system node autosupport invoke -node * -type all -message MAINT=2h
Step 2: Configure cables and ports
Disable all node-facing ports (not ISL ports) on both the new cluster switches cs1 and cs2.
You must not disable the ISL ports.
Show example
The following example shows that node-facing ports 1 through 64 are disabled on switch cs1:
cs1# config Enter configuration commands, one per line. End with CNTL/Z. cs1(config)# interface e/1-64 cs1(config-if-range)# shutdown
Verify that the ISL and the physical ports on the ISL between the two 92300YC switches cs1 and cs2 are up on ports 1/65 and 1/66:
show port-channel summaryShow example
The following example shows that the ISL ports are up on switch cs1:
cs1# show port-channel summary Flags: D - Down P - Up in port-channel (members) I - Individual H - Hot-standby (LACP only) s - Suspended r - Module-removed b - BFD Session Wait S - Switched R - Routed U - Up (port-channel) p - Up in delay-lacp mode (member) M - Not in use. Min-links not met -------------------------------------------------------------------------------- Group Port- Type Protocol Member Ports Channel -------------------------------------------------------------------------------- 1 Po1(SU) Eth LACP Eth1/65(P) Eth1/66(P)+ The following example shows that the ISL ports are up on switch cs2 :
(cs2)# show port-channel summary Flags: D - Down P - Up in port-channel (members) I - Individual H - Hot-standby (LACP only) s - Suspended r - Module-removed b - BFD Session Wait S - Switched R - Routed U - Up (port-channel) p - Up in delay-lacp mode (member) M - Not in use. Min-links not met -------------------------------------------------------------------------------- Group Port- Type Protocol Member Ports Channel -------------------------------------------------------------------------------- 1 Po1(SU) Eth LACP Eth1/65(P) Eth1/66(P) -
Display the list of neighboring devices:
show cdp neighborsThis command provides information about the devices that are connected to the system.
Show example
The following example lists the neighboring devices on switch cs1:
cs1# show cdp neighbors Capability Codes: R - Router, T - Trans-Bridge, B - Source-Route-Bridge S - Switch, H - Host, I - IGMP, r - Repeater, V - VoIP-Phone, D - Remotely-Managed-Device, s - Supports-STP-Dispute Device-ID Local Intrfce Hldtme Capability Platform Port ID cs2(FDO220329V5) Eth1/65 175 R S I s N9K-C92300YC Eth1/65 cs2(FDO220329V5) Eth1/66 175 R S I s N9K-C92300YC Eth1/66 Total entries displayed: 2+ The following example lists the neighboring devices on switch cs2:
cs2# show cdp neighbors Capability Codes: R - Router, T - Trans-Bridge, B - Source-Route-Bridge S - Switch, H - Host, I - IGMP, r - Repeater, V - VoIP-Phone, D - Remotely-Managed-Device, s - Supports-STP-Dispute Device-ID Local Intrfce Hldtme Capability Platform Port ID cs1(FDO220329KU) Eth1/65 177 R S I s N9K-C92300YC Eth1/65 cs1(FDO220329KU) Eth1/66 177 R S I s N9K-C92300YC Eth1/66 Total entries displayed: 2 -
Verify that all cluster ports are up:
network port show -ipspace ClusterEach port should display up for
Linkand healthy forHealth Status.Show example
cluster1::*> network port show -ipspace Cluster Node: node1 Speed(Mbps) Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status --------- ------------ ---------------- ---- ---- ----------- -------- e0a Cluster Cluster up 9000 auto/10000 healthy e0b Cluster Cluster up 9000 auto/10000 healthy Node: node2 Speed(Mbps) Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status --------- ------------ ---------------- ---- ---- ----------- -------- e0a Cluster Cluster up 9000 auto/10000 healthy e0b Cluster Cluster up 9000 auto/10000 healthy 4 entries were displayed. -
Verify that all cluster LIFs are up and operational:
network interface show -vserver ClusterEach cluster LIF should display true for
Is Homeand have aStatus Admin/Operof up/upShow example
cluster1::*> network interface show -vserver Cluster Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------------ ------------- ------- ----- Cluster node1_clus1 up/up 169.254.209.69/16 node1 e0a true node1_clus2 up/up 169.254.49.125/16 node1 e0b true node2_clus1 up/up 169.254.47.194/16 node2 e0a true node2_clus2 up/up 169.254.19.183/16 node2 e0b true 4 entries were displayed. -
Disable auto-revert on all of the cluster LIFs:
network interface modify -vserver Cluster -lif * -auto-revert falseShow example
cluster1::*> network interface modify -vserver Cluster -lif * -auto-revert false Logical Vserver Interface auto-revert --------- ------------- ------------ Cluster node1_clus1 false node1_clus2 false node2_clus1 false node2_clus2 false 4 entries were displayed. -
Disconnect the cable from cluster port e0a on node1, and then connect e0a to port 1 on cluster switch cs1, using the appropriate cabling supported by the 92300YC switches.
Disconnect the cable from cluster port e0a on node2, and then connect e0a to port 2 on cluster switch cs1, using the appropriate cabling supported by the 92300YC switches.
Enable all node-facing ports on cluster switch cs1.
Show example
The following example shows that ports 1/1 through 1/64 are enabled on switch cs1:
cs1# config Enter configuration commands, one per line. End with CNTL/Z. cs1(config)# interface e1/1-64 cs1(config-if-range)# no shutdown
Verify that all cluster LIFs are up, operational, and display as true for
Is Home:network interface show -vserver ClusterShow example
The following example shows that all of the LIFs are up on node1 and node2 and that
Is Homeresults are true:cluster1::*> network interface show -vserver Cluster Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home -------- ------------ ---------- ------------------ ----------- ------- ---- Cluster node1_clus1 up/up 169.254.209.69/16 node1 e0a true node1_clus2 up/up 169.254.49.125/16 node1 e0b true node2_clus1 up/up 169.254.47.194/16 node2 e0a true node2_clus2 up/up 169.254.19.183/16 node2 e0b true 4 entries were displayed. -
Display information about the status of the nodes in the cluster:
cluster showShow example
The following example displays information about the health and eligibility of the nodes in the cluster:
cluster1::*> cluster show Node Health Eligibility Epsilon -------------------- ------- ------------ ------------ node1 true true false node2 true true false 2 entries were displayed.
Disconnect the cable from cluster port e0b on node1, and then connect e0b to port 1 on cluster switch cs2, using the appropriate cabling supported by the 92300YC switches.
Disconnect the cable from cluster port e0b on node2, and then connect e0b to port 2 on cluster switch cs2, using the appropriate cabling supported by the 92300YC switches.
Enable all node-facing ports on cluster switch cs2.
Show example
The following example shows that ports 1/1 through 1/64 are enabled on switch cs2:
cs2# config Enter configuration commands, one per line. End with CNTL/Z. cs2(config)# interface e1/1-64 cs2(config-if-range)# no shutdown
Step 3: Verify the configuration
Enable auto-revert on the cluster LIFs.
network interface modify -vserver Cluster -lif * -auto-revert true -
network port show -ipspace ClusterShow example
The following example shows that all of the cluster ports are up on node1 and node2:
cluster1::*> network port show -ipspace Cluster Node: node1 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/10000 healthy false e0b Cluster Cluster up 9000 auto/10000 healthy false Node: node2 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/10000 healthy false e0b Cluster Cluster up 9000 auto/10000 healthy false 4 entries were displayed. -
Verify that all interfaces display true for
Is Home:network interface show -vserver ClusterThis might take several minutes to complete. Show example
The following example shows that all LIFs are up on node1 and node2 and that
Is Homeresults are true:cluster1::*> network interface show -vserver Cluster Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home --------- ------------ ---------- ------------------ ---------- ------- ---- Cluster node1_clus1 up/up 169.254.209.69/16 node1 e0a true node1_clus2 up/up 169.254.49.125/16 node1 e0b true node2_clus1 up/up 169.254.47.194/16 node2 e0a true node2_clus2 up/up 169.254.19.183/16 node2 e0b true 4 entries were displayed. -
Verify that both nodes each have one connection to each switch:
show cdp neighborsShow example
The following example shows the appropriate results for both switches:
(cs1)# show cdp neighbors Capability Codes: R - Router, T - Trans-Bridge, B - Source-Route-Bridge S - Switch, H - Host, I - IGMP, r - Repeater, V - VoIP-Phone, D - Remotely-Managed-Device, s - Supports-STP-Dispute Device-ID Local Intrfce Hldtme Capability Platform Port ID node1 Eth1/1 133 H FAS2980 e0a node2 Eth1/2 133 H FAS2980 e0a cs2(FDO220329V5) Eth1/65 175 R S I s N9K-C92300YC Eth1/65 cs2(FDO220329V5) Eth1/66 175 R S I s N9K-C92300YC Eth1/66 Total entries displayed: 4 (cs2)# show cdp neighbors Capability Codes: R - Router, T - Trans-Bridge, B - Source-Route-Bridge S - Switch, H - Host, I - IGMP, r - Repeater, V - VoIP-Phone, D - Remotely-Managed-Device, s - Supports-STP-Dispute Device-ID Local Intrfce Hldtme Capability Platform Port ID node1 Eth1/1 133 H FAS2980 e0b node2 Eth1/2 133 H FAS2980 e0b cs1(FDO220329KU) Eth1/65 175 R S I s N9K-C92300YC Eth1/65 cs1(FDO220329KU) Eth1/66 175 R S I s N9K-C92300YC Eth1/66 Total entries displayed: 4 -
Display information about the discovered network devices in your cluster:
network device-discovery show -protocol cdpShow example
cluster1::*> network device-discovery show -protocol cdp Node/ Local Discovered Protocol Port Device (LLDP: ChassisID) Interface Platform ----------- ------ ------------------------- ---------------- ---------------- node2 /cdp e0a cs1 0/2 N9K-C92300YC e0b cs2 0/2 N9K-C92300YC node1 /cdp e0a cs1 0/1 N9K-C92300YC e0b cs2 0/1 N9K-C92300YC 4 entries were displayed. -
Verify that the settings are disabled:
network options switchless-cluster showIt might take several minutes for the command to complete. Wait for the '3 minute lifetime to expire' announcement. Show example
The false output in the following example shows that the configuration settings are disabled:
cluster1::*> network options switchless-cluster show Enable Switchless Cluster: false
Verify the status of the node members in the cluster:
The following example shows information about the health and eligibility of the nodes in the cluster:
cluster1::*> cluster show Node Health Eligibility Epsilon -------------------- ------- ------------ -------- node1 true true false node2 true true false
Verify the connectivity of the remote cluster interfaces:
You can use the network interface check cluster-connectivity command to start an accessibility check for cluster connectivity and then display the details:
network interface check cluster-connectivity start and network interface check cluster-connectivity show
cluster1::*> network interface check cluster-connectivity start
NOTE: Wait for a number of seconds before running the show command to display the details.
cluster1::*> network interface check cluster-connectivity show
Source Destination Packet
Node Date LIF LIF Loss
node1
3/5/2022 19:21:18 -06:00 node1_clus2 node2-clus1 none
3/5/2022 19:21:20 -06:00 node1_clus2 node2_clus2 none
node2
3/5/2022 19:21:18 -06:00 node2_clus2 node1_clus1 none
3/5/2022 19:21:20 -06:00 node2_clus2 node1_clus2 none
For all ONTAP releases, you can also use the cluster ping-cluster -node <name> command to check the connectivity:
cluster1::*> cluster ping-cluster -node local Host is node2 Getting addresses from network interface table... Cluster node1_clus1 169.254.209.69 node1 e0a Cluster node1_clus2 169.254.49.125 node1 e0b Cluster node2_clus1 169.254.47.194 node2 e0a Cluster node2_clus2 169.254.19.183 node2 e0b Local = 169.254.47.194 169.254.19.183 Remote = 169.254.209.69 169.254.49.125 Cluster Vserver Id = 4294967293 Ping status: Basic connectivity succeeds on 4 path(s) Basic connectivity fails on 0 path(s) Detected 9000 byte MTU on 4 path(s): Local 169.254.47.194 to Remote 169.254.209.69 Local 169.254.47.194 to Remote 169.254.49.125 Local 169.254.19.183 to Remote 169.254.209.69 Local 169.254.19.183 to Remote 169.254.49.125 Larger than PMTU communication succeeds on 4 path(s) RPC status: 2 paths up, 0 paths down (tcp check) 2 paths up, 0 paths down (udp check)
If you suppressed automatic case creation, reenable it by invoking an AutoSupport message:
system node autosupport invoke -node * -type all -message MAINT=ENDShow example
cluster1::*> system node autosupport invoke -node * -type all -message MAINT=END
Change the privilege level back to admin:
set -privilege admin
After you've verified your SSH configuration, you can configure switch health monitoring.