Install and boot node3
Contributors netapp-pcarriga netapp-aherbin
You must install node3 in the rack, transfer node1's connections to node3, boot node3, and install ONTAP. You must also reassign any of node1's spare disks, any disks belonging to the root volume, and any non-root aggregates not relocated to node2 earlier.
About this task
You must netboot node3 if it doesn't have the same version of ONTAP 9 that is installed on node1. After you install node3, boot it from the ONTAP 9 image stored on the web server. You can then download the correct files to the boot media device for subsequent system boots. See Prepare for netboot.
However, you don't need to netboot node3 if it has the same or a later version of ONTAP 9 that is installed on node1.
Important
Steps
  1. Make sure that you have rack space for node3.
    If node1 and node2 were in separate chassis, you can put node3 in the same rack location as node1. However, if node1 was in the same chassis with node2, then you must put node3 into its own rack space, preferably close to the location of node1.
  2. Install node3 in the rack, following the Installation and Setup Instructions for your node model.
    Note If you're upgrading to a system with both nodes in the same chassis, install node4 and node3 in the chassis. If you don't install both nodes in the same chassis, when you boot node3, it behaves as if it were in a dual-chassis configuration, and when you boot node4, the interconnect between the nodes doesn't come up.
  3. Cable node3, moving the connections from node1 to node3.
    The following references help you make proper cable connections. Go to References to link to them.
    • Installation and Setup Instructions for the node3 platform
    • The appropriate disk shelf procedure
    • The HA pair management documentation
    Cable the following connections:
    • Console (remote management port)
    • Cluster ports
    • Data ports
    • Cluster and node management ports
    • Storage
    • SAN configurations: iSCSI Ethernet and FC switch ports
      Note You might not need to move the interconnect card or the cluster interconnect cable connection from node1 to node3 because most platform models have a unique interconnect card model. For the MetroCluster configuration, you must move the FC-VI cable connections from node1 to node3. If the new host does not have an FC-VI card, you might need to move the FC-VI card.
  4. Turn on the power to node3, and then interrupt the boot process by pressing Ctrl-C at the console terminal to access the boot environment prompt.
    If you are upgrading to a system with both nodes in the same chassis, node4 also reboots. However, you can disregard the node4 boot until later.
    Note When you boot node3, you might see the following warning message:
    WARNING: The battery is unfit to retain data during a power outage. This is likely because the battery is discharged but could be due to other temporary conditions.
    When the battery is ready, the boot process will complete and services will be engaged.
    To override this delay, press 'c' followed by 'Enter'
  5. If you see the warning message in Step 4, take the following actions:
    1. Check for any console messages that might indicate a problem other than a low NVRAM battery, and, if necessary, take any required corrective action.
    2. Allow the battery to charge and the boot process to complete.
      Warning Do not override the delay; failure to allow the battery to charge could result in a loss of data.
  6. At the Maintenance mode prompt, enter the following command:
    halt
    The system stops at the boot environment prompt.
  7. Take one of the following actions:
    If the system you are upgrading to is in a…​ Then…​
    Dual-chassis configuration (with controllers in different chassis)
    Go to Step 8.
    Single-chassis configuration (with controllers in the same chassis)
    1. Switch the console cable from node3 to node4.
    2. Turn on the power to node4, and then interrupt the boot process by pressing Ctrl-C at the console terminal to access the boot environment prompt.
      The power should already be on if both controllers are in the same chassis.
      Note Leave node4 at the boot environment prompt; you will return to node4 in Install and boot node4.
    3. If you see the warning message displayed in Step 4, follow the instructions in Step 5
    4. Switch the console cable back from node4 to node3.
    5. Go to Step 8.
  8. Configure node3 for ONTAP:
    set-defaults
  9. If you have NetApp Storage Encryption (NSE) drives installed, perform the following steps:
    Note If you have not already done so earlier in the procedure, see the Knowledge Base article How to tell if a drive is FIPS certified to determine the type of self-encrypting drives that are in use.
    1. Set bootarg.storageencryption.support to true or false:
      If the following drives are in use… Then…
      NSE drives that conform to FIPS 140-2 Level 2 self-encryption requirements
      setenv bootarg.storageencryption.support true
      NetApp non-FIPS SEDs
      setenv bootarg.storageencryption.support false
      Note
      You cannot mix FIPS drives with other types of drives on the same node or HA pair.
      You can mix SEDs with non-encrypting drives on the same node or HA pair.
    2. Contact NetApp Support for assistance with restoring the onboard key management information.
  10. If the version of ONTAP installed on node3 is the same or later than the version of ONTAP 9 installed on node1, list and reassign disks to the new node3:
    boot_ontap
    Warning If this new node has ever been used in any other cluster or HA pair, you must run wipeconfig before proceeding. Failure to do so might result in service outages or data loss. Contact technical support if the replacement controller was previously used, especially if the controllers were running ONTAP running in 7-Mode.
  11. Enter CTRL-C to display the boot menu.
  12. Take one of the following actions:
    If the system you are upgrading…​ Then…​
    Does not have the correct or current ONTAP version on node3
    Go to Step 13.
    Has the correct or current version of ONTAP on node3
    Go to Step 18.
  13. Configure the netboot connection by choosing one of the following actions.
    Note You must use the management port and IP as the netboot connection. Do not use a data LIF IP or else a data outage might occur while the upgrade is being performed.
    If Dynamic Host Configuration Protocol (DHCP) is…​ Then…​
    Running
    Configure the connection automatically by entering the following command at the boot environment prompt:
    ifconfig e0M -auto
    Not running
    Manually configure the connection by entering the following command at the boot environment prompt:
    ifconfig e0M -addr=filer_addr -mask=netmask -gw=gateway -dns=dns_addr -domain=dns_domain
    filer_addr is the IP address of the storage system (mandatory).
    netmask is the network mask of the storage system (mandatory).
    gateway is the gateway for the storage system (mandatory).
    dns_addr is the IP address of a name server on your network (optional).
    dns_domain is the Domain Name Service (DNS) domain name. If you use this optional parameter, you do not need a fully qualified domain name in the netboot server URL; you need only the server's host name.
    Note Other parameters might be necessary for your interface. Enter help ifconfig at the firmware prompt for details.
  14. Perform netboot on node3:
    For…​ Then…​
    FAS/AFF8000 series systems
    netboot http://<web_server_ip>/<path_to_webaccessible_directory>/netboot/kernel
    All other systems
    netboot http://<web_server_ip>/<path_to_webaccessible_directory>/<ontap_version>_image.tgz
    The <path_to_the_web-accessible_directory> leads to where you downloaded the <ontap_version>_image.tgz in Step 1 in the section Prepare for netboot.
    Note Do not interrupt the boot.
  15. From the boot menu, select option (7) Install new software first.
    This menu option downloads and installs the new ONTAP image to the boot device.
    Disregard the following message:
    This procedure is not supported for Non-Disruptive Upgrade on an HA pair
    The note applies to nondisruptive upgrades of ONTAP, and not upgrades of controllers.
    Note Always use netboot to update the new node to the desired image. If you use another method to install the image on the new controller, the wrong image might install. This issue applies to all releases of ONTAP. The netboot procedure combined with option (7) Install new software wipes the boot media and places the same ONTAP version ONTAP on both image partitions.
  16. If you are prompted to continue the procedure, enter y, and when prompted for the package, enter the following URL:
    http://<web_server_ip>/<path_to_web-accessible_directory>/<ontap_version_image>.tgz
  17. Complete the following substeps:
    1. Enter n to skip the backup recovery when you see the following prompt:
      Do you want to restore the backup configuration now? {y|n}
    2. Reboot by entering y when you see the following prompt:
      The node must be rebooted to start using the newly installed software. Do you want to reboot now? {y|n}
      The controller module reboots but stops at the boot menu because the boot device was reformatted and the configuration data needs to be restored.
  18. Select (5) Maintenance mode boot by entering 5, and then enter y when prompted to continue with the boot.
  19. Before continuing, go to Set the FC or UTA/UTA2 configuration on node3 to make any necessary changes to the FC or UTA/UTA2 ports on the node.
    Make the changes recommended in those sections, reboot the node, and go into maintenance mode.
  20. Find the system ID of node3:
    disk show -a
    The system displays the system ID of the node and information about its disks, as shown in the following example:
     *> disk show -a
     Local System ID: 536881109
     DISK     OWNER                    POOL  SERIAL   HOME          DR
     HOME                                    NUMBER
     0b.02.23 nst-fas2520-2(536880939) Pool0 KPG2RK6F nst-fas2520-2(536880939)
     0b.02.13 nst-fas2520-2(536880939) Pool0 KPG3DE4F nst-fas2520-2(536880939)
     0b.01.13 nst-fas2520-2(536880939) Pool0 PPG4KLAA nst-fas2520-2(536880939)
     0a.00.0               (536881109) Pool0 YFKSX6JG              (536881109)
    Note You might see the message disk show: No disks match option -a. after entering the command. This is not an error message so you can continue with the procedure.
  21. Reassign node1's spare disks, any disks belonging to the root, and any non-root aggregates that were not relocated to node2 earlier in Relocate non-root aggregates from node1 to node2.
    Enter the appropriate form of the disk reassign command based on whether your system has shared disks:
    Note If you have shared disks, hybrid aggregates, or both on your system, you must use the correct disk reassign command from the following table.
    If disk type is…​ Then run the command…​
    With shared disks
    disk reassign -s node1_sysid -d node3_sysid -p node2_sysid
    Without shared disks
    For the node1_sysid value, use the information captured in Record node1 information. To obtain the value for node3_sysid, use the sysconfig command.
    Note The -p option is only required in maintenance mode when shared disks are present.
    The disk reassign command reassigns only those disks for which node1_sysid is the current owner.
    The system displays the following message:
    Partner node must not be in Takeover mode during disk reassignment from maintenance mode.
    Serious problems could result!!
    Do not proceed with reassignment if the partner is in takeover mode. Abort reassignment (y/n)?
  22. Enter n.
    After the node becomes operational, you must perform a takeover and giveback of the HA partner node to ensure disk reassignment is successful.
    Do you want to continue (y/n)?
  23. Enter y
    Disk ownership will be updated on all disks previously belonging to Filer with sysid <sysid>.
  24. Enter y.
  25. If you are upgrading from a system with external disks to a system that supports internal and external disks (AFF A800 systems, for example), set the node1 aggregate as root to confirm that node3 boots from the root aggregate of node1.
    Warning Warning: You must perform the following substeps in the exact order shown; failure to do so might cause an outage or even data loss.
    The following procedure sets node3 to boot from the root aggregate of node1:
    1. Check the RAID, plex, and checksum information for the node1 aggregate:
      aggr status -r
    2. Check the status of the node1 aggregate:
      aggr status
    3. Bring the node1 aggregate online, if necessary:
      aggr_online root_aggr_from_node1
    4. Prevent the node3 from booting from its original root aggregate:
      aggr offline root_aggr_on_node3
    5. Set the node1 root aggregate as the new root aggregate for node3:
      aggr options aggr_from_node1 root
    6. Verify that the root aggregate of node3 is offline and the root aggregate for the disks brought over from node1 is online and set to root:
      aggr status
      Note Failing to perform the previous substep might cause node3 to boot from the internal root aggregate, or it might cause the system to assume a new cluster configuration exists or prompt you to identify one.
      The following shows an example of the command output:
          Aggr State               Status          Options
     aggr0_nst_fas8080_15 online   raid_dp, aggr   root, nosnap=on
                                   fast zeroed
                                   64-bit
       aggr0 offline               raid_dp, aggr   diskroot
                                   fast zeroed
                                   64-bit
  26. Verify that the controller and chassis are configured as ha:
    ha-config show
    The following example shows the output of the ha-config show command:
     *> ha-config show
        Chassis HA configuration: ha
        Controller HA configuration: ha
    Systems record in a programmable ROM (PROM) whether they are in an HA pair or stand-alone configuration. The state must be the same on all components within the stand-alone system or HA pair.
    If the controller and chassis are not configured as "ha", use the following commands to correct the configuration:
    ha-config modify controller ha
    ha-config modify chassis ha
    If you have a MetroCluster configuration, use the following commands to modify the controller and chassis:
    ha-config modify controller mcc
    ha-config modify chassis mcc
  27. Destroy the mailboxes on node3:
    mailbox destroy local
    The console displays the following message:
    Destroying mailboxes forces a node to create new empty mailboxes, which clears any takeover state, removes all knowledge of out-of-date plexes of mirrored volumes, and will prevent management services from going online in 2-node cluster HA configurations. Are you sure you want to destroy the local mailboxes?
  28. Enter y at the prompt to confirm that you want to destroy the local mailboxes.
  29. Exit maintenance mode:
    halt
  30. On node2, check the system date, time, and time zone:
    date
  31. On node3, check the date at the boot environment prompt:
    show date
  32. If necessary, set the date on node3:
    set date mm/dd/yyyy
  33. On node3, check the time at the boot environment prompt:
    show time
  34. If necessary, set the time on node3:
    set time hh:mm:ss
  35. Verify the partner system ID is set correctly as noted in Step 21 under -p switch:
    printenv partner-sysid
  36. If necessary, set the partner system ID on node3:
    setenv partner-sysid node2_sysid
    Save the settings:
    saveenv
  37. Access the boot menu at the boot environment prompt:
    boot_ontap menu
  38. At the boot menu, select option (6) Update flash from backup config by entering 6 at the prompt.
    This will replace all flash-based configuration with the last backup to disks. Are you sure you want to continue?:
  39. Enter y at the prompt.
    The boot proceeds normally, and the system then asks you to confirm the system ID mismatch.
    Note The system might reboot twice before displaying the mismatch warning.
  40. Confirm the mismatch as shown in the following example:
    WARNING: System id mismatch. This usually occurs when replacing CF or NVRAM cards!
    Override system id (y|n) ? [n] y
    The node might go through one round of reboot before booting normally.
  41. Log in to node3.