StorageGRID appliances
Configure network links for a StorageGRID appliance
Contributors netapp-perveilerk netapp-ivanad
You can configure network links for the ports used to connect the appliance to the Grid Network, the Client Network, and the Admin Network. You can set the link speed as well as the port and network bond modes.
Tip If you are using ConfigBuilder to generate a JSON file, you can configure the network links automatically. See Automate appliance installation and configuration.
Before you begin
  • You have obtained the additional equipment required for your cable type and link speed.
  • You have installed the correct transceivers in the ports, based on the link speed you plan to use.
  • You have connected the network ports to switches that support your chosen speed.
If you plan to use Aggregate port bond mode, LACP network bond mode, or VLAN tagging:
  • You have connected the network ports on the appliance to switches that can support VLAN and LACP.
  • If multiple switches are participating in the LACP bond, the switches support multi-chassis link aggregation groups (MLAG), or equivalent.
  • You understand how to configure the switches to use VLAN, LACP, and MLAG or equivalent.
  • You know the unique VLAN tag to use for each network. This VLAN tag will be added to each network packet to ensure that network traffic is routed to the correct network.
About this task
You only need to configure the settings on the Link Configuration page if you want to use values other than the default settings.
Note LACP PDU rate changes that are made following these instructions remain persistent in the StorageGRID environment. To make temporary changes to the LACP PDU rate when performing maintenance operations on network components installed in your appliance, see Temporarily changing the LACP PDU rate.
The figures and tables summarize the options for the port bond mode and network bond mode for each appliance. See the following for more information:
SG100 and SG1000
Fixed port bond mode (default)
The figures show how the four network ports on the SG1000 or SG100 are bonded in fixed port bond mode (default configuration).
SG1000:
SG1000 Fixed Port Bond Mode
SG100:
SG100 Fixed Port Bond Mode
Callout Which ports are bonded
C
Ports 1 and 3 are bonded together for the Client Network, if this network is used.
G
Ports 2 and 4 are bonded together for the Grid Network.
The table summarizes the options for configuring the four network ports. You only need to configure the settings on the Link Configuration page if you want to use a non-default setting.
Network bond mode Client Network disabled Client Network enabled (default)
Active-Backup (default)
  • Ports 2 and 4 use an active-backup bond for the Grid Network.
  • Ports 1 and 3 aren't used.
  • A VLAN tag is optional.
  • Ports 1 and 3 use an active-backup bond for the Client Network.
  • VLAN tags can be specified for both networks for the convenience of the network administrator.
LACP (802.3ad)
  • Ports 2 and 4 use an LACP bond for the Grid Network.
  • LACP PDU rate and LACP transmit hash policy values can be specified in the Grid Network section.
  • Ports 1 and 3 use an LACP bond for the Client Network.
  • LACP PDU rate and LACP transmit hash policy values can be specified in the Grid Network and Client Network sections.
These figures show how the four network ports are bonded in aggregate port bond mode.
SG1000:
Aggregate Port Bond Mode SG1000
SG100:
1
All four ports are grouped in a single LACP bond, allowing all ports to be used for Grid Network and Client Network traffic.
LACP (802.3ad) only
  • Ports 1-4 use a single LACP bond for the Grid Network.
  • A single VLAN tag identifies Grid Network packets.
  • LACP PDU rate and LACP transmit hash policy values can be specified in the Link settings section.
  • Ports 1-4 use a single LACP bond for the Grid Network and the Client Network.
  • Two VLAN tags allow Grid Network packets to be segregated from Client Network packets.
Active-Backup network bond mode for management ports
These figures show how the two 1-GbE management ports on the appliances are bonded in Active-Backup network bond mode for the Admin Network.
SG1000:
Admin Network Ports Bonded SG1000
SG100:
SG110 and SG1100
The figures show how the four network ports on the SG1100 or SG110 are bonded in fixed port bond mode (default configuration).
SG1100:
SG1100 Fixed Port Bond Mode
SG110:
SG110 Fixed Port Bond Mode
C
G
LACP (802.3ad)
SG1100:
Aggregate Port Bond Mode SG1100
SG110:
SG110 Aggregate Port Bond Mode
1
The table summarizes the options for configuring the network ports. You only need to configure the settings on the Link Configuration page if you want to use a non-default setting.
LACP (802.3ad) only
SG1100:
Admin Network Ports Bonded SG1100
SG110:
SG120 and SG1200
The figures show how the four network ports on the SG120 and SG1200 are bonded in fixed port bond mode (default configuration).
SG120:
SG120 Fixed Port Bond Mode
SG1200:
SG1200 Fixed Port Bond Mode
C
G
LACP (802.3ad)
SG120:
SG120 Aggregate Port Bond Mode
SG1200:
SG1200Aggregate Port Bond Mode
1
LACP (802.3ad) only
SG120:
Admin Network Ports Bonded SG120
SG1200:
Admin Network Ports Bonded SG1200
SG5700
This figure shows how the four 10/25-GbE ports are bonded in Fixed port bond mode (default configuration).
Image showing how the 10/25-GbE ports on the E5700SG controller are bonded in fixed mode
C
G
The table summarizes the options for configuring the four 10/25-GbE ports. You only need to configure the settings on the Link Configuration page if you want to use a non-default setting.
LACP (802.3ad)
This figure shows how the four 10/25-GbE ports are bonded in Aggregate port bond mode.
Image showing how the 10/25-GbE ports on the E5700SG controller are bonded in aggregate mode
1
LACP (802.3ad) only
This figure shows how the two 1-GbE management ports on the E5700SG controller are bonded in Active-Backup network bond mode for the Admin Network.
E5700SG Bonded management Ports
SG5800
Image showing how the 10/25-GbE ports on the SG5800 controller are bonded in fixed mode
C
G
LACP (802.3ad)
Image showing how the 10/25-GbE ports on the SG5800 controller are bonded in aggregate mode
1
LACP (802.3ad) only
SG6000
This figure shows how the four network ports are bonded in fixed port bond mode (default configuration)
Image showing how the network ports on the SG6000-CN controller are bonded in fixed mode
C
G
LACP (802.3ad)
This figure shows how the four network ports are bonded in aggregate port bond mode.
Image showing how the network ports on the SG6000-CN controller are bonded in aggregate mode
1
LACP (802.3ad) only
This figure shows how the two 1-GbE management ports on the SG6000-CN controller are bonded in Active-Backup network bond mode for the Admin Network.
SG6100
The figure shows how the four network ports are bonded in fixed port bond mode (default configuration).
SGF6112:
SGF6112 Fixed Port Bond Mode
SG6100:
SG6100-CN Fixed Port Bond Mode
C
G
LACP (802.3ad)
The figure shows how the four network ports are bonded in aggregate port bond mode.
SGF6112:
SGF6112 Aggregate Port Bond Mode
SG6100:
SG6100-CN Aggregate Port Bond Mode
1
LACP (802.3ad) only
This figure shows how the two 1-GbE management ports are bonded in Active-Backup network bond mode for the Admin Network.
SGF6112:
Admin Network Ports Bonded SGF6112
SG6100:
Admin Network Ports Bonded SG6100-CN
SG6200
SGF6212:
SGF6212 Fixed Port Bond Mode
SG6200-CN:
SG6200-CN Fixed Port Bond Mode
C
G
LACP (802.3ad)
SGF6212:
SGF6212 Aggregate Port Bond Mode
SG6200:
SG6200-CN Aggregate Port Bond Mode
1
LACP (802.3ad) only
SGF6212:
Admin Network Ports Bonded SGF6212
SG6200:
Admin Network Ports Bonded SG6200-CN
Steps
  1. From the menu bar of the StorageGRID Appliance Installer, click Configure Networking > Link Configuration.
    The Network Link Configuration page displays a diagram of your appliance with the network and management ports numbered.
    The Link Status table lists the link state, link speed, and other statistics of the numbered ports.
    Note For the SG5800, the link state for port 1 is unavailable in software and must be physically verified using the status LED on the SG5800 controller.
    The first time you access this page, the default values are:
    • Link Speed is set to Auto.
    • Port bond mode is set to Fixed.
    • LACP transmit hash policy is set to Layer2+3.
    • LACP PDU rate is set to Fast.
    • Network bond mode is set to Active-Backup for the Grid Network.
    • The Admin Network is enabled, and the network bond mode is set to Independent.
    • The Client Network is enabled.
  2. Select the link speed for the network ports from the Link speed drop-down list.
    The network switches you are using for the Grid Network and the Client Network must also support and be configured for this speed. You must use the appropriate adapters or transceivers for the configured link speed. Use Auto link speed when possible because this option negotiates both link speed and Forward Error Correction (FEC) mode with the link partner.
    If you plan to use the 25-GbE link speed for the SG6200, SG6100, SG6000, SG5800, or SG5700 network ports:
    • Use SFP28 transceivers and SFP28 TwinAx cables or optical cables.
    • For the SG5700, select 25GbE from the Link speed drop-down list.
    • For the SG5800, SG6000, SG6100, or SG6200, select Auto from the Link speed drop-down list.
  3. Enable or disable the StorageGRID networks you plan to use.
    The Grid Network is required. You can't disable this network.
    1. If the appliance is not connected to the Admin Network, clear the Enable network checkbox for the Admin Network.
    2. If the appliance is connected to the Client Network, select the Enable network checkbox for the Client Network.
      The Client Network settings for the data NIC ports are now shown.
  4. Refer to the fixed and aggregate port bond mode configuration table for each appliance type, and configure the port bond mode and the network bond mode to match your network configuration.
    You must specify a unique VLAN tags for the Grid and the Client Networks. You can select values between 0 and 4095.
  5. When you are satisfied with your selections, click Save.
    Note You might lose your connection if you made changes to the network or link you are connected through. If you aren't reconnected within 1 minute, re-enter the URL for the StorageGRID Appliance Installer using one of the other IP addresses assigned to the appliance:
    https://appliance_IP:8443