ONTAP MetroCluster
Prepare the MetroCluster IP system for upgrade
Contributors netapp-aoife netapp-revathid
Before making any changes to the existing MetroCluster configuration, check the health of the configuration, prepare the new platforms, and perform other miscellaneous tasks.
Update the MetroCluster switch RCFs before upgrading controllers
Depending on the old and new platform models, you might need to update the MetroCluster switch reference configuration files (RCFs) before you upgrade controllers.
About this task
Perform this task in the following circumstances:
  • The switch RCF configuration is not on the minimum version.
  • You need to change VLAN IDs used by the back-end MetroCluster connections.
Before you begin
Determine whether you need to update the RCFs before you upgrade your controllers:
  • If the switch configuration wasn't configured with the minimum supported RCF version, you need to update the RCFs before you upgrade your controllers:
    Switch model
    Required RCF version
    Cisco 3132Q-V
    1.7 or later
    Cisco 3232C
    1.7 or later
    Broadcom BES-53248
    1.3 or later
    NVIDIA SN2100
    2.0 or later
  • If both of your old and new platform models are in the following list, you do not need to update the VLAN ID before you upgrade controllers:
    • FAS8200 or AFF A300
    • AFF A320
    • FAS9000 or AFF A700
    • AFF A800, AFF C800, ASA A800, or ASA C800
      If either of your old or new platform models are not listed above, you must confirm that the MetroCluster interfaces are using a supported VLAN ID. Supported VLAN IDs for the MetroCluster interfaces are: 10, 20, or in the range of 101 to 4096.
      Caution
      • If the VLAN ID is not 10, 20, or in the range of 101 to 4096, you must upgrade the switch RCF before you upgrade controllers.
      • The local cluster connections can use any VLAN, they don't need to be in the given range.
      • The new RCF that you are upgrading to must use the VLANs 10, 20, or be in the range 101 to 4096. Don't change the VLAN for the local cluster unless it is required.
Steps
  1. Prepare the IP switches for the application of the new RCFs.
    Follow the steps in the section for your switch vendor:
    Note You should update the switches in the following order: switch_A_1, switch_B_1, switch_A_2, switch_B_2.
  2. Download and install the RCFs.
Map ports from the old nodes to the new nodes
You must verify that the physical ports on node_A_1-old map correctly to the physical ports on node_A_1-new. This allows node_A_1-new to communicate with other nodes in the cluster and with the network after the upgrade.
About this task
When the new node first boots during the upgrade process, it replays the most recent configuration of the old node it's replacing. When you boot node_A_1-new, ONTAP attempts to host LIFs on the same ports that were used on node_A_1-old. This means that you have to adjust the port and LIF configuration as part of the upgrade so it's compatible with the configuration of the old node. During the upgrade procedure, you perform steps on both the old and new nodes to ensure correct configuration for the cluster, management, and data LIFs
The following table shows examples of configuration changes related to the port requirements of the new nodes.
Cluster interconnect physical ports
Old controller
New controller
Required action
e0a, e0b
e3a, e3b
No matching port. After the upgrade, you must recreate the cluster ports.
e0c, e0d
e0a,e0b,e0c,e0d
e0c and e0d are matching ports. You don't have to change the configuration, but after the upgrade you can spread your cluster LIFs across the available cluster ports.
Steps
  1. Determine what physical ports are available on the new controllers and what LIFs can be hosted on the ports.
    The controller's port usage depends on the platform module and which switches you will use in the MetroCluster IP configuration. You can gather the port usage of the new platforms from the Hardware Universe.
  2. Plan your port usage and fill in the following tables for reference for each of the new nodes.
    You will refer to the table as you carry out the upgrade procedure.
    node_A_1-old
    node_A_1-new
    LIF
    Ports
    IPspaces
    Broadcast domains
    Ports
    IPspaces
    Broadcast domains
    Cluster 1
    Cluster 2
    Cluster 3
    Cluster 4
    Node management
    Cluster management
    Data 1
    Data 2
    Data 3
    Data 4
    SAN
    Intercluster port
Netboot the new controllers
After you install the new nodes, you need to netboot to ensure the new nodes are running the same version of ONTAP as the original nodes. The term netboot means you are booting from an ONTAP image stored on a remote server. When preparing for netboot, you must put a copy of the ONTAP 9 boot image onto a web server that the system can access.
Steps
  1. Netboot the new controllers:
    1. Access the NetApp Support Site to download the files used for performing the netboot of the system.
    2. Download the appropriate ONTAP software from the software download section of the NetApp Support Site and store the ontap-version_image.tgz file on a web-accessible directory.
    3. Change to the web-accessible directory and verify that the files you need are available.
      Your directory listing should contain a netboot folder with a kernel file:
      _ontap-version_image.tgz
      You don't need to extract the _ontap-version_image.tgz file.
    4. At the LOADER prompt, configure the netboot connection for a management LIF:
      If IP addressing is…​
      Then…​
      DHCP
      Configure the automatic connection:
      ifconfig e0M -auto
      Static
      Configure the manual connection:
      ifconfig e0M -addr=ip_addr -mask=netmask -gw=gateway
    5. Perform the netboot.
      netboot http://_web_server_ip/path_to_web-accessible_directory/ontap-version_image.tgz
    6. From the boot menu, select option (7) Install new software first to download and install the new software image to the boot device.
      Disregard the following message:
      "This procedure is not supported for Non-Disruptive Upgrade on an HA pair". It applies to nondisruptive upgrades of software, not to upgrades of controllers.
    7. If you are prompted to continue the procedure, enter y, and when prompted for the package, enter the URL of the image file:
      http://web_server_ip/path_to_web-accessible_directory/ontap-version_image.tgz
    8. Enter the user name and password if applicable, or press Enter to continue.
    9. Enter n to skip the backup recovery when you see a prompt similar to the following:
      Do you want to restore the backup configuration now? {y|n} n
    10. Reboot by entering y when you see a prompt similar to the following:
      The node must be rebooted to start using the newly installed software. Do you want to reboot now? {y|n} y
      Note You must reboot the node in order to use the newly installed software.
Clear the configuration on a controller module
Before using a new controller module in the MetroCluster configuration, you must clear the existing configuration.
Steps
  1. If necessary, halt the node to display the LOADER prompt:
    halt
  2. At the LOADER prompt, set the environmental variables to default values:
    set-defaults
  3. Save the environment:
    saveenv
  4. At the LOADER prompt, launch the boot menu:
    boot_ontap menu
  5. At the boot menu prompt, clear the configuration:
    wipeconfig
    Respond yes to the confirmation prompt.
    The node reboots and the boot menu is displayed again.
  6. At the boot menu, select option 5 to boot the system into Maintenance mode.
Verify MetroCluster health before site upgrade
You verify the health and connectivity of the MetroCluster configuration before performing the upgrade.
Caution After you upgrade the controllers at the first site and before you upgrade the second, running metrocluster check run followed by metrocluster check show returns an error in the config-replication field. This error indicates an NVRAM size mismatch between the nodes at each site and it's the expected behavior when there are different platform models on both sites. You can ignore the error until the controller upgrade is completed for all nodes in the DR group.
Steps
  1. Verify the operation of the MetroCluster configuration in ONTAP:
    1. Check whether the nodes are multipathed:
      node run -node <node_name> sysconfig -a
      Issue this command for each node in the MetroCluster configuration.
    2. Verify that there are no broken disks in the configuration:
      storage disk show -broken
      Issue this command on each node in the MetroCluster configuration.
    3. Check for any health alerts:
      system health alert show
      Issue this command on each cluster.
    4. Verify the licenses on the clusters:
      system license show
    5. Verify the devices connected to the nodes:
      network device-discovery show
    6. Verify that the time zone and time is set correctly on both sites:
      cluster date show
      Issue this command on each cluster. You can use the cluster date commands to configure the time and time zone.
  2. Confirm the operational mode of the MetroCluster configuration and perform a MetroCluster check.
    1. Confirm the MetroCluster configuration and that the operational mode is normal:
      metrocluster show
    2. Confirm that all expected nodes are shown:
      metrocluster node show
    3. Issue the following command:
    4. Display the results of the MetroCluster check:
  3. Check the MetroCluster cabling with the Config Advisor tool.
    1. Download and run Config Advisor.
    2. After running Config Advisor, review the tool's output and follow the recommendations in the output to address any issues discovered.
Gather information before the upgrade
Before upgrading, you must gather information for each of the nodes, and, if necessary, adjust the network broadcast domains, remove any VLANs and interface groups, and gather encryption information.
Steps
  1. Record the physical cabling for each node, labelling cables as needed to allow correct cabling of the new nodes.
  2. Gather interconnect, port, and LIF information for each node.
    Gather the output of the following commands for each node:
    • metrocluster interconnect show
    • metrocluster configuration-settings connection show
    • network interface show -role cluster,node-mgmt
    • network port show -node <node_name> -type physical
    • network port vlan show -node <node_name>
    • network port ifgrp show -node <node_name> -instance
    • network port broadcast-domain show
    • network port reachability show -detail
    • network ipspace show
    • volume show
    • storage aggregate show
    • system node run -node <node_name> sysconfig -a
    • aggr show -r
    • disk show
    • system node run <node-name> disk show
    • vol show -fields type
    • vol show -fields type , space-guarantee
    • vserver fcp initiator show
    • storage disk show
    • metrocluster configuration-settings interface show
  3. Gather the UUIDs for the site_B (the site whose platforms are currently being upgraded):
    metrocluster node show -fields node-cluster-uuid, node-uuid
    These values must be configured accurately on the new site_B controller modules to ensure a successful upgrade. Copy the values to a file so that you can copy them into the commands later in the upgrade process.
    The following example shows the command output with the UUIDs:
    cluster_B::> metrocluster node show -fields node-cluster-uuid, node-uuid
      (metrocluster node show)
    dr-group-id cluster     node   node-uuid                            node-cluster-uuid
    1           cluster_A node_A_1 f03cb63c-9a7e-11e7-b68b-00a098908039 ee7db9d5-9a82-11e7-b68b-00a098908039
    1           cluster_A node_A_2 aa9a7a7a-9a81-11e7-a4e9-00a098908c35 ee7db9d5-9a82-11e7-b68b-00a098908039
    1           cluster_B node_B_1 f37b240b-9ac1-11e7-9b42-00a098c9e55d 07958819-9ac6-11e7-9b42-00a098c9e55d
    1           cluster_B node_B_2 bf8e3f8f-9ac4-11e7-bd4e-00a098ca379f 07958819-9ac6-11e7-9b42-00a098c9e55d
    4 entries were displayed.
    cluster_B::*
    NetApp recommends that you record the UUIDs in a table similar to the following:
    Cluster or node
    UUID
    cluster_B
    node_B_1
    node_B_2
    cluster_A
    node_A_1
    node_A_2
  4. If the MetroCluster nodes are in a SAN configuration, collect the relevant information.
    Gather the output of the following commands:
    • fcp adapter show -instance
    • fcp interface show -instance
    • iscsi interface show
    • ucadmin show
  5. If the MetroCluster nodes are configured with an external key manager for the admin SVM (cluster), copy the key server information to a secure location. If the Onboard Key Manager is configured, copy the backup information and passphrase to a secure location.
    Onboard Key Manager
    1. Run the following command to display the Onboard Key Manager backup:
      security key-manager onboard show-backup
      You'll also need the most up-to-date Onboard Key Manager passphrase later in the upgrade procedure.
      For additional information, see Back up onboard key management information manually.
    External key manager
    Gather the external key management information that you'll need to restore the key manager configuration later in the procedure.
    1. Display the name of the admin SVM (cluster).
      vserver show -type admin
      In this example, the admin SVM name is cluster_B:
      cluster_B::*> vserver show -type admin
                                     Admin      Operational Root
      Vserver     Type    Subtype    State      State       Volume     Aggregate
      cluster_B
                  admin   -          -          -           -          -
    2. Obtain the address and port number of a primary key server associated with the external key manager configured on the admin SVM (cluster):
      Note
      • The admin SVM can have up to four primary key servers but you'll only need the port number and address of one of the primary key servers to restore the key management configuration later in the procedure.
      • If there is a username and password associated with the primary key server you choose, you'll also need that information for the recovery process.
      security key-manager external show -instance -vserver <admin_svm_name>
      cluster_B::> security key-manager external show -instance -vserver cluster_B
                        Vserver: cluster_B
             Client Certificate: NTAPKM_C
         Server CA Certificates: NTAPKM_I, NTAPKM_R
             Primary Key Server: 172.18.27.34:12014
                        Timeout: 25
                       Username:
                    Policy name: -
          Secondary Key Servers: -
          Create/Remove Timeout: 10
    3. If you are running ONTAP 9.16.1 or later, obtain the keystore UUID for the admin SVM.
      security key-manager show-key-store -vserver <admin_svm_name> -fields uuid
      cluster_B::*>  security key-manager show-key-store -vserver cluster_B -fields uuid
      vserver         uuid
      cluster_B        f281aa55-d635-11f0-93bc-005056bb68f2
      cluster_B::*
    4. Save the information you gathered in a secure location for use later in the procedure. You should now have gathered the following information:
      • The port number and address of one of the primary key servers for the admin SVM
      • The user name and password if one is associated with the chosen primary key server
      • The keystore UUID for the admin SVM (required in ONTAP 9.16.1 or later)
  6. Gather the system IDs of the existing nodes:
    metrocluster node show -fields node-systemid,ha-partner-systemid,dr-partner-systemid,dr-auxiliary-systemid
    The following output shows the reassigned drives.
    ::> metrocluster node show -fields node-systemid,ha-partner-systemid,dr-partner-systemid,dr-auxiliary-systemid
    dr-group-id cluster     node     node-systemid ha-partner-systemid dr-partner-systemid dr-auxiliary-systemid
    1           cluster_A node_A_1   537403324     537403323           537403321           537403322
    1           cluster_A node_A_2   537403323     537403324           537403322           537403321
    1           cluster_B node_B_1   537403322     537403321           537403323           537403324
    1           cluster_B node_B_2   537403321     537403322           537403324           537403323
Remove Mediator or Tiebreaker monitoring
Before the upgrading the platforms, you must remove monitoring if the MetroCluster configuration is monitored with the Tiebreaker or Mediator utility.
Steps
  1. Change to the advanced privilege level:
    set -privilege advanced
  2. Collect the output for the following command:
    storage iscsi-initiator show
  3. Remove the existing MetroCluster configuration from Tiebreaker, Mediator, or other software that can initiate switchover.
    If you are using…​
    Use this procedure…​
    Tiebreaker
    Mediator
    Issue the following command from the ONTAP prompt:
    metrocluster configuration-settings mediator remove
    Third-party applications
    Refer to the product documentation.
Send a custom AutoSupport message prior to maintenance
Before performing the maintenance, you should issue an AutoSupport message to notify NetApp technical support that maintenance is underway. Informing technical support that maintenance is underway prevents them from opening a case on the assumption that a disruption has occurred.
About this task
This task must be performed on each MetroCluster site.
Steps
  1. Log in to the cluster.
  2. Invoke an AutoSupport message indicating the start of the maintenance:
    system node autosupport invoke -node * -type all -message MAINT=maintenance-window-in-hours
    The maintenance-window-in-hours parameter specifies the length of the maintenance window, with a maximum of 72 hours. If the maintenance is completed before the time has elapsed, you can invoke an AutoSupport message indicating the end of the maintenance period:
    system node autosupport invoke -node * -type all -message MAINT=end
  3. Repeat these steps on the partner site.