Install or upgrade the RCF on Cisco Nexus 3232C cluster switches
Install the reference configuration file (RCF) on Cisco Nexus 3232C cluster switches after initial setup, or upgrade your RCF version when a newer version is available.
You can also use this procedure to upgrade your RCF version. Refer to the Knowledge Base article How to clear configuration on a Cisco interconnect switch while retaining remote connectivity for further information when upgrading your RCF.
Review requirements
A current backup of the switch configuration.
A fully functioning cluster (no errors in the logs or similar issues).
The current Reference Configuration File (RCF).
A console connection to the switch, required when installing the RCF.
Cisco Ethernet switch page Consult the switch compatibility table for the supported ONTAP and RCF versions. Note that there can be command dependencies between the command syntax in the RCF and that found in versions of NX-OS.
Cisco Nexus 3000 Series Switches. Refer to the appropriate software and upgrade guides available on the Cisco web site for complete documentation on the Cisco switch upgrade and downgrade procedures.
Install the file
The examples in this procedure use the following switch and node nomenclature:
The names of the two Cisco switches are
cs1andcs2. -
The node names are
cluster1-01,cluster1-02,cluster1-03, andcluster1-04. -
The cluster LIF names are
cluster1-01_clus1,cluster1-01_clus2,cluster1-02_clus1,cluster1-02_clus2,cluster1-03_clus1,cluster1-03_clus2,cluster1-04_clus1, andcluster1-04_clus2. -
The
cluster1::*>prompt indicates the name of the cluster.
The procedure requires the use of both ONTAP commands and Cisco Nexus 3000 Series Switches commands; ONTAP commands are used unless otherwise indicated.
No operational inter-switch link (ISL) is needed during this procedure. This is by design because RCF version changes can affect ISL connectivity temporarily. To ensure non-disruptive cluster operations, the following procedure migrates all of the cluster LIFs to the operational partner switch while performing the steps on the target switch.
Be sure to complete the procedure in Prepare to install NX-OS and RCF, and then follow the steps below.
Display the cluster ports on each node that are connected to the cluster switches:
network device-discovery showShow example
cluster1::*> network device-discovery show Node/ Local Discovered Protocol Port Device (LLDP: ChassisID) Interface Platform ----------- ------ ------------------------- ---------------- -------- cluster1-01/cdp e0a cs1 Ethernet1/7 N3K-C3232C e0d cs2 Ethernet1/7 N3K-C3232C cluster1-02/cdp e0a cs1 Ethernet1/8 N3K-C3232C e0d cs2 Ethernet1/8 N3K-C3232C cluster1-03/cdp e0a cs1 Ethernet1/1/1 N3K-C3232C e0b cs2 Ethernet1/1/1 N3K-C3232C cluster1-04/cdp e0a cs1 Ethernet1/1/2 N3K-C3232C e0b cs2 Ethernet1/1/2 N3K-C3232C cluster1::*> -
Check the administrative and operational status of each cluster port.
Verify that all the cluster ports are up with a healthy status:
network port show –role clusterShow example
cluster1::*> network port show -role cluster Node: cluster1-01 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/100000 healthy false e0d Cluster Cluster up 9000 auto/100000 healthy false Node: cluster1-02 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/100000 healthy false e0d Cluster Cluster up 9000 auto/100000 healthy false 8 entries were displayed. Node: cluster1-03 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/10000 healthy false e0b Cluster Cluster up 9000 auto/10000 healthy false Node: cluster1-04 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/10000 healthy false e0b Cluster Cluster up 9000 auto/10000 healthy false cluster1::*> -
Verify that all the cluster interfaces (LIFs) are on the home port:
network interface show -role clusterShow example
cluster1::*> network interface show -role cluster Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ------------------ ---------- ----------------- ------------ ------- ---- Cluster cluster1-01_clus1 up/up 169.254.3.4/23 cluster1-01 e0a true cluster1-01_clus2 up/up 169.254.3.5/23 cluster1-01 e0d true cluster1-02_clus1 up/up 169.254.3.8/23 cluster1-02 e0a true cluster1-02_clus2 up/up 169.254.3.9/23 cluster1-02 e0d true cluster1-03_clus1 up/up 169.254.1.3/23 cluster1-03 e0a true cluster1-03_clus2 up/up 169.254.1.1/23 cluster1-03 e0b true cluster1-04_clus1 up/up 169.254.1.6/23 cluster1-04 e0a true cluster1-04_clus2 up/up 169.254.1.7/23 cluster1-04 e0b true 8 entries were displayed. cluster1::*> -
Verify that the cluster displays information for both cluster switches:
system cluster-switch show -is-monitoring-enabled-operational trueShow example
cluster1::*> system cluster-switch show -is-monitoring-enabled-operational true Switch Type Address Model --------------------------- ------------------ ---------------- --------------- cs1 cluster-network 10.233.205.92 NX3232C Serial Number: FOXXXXXXXGS Is Monitored: true Reason: None Software Version: Cisco Nexus Operating System (NX-OS) Software, Version 9.3(4) Version Source: CDP cs2 cluster-network 10.233.205.93 NX3232C Serial Number: FOXXXXXXXGD Is Monitored: true Reason: None Software Version: Cisco Nexus Operating System (NX-OS) Software, Version 9.3(4) Version Source: CDP 2 entries were displayed.
Disable auto-revert on the cluster LIFs.
Show example
cluster1::*> network interface modify -vserver Cluster -lif * -auto-revert false
On cluster switch cs2, shut down the ports connected to the cluster ports of the nodes.
Show example
cs2(config)# interface eth1/1/1-2,eth1/7-8 cs2(config-if-range)# shutdown
Verify that the cluster ports have migrated to the ports hosted on cluster switch cs1. This might take a few seconds.
cluster1::*> network interface show -role cluster Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ----------------- ---------- ------------------ ------------- ------- ---- Cluster cluster1-01_clus1 up/up 169.254.3.4/23 cluster1-01 e0a true cluster1-01_clus2 up/up 169.254.3.5/23 cluster1-01 e0a false cluster1-02_clus1 up/up 169.254.3.8/23 cluster1-02 e0a true cluster1-02_clus2 up/up 169.254.3.9/23 cluster1-02 e0a false cluster1-03_clus1 up/up 169.254.1.3/23 cluster1-03 e0a true cluster1-03_clus2 up/up 169.254.1.1/23 cluster1-03 e0a false cluster1-04_clus1 up/up 169.254.1.6/23 cluster1-04 e0a true cluster1-04_clus2 up/up 169.254.1.7/23 cluster1-04 e0a false 8 entries were displayed. cluster1::*> -
Verify that the cluster is healthy:
cluster showShow example
cluster1::*> cluster show Node Health Eligibility Epsilon -------------------- ------- ------------ ------- cluster1-01 true true false cluster1-02 true true false cluster1-03 true true true cluster1-04 true true false 4 entries were displayed. cluster1::*>
If you have not already done so, save a copy of the current switch configuration by copying the output of the following command to a text file:
show running-config -
Record any custom additions between the current
running-configand the RCF file in use. -
Save basic configuration details to the
write_erase.cfgfile on the bootflash.When upgrading or applying a new RCF, you must erase the switch settings and perform basic configuration. You must be connected to the switch serial console port to set up the switch again. cs2# show run | section "switchname" > bootflash:write_erase.cfgcs2# show run | section "hostname" >> bootflash:write_erase.cfgcs2# show run | i "username admin password" >> bootflash:write_erase.cfgcs2# show run | section "vrf context management" >> bootflash:write_erase.cfgcs2# show run | section "interface mgmt0" >> bootflash:write_erase.cfg -
For RCF version 1.12 and later, run the following commands:
cs2# echo "hardware access-list tcam region racl-lite 512" >> bootflash:write_erase.cfgcs2# echo "hardware access-list tcam region qos 256" >> bootflash:write_erase.cfgRefer to the Knowledge Base article How to clear configuration on a Cisco interconnect switch while retaining remote connectivity for further details.
Verify that the
write_erase.cfgfile is populated as expected:show file bootflash:write_erase.cfg -
Issue the
write erasecommand to erase the current saved configuration:cs2# write eraseWarning: This command will erase the startup-configuration.Do you wish to proceed anyway? (y/n) [n] y -
Copy the previously saved basic configuration into the startup configuration.
cs2# copy bootflash:write_erase.cfg startup-config -
Perform a reboot of the switch:
cs2# reloadThis command will reboot the system. (y/n)? [n] y -
Copy the RCF to the bootflash of switch cs2 using one of the following transfer protocols: FTP, TFTP, SFTP, or SCP. For more information on Cisco commands, refer to the appropriate guide in the Cisco Nexus 3000 Series NX-OS Command Reference
Show example
This example shows TFTP being used to copy an RCF to the bootflash on switch cs2:
cs2# copy tftp: bootflash: vrf management Enter source filename: Nexus_3232C_RCF_v1.6-Cluster-HA-Breakout.txt Enter hostname for the tftp server: 172.22.201.50 Trying to connect to tftp server......Connection to Server Established. TFTP get operation was successful Copy complete, now saving to disk (please wait)...
Apply the RCF previously downloaded to the bootflash.
Show example
This example shows the RCF file
Nexus_3232C_RCF_v1.6-Cluster-HA-Breakout.txtbeing installed on switch cs2:cs2# copy Nexus_3232C_RCF_v1.6-Cluster-HA-Breakout.txt running-config echo-commands
Examine the banner output from the
show banner motdcommand. You must read and follow the instructions under Important Notes to make sure the proper configuration and operation of the switch.Show example
cs2# show banner motd ****************************************************************************** * NetApp Reference Configuration File (RCF) * * Switch : Cisco Nexus 3232C * Filename : Nexus_3232C_RCF_v1.6-Cluster-HA-Breakout.txt * Date : Oct-20-2020 * Version : v1.6 * * Port Usage : Breakout configuration * Ports 1- 3: Breakout mode (4x10GbE) Intra-Cluster Ports, int e1/1/1-4, * e1/2/1-4, e1/3/1-4 * Ports 4- 6: Breakout mode (4x25GbE) Intra-Cluster/HA Ports, int e1/4/1-4, * e1/5/1-4, e1/6/1-4 * Ports 7-30: 40/100GbE Intra-Cluster/HA Ports, int e1/7-30 * Ports 31-32: Intra-Cluster ISL Ports, int e1/31-32 * Ports 33-34: 10GbE Intra-Cluster 10GbE Ports, int e1/33-34 * * IMPORTANT NOTES * - Load Nexus_3232C_RCF_v1.6-Cluster-HA.txt for non breakout config * * - This RCF utilizes QoS and requires TCAM re-configuration, requiring RCF * to be loaded twice with the Cluster Switch rebooted in between. * * - Perform the following 4 steps to ensure proper RCF installation: * * (1) Apply RCF first time, expect following messages: * - Please save config and reload the system... * - Edge port type (portfast) should only be enabled on ports... * - TCAM region is not configured for feature QoS class IPv4 ingress... * * (2) Save running-configuration and reboot Cluster Switch * * (3) After reboot, apply same RCF second time and expect following messages: * - % Invalid command at '^' marker * - Syntax error while parsing... * * (4) Save running-configuration again ******************************************************************************
When applying the RCF for the first time, the ERROR: Failed to write VSH commands message is expected and can be ignored. -
Verify that the RCF file is the correct newer version:
show running-configWhen you check the output to verify you have the correct RCF, make sure that the following information is correct:
The RCF banner
The node and port settings
Customizations
The output varies according to your site configuration. Check the port settings and refer to the release notes for any changes specific to the RCF that you have installed.
Reapply any previous customizations to the switch configuration. Refer to Review cabling and configuration considerations for details of any further changes required.
After you verify the RCF versions and switch settings are correct, copy the running-config file to the startup-config file.
cs2# copy running-config startup-config [########################################] 100% Copy complete
Reboot switch cs2. You can ignore the "cluster ports down" events reported on the nodes while the switch reboots.
cs2# reload This command will reboot the system. (y/n)? [n] y
Apply the same RCF and save the running configuration for a second time.
Show example
cs2# copy Nexus_3232C_RCF_v1.6-Cluster-HA-Breakout.txt running-config echo-commands cs2# copy running-config startup-config [########################################] 100% Copy complete
Verify the health of cluster ports on the cluster.
Verify that e0d ports are up and healthy across all nodes in the cluster:
network port show -role clusterShow example
cluster1::*> network port show -role cluster Node: cluster1-01 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/10000 healthy false e0b Cluster Cluster up 9000 auto/10000 healthy false Node: cluster1-02 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/10000 healthy false e0b Cluster Cluster up 9000 auto/10000 healthy false Node: cluster1-03 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/100000 healthy false e0d Cluster Cluster up 9000 auto/100000 healthy false Node: cluster1-04 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/100000 healthy false e0d Cluster Cluster up 9000 auto/100000 healthy false 8 entries were displayed. -
Verify the switch health from the cluster (this might not show switch cs2, since LIFs are not homed on e0d).
Show example
cluster1::*> network device-discovery show -protocol cdp Node/ Local Discovered Protocol Port Device (LLDP: ChassisID) Interface Platform ----------- ------ ------------------------- ----------------- -------- cluster1-01/cdp e0a cs1 Ethernet1/7 N3K-C3232C e0d cs2 Ethernet1/7 N3K-C3232C cluster01-2/cdp e0a cs1 Ethernet1/8 N3K-C3232C e0d cs2 Ethernet1/8 N3K-C3232C cluster01-3/cdp e0a cs1 Ethernet1/1/1 N3K-C3232C e0b cs2 Ethernet1/1/1 N3K-C3232C cluster1-04/cdp e0a cs1 Ethernet1/1/2 N3K-C3232C e0b cs2 Ethernet1/1/2 N3K-C3232C cluster1::*> system cluster-switch show -is-monitoring-enabled-operational true Switch Type Address Model --------------------------- ------------------ ---------------- ----- cs1 cluster-network 10.233.205.90 N3K-C3232C Serial Number: FOXXXXXXXGD Is Monitored: true Reason: None Software Version: Cisco Nexus Operating System (NX-OS) Software, Version 9.3(4) Version Source: CDP cs2 cluster-network 10.233.205.91 N3K-C3232C Serial Number: FOXXXXXXXGS Is Monitored: true Reason: None Software Version: Cisco Nexus Operating System (NX-OS) Software, Version 9.3(4) Version Source: CDP 2 entries were displayed.You might observe the following output on the cs1 switch console depending on the RCF version previously loaded on the switch
2020 Nov 17 16:07:18 cs1 %$ VDC-1 %$ %STP-2-UNBLOCK_CONSIST_PORT: Unblocking port port-channel1 on VLAN0092. Port consistency restored. 2020 Nov 17 16:07:23 cs1 %$ VDC-1 %$ %STP-2-BLOCK_PVID_PEER: Blocking port-channel1 on VLAN0001. Inconsistent peer vlan. 2020 Nov 17 16:07:23 cs1 %$ VDC-1 %$ %STP-2-BLOCK_PVID_LOCAL: Blocking port-channel1 on VLAN0092. Inconsistent local vlan.
It can take up to 5 minutes for the cluster nodes to report as healthy. -
On cluster switch cs1, shut down the ports connected to the cluster ports of the nodes.
Show example
The following example uses the interface example output from step 1:
cs1(config)# interface eth1/1/1-2,eth1/7-8 cs1(config-if-range)# shutdown
Verify that the cluster LIFs have migrated to the ports hosted on switch cs2. This might take a few seconds.
cluster1::*> network interface show -role cluster Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ------------------ ---------- ------------------ ------------------- ------- ---- Cluster cluster1-01_clus1 up/up 169.254.3.4/23 cluster1-01 e0d false cluster1-01_clus2 up/up 169.254.3.5/23 cluster1-01 e0d true cluster1-02_clus1 up/up 169.254.3.8/23 cluster1-02 e0d false cluster1-02_clus2 up/up 169.254.3.9/23 cluster1-02 e0d true cluster1-03_clus1 up/up 169.254.1.3/23 cluster1-03 e0b false cluster1-03_clus2 up/up 169.254.1.1/23 cluster1-03 e0b true cluster1-04_clus1 up/up 169.254.1.6/23 cluster1-04 e0b false cluster1-04_clus2 up/up 169.254.1.7/23 cluster1-04 e0b true 8 entries were displayed. cluster1::*> -
cluster1::*> cluster show Node Health Eligibility Epsilon -------------------- -------- ------------- ------- cluster1-01 true true false cluster1-02 true true false cluster1-03 true true true cluster1-04 true true false 4 entries were displayed. cluster1::*>
Repeat Steps 7 to 23 on switch cs1.
Enable auto-revert on the cluster LIFs.
cluster1::*> network interface modify -vserver Cluster -lif * -auto-revert true
Verify that the switch ports connected to the cluster ports are up.
Show example
cs1# show interface brief | grep up . . Eth1/1/1 1 eth access up none 10G(D) -- Eth1/1/2 1 eth access up none 10G(D) -- Eth1/7 1 eth trunk up none 100G(D) -- Eth1/8 1 eth trunk up none 100G(D) -- . .
Verify that the ISL between cs1 and cs2 is functional:
show port-channel summaryShow example
cs1# show port-channel summary Flags: D - Down P - Up in port-channel (members) I - Individual H - Hot-standby (LACP only) s - Suspended r - Module-removed b - BFD Session Wait S - Switched R - Routed U - Up (port-channel) p - Up in delay-lacp mode (member) M - Not in use. Min-links not met -------------------------------------------------------------------------------- Group Port- Type Protocol Member Ports Channel -------------------------------------------------------------------------------- 1 Po1(SU) Eth LACP Eth1/31(P) Eth1/32(P) cs1# -
Verify that the cluster LIFs have reverted to their home port:
cluster1::*> network interface show -role cluster Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ------------------ ---------- ------------------ ------------------- ------- ---- Cluster cluster1-01_clus1 up/up 169.254.3.4/23 cluster1-01 e0d true cluster1-01_clus2 up/up 169.254.3.5/23 cluster1-01 e0d true cluster1-02_clus1 up/up 169.254.3.8/23 cluster1-02 e0d true cluster1-02_clus2 up/up 169.254.3.9/23 cluster1-02 e0d true cluster1-03_clus1 up/up 169.254.1.3/23 cluster1-03 e0b true cluster1-03_clus2 up/up 169.254.1.1/23 cluster1-03 e0b true cluster1-04_clus1 up/up 169.254.1.6/23 cluster1-04 e0b true cluster1-04_clus2 up/up 169.254.1.7/23 cluster1-04 e0b true 8 entries were displayed. cluster1::*>If any cluster LIFS have not returned to their home ports, revert them manually:
network interface revert -vserver vserver_name -lif lif_name -
cluster1::*> cluster show Node Health Eligibility Epsilon -------------------- ------- ------------- ------- cluster1-01 true true false cluster1-02 true true false cluster1-03 true true true cluster1-04 true true false 4 entries were displayed. cluster1::*>
Verify the connectivity of the remote cluster interfaces:
You can use the network interface check cluster-connectivity command to start an accessibility check for cluster connectivity and then display the details:
network interface check cluster-connectivity start and network interface check cluster-connectivity show
cluster1::*> network interface check cluster-connectivity start
NOTE: Wait for a number of seconds before running the show command to display the details.
cluster1::*> network interface check cluster-connectivity show
Source Destination Packet
Node Date LIF LIF Loss
cluster1-01
3/5/2022 19:21:18 -06:00 cluster1-01_clus2 cluster1-02_clus1 none
3/5/2022 19:21:20 -06:00 cluster1-01_clus2 cluster1-02_clus2 none
cluster1-02
3/5/2022 19:21:18 -06:00 cluster1-02_clus2 cluster1-01_clus1 none
3/5/2022 19:21:20 -06:00 cluster1-02_clus2 cluster1-01_clus2 none
cluster1-03
cluster1-04
For all ONTAP releases, you can also use the cluster ping-cluster -node <name> command to check the connectivity:
cluster1::*> cluster ping-cluster -node local
Host is cluster1-03
Getting addresses from network interface table...
Cluster cluster1-03_clus1 169.254.1.3 cluster1-03 e0a
Cluster cluster1-03_clus2 169.254.1.1 cluster1-03 e0b
Cluster cluster1-04_clus1 169.254.1.6 cluster1-04 e0a
Cluster cluster1-04_clus2 169.254.1.7 cluster1-04 e0b
Cluster cluster1-01_clus1 169.254.3.4 cluster1-01 e0a
Cluster cluster1-01_clus2 169.254.3.5 cluster1-01 e0d
Cluster cluster1-02_clus1 169.254.3.8 cluster1-02 e0a
Cluster cluster1-02_clus2 169.254.3.9 cluster1-02 e0d
Local = 169.254.1.3 169.254.1.1
Remote = 169.254.1.6 169.254.1.7 169.254.3.4 169.254.3.5 169.254.3.8 169.254.3.9
Cluster Vserver Id = 4294967293
Ping status:
Basic connectivity succeeds on 12 path(s)
Basic connectivity fails on 0 path(s)
Detected 9000 byte MTU on 12 path(s):
Local 169.254.1.3 to Remote 169.254.1.6
Local 169.254.1.3 to Remote 169.254.1.7
Local 169.254.1.3 to Remote 169.254.3.4
Local 169.254.1.3 to Remote 169.254.3.5
Local 169.254.1.3 to Remote 169.254.3.8
Local 169.254.1.3 to Remote 169.254.3.9
Local 169.254.1.1 to Remote 169.254.1.6
Local 169.254.1.1 to Remote 169.254.1.7
Local 169.254.1.1 to Remote 169.254.3.4
Local 169.254.1.1 to Remote 169.254.3.5
Local 169.254.1.1 to Remote 169.254.3.8
Local 169.254.1.1 to Remote 169.254.3.9
Larger than PMTU communication succeeds on 12 path(s)
RPC status:
6 paths up, 0 paths down (tcp check)
6 paths up, 0 paths down (udp check)