Migrate from a switchless cluster environment to a switched NetApp CN1610 cluster environment
If you have an existing two-node switchless cluster environment, you can migrate to a two-node switched cluster environment using CN1610 cluster network switches that enables you to scale beyond two nodes.
Review requirements
For a two-node switchless configuration, ensure that:
The two-node switchless configuration is properly set up and functioning.
The nodes are running ONTAP 8.2 or later.
All cluster ports are in the
up
state. -
All cluster logical interfaces (LIFs) are in the
up
state and on their home ports.
For the CN1610 cluster switch configuration:
The CN1610 cluster switch infrastructure are fully functional on both switches.
Both switches have management network connectivity.
There is console access to the cluster switches.
CN1610 node-to-node switch and switch-to-switch connections use twinax or fiber cables.
The Hardware Universe contains more information about cabling.
Inter-Switch Link (ISL) cables are connected to ports 13 through 16 on both CN1610 switches.
Initial customization of both the CN1610 switches are completed.
Any previous site customization, such as SMTP, SNMP, and SSH should be copied to the new switches.
Migrate the switches
The examples in this procedure use the following cluster switch and node nomenclature:
The names of the CN1610 switches are cs1 and cs2.
The names of the LIFs are clus1 and clus2.
The names of the nodes are node1 and node2.
The
cluster::*>
prompt indicates the name of the cluster. -
The cluster ports used in this procedure are e1a and e2a.
The Hardware Universe contains the latest information about the actual cluster ports for your platforms.
Step 1: Prepare for migration
Change the privilege level to advanced, entering
y
when prompted to continue:set -privilege advanced
The advanced prompt (*>) appears.
If AutoSupport is enabled on this cluster, suppress automatic case creation by invoking an AutoSupport message:
system node autosupport invoke -node * -type all -message MAINT=xh
x is the duration of the maintenance window in hours.
The AutoSupport message notifies technical support of this maintenance task so that automatic case creation is suppressed during the maintenance window. Show example
The following command suppresses automatic case creation for two hours:
cluster::*> system node autosupport invoke -node * -type all -message MAINT=2h
Step 2: Configure ports
Disable all of the node-facing ports (not ISL ports) on both the new cluster switches cs1 and cs2.
You must not disable the ISL ports.
Show example
The following example shows that node-facing ports 1 through 12 are disabled on switch cs1:
(cs1)> enable (cs1)# configure (cs1)(Config)# interface 0/1-0/12 (cs1)(Interface 0/1-0/12)# shutdown (cs1)(Interface 0/1-0/12)# exit (cs1)(Config)# exit
The following example shows that node-facing ports 1 through 12 are disabled on switch cs2:
(c2)> enable (cs2)# configure (cs2)(Config)# interface 0/1-0/12 (cs2)(Interface 0/1-0/12)# shutdown (cs2)(Interface 0/1-0/12)# exit (cs2)(Config)# exit
Verify that the ISL and the physical ports on the ISL between the two CN1610 cluster switches cs1 and cs2 are
up
:show port-channel
Show example
The following example shows that the ISL ports are
up
on switch cs1:(cs1)# show port-channel 3/1 Local Interface................................ 3/1 Channel Name................................... ISL-LAG Link State..................................... Up Admin Mode..................................... Enabled Type........................................... Static Load Balance Option............................ 7 (Enhanced hashing mode) Mbr Device/ Port Port Ports Timeout Speed Active ------ ------------- --------- ------- 0/13 actor/long 10G Full True partner/long 0/14 actor/long 10G Full True partner/long 0/15 actor/long 10G Full True partner/long 0/16 actor/long 10G Full True partner/long
up
on switch cs2:(cs2)# show port-channel 3/1 Local Interface................................ 3/1 Channel Name................................... ISL-LAG Link State..................................... Up Admin Mode..................................... Enabled Type........................................... Static Load Balance Option............................ 7 (Enhanced hashing mode) Mbr Device/ Port Port Ports Timeout Speed Active ------ ------------- --------- ------- 0/13 actor/long 10G Full True partner/long 0/14 actor/long 10G Full True partner/long 0/15 actor/long 10G Full True partner/long 0/16 actor/long 10G Full True partner/long
Display the list of neighboring devices:
show isdp neighbors
This command provides information about the devices that are connected to the system.
Show example
The following example lists the neighboring devices on switch cs1:
(cs1)# show isdp neighbors Capability Codes: R - Router, T - Trans Bridge, B - Source Route Bridge, S - Switch, H - Host, I - IGMP, r - Repeater Device ID Intf Holdtime Capability Platform Port ID ---------------------- ------------ --------- ------------ --------- ------------ cs2 0/13 11 S CN1610 0/13 cs2 0/14 11 S CN1610 0/14 cs2 0/15 11 S CN1610 0/15 cs2 0/16 11 S CN1610 0/16
The following example lists the neighboring devices on switch cs2:
(cs2)# show isdp neighbors Capability Codes: R - Router, T - Trans Bridge, B - Source Route Bridge, S - Switch, H - Host, I - IGMP, r - Repeater Device ID Intf Holdtime Capability Platform Port ID ---------------------- ------------ --------- ------------ --------- ------------ cs1 0/13 11 S CN1610 0/13 cs1 0/14 11 S CN1610 0/14 cs1 0/15 11 S CN1610 0/15 cs1 0/16 11 S CN1610 0/16
Display the list of cluster ports:
network port show
Show example
The following example shows the available cluster ports:
cluster::*> network port show -ipspace Cluster Node: node1 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/10000 healthy false e0b Cluster Cluster up 9000 auto/10000 healthy false e0c Cluster Cluster up 9000 auto/10000 healthy false e0d Cluster Cluster up 9000 auto/10000 healthy false e4a Cluster Cluster up 9000 auto/10000 healthy false e4b Cluster Cluster up 9000 auto/10000 healthy false Node: node2 Ignore Speed(Mbps) Health Health Port IPspace Broadcast Domain Link MTU Admin/Oper Status Status --------- ------------ ---------------- ---- ---- ----------- -------- ------ e0a Cluster Cluster up 9000 auto/10000 healthy false e0b Cluster Cluster up 9000 auto/10000 healthy false e0c Cluster Cluster up 9000 auto/10000 healthy false e0d Cluster Cluster up 9000 auto/10000 healthy false e4a Cluster Cluster up 9000 auto/10000 healthy false e4b Cluster Cluster up 9000 auto/10000 healthy false 12 entries were displayed.
Verify that each cluster port is connected to the corresponding port on its partner cluster node:
run * cdpd show-neighbors
Show example
The following example shows that cluster ports e1a and e2a are connected to the same port on their cluster partner node:
cluster::*> run * cdpd show-neighbors 2 entries were acted on. Node: node1 Local Remote Remote Remote Hold Remote Port Device Interface Platform Time Capability ------ --------------- ---------------------- ---------------- ----- ---------- e1a node2 e1a FAS3270 137 H e2a node2 e2a FAS3270 137 H Node: node2 Local Remote Remote Remote Hold Remote Port Device Interface Platform Time Capability ------ --------------- ---------------------- ---------------- ----- ---------- e1a node1 e1a FAS3270 161 H e2a node1 e2a FAS3270 161 H
Verify that all of the cluster LIFs are
up
and operational:network interface show -vserver Cluster
Each cluster LIF should display
true
in the “Is Home” column.Show example
cluster::*> network interface show -vserver Cluster Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------- ------------- ------- ---- node1 clus1 up/up 10.10.10.1/16 node1 e1a true clus2 up/up 10.10.10.2/16 node1 e2a true node2 clus1 up/up 10.10.11.1/16 node2 e1a true clus2 up/up 10.10.11.2/16 node2 e2a true 4 entries were displayed.
The following modification and migration commands in steps 10 through 13 must be done from the local node. -
Verify that all cluster ports are
up
:network port show -ipspace Cluster
Show example
cluster::*> network port show -ipspace Cluster Auto-Negot Duplex Speed (Mbps) Node Port Role Link MTU Admin/Oper Admin/Oper Admin/Oper ------ ------ ------------ ----- ----- ----------- ---------- ------------ node1 e1a clus1 up 9000 true/true full/full auto/10000 e2a clus2 up 9000 true/true full/full auto/10000 node2 e1a clus1 up 9000 true/true full/full auto/10000 e2a clus2 up 9000 true/true full/full auto/10000 4 entries were displayed.
Set the
-auto-revert
parameter tofalse
on cluster LIFs clus1 and clus2 on both nodes:network interface modify
Show example
cluster::*> network interface modify -vserver node1 -lif clus1 -auto-revert false cluster::*> network interface modify -vserver node1 -lif clus2 -auto-revert false cluster::*> network interface modify -vserver node2 -lif clus1 -auto-revert false cluster::*> network interface modify -vserver node2 -lif clus2 -auto-revert false
For release 8.3 and later, use the following command: network interface modify -vserver Cluster -lif * -auto-revert false
Ping the cluster ports to verify the cluster connectivity:
cluster ping-cluster local
The command output shows connectivity between all of the cluster ports.
Migrate clus1 to port e2a on the console of each node:
network interface migrate
Show example
The following example shows the process for migrating clus1 to port e2a on node1 and node2:
cluster::*> network interface migrate -vserver node1 -lif clus1 -source-node node1 -dest-node node1 -dest-port e2a cluster::*> network interface migrate -vserver node2 -lif clus1 -source-node node2 -dest-node node2 -dest-port e2a
For release 8.3 and later, use the following command: network interface migrate -vserver Cluster -lif clus1 -destination-node node1 -destination-port e2a
Verify that the migration took place:
Show example
The following example verifies that clus1 is migrated to port e2a on node1 and node2:
cluster::*> network interface show -vserver Cluster Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------- ------------- ------- ---- node1 clus1 up/up 10.10.10.1/16 node1 e2a false clus2 up/up 10.10.10.2/16 node1 e2a true node2 clus1 up/up 10.10.11.1/16 node2 e2a false clus2 up/up 10.10.11.2/16 node2 e2a true 4 entries were displayed.
Shut down cluster port e1a on both nodes:
network port modify
Show example
The following example shows how to shut down the port e1a on node1 and node2:
cluster::*> network port modify -node node1 -port e1a -up-admin false cluster::*> network port modify -node node2 -port e1a -up-admin false
Verify the port status:
network port show
Show example
The following example shows that port e1a is
down
on node1 and node2:cluster::*> network port show -role cluster Auto-Negot Duplex Speed (Mbps) Node Port Role Link MTU Admin/Oper Admin/Oper Admin/Oper ------ ------ ------------ ---- ----- ----------- ---------- ------------ node1 e1a clus1 down 9000 true/true full/full auto/10000 e2a clus2 up 9000 true/true full/full auto/10000 node2 e1a clus1 down 9000 true/true full/full auto/10000 e2a clus2 up 9000 true/true full/full auto/10000 4 entries were displayed.
Disconnect the cable from cluster port e1a on node1, and then connect e1a to port 1 on cluster switch cs1, using the appropriate cabling supported by the CN1610 switches.
Disconnect the cable from cluster port e1a on node2, and then connect e1a to port 2 on cluster switch cs1, using the appropriate cabling supported by the CN1610 switches.
Enable all of the node-facing ports on cluster switch cs1.
Show example
The following example shows that ports 1 through 12 are enabled on switch cs1:
(cs1)# configure (cs1)(Config)# interface 0/1-0/12 (cs1)(Interface 0/1-0/12)# no shutdown (cs1)(Interface 0/1-0/12)# exit (cs1)(Config)# exit
Enable the first cluster port e1a on each node:
network port modify
Show example
The following example shows how to enable the port e1a on node1 and node2:
cluster::*> network port modify -node node1 -port e1a -up-admin true cluster::*> network port modify -node node2 -port e1a -up-admin true
Verify that all of the cluster ports are
up
Show example
The following example shows that all of the cluster ports are
up
on node1 and node2:cluster::*> network port show -ipspace Cluster Auto-Negot Duplex Speed (Mbps) Node Port Role Link MTU Admin/Oper Admin/Oper Admin/Oper ------ ------ ------------ ---- ----- ----------- ---------- ------------ node1 e1a clus1 up 9000 true/true full/full auto/10000 e2a clus2 up 9000 true/true full/full auto/10000 node2 e1a clus1 up 9000 true/true full/full auto/10000 e2a clus2 up 9000 true/true full/full auto/10000 4 entries were displayed.
Revert clus1 (which was previously migrated) to e1a on both nodes:
network interface revert
Show example
The following example shows how to revert clus1 to the port e1a on node1 and node2:
cluster::*> network interface revert -vserver node1 -lif clus1 cluster::*> network interface revert -vserver node2 -lif clus1
For release 8.3 and later, use the following command: network interface revert -vserver Cluster -lif <nodename_clus<N>>
up
, operational, and display astrue
in the "Is Home" column:network interface show -vserver Cluster
Show example
The following example shows that all of the LIFs are
up
on node1 and node2 and that the "Is Home" column results aretrue
:cluster::*> network interface show -vserver Cluster Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------- ------------- ------- ---- node1 clus1 up/up 10.10.10.1/16 node1 e1a true clus2 up/up 10.10.10.2/16 node1 e2a true node2 clus1 up/up 10.10.11.1/16 node2 e1a true clus2 up/up 10.10.11.2/16 node2 e2a true 4 entries were displayed.
Display information about the status of the nodes in the cluster:
cluster show
Show example
The following example displays information about the health and eligibility of the nodes in the cluster:
cluster::*> cluster show Node Health Eligibility Epsilon -------------------- ------- ------------ ------------ node1 true true false node2 true true false
Migrate clus2 to port e1a on the console of each node:
Show example
The following example shows the process for migrating clus2 to port e1a on node1 and node2:
cluster::*> network interface migrate -vserver node1 -lif clus2 -source-node node1 -dest-node node1 -dest-port e1a cluster::*> network interface migrate -vserver node2 -lif clus2 -source-node node2 -dest-node node2 -dest-port e1a
For release 8.3 and later, use the following command: network interface migrate -vserver Cluster -lif node1_clus2 -dest-node node1 -dest-port e1a
Show example
The following example verifies that clus2 is migrated to port e1a on node1 and node2:
cluster::*> network interface show -vserver Cluster Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------- ------------- ------- ---- node1 clus1 up/up 10.10.10.1/16 node1 e1a true clus2 up/up 10.10.10.2/16 node1 e1a false node2 clus1 up/up 10.10.11.1/16 node2 e1a true clus2 up/up 10.10.11.2/16 node2 e1a false 4 entries were displayed.
Shut down cluster port e2a on both nodes:
network port modify
Show example
The following example shows how to shut down the port e2a on node1 and node2:
cluster::*> network port modify -node node1 -port e2a -up-admin false cluster::*> network port modify -node node2 -port e2a -up-admin false
network port show
Show example
The following example shows that port e2a is
down
on node1 and node2:cluster::*> network port show -role cluster Auto-Negot Duplex Speed (Mbps) Node Port Role Link MTU Admin/Oper Admin/Oper Admin/Oper ------ ------ ------------ ---- ----- ----------- ---------- ------------ node1 e1a clus1 up 9000 true/true full/full auto/10000 e2a clus2 down 9000 true/true full/full auto/10000 node2 e1a clus1 up 9000 true/true full/full auto/10000 e2a clus2 down 9000 true/true full/full auto/10000 4 entries were displayed.
Disconnect the cable from cluster port e2a on node1, and then connect e2a to port 1 on cluster switch cs2, using the appropriate cabling supported by the CN1610 switches.
Disconnect the cable from cluster port e2a on node2, and then connect e2a to port 2 on cluster switch cs2, using the appropriate cabling supported by the CN1610 switches.
Enable all of the node-facing ports on cluster switch cs2.
Show example
The following example shows that ports 1 through 12 are enabled on switch cs2:
(cs2)# configure (cs2)(Config)# interface 0/1-0/12 (cs2)(Interface 0/1-0/12)# no shutdown (cs2)(Interface 0/1-0/12)# exit (cs2)(Config)# exit
Enable the second cluster port e2a on each node.
Show example
The following example shows how to enable the port e2a on node1 and node2:
cluster::*> network port modify -node node1 -port e2a -up-admin true cluster::*> network port modify -node node2 -port e2a -up-admin true
up
Show example
up
Revert clus2 (which was previously migrated) to e2a on both nodes:
Show example
The following example shows how to revert clus2 to the port e2a on node1 and node2:
cluster::*> network interface revert -vserver node1 -lif clus2 cluster::*> network interface revert -vserver node2 -lif clus2
For release 8.3 and later, the commands are: cluster::*> network interface revert -vserver Cluster -lif node1_clus2
andcluster::*> network interface revert -vserver Cluster -lif node2_clus2
Step 3: Complete the configuration
Verify that all of the interfaces display
true
Show example
up
:cluster::*> network interface show -vserver Cluster Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------------ ----------- ------- ---- node1 clus1 up/up 10.10.10.1/16 node1 e1a true clus2 up/up 10.10.10.2/16 node1 e2a true node2 clus1 up/up 10.10.11.1/16 node2 e1a true clus2 up/up 10.10.11.2/16 node2 e2a true
Verify that both nodes have two connections to each switch:
show isdp neighbors
Show example
The following example shows the appropriate results for both switches:
(cs1)# show isdp neighbors Capability Codes: R - Router, T - Trans Bridge, B - Source Route Bridge, S - Switch, H - Host, I - IGMP, r - Repeater Device ID Intf Holdtime Capability Platform Port ID ---------------------- ------------ --------- ------------ --------- ------------ node1 0/1 132 H FAS3270 e1a node2 0/2 163 H FAS3270 e1a cs2 0/13 11 S CN1610 0/13 cs2 0/14 11 S CN1610 0/14 cs2 0/15 11 S CN1610 0/15 cs2 0/16 11 S CN1610 0/16 (cs2)# show isdp neighbors Capability Codes: R - Router, T - Trans Bridge, B - Source Route Bridge, S - Switch, H - Host, I - IGMP, r - Repeater Device ID Intf Holdtime Capability Platform Port ID ---------------------- ------------ --------- ------------ --------- ------------ node1 0/1 132 H FAS3270 e2a node2 0/2 163 H FAS3270 e2a cs1 0/13 11 S CN1610 0/13 cs1 0/14 11 S CN1610 0/14 cs1 0/15 11 S CN1610 0/15 cs1 0/16 11 S CN1610 0/16
Display information about the devices in your configuration:
network device discovery show
Disable the two-node switchless configuration settings on both nodes using the advanced privilege command:
network options detect-switchless modify
Show example
The following example shows how to disable the switchless configuration settings:
cluster::*> network options detect-switchless modify -enabled false
For release 9.2 and later, skip this step since the configuration is automatically converted. -
Verify that the settings are disabled:
network options detect-switchless-cluster show
Show example
The
false
output in the following example shows that the configuration settings are disabled:cluster::*> network options detect-switchless-cluster show Enable Switchless Cluster Detection: false
For release 9.2 and later, wait until Enable Switchless Cluster
is set to false. This can take up to three minutes. -
Configure clusters clus1 and clus2 to auto revert on each node and confirm.
Show example
cluster::*> network interface modify -vserver node1 -lif clus1 -auto-revert true cluster::*> network interface modify -vserver node1 -lif clus2 -auto-revert true cluster::*> network interface modify -vserver node2 -lif clus1 -auto-revert true cluster::*> network interface modify -vserver node2 -lif clus2 -auto-revert true
For release 8.3 and later, use the following command: network interface modify -vserver Cluster -lif * -auto-revert true
to enable auto-revert on all nodes in the cluster. -
Verify the status of the node members in the cluster:
cluster show
Show example
The following example shows information about the health and eligibility of the nodes in the cluster:
If you suppressed automatic case creation, reenable it by invoking an AutoSupport message:
Show example
cluster::*> system node autosupport invoke -node * -type all -message MAINT=END
Change the privilege level back to admin:
set -privilege admin
