ONTAP MetroCluster
Power off and power on a single site in a MetroCluster FC configuration
Contributors netapp-aoife
If you need to perform site maintenance or relocate a single site in a MetroCluster FC configuration, you must know how to power off and power on the site.
If you need to relocate and reconfigure a site (for example, if you need to expand from a four-node to an eight-node cluster), you cannot complete these tasks at the same time. This procedure only covers the steps that are required to perform site maintenance or to relocate a site without changing its configuration.
The following diagram shows a MetroCluster configuration. Cluster_B is powered off for maintenance.
power on off data center
Power off a MetroCluster site
You must power off a site and all of the equipment before site maintenance or relocation can begin.
About this task
All the commands in the following steps are issued from the site that remains powered on.
Steps
  1. Before you begin, check that any non-mirrored aggregates at the site are offline.
  2. Verify the operation of the MetroCluster configuration in ONTAP:
    1. Check whether the system is multipathed:
      node run -node node-name sysconfig -a
    2. Check for any health alerts on both clusters:
      system health alert show
    3. Confirm the MetroCluster configuration and that the operational mode is normal:
      metrocluster show
    4. Perform a MetroCluster check:
      metrocluster check run
    5. Display the results of the MetroCluster check:
      metrocluster check show
    6. Check for any health alerts on the switches (if present):
      storage switch show
    7. Run Config Advisor.
    8. After running Config Advisor, review the tool's output and follow the recommendations in the output to address any issues discovered.
  3. From the site you want to remain up, implement the switchover:
    metrocluster switchover
    cluster_A::*> metrocluster switchover
    The operation can take several minutes to complete.
    The unmirrored aggregates will only be online after a switchover if the remote disks in the aggregate are accessible. If the ISLs fail, the local node might be unable to access the data in the unmirrored remote disks. The failure of an aggregate can lead to a reboot of the local node.
  4. Monitor and verify the completion of the switchover:
    metrocluster operation show
    cluster_A::*> metrocluster operation show
      Operation: Switchover
     Start time: 10/4/2012 19:04:13
    State: in-progress
       End time: -
         Errors:
          State: successful
       End time: 10/4/2012 19:04:22
         Errors: -
  5. Move any volumes and LUNs that belong to unmirrored aggregates offline.
    1. Move the volumes offline.
      cluster_A::* volume offline <volume name>
    2. Move the LUNs offline.
      cluster_A::* lun offline lun_path <lun_path>
  6. Move unmirrored aggregates offline: storage aggregate offline
    cluster_A*::> storage aggregate offline -aggregate <aggregate-name>
  7. Depending on your configuration and ONTAP version, identify and move offline affected plexes that are located at the disaster site (Cluster_B).
    You should move the following plexes offline:
    • Non-mirrored plexes residing on disks located at the disaster site.
      If you do not move the non-mirrored plexes at the disaster site offline, an outage might occur when the disaster site is later powered off.
    • Mirrored plexes residing on disks located at the disaster site for aggregate mirroring. After they are moved offline, the plexes are inaccessible.
    1. Identify the affected plexes.
      Plexes that are owned by nodes at the surviving site consist of Pool1 disks. Plexes that are owned by nodes at the disaster site consist of Pool0 disks.
      Cluster_A::> storage aggregate plex show -fields aggregate,status,is-online,Plex,pool
      aggregate    plex  status        is-online pool
      Node_B_1_aggr0 plex0 normal,active true     0
      Node_B_1_aggr0 plex1 normal,active true     1
      Node_B_2_aggr0 plex0 normal,active true     0
      Node_B_2_aggr0 plex5 normal,active true     1
      Node_B_1_aggr1 plex0 normal,active true     0
      Node_B_1_aggr1 plex3 normal,active true     1
      Node_B_2_aggr1 plex0 normal,active true     0
      Node_B_2_aggr1 plex1 normal,active true     1
      Node_A_1_aggr0 plex0 normal,active true     0
      Node_A_1_aggr0 plex4 normal,active true     1
      Node_A_1_aggr1 plex0 normal,active true     0
      Node_A_1_aggr1 plex1 normal,active true     1
      Node_A_2_aggr0 plex0 normal,active true     0
      Node_A_2_aggr0 plex4 normal,active true     1
      Node_A_2_aggr1 plex0 normal,active true     0
      Node_A_2_aggr1 plex1 normal,active true     1
      14 entries were displayed.
      Cluster_A::>
      The affected plexes are those that are remote to cluster A. The following table shows whether the disks are local or remote relative to cluster A:
      Node
      Disks in pool
      Should the disks be set offline?
      Example of plexes to be moved offline
      Node _A_1 and Node _A_2
      Disks in pool 0
      No. Disks are local to cluster A.
      Disks in pool 1
      Yes. Disks are remote to cluster A.
      Node_A_1_aggr0/plex4
      Node_A_1_aggr1/plex1
      Node_A_2_aggr0/plex4
      Node_A_2_aggr1/plex1
      Node _B_1 and Node _B_2
      Disks in pool 0
      Node_B_1_aggr1/plex0
      Node_B_1_aggr0/plex0
      Node_B_2_aggr0/plex0
      Node_B_2_aggr1/plex0
      Disks in pool 1
    2. Move the affected plexes offline:
      storage aggregate plex offline
      storage aggregate plex offline -aggregate Node_B_1_aggr0 -plex plex0
      Note Perform this step for all plexes that have disks that are remote to Cluster_A.
  8. Persistently offline the ISL switch ports according to the switch type.
    Switch type
    Action
    For Brocade FC switches…​
    1. Use the portcfgpersistentdisable <port> command to persistently disable the ports as shown in the following example. This must be done on both switches at the surviving site.
       Switch_A_1:admin> portcfgpersistentdisable 14
       Switch_A_1:admin> portcfgpersistentdisable 15
       Switch_A_1:admin>
    2. Verify that the ports are disabled using the switchshow command shown in the following example:
       Switch_A_1:admin> switchshow
       switchName:	Switch_A_1
       switchType:	109.1
       switchState:	Online
       switchMode:	Native
       switchRole:	Principal
       switchDomain:	2
       switchId:	fffc02
       switchWwn:	10:00:00:05:33:88:9c:68
       zoning:		ON (T5_T6)
       switchBeacon:	OFF
       FC Router:	OFF
       FC Router BB Fabric ID:	128
       Address Mode:	0
        Index Port Address Media Speed State     Proto
         14  14   020e00   id    16G   No_Light    FC  Disabled (Persistent)
         15  15   020f00   id    16G   No_Light    FC  Disabled (Persistent)
       Switch_A_1:admin>
    For Cisco FC switches…​
    1. Use the interface command to persistently disable the ports. The following example shows ports 14 and 15 being disabled:
       Switch_A_1# conf t
       Switch_A_1(config)# interface fc1/14-15
       Switch_A_1(config)# shut
       Switch_A_1(config-if)# end
       Switch_A_1# copy running-config startup-config
    2. Verify that the switch port is disabled using the show interface brief command as shown in the following example:
       Switch_A_1# show interface brief
       Switch_A_1
  9. Power off the equipment at the disaster site.
    The following equipment must be turned off in the order shown:
    • MetroCluster FC switches
    • Storage controllers - the storage controllers should currently be at the LOADER prompt, you must power them off completely.
    • Storage shelves
    • ATTO FibreBridges (if present)
Relocating the powered-off site of the MetroCluster
After the site is powered off, you can begin maintenance work. The procedure is the same whether the MetroCluster components are relocated within the same data center or relocated to a different data center.
  • The hardware should be cabled in the same way as the previous site.
  • If the Inter-Switch Link (ISL) speed, length, or number has changed, they all need to be reconfigured.
Steps
  1. Verify that the cabling for all components is carefully recorded so that it can be correctly reconnected at the new location.
  2. Physically relocate all the hardware, storage controllers, FC switches, FibreBridges, and storage shelves.
  3. Configure the ISL ports and verify the intersite connectivity.
    1. Power on the FC switches.
      Note Do not power up any other equipment.
    2. Enable the ports.
      Enable the ports according to the correct switch types in the following table:
      Switch type
      Command
      1. Use the portcfgpersistentenable <port number> command to persistently enable the port. This must be done on both switches at the surviving site.
        The following example shows ports 14 and 15 being enabled on Switch_A_1.
        switch_A_1:admin> portcfgpersistentenable 14
        switch_A_1:admin> portcfgpersistentenable 15
        switch_A_1:admin>
      2. Verify that the switch port is enabled: switchshow
        The following example shows that ports 14 and 15 are enabled:
        switch_A_1:admin> switchshow
        switchType:	109.1
        switchState:	Online
        switchMode:	Native
        switchDomain:	2
        switchId:	fffc02
        zoning:		ON (T5_T6)
        switchBeacon:	OFF
        FC Router:	OFF
        Address Mode:	0
         14  14   020e00   id    16G   Online      FC  E-Port  10:00:00:05:33:86:89:cb "Switch_A_1"
         15  15   020f00   id    16G   Online      FC  E-Port  10:00:00:05:33:86:89:cb "Switch_A_1" (downstream)
        switch_A_1:admin>
      1. Enter the interface command to enable the port.
         switch_A_1# conf t
         switch_A_1(config)# interface fc1/14-15
         switch_A_1(config)# no shut
         switch_A_1(config-if)# end
         switch_A_1# copy running-config startup-config
      2. Verify that the switch port is enabled: show interface brief
         switch_A_1# show interface brief
         switch_A_1#
  4. Use tools on the switches (as they are available) to verify the intersite connectivity.
    Note You should only proceed if the links are correctly configured and stable.
  5. Disable the links again if they are found to be stable.
    Disable the ports based on whether you are using Brocade or Cisco switches as shown in the following table:
    Switch type
    Command
    1. Enter the portcfgpersistentdisable <port_number> command to persistently disable the port.
      This must be done on both switches at the surviving site. The following example shows ports 14 and 15 being disabled on Switch_A_1:
       switch_A_1:admin> portpersistentdisable 14
       switch_A_1:admin> portpersistentdisable 15
       switch_A_1:admin>
    2. Verify that the switch port is disabled: switchshow
      The following example shows that ports 14 and 15 are disabled:
      switchType:	109.1
      switchState:	Online
      switchMode:	Native
      switchDomain:	2
      switchId:	fffc02
      zoning:		ON (T5_T6)
      switchBeacon:	OFF
      FC Router:	OFF
      Address Mode:	0
      switch_A_1:admin>
    1. Disable the port using the interface command.
      The following example shows ports fc1/14 and fc1/15 being disabled on Switch A_1:
      switch_A_1# conf t
      switch_A_1(config)# shut
    2. Verify that the switch port is disabled using the show interface brief command.
        switch_A_1#
Powering on the MetroCluster configuration and returning to normal operation
After maintenance has been completed or the site has been moved, you must power on the site and reestablish the MetroCluster configuration.
About this task
All the commands in the following steps are issued from the site that you power on.
Steps
  1. Power on the switches.
    You should power on the switches first. They might have been powered on during the previous step if the site was relocated.
    1. Reconfigure the Inter-Switch Link (ISL) if required or if this was not completed as part of the relocation.
    2. Enable the ISL if fencing was completed.
    3. Verify the ISL.
  2. Disable the ISLs on the FC switches.
  3. Power on the storage controllers and wait until you see the LOADER prompt. The controllers must not be fully booted.
    If auto boot is enabled, press Ctrl+C to stop the controllers from automatically booting.
  4. Power on the shelves and allow enough time for them to power on completely.
  5. Power on the FibreBridge bridges.
    1. On the FC switches, verify that the ports connecting the bridges are coming online.
      You can use a command such as switchshow for Brocade switches, and show interface brief for Cisco switches.
    2. Verify that the shelves and disks on the bridges are clearly visible.
      You can use a command such as sastargets on the ATTO CLI.
  6. Enable the ISLs on the FC switches.
    Enable the ports based on whether you are using Brocade or Cisco switches as shown in the following table:
    Switch type
    Command
    1. Enter the portcfgpersistentenable <port> command to persistently enable the ports. This must be done on both switches at the surviving site.
      The following example shows ports 14 and 15 being enabled on Switch_A_1:
       Switch_A_1:admin> portcfgpersistentenable 14
       Switch_A_1:admin> portcfgpersistentenable 15
       Switch_A_1:admin>
    2. Verify that the switch port is enabled using the
      switchshow command:
       switchType:	109.1
       switchState:	Online
       switchMode:	Native
       switchDomain:	2
       switchId:	fffc02
       zoning:		ON (T5_T6)
       switchBeacon:	OFF
       FC Router:	OFF
       Address Mode:	0
       switch_A_1:admin>
    1. Use the interface command to enable the ports.
      The following example shows port fc1/14 and fc1/15 being enabled on Switch A_1:
       switch_A_1# conf t
      switch_A_1#
  7. Verify that the storage is visible from the surviving site. Bring the offline plexes back online. This restarts the resync operations and reestablishes the SyncMirror.
  8. Reestablish the MetroCluster configuration.
    Follow the instructions in Verifying that your system is ready for a switchback to perform healing and switchback operations according to your MetroCluster configuration.