Replace the caching module - AFF A700
You must replace the caching module in the controller module when your system registers a single AutoSupport (ASUP) message that the module has gone offline; failure to do so results in performance degradation. If AutoSupport is not enabled, you can locate the failed caching module by the fault LED on the front of the module. You can also add or replace the 1TB, X9170A core dump module, which is required if you are installing NS224 drive shelves in an AFF A700 system.
You must replace the failed component with a replacement FRU component you received from your provider.
For instructions about hot swapping the caching module, see Hot-swapping a caching module.
When removing, replacing, or adding caching or core dump modules, the target node must be halted to the LOADER.
AFF A700 supports the 1TB core dump module, X9170A, which is required if you are adding NS224 drive shelves.
The core dump modules can be installed in slots 6-1 and 6-2. The recommended best practice is to install the module in slot 6-1.
The X9170A core dump module is not hot-swappable.
Step 1: Shut down the impaired controller
You can shut down or take over the impaired controller using different procedures, depending on the storage system hardware configuration.
To shut down the impaired controller, you must determine the status of the controller and, if necessary, take over the controller so that the healthy controller continues to serve data from the impaired controller storage.
If you have a SAN system, you must have checked event messages (
cluster kernel-service show
) for impaired controller SCSI blade. Thecluster kernel-service show
command displays the node name, quorum status of that node, availability status of that node, and operational status of that node.Each SCSI-blade process should be in quorum with the other nodes in the cluster. Any issues must be resolved before you proceed with the replacement.
If you have a cluster with more than two nodes, it must be in quorum. If the cluster is not in quorum or a healthy controller shows false for eligibility and health, you must correct the issue before shutting down the impaired controller; see Synchronize a node with the cluster.
If AutoSupport is enabled, suppress automatic case creation by invoking an AutoSupport message:
system node autosupport invoke -node * -type all -message MAINT=number_of_hours_downh
The following AutoSupport message suppresses automatic case creation for two hours:
Disable automatic giveback from the console of the healthy controller:
storage failover modify –node local -auto-giveback false
When you see Do you want to disable auto-giveback?, enter y
Take the impaired controller to the LOADER prompt:
If the impaired controller is displaying… Then… The LOADER prompt
Go to the next step.
Waiting for giveback…
Press Ctrl-C, and then respond
y
when prompted.System prompt or password prompt
Take over or halt the impaired controller from the healthy controller:
storage failover takeover -ofnode impaired_node_name
When the impaired controller shows Waiting for giveback…, press Ctrl-C, and then respond
y
To shut down the impaired controller, you must determine the status of the controller and, if necessary, switch over the controller so that the healthy controller continues to serve data from the impaired controller storage.
If you are using NetApp Storage Encryption, you must have reset the MSID using the instructions in the "Return a FIPS drive or SED to unprotected mode" section of NetApp Encryption overview with the CLI.
You must leave the power supplies turned on at the end of this procedure to provide power to the healthy controller.
Check the MetroCluster status to determine whether the impaired controller has automatically switched over to the healthy controller:
metrocluster show
Depending on whether an automatic switchover has occurred, proceed according to the following table:
If the impaired controller… Then… Has automatically switched over
Proceed to the next step.
Has not automatically switched over
Perform a planned switchover operation from the healthy controller:
metrocluster switchover
Has not automatically switched over, you attempted switchover with the
command, and the switchover was vetoedReview the veto messages and, if possible, resolve the issue and try again. If you are unable to resolve the issue, contact technical support.
Resynchronize the data aggregates by running the
metrocluster heal -phase aggregates
command from the surviving cluster.controller_A_1::> metrocluster heal -phase aggregates [Job 130] Job succeeded: Heal Aggregates is successful.
If the healing is vetoed, you have the option of reissuing the
metrocluster heal
command with the-override-vetoes
parameter. If you use this optional parameter, the system overrides any soft vetoes that prevent the healing operation. -
Verify that the operation has been completed by using the metrocluster operation show command.
controller_A_1::> metrocluster operation show Operation: heal-aggregates State: successful Start Time: 7/25/2016 18:45:55 End Time: 7/25/2016 18:45:56 Errors: -
Check the state of the aggregates by using the
storage aggregate show
command.controller_A_1::> storage aggregate show Aggregate Size Available Used% State #Vols Nodes RAID Status --------- -------- --------- ----- ------- ------ ---------------- ------------ ... aggr_b2 227.1GB 227.1GB 0% online 0 mcc1-a2 raid_dp, mirrored, normal...
Heal the root aggregates by using the
metrocluster heal -phase root-aggregates
command.mcc1A::> metrocluster heal -phase root-aggregates [Job 137] Job succeeded: Heal Root Aggregates is successful
metrocluster heal
command with the -override-vetoes parameter. If you use this optional parameter, the system overrides any soft vetoes that prevent the healing operation. -
Verify that the heal operation is complete by using the
command on the destination cluster:mcc1A::> metrocluster operation show Operation: heal-root-aggregates State: successful Start Time: 7/29/2016 20:54:41 End Time: 7/29/2016 20:54:42 Errors: -
On the impaired controller module, disconnect the power supplies.
Step 2: Replace or add a caching module
The NVMe SSD Flash Cache modules (FlashCache or caching modules) are separate modules. They are located in the front of the NVRAM module. To replace or add a caching module, locate it on the rear of the system on slot 6, and then follow the specific sequence of steps to replace it.
Your storage system must meet certain criteria depending on your situation:
It must have the appropriate operating system for the caching module you are installing.
It must support the caching capacity.
The target node must be at the LOADER prompt before adding or replacing the caching module.
The replacement caching module must have the same capacity as the failed caching module, but can be from a different supported vendor.
All other components in the storage system must be functioning properly; if not, you must contact technical support.
If you are not already grounded, properly ground yourself.
Locate the failed caching module, in slot 6, by the lit amber Attention LED on the front of the caching module.
Remove the caching module:
If you are adding another caching module to your system, remove the blank module and go to the next step. Orange release button.
Caching module cam handle.
Press the orange release button on the front of the caching module.
Do not use the numbered and lettered I/O cam latch to eject the caching module. The numbered and lettered I/O cam latch ejects the entire NVRAM10 module and not the caching module. -
Rotate the cam handle until the caching module begins to slide out of the NVRAM10 module.
Gently pull the cam handle straight toward you to remove the caching module from the NVRAM10 module.
Be sure to support the caching module as you remove it from the NVRAM10 module.
Install the caching module:
Align the edges of the caching module with the opening in the NVRAM10 module.
Gently push the caching module into the bay until the cam handle engages.
Rotate the cam handle until it locks into place.
Step 3: Add or replace an X9170A core dump module
The 1TB cache core dump, X9170A, is only used in the AFF A700 systems. The core dump module cannot be hot-swapped. The core dump module typically is located in the front of the NVRAM module in slot 6-1 in the rear of the system. To replace or add the core dump module, locate slot 6-1, and then follow the specific sequence of steps to add or replace it.
Your system must be running ONTAP 9.8 or later in order to add a core dump module.
The target node must be at the LOADER prompt before adding or replacing the code dump module.
You must have received two X9170 core dump modules; one for each controller.
If you are replacing a failed core dump module, locate and remove it:
Core dump module cam handle.
Locate the failed module by the amber Attention LED on the front of the module.
Press the orange release button on the front of the core dump module.
Do not use the numbered and lettered I/O cam latch to eject the core dump module. The numbered and lettered I/O cam latch ejects the entire NVRAM10 module and not the core dump module. -
Rotate the cam handle until the core dump module begins to slide out of the NVRAM10 module.
Gently pull the cam handle straight toward you to remove the core dump module from the NVRAM10 module and set it aside.
Be sure to support the core dump module as you remove it from the NVRAM10 module.
Install the core dump module:
If you are installing a new core dump module, remove the blank module from slot 6-1.
Align the edges of the core dump module with the opening in the NVRAM10 module.
Gently push the core dump module into the bay until the cam handle engages.
Step 4: Reboot the controller after FRU replacement
After you replace the FRU, you must reboot the controller module.
To boot ONTAP from the LOADER prompt, enter
bye
Step 5: Switch back aggregates in a two-node MetroCluster configuration
After you have completed the FRU replacement in a two-node MetroCluster configuration, you can perform the MetroCluster switchback operation. This returns the configuration to its normal operating state, with the sync-source storage virtual machines (SVMs) on the formerly impaired site now active and serving data from the local disk pools.
This task only applies to two-node MetroCluster configurations.
Verify that all nodes are in the
enabled
state:metrocluster node show
cluster_B::> metrocluster node show DR Configuration DR Group Cluster Node State Mirroring Mode ----- ------- -------------- -------------- --------- -------------------- 1 cluster_A controller_A_1 configured enabled heal roots completed cluster_B controller_B_1 configured enabled waiting for switchback recovery 2 entries were displayed.
Verify that resynchronization is complete on all SVMs:
metrocluster vserver show
Verify that any automatic LIF migrations being performed by the healing operations were completed successfully:
metrocluster check lif show
Perform the switchback by using the
metrocluster switchback
command from any node in the surviving cluster. -
Verify that the switchback operation has completed:
metrocluster show
The switchback operation is still running when a cluster is in the
waiting-for-switchback
state:cluster_B::> metrocluster show Cluster Configuration State Mode -------------------- ------------------- --------- Local: cluster_B configured switchover Remote: cluster_A configured waiting-for-switchback
The switchback operation is complete when the clusters are in the
normal
state.:cluster_B::> metrocluster show Cluster Configuration State Mode -------------------- ------------------- --------- Local: cluster_B configured normal Remote: cluster_A configured normal
If a switchback is taking a long time to finish, you can check on the status of in-progress baselines by using the
metrocluster config-replication resync-status show
command. -
Reestablish any SnapMirror or SnapVault configurations.
Step 6: Return the failed part to NetApp
Return the failed part to NetApp, as described in the RMA instructions shipped with the kit. See the Part Return & Replacements page for further information.