Replace the NVRAM module and/or NVRAM DIMMs - AFF A900
The NVRAM module consists of the NVRAM11 and DIMMs. You can replace a failed NVRAM module or the DIMMs inside the NVRAM module. To replace a failed NVRAM module, you must remove it from the chassis, move the DIMMs to the replacement module, and install the replacement NVRAM module into the chassis.
To replace and NVRAM DIMM, you must remove the NVRAM module from the chassis, replace the failed DIMM in the module, and then reinstall the NVRAM module.
Because the system ID is derived from the NVRAM module, if replacing the module, disks belonging to the system are reassigned to a new system ID.
All disk shelves must be working properly.
If your system is in an HA pair, the partner controller must be able to take over the controller associated with the NVRAM module that is being replaced.
This procedure uses the following terminology:
The impaired controller is the controller on which you are performing maintenance.
The healthy controller is the HA partner of the impaired controller.
This procedure includes steps for automatically reassigning disks to the controller module associated with the new NVRAM module. You must reassign the disks when directed to in the procedure. Completing the disk reassignment before giveback can cause issues.
You must replace the failed component with a replacement FRU component you received from your provider.
You cannot change any disks or disk shelves as part of this procedure.
Step 1: Shut down the impaired controller
Shut down or take over the impaired controller using one of the following options.
To shut down the impaired controller, you must determine the status of the controller and, if necessary, take over the controller so that the healthy controller continues to serve data from the impaired controller storage.
If you have a SAN system, you must have checked event messages (
cluster kernel-service show
) for impaired controller SCSI blade. Thecluster kernel-service show
command displays the node name, quorum status of that node, availability status of that node, and operational status of that node.Each SCSI-blade process should be in quorum with the other nodes in the cluster. Any issues must be resolved before you proceed with the replacement.
If you have a cluster with more than two nodes, it must be in quorum. If the cluster is not in quorum or a healthy controller shows false for eligibility and health, you must correct the issue before shutting down the impaired controller; see Synchronize a node with the cluster.
If AutoSupport is enabled, suppress automatic case creation by invoking an AutoSupport message:
system node autosupport invoke -node * -type all -message MAINT=number_of_hours_downh
The following AutoSupport message suppresses automatic case creation for two hours:
Disable automatic giveback from the console of the healthy controller:
storage failover modify –node local -auto-giveback false
When you see Do you want to disable auto-giveback?, enter y
Take the impaired controller to the LOADER prompt:
If the impaired controller is displaying… Then… The LOADER prompt
Go to the next step.
Waiting for giveback…
Press Ctrl-C, and then respond
y
when prompted.System prompt or password prompt
Take over or halt the impaired controller from the healthy controller:
storage failover takeover -ofnode impaired_node_name
When the impaired controller shows Waiting for giveback…, press Ctrl-C, and then respond
y
Do not use this procedure if your system is in a two-node MetroCluster configuration. |
If you have a MetroCluster configuration, you must have confirmed that the MetroCluster Configuration State is configured and that the nodes are in an enabled and normal state (
metrocluster node show
cluster1:*> system node autosupport invoke -node * -type all -message MAINT=2h
y
when prompted.System prompt or password prompt (enter system password)
y
Step 2: Replace the NVRAM module
To replace the NVRAM module, locate it in slot 6 in the chassis and follow the specific sequence of steps.
If you are not already grounded, properly ground yourself.
Remove the target NVRAM module from the chassis:
Depress the lettered and numbered cam button.
The cam button moves away from the chassis.
Rotate the cam latch down until it is in a horizontal position.
The NVRAM module disengages from the chassis and moves out a few inches.
Remove the NVRAM module from the chassis by pulling on the pull tabs on the sides of the module face.
Animation - Replace the NVRAM module
Lettered and numbered cam latch
Cam latch completely unlocked
Set the NVRAM module on a stable surface and remove the cover from the NVRAM module by pushing down on the blue locking button on the cover, and then, while holding down the blue button, slide the lid off the NVRAM module.
Cover locking button
DIMM and DIMM ejector tabs
Remove the DIMMs, one at a time, from the old NVRAM module and install them in the replacement NVRAM module.
Close the cover on the module.
Install the replacement NVRAM module into the chassis:
Align the module with the edges of the chassis opening in slot 6.
Gently slide the module into the slot until the lettered and numbered cam latch begins to engage with the I/O cam pin, and then push the cam latch all the way up to lock the module in place.
Step 3: Replace a NVRAM DIMM
To replace NVRAM DIMMs in the NVRAM module, you must remove the NVRAM module, open the module, and then replace the target DIMM.
Animation - Replace NVRAM DIMM
cam latch completely unlocked
Locate the DIMM to be replaced inside the NVRAM module, and then remove it by pressing down on the DIMM locking tabs and lifting the DIMM out of the socket.
Install the replacement DIMM by aligning the DIMM with the socket and gently pushing the DIMM into the socket until the locking tabs lock in place.
Install the NVRAM module into the chassis:
Step 4: Reboot the controller
After you replace the FRU, you must reboot the controller module.
To boot ONTAP from the LOADER prompt, enter
bye
Step 5: Reassign disks
You must confirm the system ID change when you boot the replacement controller and then verify that the change was implemented.
Disk reassignment is only needed when replacing the NVRAM module and does not apply to NVRAM DIMM replacement. |
If the replacement controller is in Maintenance mode (showing the
prompt), exit Maintenance mode and go to the LOADER prompt:halt
From the LOADER prompt on the replacement controller, boot the controller and entering y if you are prompted to override the system ID due to a system ID mismatch.
Wait until the Waiting for giveback… message is displayed on the console of the controller with the replacement module and then, from the healthy controller, verify that the new partner system ID has been automatically assigned:
storage failover show
In the command output, you should see a message that the system ID has changed on the impaired controller, showing the correct old and new IDs. In the following example, node2 has undergone replacement and has a new system ID of 151759706.
node1:> storage failover show Takeover Node Partner Possible State Description ------------ ------------ -------- ------------------------------------- node1 node2 false System ID changed on partner (Old: 151759755, New: 151759706), In takeover node2 node1 - Waiting for giveback (HA mailboxes)
Give back the controller:
From the healthy controller, give back the replaced controller's storage:
storage failover giveback -ofnode replacement_node_name
The replacement controller takes back its storage and completes booting.
If you are prompted to override the system ID due to a system ID mismatch, you should enter
y
.If the giveback is vetoed, you can consider overriding the vetoes. For more information, see the Manual giveback commands topic to override the veto.
After the giveback has been completed, confirm that the HA pair is healthy and that takeover is possible:
The output from the
command should not include the System ID changed on partner message.
Verify that the disks were assigned correctly:
storage disk show -ownership
The disks belonging to the replacement controller should show the new system ID. In the following example, the disks owned by node1 now show the new system ID, 151759706:
node1:> storage disk show -ownership Disk Aggregate Home Owner DR Home Home ID Owner ID DR Home ID Reserver Pool ----- ------ ----- ------ -------- ------- ------- ------- --------- --- 1.0.0 aggr0_1 node1 node1 - 151759706 151759706 - 151759706 Pool0 1.0.1 aggr0_1 node1 node1 151759706 151759706 - 151759706 Pool0 . . .
If the system is in a MetroCluster configuration, monitor the status of the controller:
The MetroCluster configuration takes a few minutes after the replacement to return to a normal state, at which time each controller will show a configured state, with DR Mirroring enabled and a mode of normal. The
metrocluster node show -fields node-systemid
command output displays the old system ID until the MetroCluster configuration returns to a normal state. -
If the controller is in a MetroCluster configuration, depending on the MetroCluster state, verify that the DR home ID field shows the original owner of the disk if the original owner is a controller on the disaster site.
This is required if both of the following are true:
The MetroCluster configuration is in a switchover state.
The replacement controller is the current owner of the disks on the disaster site.
If your system is in a MetroCluster configuration, verify that each controller is configured:
metrocluster node show - fields configuration-state
node1_siteA::> metrocluster node show -fields configuration-state dr-group-id cluster node configuration-state ----------- ---------------------- -------------- ------------------- 1 node1_siteA node1mcc-001 configured 1 node1_siteA node1mcc-002 configured 1 node1_siteB node1mcc-003 configured 1 node1_siteB node1mcc-004 configured 4 entries were displayed.
Verify that the expected volumes are present for each controller:
vol show -node node-name
If storage encryption is enabled, you must restore functionality.
If you disabled automatic takeover on reboot, enable it from the healthy controller:
storage failover modify -node replacement-node-name -onreboot true
Step 6: Restore Storage and Volume Encryption functionality
If you have storage encryption enabled, use the appropriate procedure.
This step does not apply to NVRAM DIMM replacement. |
Boot the node to the boot menu.
Select option 10,
Set onboard key management recovery secrets
Enter the passphrase for the onboard key manager you obtained from the customer.
At the prompt, paste the backup key data from the output of
security key-manager backup show
ORsecurity key-manager onboard show-backup
command.Example of backup data:
--------------------------BEGIN BACKUP--------------------------
TmV0QXBwIEtleSBCbG9iAAEAAAAEAAAAcAEAAAAAAADuD+byAAAAACEAAAAAAAAA QAAAAAAAAABvOlH0AAAAAMh7qDLRyH1DBz12piVdy9ATSFMT0C0TlYFss4PDjTaV dzRYkLd1PhQLxAWJwOIyqSr8qY1SEBgm1IWgE5DLRqkiAAAAAAAAACgAAAAAAAAA 3WTh7gAAAAAAAAAAAAAAAAIAAAAAAAgAZJEIWvdeHr5RCAvHGclo+wAAAAAAAAAA IgAAAAAAAAAoAAAAAAAAAEOTcR0AAAAAAAAAAAAAAAACAAAAAAAJAGr3tJA/ LRzUQRHwv+1aWvAAAAAAAAAAACQAAAAAAAAAgAAAAAAAAACdhTcvAAAAAJ1PXeBf ml4NBsSyV1B4jc4A7cvWEFY6lLG6hc6tbKLAHZuvfQ4rIbYAAAAAAAAAAAAAAAAA AAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAA AAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAA . . . . H4nPQM0nrDRYRa9SCv8AAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAA AAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAAA AAAAAAAA
---------------------------END BACKUP---------------------------
The controller returns to the boot menu. -
Select option 1,
Normal Boot
Give back only the CFO aggregates with the
storage failover giveback -fromnode local -only-cfo-aggregates true
command.-
If the command fails because of a failed disk, physically disengage the failed disk, but leave the disk in the slot until a replacement is received.
If the command fails because of an open CIFS session, check with the customer how to close out CIFS sessions.
Terminating CIFS can cause loss of data. -
If the command fails because the partner "not ready", wait 5 minutes for the NVRAMs to synchronize.
If the command fails because of an NDMP, SnapMirror, or SnapVault process, disable the process. See the appropriate content for more information.
Once the giveback completes, check the failover and giveback status with the
andstorage failover show-giveback
commands.Only the CFO aggregates (root aggregate and CFO style data aggregates) will be shown.
Run the security key-manager onboard sync:
Run the
command and then enter the passphrase when prompted. -
Enter the
security key-manager key-query
command to see a detailed view of all keys stored in the onboard key manager and verify that theRestored
column =yes/true
for all authentication keys.If the Restored
column = anything other thanyes/true
, contact Customer Support. -
Wait 10 minutes for the key to synchronize across the cluster.
Move the console cable to the partner controller.
Give back the target controller using the
command. -
Check the giveback status, three minutes after it reports complete, using the
command.If giveback is not complete after 20 minutes, contact Customer Support.
At the clustershell prompt, enter the net int show -is-home false command to list the logical interfaces that are not on their home controller and port.
If any interfaces are listed as
false
, revert those interfaces back to their home port using the net int revert command. -
Move the console cable to the target controller and run the
version -v
command to check the ONTAP versions. -
Restore automatic giveback if you disabled it by using the
command. -
Reset the MSID if it was previously set and was captured at the beginning of this procedure:
Assign a data authentication key to a FIPS drive or SED using the
storage encryption disk modify -disk disk_ID -data-key-id key_ID
command.You can use the security key-manager key query -key-type NSE-AK
command to view key IDs. -
Verify that the authentication keys have been assigned using the
storage encryption disk show
command.
Boot the controller to the boot menu.
Select option 11,
Configure node for external key management
Enter the management certificate information at the prompts.
The controller returns to the boot menu after the management certificate information is completed. -
Select option 1,
Normal Boot
Move the console cable to the partner controller and give back the target controller storage using the storage failover giveback -fromnode local -only-cfo-aggregates true local command.
If the command fails because of an open CIFS sessions, check with customer how to close out CIFS sessions.
If the command fails because the partner is "not ready", wait 5 minutes for the NVMEMs to synchronize.
Wait 3 minutes and check the failover status with the storage failover show command.
command to list the logical interfaces that are not on their home controller and port.If any interfaces are listed as
false
, revert those interfaces back to their home port using thenet int revert
command. -
version -v
command. -
Use the
at the clustershell prompt, to review the output. -
Use the
command to display the encryption and authentication keys that are stored on the key management servers.-
If the
Restored
column =yes/true
, you are done and can proceed to complete the replacement process. -
If the
Key Manager type
=external
and theRestored
, use the security key-manager external restore command to restore the key IDs of the authentication keys.If the command fails, contact Customer Support. -
If the
Key Manager type
=onboard
and theRestored
, use the security key-manager onboard sync command to re-sync the Key Manager type.Use the
command to verify that theRestored
column =yes/true
Connect the console cable to the partner controller.
Give back the controller using the storage failover giveback -fromnode local command.
command. -
command.
Step 7: Return the failed part to NetApp
Return the failed part to NetApp, as described in the RMA instructions shipped with the kit. See the Part Return & Replacements page for further information.