StorageGRID appliances
Troubleshoot hardware installation for an SG5700 or SG6000
Contributors netapp-perveilerk netapp-pcarriga
If you encounter issues during the installation, you might find it helpful to review troubleshooting information related to hardware setup and connectivity issues.
View boot-up codes (SG6000-CN controller)
When you apply power to the appliance, the BMC logs a series of boot-up codes for the SG6000-CN controller. You can view these codes in several ways.
Before you begin
  • You know how to access the BMC dashboard.
  • If you want to use serial-over-LAN (SOL), you have experience using IPMI SOL console applications.
Steps
  1. Select one of the following methods for viewing the boot-up codes for the appliance controller, and gather the required equipment.
    Method Required equipment
    VGA console
    • VGA-capable monitor
    • VGA cable
    KVM
    • RJ-45 cable
    Serial port
    • DB-9 serial cable
    • Virtual serial terminal
    SOL
  2. If you are using a VGA console, perform these steps:
    1. Connect a VGA-capable monitor to the VGA port on the back of the appliance.
    2. View the codes displayed on the monitor.
  3. If you are using BMC KVM, perform these steps:
    1. Connect to the BMC management port and log in to the BMC web interface.
    2. Select Remote Control.
    3. Launch the KVM.
    4. View the codes on the virtual monitor.
  4. If you are using a serial port and terminal, perform these steps:
    1. Connect to the DB-9 serial port on the back of the appliance.
    2. Use settings 115200 8-N-1.
    3. View the codes printed over the serial terminal.
  5. If you are using SOL, perform these steps:
    1. Connect to the IPMI SOL using the BMC IP address and login credentials.
      ipmitool -I lanplus -H BMC_Port_IP -U admin -P Password sol activate
      Note In some cases the default username for an SG6000 appliance might be root instead of admin.
    2. View the codes on the virtual serial terminal.
  6. Use the table to look up the codes for your appliance.
    Code Indicates
    HT
    The master boot script is waiting for OS boot to complete.
    HI
    The master boot script has started.
    PP
    The system is checking to see if the FPGA needs to be updated.
    HP
    The system is checking to see if the network interface card (NIC) firmware needs to be updated.
    RB
    The system is rebooting after applying firmware updates.
    FP
    The hardware subsystem firmware update checks have been completed. Inter-controller communication services are starting.
    HE
    For an appliance Storage Node only:
    The system is awaiting connectivity with the storage controllers and synchronizing with the SANtricity operating system.
    Note: If the boot-up procedure does not progress past this stage, perform these steps:
    1. Confirm that the four interconnect cables between the SG6000-CN controller and the two storage controllers are securely connected.
    2. As required, replace one or more of the cables, and try again.
    3. If this does not resolve the issue, contact technical support.
    HC
    The system is checking for existing StorageGRID installation data.
    HO
    The StorageGRID Appliance Installer is running.
    HA
    StorageGRID is running.
View error codes (SG6000-CN controller)
If a hardware error occurs when the SG6000-CN controller is booting up, the BMC logs an error code. As required, you can view these error codes using the BMC interface or the appliance serial port, and then work with technical support to resolve the issue.
Note
Before you begin
If your BMC does not have a BIOS POST Code menu item, access the error codes using the appliance serial port.
  • If you are using the BMC, you know how to access the BMC dashboard.
  • If you are using a serial port and terminal, gather the required equipment:
    • DB-9 serial cable
Steps
  1. Access the error codes using one of the following methods.
    BMC
    If you are using the BMC, perform these steps:
    1. Access the BMC dashboard.
    2. From the BMC dashboard, select BIOS POST Code.
    3. Review the information displayed for Current Code and the Previous Code.
    Serial port
    If you are using a serial port and terminal, perform these steps to view the error codes. BIOS POST codes display on the serial console when the appliance reboots.
  2. If any of the following error codes are shown, work with technical support to resolve the issue.
    Code Indicates
    0x0E
    Microcode not found
    0x0F
    Microcode not loaded
    0x50
    Memory initialization error. Invalid memory type or incompatible memory speed.
    0x51
    Memory initialization error. SPD reading has failed.
    0x52
    Memory initialization error. Invalid memory size or memory modules don't match.
    0x53
    Memory initialization error. No usable memory detected.
    0x54
    Unspecified memory initialization error
    0x55
    Memory not installed
    0x56
    Invalid CPU type or speed
    0x57
    CPU mismatch
    0x58
    CPU self-test failed, or possible CPU cache error
    0x59
    CPU micro-code is not found, or micro-code update failed
    0x5A
    Internal CPU error
    0x5B
    Reset PPI is not available
    0x5C
    PEI phase BMC self-test failure
    0xD0
    CPU initialization error
    0xD1
    North bridge initialization error
    0xD2
    South bridge initialization error
    0xD3
    Some architectural protocols aren't available
    0xD4
    PCI resource allocation error. Out of resources.
    0xD5
    No space for legacy option ROM
    0xD6
    No console output devices are found
    0xD7
    No console input devices are found
    0xD8
    Invalid password
    0xD9
    Error loading boot option (LoadImage returned error)
    0xDA
    Boot option failed (StartImage returned error)
    0xDB
    Flash update failed
    0xDC
    Reset protocol is not available
    0xDD
    DXE phase BMC self-test failure
    0xE8
    MRC: ERR_NO_MEMORY
    0xE9
    MRC: ERR_LT_LOCK
    0xEA
    MRC: ERR_DDR_INIT
    0xEB
    MRC: ERR_MEM_TEST
    0xEC
    MRC: ERR_VENDOR_SPECIFIC
    0xED
    MRC: ERR_DIMM_COMPAT
    0xEE
    MRC: ERR_MRC_COMPATIBILITY
    0xEF
    MRC: ERR_MRC_STRUCT
    0xF0
    MRC: ERR_SET_VDD
    0xF1
    MRC: ERR_IOT_MEM_BUFFER
    0xF2
    MRC: ERR_RC_INTERNAL
    0xF3
    MRC: ERR_INVALID_REG_ACCESS
    0xF4
    MRC: ERR_SET_MC_FREQ
    0xF5
    MRC: ERR_READ_MC_FREQ
    0x70
    MRC: ERR_DIMM_CHANNEL
    0x74
    MRC: ERR_BIST_CHECK
    0xF6
    MRC: ERR_SMBUS
    0xF7
    MRC: ERR_PCU
    0xF8
    MRC: ERR_NGN
    0xF9
    MRC: ERR_INTERLEAVE_FAILURE
Hardware setup appears to hang (SG6000 or SG5700)
The StorageGRID Appliance Installer might not be available if hardware faults or cabling errors prevent the storage controllers or the appliance controller from completing their boot-up processing.
Example 1. Steps
SG5700
  1. Watch the codes on the SG5700 seven-segment displays.
    While the hardware is initializing during power up, the two seven-segment displays show a sequence of codes. When the hardware boots successfully, the seven-segment displays show different codes for each controller.
  2. Review the codes on the seven-segment display for the E5700SG controller.
    Note The installation and provisioning take time. Some installation phases don't report updates to the StorageGRID Appliance Installer for several minutes.
    If an error occurs, the seven-segment display flashes a sequence, such as HE.
  3. To understand what these codes mean, see the following resources:
    Controller Reference
    E5700SG controller
    • “Status indicators on the E5700SG controller”
    • “HE error: Error synchronizing with SANtricity OS Software”
    E2800 controller
    Note: The codes described for the E-Series E5700 controller don't apply to the E5700SG controller in the appliance.
  4. If this does not resolve the issue, contact technical support.
SG6000
  1. For the storage controllers, watch the codes on the seven-segment displays.
    While the hardware is initializing during power up, the two seven-segment displays show a sequence of codes. When the hardware boots successfully, both seven-segment displays show 99.
  2. Review the LEDs on the SG6000-CN controller and the boot-up and error codes displayed in the BMC.
  3. If you need help resolving an issue, contact technical support.
Connection issues (SG5700 or SG6000)
If you encounter connection issues during the StorageGRID appliance installation, you should perform the corrective action steps listed.
Unable to connect to SG6000 appliance
If you can't connect to the appliance, there might be a network issue, or the hardware installation might not have been completed successfully.
Steps
  1. If you are unable to connect to SANtricity System Manager:
    1. Try to ping the appliance using the IP address for either storage controller on the management network for SANtricity System Manager:
      ping Storage_Controller_IP
    2. If you receive no response from the ping, confirm you are using the correct IP address.
      Use the IP address for management port 1 on either storage controller.
    3. If the IP address is correct, check appliance cabling and the network setup.
      If that does not resolve the issue, contact technical support.
    4. If the ping was successful, open a web browser.
    5. Enter the URL for SANtricity System Manager:
      https://Storage_Controller_IP
      The log in page for SANtricity System Manager appears.
  2. If you are unable to connect to the SG6000-CN controller:
    1. Try to ping the appliance using the IP address for the SG6000-CN controller:
      ping SG6000-CN_Controller_IP
      You can use the IP address of the appliance on the Grid Network, the Admin Network, or the Client Network.
    3. If the IP address is correct, check appliance cabling, SFP transceivers, and the network setup.
    4. If physical access to the SG6000-CN is available, you can use a direct connection to the permanent link-local IP 169.254.0.1 to check controller networking configuration and update if necessary. For detailed instructions, see step 2 in Accessing StorageGRID Appliance Installer.
    5. If the ping was successful, open a web browser.
    6. Enter the URL for the StorageGRID Appliance Installer:
      https://SG6000-CN_Controller_IP:8443
      The Home page appears.
SG6060 expansion shelves don't appear in Appliance Installer
If you have installed expansion shelves for the SG6060 and they don't appear in the StorageGRID Appliance Installer, you should verify that the shelves have been completely installed and powered on.
About this task
You can verify that the expansion shelves are connected to the appliance by viewing the following information in the StorageGRID Appliance Installer:
  • The Home page contains a message about expansion shelves.
    Expansion Shelves Msg
  • The Advanced > RAID Mode page indicates by number of drives whether or not the appliance includes expansion shelves. For example, in the following screen shot, two SSDs and 178 HDDs are shown. An SG6060 with two expansion shelves contains 180 total drives.
Number of Drives
If the StorageGRID Appliance Installer pages don't indicate that expansion shelves are present, follow this procedure.
Steps
  1. Verify that all required cables have been firmly connected. See Cable appliance.
  2. Verify that you have powered on the expansion shelves. See Connect power cords and apply power (SG6000).
Unable to connect to SG5700 appliance
Steps
    1. Try to ping the appliance using the IP address for the E2800 controller on the management network for SANtricity System Manager:
      ping E2800_Controller_IP
      Use the IP address for management port 1 on the E2800 controller.
      https://E2800_Controller_IP
  2. If you are unable to connect to the E5700SG controller:
    1. Try to ping the appliance using the IP address for the E5700SG controller:
      ping E5700SG_Controller_IP
    5. Enter the URL for the StorageGRID Appliance Installer:
      https://E5700SG_Controller_IP:8443
HE error: Error synchronizing with SANtricity OS Software (SG5700)
The seven-segment display on the compute controller shows an HE error code if the StorageGRID Appliance Installer can't synchronize with SANtricity OS Software.
About this task
If an HE error code is displayed, perform this corrective action.
Steps
  1. Check the integrity of the two SAS interconnect cables, and confirm they are securely connected.
  2. As required, replace one or both of the cables, and try again.