Prepare the nodes for upgrade
Before you can replace the original nodes, you must confirm that they are in an HA pair, have no missing or failed disks, can access each other's storage, and do not own data LIFs assigned to the other nodes in the cluster. You also must collect information about the original nodes and, if the cluster is in a SAN environment, confirm that all the nodes in the cluster are in quorum.
Confirm that each of the original nodes has enough resources to adequately support the workload of both nodes during takeover mode.
Refer to References to link to HA pair management and follow the Best practices for HA pairs section. Neither of the original nodes should be running at more than 50 percent utilization; if a node is running at less than 50 percent utilization, it can handle the loads for both nodes during the controller upgrade.
Complete the following substeps to create a performance baseline for the original nodes:
Make sure that the diagnostic user account is unlocked.
The diagnostic user account is intended only for low-level diagnostic purposes and should be used only with guidance from technical support.
For information about unlocking the user accounts, refer to References to link to the System Administration Reference.
Refer to References to link to the NetApp Support Site and download the Performance and Statistics Collector (Perfstat Converged).
The Perfstat Converged tool lets you establish a performance baseline for comparison after the upgrade.
Create a performance baseline, following the instructions on the NetApp Support Site.
Refer to References to link to the NetApp Support Site and open a support case on the NetApp Support Site.
You can use the case to report any issues that might arise during the upgrade.
Verify that NVMEM or NVRAM batteries of node3 and node4 are charged, and charge them if they are not.
You must physically check node3 and node4 to see if the NVMEM or NVRAM batteries are charged. For information about the LEDs for the model of node3 and node4, refer to References to link to the Hardware Universe.
Do not try to clear the NVRAM contents. If there is a need to clear the contents of NVRAM, contact NetApp technical support. -
Check the version of ONTAP on node3 and node4.
The new nodes must have the same version of ONTAP 9.x installed on them that is installed on the original nodes. If the new nodes have a different version of ONTAP installed, you must netboot the new controllers after you install them. For instructions on how to upgrade ONTAP, refer to References to link to Upgrade ONTAP.
Information about the version of ONTAP on node3 and node4 should be included in the shipping boxes. The ONTAP version is displayed when the node boots up or you can boot the node to maintenance mode and run the command:
version -
Check whether you have two or four cluster LIFs on node1 and node2:
network interface show -role clusterThe system displays any cluster LIFs, as shown in the following example:
cluster::> network interface show -role cluster Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ------- ---------- ---------- ---------------- -------- ------- ---- node1 clus1 up/up 172.17.177.2/24 node1 e0c true clus2 up/up 172.17.177.6/24 node1 e0e true node2 clus1 up/up 172.17.177.3/24 node2 e0c true clus2 up/up 172.17.177.7/24 node2 e0e true -
If you have two or four cluster LIFs on node1 or node2, make sure that you can ping both cluster LIFs across all the available paths by completing the following substeps:
Enter the advanced privilege level:
set -privilege advancedThe system displays the following message:
Warning: These advanced commands are potentially dangerous; use them only when directed to do so by NetApp personnel. Do you wish to continue? (y or n):
Enter
y. -
Ping the nodes and test the connectivity:
cluster ping-cluster -node node_nameThe system displays a message similar to the following example:
cluster::*> cluster ping-cluster -node node1 Host is node1 Getting addresses from network interface table... Local = 10.254.231.102 10.254.91.42 Remote = 10.254.42.25 10.254.16.228 Ping status: ... Basic connectivity succeeds on 4 path(s) Basic connectivity fails on 0 path(s) ................ Detected 1500 byte MTU on 4 path(s): Local 10.254.231.102 to Remote 10.254.16.228 Local 10.254.231.102 to Remote 10.254.42.25 Local 10.254.91.42 to Remote 10.254.16.228 Local 10.254.91.42 to Remote 10.254.42.25 Larger than PMTU communication succeeds on 4 path(s) RPC status: 2 paths up, 0 paths down (tcp check) 2 paths up, 0 paths down (udp check)
If the node uses two cluster ports, you should see that it is able to communicate on four paths, as shown in the example.
Return to the administrative level privilege:
set -privilege admin
Confirm that node1 and node2 are in an HA pair and verify that the nodes are connected to each other, and that takeover is possible:
storage failover showThe following example shows the output when the nodes are connected to each other and
takeover is possible:cluster::> storage failover show Takeover Node Partner Possible State Description -------------- -------------- -------- ------------------------------- node1 node2 true Connected to node2 node2 node1 true Connected to node1Neither node should be in partial giveback. The following example shows that node1 is in partial giveback:
cluster::> storage failover show Takeover Node Partner Possible State Description -------------- -------------- -------- ------------------------------- node1 node2 true Connected to node2, Partial giveback node2 node1 true Connected to node1If either node is in partial giveback, use the
storage failover givebackcommand to perform the giveback, and then use thestorage failover show-givebackcommand to make sure that no aggregates still need to be given back. For detailed information about the commands, refer to References to link to HA pair management. -
Confirm that neither node1 nor node2 owns the aggregates for which it is the current owner (but not the home owner):
storage aggregate show -nodes node_name -is-home false -fields owner-name, home-name, stateIf neither node1 nor node2 owns aggregates for which it is the current owner (but not the home owner), the system returns a message similar to the following example:
cluster::> storage aggregate show -node node2 -is-home false -fields owner-name,home-name,state There are no entries matching your query.
The following example shows the output of the command for a node named node2 that is the home owner, but not the current owner, of four aggregates:
cluster::> storage aggregate show -node node2 -is-home false -fields owner-name,home-name,state aggregate home-name owner-name state ------------- ------------ ------------ ------ aggr1 node1 node2 online aggr2 node1 node2 online aggr3 node1 node2 online aggr4 node1 node2 online 4 entries were displayed. -
Take one of the following actions:
If the command in Step 9… Then… Had blank output
Skip Step 11 and go to Step 12.
Had output
Go to Step 11.
If either node1 or node2 owns aggregates for which it is the current owner but not the home owner, complete the following substeps:
Return the aggregates currently owned by the partner node to the home owner node:
storage failover giveback -ofnode home_node_name -
Verify that neither node1 nor node2 still owns aggregates for which it is the current owner (but not the home owner):
storage aggregate show -nodes node_name -is-home false -fields owner-name, home-name, stateThe following example shows the output of the command when a node is both the current owner and home owner of aggregates:
cluster::> storage aggregate show -nodes node1 -is-home true -fields owner-name,home-name,state aggregate home-name owner-name state ------------- ------------ ------------ ------ aggr1 node1 node1 online aggr2 node1 node1 online aggr3 node1 node1 online aggr4 node1 node1 online 4 entries were displayed.
Confirm that node1 and node2 can access each other's storage and verify that no disks are missing:
storage failover show -fields local-missing-disks,partner-missing-disksThe following example shows the output when no disks are missing:
cluster::> storage failover show -fields local-missing-disks,partner-missing-disks node local-missing-disks partner-missing-disks -------- ------------------- --------------------- node1 None None node2 None None
If any disks are missing, refer to References to link to Disk and aggregate management with the CLI, Logical storage management with the CLI, and HA pair management to configure storage for the HA pair.
Confirm that node1 and node2 are healthy and eligible to participate in the cluster:
cluster showThe following example shows the output when both nodes are eligible and healthy:
cluster::> cluster show Node Health Eligibility --------------------- ------- ------------ node1 true true node2 true true
Set the privilege level to advanced:
set -privilege advanced -
Confirm that node1 and node2 are running the same ONTAP release:
system node image show -node node1,node2 -iscurrent trueThe following example shows the output of the command:
cluster::*> system node image show -node node1,node2 -iscurrent true Is Is Install Node Image Default Current Version Date -------- ------- ------- ------- --------- ------------------- node1 image1 true true 9.1 2/7/2017 20:22:06 node2 image1 true true 9.1 2/7/2017 20:20:48 2 entries were displayed. -
Verify that neither node1 nor node2 owns any data LIFs that belong to other nodes in the cluster and check the
Current NodeandIs Homecolumns in the output:network interface show -role data -is-home false -curr-node node_nameThe following example shows the output when node1 has no LIFs that are home-owned by other nodes in the cluster:
cluster::> network interface show -role data -is-home false -curr-node node1 There are no entries matching your query.
The following example shows the output when node1 owns data LIFs home-owned by the other node:
cluster::> network interface show -role data -is-home false -curr-node node1 Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------------ ------------- ------- ---- vs0 data1 up/up 172.18.103.137/24 node1 e0d false data2 up/up 172.18.103.143/24 node1 e0f false 2 entries were displayed. -
If the output in Step 15 shows that either node1 or node2 owns any data LIFs home-owned by other nodes in the cluster, migrate the data LIFs away from node1 or node2:
network interface revert -vserver * -lif *For detailed information about the
network interface revertcommand, refer to References to link to the ONTAP 9 Command reference. -
Check whether node1 or node2 owns any failed disks:
storage disk show -nodelist node1,node2 -brokenIf any of the disks have failed, remove them, following instructions in the Disk and aggregate management with the CLI. (Refer to References to link to Disk and aggregate management with the CLI.)
Collect information about node1 and node2 by completing the following substeps and recording the output of each command:
You will use this information later in the procedure.
If you have a system with more than two cluster ports per node, such as an FAS8080 or an AFF8080 system, before you start the upgrade, you must migrate and re-home the cluster LIFs to two cluster ports per node. If you perform the controller upgrade with more than two cluster ports per node, cluster LIFs might be missing on the new controller after the upgrade.
Record the model, system ID, and serial number of both nodes:
system node show -node node1,node2 -instanceYou will use the information to reassign disks and decommission the original nodes. -
Enter the following command on both node1 and node2 and record information about the shelves, number of disks in each shelf, flash storage details, memory, NVRAM, and network cards from the output:
run -node node_name sysconfigYou can use the information to identify parts or accessories that you might want to transfer to node3 or node4. -
Enter the following command on both node1 and node2 and record the aggregates that are online on both nodes:
storage aggregate show -node node_name -state onlineYou can use this information and the information in the following substep to verify that the aggregates and volumes remain online throughout the procedure, except for the brief period when they are offline during relocation. -
Enter the following command on both node1 and node2 and record the volumes that are offline on both nodes:
volume show -node node_name -state offlineAfter the upgrade, you will run the command again and compare the output with the output in this step to see if any other volumes have gone offline.
Enter the following commands to see if any interface groups or VLANs are configured on node1 or node2:
network port ifgrp shownetwork port vlan showMake note of whether interface groups or VLANs are configured on node1 or node2; you need that information in the next step and later in the procedure.
Complete the following substeps on both node1 and node2 to confirm that physical ports can be mapped correctly later in the procedure:
Enter the following command to see if there are failover groups on the node other than
clusterwide:network interface failover-groups showFailover groups are sets of network ports present on the system. Because upgrading the controller hardware can change the location of physical ports, failover groups can be inadvertently changed during the upgrade.
The system displays failover groups on the node, as shown in the following example:
cluster::> network interface failover-groups show Vserver Group Targets ------------------- ----------------- ---------- Cluster Cluster node1:e0a, node1:e0b node2:e0a, node2:e0b fg_6210_e0c Default node1:e0c, node1:e0d node1:e0e, node2:e0c node2:e0d, node2:e0e 2 entries were displayed. -
If there are failover groups present other than
clusterwide, record the failover group names and the ports that belong to the failover groups. -
Enter the following command to see if there are any VLANs configured on the node:
network port vlan show -node node_nameVLANs are configured over physical ports. If the physical ports change, then the VLANs need to be re-created later in the procedure.
The system displays VLANs configured on the node, as shown in the following example:
cluster::> network port vlan show Network Network Node VLAN Name Port VLAN ID MAC Address ------ --------- ------- ------- ------------------ node1 e1b-70 e1b 70 00:15:17:76:7b:69
If there are VLANs configured on the node, take note of each network port and VLAN ID pairing.
If interface groups or VLANS are… Then… On node1 or node2
Not on node1 or node2
Go to Step 24.
If you do not know if node1 and node2 are in a SAN or non-SAN environment, enter the following command and examine its output:
network interface show -vserver vserver_name -data-protocol iscsi|fcpIf neither iSCSI nor FC is configured for the SVM, the command displays a message similar to the following example:
cluster::> network interface show -vserver Vserver8970 -data-protocol iscsi|fcp There are no entries matching your query.
You can confirm that the node is in a NAS environment by using the
network interface showcommand with the-data-protocol nfs|cifsparameters.If either iSCSI or FC is configured for the SVM, the command displays a message similar to the following example:
cluster::> network interface show -vserver vs1 -data-protocol iscsi|fcp Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home -------- ---------- ---------- ------------------ -------- ------- ---- vs1 vs1_lif1 up/down 172.17.176.20/24 node1 0d true -
Verify that all the nodes in the cluster are in quorum by completing the following substeps:
Enter
y. -
Verify the cluster service state in the kernel, once for each node:
cluster kernel-service showThe system displays a message similar to the following example:
cluster::*> cluster kernel-service show Master Cluster Quorum Availability Operational Node Node Status Status Status ------------- ------------- ------------- ------------- ------------- node1 node1 in-quorum true operational node2 in-quorum true operational 2 entries were displayed.Nodes in a cluster are in quorum when a simple majority of nodes are healthy and can communicate with each other. For more information, refer to References to link to the System Administration Reference.
Return to the administrative privilege level:
If the cluster… Then… Has SAN configured
Go to Step 26.
Does not have SAN configured
Go to Step 29.
Verify that there are SAN LIFs on node1 and node2 for each SVM that has either SAN iSCSI or FC service enabled by entering the following command and examining its output:
network interface show -data-protocol iscsi|fcp -home-node node_nameThe command displays SAN LIF information for node1 and node2. The following examples show the status in the Status Admin/Oper column as up/up, indicating that SAN iSCSI and FC service are enabled:
cluster::> network interface show -data-protocol iscsi|fcp Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home ----------- ---------- ---------- ------------------ --------- ------- ---- a_vs_iscsi data1 up/up 10.228.32.190/21 node1 e0a true data2 up/up 10.228.32.192/21 node2 e0a true b_vs_fcp data1 up/up 20:09:00:a0:98:19:9f:b0 node1 0c true data2 up/up 20:0a:00:a0:98:19:9f:b0 node2 0c true c_vs_iscsi_fcp data1 up/up 20:0d:00:a0:98:19:9f:b0 node2 0c true data2 up/up 20:0e:00:a0:98:19:9f:b0 node2 0c true data3 up/up 10.228.34.190/21 node2 e0b true data4 up/up 10.228.34.192/21 node2 e0b trueAlternatively, you can view more detailed LIF information by entering the following
command:network interface show -instance -data-protocol iscsi|fcp -
Capture the default configuration of any FC ports on the original nodes by entering the following command and recording the output for your systems:
ucadmin showThe command displays information about all FC ports in the cluster, as shown in the following example:
cluster::> ucadmin show Current Current Pending Pending Admin Node Adapter Mode Type Mode Type Status ------- ------- ------- --------- ------- --------- ----------- node1 0a fc initiator - - online node1 0b fc initiator - - online node1 0c fc initiator - - online node1 0d fc initiator - - online node2 0a fc initiator - - online node2 0b fc initiator - - online node2 0c fc initiator - - online node2 0d fc initiator - - online 8 entries were displayed.You can use the information after the upgrade to set the configuration of FC ports on the new nodes.
Complete the following substeps:
Enter the following command on one of the original nodes and record the output:
service-processor show -node * -instanceThe system displays detailed information about the SP on both nodes.
Confirm that the SP status is
online. -
Confirm that the SP network is configured.
Record the IP address and other information about the SP.
You might want to reuse the network parameters of the remote management devices, in this case the SPs, from the original system for the SPs on the new nodes.
For detailed information about the SP, refer to References to link to the System Administration Reference and the ONTAP 9 Command reference.
If you want the new nodes to have the same licensed functionality as the original nodes, enter the following command to see the cluster licenses on the original system:
system license show -owner *The following example shows the site licenses for cluster1:
system license show -owner * Serial Number: 1-80-000013 Owner: cluster1 Package Type Description Expiration ----------------- ------- --------------------- ----------- Base site Cluster Base License - NFS site NFS License - CIFS site CIFS License - SnapMirror site SnapMirror License - FlexClone site FlexClone License - SnapVault site SnapVault License - 6 entries were displayed.
Obtain new license keys for the new nodes at the NetApp Support Site. Refer to References to link to NetApp Support Site.
If the site does not have the license keys you need, contact your NetApp sales representative.
Check whether the original system has AutoSupport enabled by entering the following command on each node and examining its output:
system node autosupport show -node node1,node2The command output shows whether AutoSupport is enabled, as shown in the following example:
cluster::> system node autosupport show -node node1,node2 Node State From To Mail Hosts ---------------- --------- ------------- ---------------- ---------- node1 enable Postmaster admin@netapp.com mailhost node2 enable Postmaster - mailhost 2 entries were displayed.
If the original system… Then… Has AutoSupport enabled…
Go to Step 34.
Does not have AutoSupport enabled…
Enable AutoSupport by following the instructions in the System Administration Reference. (Refer to References to link to the System Administration Reference.)
Note: AutoSupport is enabled by default when you configure your storage system for the first time. Although you can disable AutoSupport at any time, you should leave it enabled. Enabling AutoSupport can significantly help identify problems and solutions should a problem occur on your storage system.
Verify that AutoSupport is configured with the correct mailhost details and recipient e-mail IDs by entering the following command on both of the original nodes and examining the output:
system node autosupport show -node node_name -instanceFor detailed information about AutoSupport, refer to References to link to the System Administration Reference and the ONTAP 9 Command reference.
Send an AutoSupport message to NetApp for node1 by entering the following command:
system node autosupport invoke -node node1 -type all -message "Upgrading node1 from platform_old to platform_new"Do not send an AutoSupport message to NetApp for node2 at this point; you do so later in the procedure. -
Verify that the AutoSupport message was sent by entering the following command and examining its output:
system node autosupport show -node node1 -instanceThe fields
Last Subject Sent:andLast Time Sent:contain the message title of the last message sent and the time the message was sent. -
If your system uses self-encrypting drives, see the Knowledge Base article How to tell if a drive is FIPS certified to determine the type of self-encrypting drives that are in use on the HA pair that you are upgrading. ONTAP software supports two types of self-encrypting drives:
FIPS-certified NetApp Storage Encryption (NSE) SAS or NVMe drives
Non-FIPS self-encrypting NVMe drives (SED)
You cannot mix FIPS drives with other types of drives on the same node or HA pair.
You can mix SEDs with non-encrypting drives on the same node or HA pair.
After preparing the nodes for upgrade, manage authentication keys using the Onboard Key Manager.