Migrate a CN1610 cluster switch to a Cisco Nexus 3232C cluster switch
To replace the existing CN1610 cluster switches in a cluster with Cisco Nexus 3232C cluster switches, you must perform a specific sequence of tasks.
Review requirements
Before migration, be sure to review Migration requirements.
The procedure requires the use of both ONTAP commands and Cisco Nexus 3000 Series Switches commands; ONTAP commands are used unless otherwise indicated. |
If necessary, refer to the following for more information:
Migrate the switches
The examples in this procedure use four nodes: Two nodes use four 10 GbE cluster interconnect ports: e0a, e0b, e0c, and e0d. The other two nodes use two 40 GbE cluster interconnect fiber cables: e4a and e4e. The Hardware Universe has information about the cluster fiber cables on your platforms. See What additional information do I need to install my equipment that is not in HWU? for more information about switch installation requirements.
The examples in this procedure use the following switch and node nomenclature:
The nodes are n1, n2, n3, and n4.
The command outputs might vary depending on different releases of ONTAP software.
The CN1610 switches to be replaced are CL1 and CL2.
The Nexus 3232C switches to replace the CN1610 switches are C1 and C2.
n1_clus1 is the first cluster logical interface (LIF) that is connected to cluster switch 1 (CL1 or C1) for node n1.
n1_clus2 is the first cluster LIF that is connected to cluster switch 2 (CL2 or C2) for node n1.
n1_clus3 is the second LIF that is connected to cluster switch 2 (CL2 or C2) for node n1.
n1_clus4 is the second LIF that is connected to cluster switch 1 (CL1 or C1) for node n1.
The number of 10 GbE and 40/100 GbE ports are defined in the reference configuration files (RCFs) available at Cisco® Cluster Network Switch Reference Configuration File Download.
Step 1: Prepare for migration
If AutoSupport is enabled on this cluster, suppress automatic case creation by invoking an AutoSupport message:
system node autosupport invoke -node * -type all -message MAINT=xhx is the duration of the maintenance window in hours.
The message notifies technical support of this maintenance task so that automatic case creation is suppressed during the maintenance window.
Display information about the devices in your configuration:
network device-discovery showShow example
The following example displays how many cluster interconnect interfaces have been configured in each node for each cluster interconnect switch:
cluster::> network device-discovery show Local Discovered Node Port Device Interface Platform ------ ------ ------------ ----------- ---------- n1 /cdp e0a CL1 0/1 CN1610 e0b CL2 0/1 CN1610 e0c CL2 0/2 CN1610 e0d CL1 0/2 CN1610 n2 /cdp e0a CL1 0/3 CN1610 e0b CL2 0/3 CN1610 e0c CL2 0/4 CN1610 e0d CL1 0/4 CN1610 8 entries were displayed. -
Determine the administrative or operational status for each cluster interface.
Display the cluster network port attributes:
network port show -role clusterShow example
cluster::*> network port show -role cluster (network port show) Node: n1 Broadcast Speed (Mbps) Health Ignore Port IPspace Domain Link MTU Admin/Open Status Health Status ----- --------- ---------- ----- ----- ------------ ------ ------------- e0a cluster cluster up 9000 auto/10000 - e0b cluster cluster up 9000 auto/10000 - e0c cluster cluster up 9000 auto/10000 - - e0d cluster cluster up 9000 auto/10000 - - Node: n2 Broadcast Speed (Mbps) Health Ignore Port IPspace Domain Link MTU Admin/Open Status Health Status ----- --------- ---------- ----- ----- ------------ ------ ------------- e0a cluster cluster up 9000 auto/10000 - e0b cluster cluster up 9000 auto/10000 - e0c cluster cluster up 9000 auto/10000 - e0d cluster cluster up 9000 auto/10000 - 8 entries were displayed. -
Display information about the logical interfaces:
network interface show -role clusterShow example
cluster::*> network interface show -role cluster (network interface show) Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home -------- ---------- ----------- -------------- -------- -------- ----- Cluster n1_clus1 up/up 10.10.0.1/24 n1 e0a true n1_clus2 up/up 10.10.0.2/24 n1 e0b true n1_clus3 up/up 10.10.0.3/24 n1 e0c true n1_clus4 up/up 10.10.0.4/24 n1 e0d true n2_clus1 up/up 10.10.0.5/24 n2 e0a true n2_clus2 up/up 10.10.0.6/24 n2 e0b true n2_clus3 up/up 10.10.0.7/24 n2 e0c true n2_clus4 up/up 10.10.0.8/24 n2 e0d true 8 entries were displayed. -
Display information about the discovered cluster switches:
system cluster-switch showShow example
The following example displays the cluster switches that are known to the cluster along with their management IP addresses:
cluster::> system cluster-switch show Switch Type Address Model ----------------------------- ---------------- ------------- -------- CL1 cluster-network 10.10.1.101 CN1610 Serial Number: 01234567 Is Monitored: true Reason: Software Version: 1.2.0.7 Version Source: ISDP CL2 cluster-network 10.10.1.102 CN1610 Serial Number: 01234568 Is Monitored: true Reason: Software Version: 1.2.0.7 Version Source: ISDP 2 entries displayed.
Verify that the appropriate RCF and image are installed on the new 3232C switches as necessary for your requirements, and make any essential site customizations.
You should prepare both switches at this time. If you need to upgrade the RCF and image, you must complete the following procedure:
See Cisco Ethernet Switches on the NetApp Support Site.
Note your switch and the required software versions in the table on that page.
Download the appropriate version of the RCF.
Click CONTINUE on the Description page, accept the license agreement, and then follow the instructions on the Download page to download the RCF.
Download the appropriate version of the image software at Cisco® Cluster and Management Network Switch Reference Configuration File Download.
Migrate the LIFs associated with the second CN1610 switch that you plan to replace:
network interface migrate -vserver vserver-name -lif lif-name -source-node source-node-name destination-node destination-node-name -destination-port destination-port-nameShow example
You must migrate each LIF individually as shown in the following example:
cluster::*> network interface migrate -vserver cluster -lif n1_clus2 -source-node n1 -destination-node n1 -destination-port e0a cluster::*> network interface migrate -vserver cluster -lif n1_clus3 -source-node n1 -destination-node n1 -destination-port e0d cluster::*> network interface migrate -vserver cluster -lif n2_clus2 -source-node n2 -destination-node n2 -destination-port e0a cluster::*> network interface migrate -vserver cluster -lif n2_clus3 -source-node n2 -destination-node n2 -destination-port e0d
Verify the cluster's health:
cluster::*> network interface show -role cluster (network interface show) Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home -------- ---------- ----------- --------------- -------- -------- ----- Cluster n1_clus1 up/up 10.10.0.1/24 n1 e0a true n1_clus2 up/up 10.10.0.2/24 n1 e0a false n1_clus3 up/up 10.10.0.3/24 n1 e0d false n1_clus4 up/up 10.10.0.4/24 n1 e0d true n2_clus1 up/up 10.10.0.5/24 n2 e0a true n2_clus2 up/up 10.10.0.6/24 n2 e0a false n2_clus3 up/up 10.10.0.7/24 n2 e0d false n2_clus4 up/up 10.10.0.8/24 n2 e0d true 8 entries were displayed.
Step 2: Replace cluster switch CL2 with C2
Shut down the cluster interconnect ports that are physically connected to switch CL2:
network port modify -node node-name -port port-name -up-admin falseShow example
The following example shows the four cluster interconnect ports being shut down for node n1 and node n2:
cluster::*> network port modify -node n1 -port e0b -up-admin false cluster::*> network port modify -node n1 -port e0c -up-admin false cluster::*> network port modify -node n2 -port e0b -up-admin false cluster::*> network port modify -node n2 -port e0c -up-admin false
Verify the connectivity of the remote cluster interfaces:
You can use the network interface check cluster-connectivity command to start an accessibility check for cluster connectivity and then display the details:
network interface check cluster-connectivity start and network interface check cluster-connectivity show
cluster1::*> network interface check cluster-connectivity start
NOTE: Wait for a number of seconds before running the show command to display the details.
cluster1::*> network interface check cluster-connectivity show
Source Destination Packet
Node Date LIF LIF Loss
n1
3/5/2022 19:21:18 -06:00 n1_clus2 n2-clus1 none
3/5/2022 19:21:20 -06:00 n1_clus2 n2_clus2 none
n2
3/5/2022 19:21:18 -06:00 n2_clus2 n1_clus1 none
3/5/2022 19:21:20 -06:00 n2_clus2 n1_clus2 none
For all ONTAP releases, you can also use the cluster ping-cluster -node <name> command to check the connectivity:
cluster1::*> cluster ping-cluster -node local
Host is n1
Getting addresses from network interface table...
Cluster n1_clus1 n1 e0a 10.10.0.1
Cluster n1_clus2 n1 e0b 10.10.0.2
Cluster n1_clus3 n1 e0c 10.10.0.3
Cluster n1_clus4 n1 e0d 10.10.0.4
Cluster n2_clus1 n2 e0a 10.10.0.5
Cluster n2_clus2 n2 e0b 10.10.0.6
Cluster n2_clus3 n2 e0c 10.10.0.7
Cluster n2_clus4 n2 e0d 10.10.0.8
Local = 10.10.0.1 10.10.0.2 10.10.0.3 10.10.0.4
Remote = 10.10.0.5 10.10.0.6 10.10.0.7 10.10.0.8
Cluster Vserver Id = 4294967293
Ping status:....
Basic connectivity succeeds on 16 path(s)
Basic connectivity fails on 0 path(s)
Detected 9000 byte MTU on 16 path(s):
Local 10.10.0.1 to Remote 10.10.0.5
Local 10.10.0.1 to Remote 10.10.0.6
Local 10.10.0.1 to Remote 10.10.0.7
Local 10.10.0.1 to Remote 10.10.0.8
Local 10.10.0.2 to Remote 10.10.0.5
Local 10.10.0.2 to Remote 10.10.0.6
Local 10.10.0.2 to Remote 10.10.0.7
Local 10.10.0.2 to Remote 10.10.0.8
Local 10.10.0.3 to Remote 10.10.0.5
Local 10.10.0.3 to Remote 10.10.0.6
Local 10.10.0.3 to Remote 10.10.0.7
Local 10.10.0.3 to Remote 10.10.0.8
Local 10.10.0.4 to Remote 10.10.0.5
Local 10.10.0.4 to Remote 10.10.0.6
Local 10.10.0.4 to Remote 10.10.0.7
Local 10.10.0.4 to Remote 10.10.0.8
Larger than PMTU communication succeeds on 16 path(s)
RPC status:
4 paths up, 0 paths down (tcp check)
4 paths up, 0 paths down (udp check)
Shut down the ISL ports 13 through 16 on the active CN1610 switch CL1 using the appropriate command.
For more information on Cisco commands, see the guides listed in the Cisco Nexus 3000 Series NX-OS Command References.
Show example
The following example shows ISL ports 13 through 16 being shut down on the CN1610 switch CL1:
(CL1)# configure (CL1)(Config)# interface 0/13-0/16 (CL1)(Interface 0/13-0/16)# shutdown (CL1)(Interface 0/13-0/16)# exit (CL1)(Config)# exit (CL1)#
Build a temporary ISL between CL1 and C2:
Show example
The following example shows a temporary ISL being built between CL1 (ports 13-16) and C2 (ports e1/24/1-4) using the Cisco
switchport mode trunkcommand:C2# configure C2(config)# interface port-channel 2 C2(config-if)# switchport mode trunk C2(config-if)# spanning-tree port type network C2(config-if)# mtu 9216 C2(config-if)# interface breakout module 1 port 24 map 10g-4x C2(config)# interface e1/24/1-4 C2(config-if-range)# switchport mode trunk C2(config-if-range)# mtu 9216 C2(config-if-range)# channel-group 2 mode active C2(config-if-range)# exit C2(config-if)# exit
Remove the cables that are attached to the CN1610 switch CL2 on all the nodes.
Using supported cabling, you must reconnect the disconnected ports on all the nodes to the Nexus 3232C switch C2.
Remove four ISL cables from ports 13 to 16 on the CN1610 switch CL1.
You must attach the appropriate Cisco QSFP28 to SFP+ breakout cables connecting port 1/24 on the new Cisco 3232C switch C2 to ports 13 to 16 on the existing CN1610 switch CL1.
When reconnecting any cables to the new Cisco 3232C switch, the cables used must be either optical fiber or Cisco twinax cables.
Make the ISL dynamic by configuring the ISL interface 3/1 on the active CN1610 switch to disable the static mode.
This configuration matches with the ISL configuration on the 3232C switch C2 when the ISLs are brought up on both switches.
Show example
The following example shows the ISL interface 3/1 being configured to make the ISL dynamic:
(CL1)# configure (CL1)(Config)# interface 3/1 (CL1)(Interface 3/1)# no port-channel static (CL1)(Interface 3/1)# exit (CL1)(Config)# exit (CL1)#
Bring up ISLs 13 through 16 on the active CN1610 switch CL1.
Show example
The following example shows ISL ports 13 through 16 being brought up on the port-channel interface 3/1:
(CL1)# configure (CL1)(Config)# interface 0/13-0/16,3/1 (CL1)(Interface 0/13-0/16,3/1)# no shutdown (CL1)(Interface 0/13-0/16,3/1)# exit (CL1)(Config)# exit (CL1)#
Verify that the ISLs are
upon the CN1610 switch CL1.The "Link State" should be
Up, "Type" should beDynamic, and the "Port Active" column should beTruefor ports 0/13 to 0/16.Show example
The following example shows the ISLs being verified as
upon the CN1610 switch CL1:(CL1)# show port-channel 3/1 Local Interface................................ 3/1 Channel Name................................... ISL-LAG Link State..................................... Up Admin Mode..................................... Enabled Type........................................... Dynamic Load Balance Option............................ 7 (Enhanced hashing mode) Mbr Device/ Port Port Ports Timeout Speed Active ------ ------------- ---------- ------- 0/13 actor/long 10 Gb Full True partner/long 0/14 actor/long 10 Gb Full True partner/long 0/15 actor/long 10 Gb Full True partner/long 0/16 actor/long 10 Gb Full True partner/long -
upon the 3232C switch C2:show port-channel summaryFor more information on Cisco commands, see the guides listed in the Cisco Nexus 3000 Series NX-OS Command References.
Ports Eth1/24/1 through Eth1/24/4 should indicate
(P), meaning that all four ISL ports are up in the port channel. Eth1/31 and Eth1/32 should indicate(D)as they are not connected.Show example
upon the 3232C switch C2:C2# show port-channel summary Flags: D - Down P - Up in port-channel (members) I - Individual H - Hot-standby (LACP only) s - Suspended r - Module-removed S - Switched R - Routed U - Up (port-channel) M - Not in use. Min-links not met ------------------------------------------------------------------------------ Group Port- Type Protocol Member Ports Channel ------------------------------------------------------------------------------ 1 Po1(SU) Eth LACP Eth1/31(D) Eth1/32(D) 2 Po2(SU) Eth LACP Eth1/24/1(P) Eth1/24/2(P) Eth1/24/3(P) Eth1/24/4(P) -
Bring up all of the cluster interconnect ports that are connected to the 3232C switch C2 on all of the nodes:
network port modify -node node-name -port port-name -up-admin trueShow example
The following example shows how to bring up the cluster interconnect ports connected to the 3232C switch C2:
cluster::*> network port modify -node n1 -port e0b -up-admin true cluster::*> network port modify -node n1 -port e0c -up-admin true cluster::*> network port modify -node n2 -port e0b -up-admin true cluster::*> network port modify -node n2 -port e0c -up-admin true
Revert all of the migrated cluster interconnect LIFs that are connected to C2 on all of the nodes:
network interface revert -vserver cluster -lif lif-nameShow example
cluster::*> network interface revert -vserver cluster -lif n1_clus2 cluster::*> network interface revert -vserver cluster -lif n1_clus3 cluster::*> network interface revert -vserver cluster -lif n2_clus2 cluster::*> network interface revert -vserver cluster -lif n2_clus3
Verify that all of the cluster interconnect ports are reverted to their home ports:
The following example shows that the LIFs on clus2 are reverted to their home ports; the LIFs are successfully reverted if the ports in the "Current Port" column have a status of
truein the "Is Home" column. If the "Is Home" value isfalse, then the LIF is not reverted.cluster::*> network interface show -role cluster (network interface show) Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home -------- ---------- ----------- -------------- -------- -------- ----- Cluster n1_clus1 up/up 10.10.0.1/24 n1 e0a true n1_clus2 up/up 10.10.0.2/24 n1 e0b true n1_clus3 up/up 10.10.0.3/24 n1 e0c true n1_clus4 up/up 10.10.0.4/24 n1 e0d true n2_clus1 up/up 10.10.0.5/24 n2 e0a true n2_clus2 up/up 10.10.0.6/24 n2 e0b true n2_clus3 up/up 10.10.0.7/24 n2 e0c true n2_clus4 up/up 10.10.0.8/24 n2 e0d true 8 entries were displayed. -
Verify that all of the cluster ports are connected:
The following example shows the output verifying all of the cluster interconnects are
up:cluster::*> network port show -role cluster (network port show) Node: n1 Broadcast Speed (Mbps) Health Ignore Port IPspace Domain Link MTU Admin/Open Status Health Status ----- --------- ----------- ----- ----- ------------ -------- ------------- e0a cluster cluster up 9000 auto/10000 - e0b cluster cluster up 9000 auto/10000 - e0c cluster cluster up 9000 auto/10000 - - e0d cluster cluster up 9000 auto/10000 - - Node: n2 Broadcast Speed (Mbps) Health Ignore Port IPspace Domain Link MTU Admin/Open Status Health Status ----- --------- ----------- ----- ----- ------------ -------- ------------- e0a cluster cluster up 9000 auto/10000 - e0b cluster cluster up 9000 auto/10000 - e0c cluster cluster up 9000 auto/10000 - e0d cluster cluster up 9000 auto/10000 - 8 entries were displayed. -
n1
n2
Host is n1
Ping status:....
RPC status:
Migrate the LIFs that are associated with the first CN1610 switch CL1:
network interface migrate -vserver cluster -lif lif-name -source-node node-nameShow example
You must migrate each cluster LIF individually to the appropriate cluster ports hosted on cluster switch C2 as shown in the following example:
cluster::*> network interface migrate -vserver cluster -lif n1_clus1 -source-node n1 -destination-node n1 -destination-port e0b cluster::*> network interface migrate -vserver cluster -lif n1_clus4 -source-node n1 -destination-node n1 -destination-port e0c cluster::*> network interface migrate -vserver cluster -lif n2_clus1 -source-node n2 -destination-node n2 -destination-port e0b cluster::*> network interface migrate -vserver cluster -lif n2_clus4 -source-node n2 -destination-node n2 -destination-port e0c
Step 3: Replace cluster switch CL1 with C1
Verify the cluster's status:
The following example shows that the required cluster LIFs have been migrated to the appropriate cluster ports hosted on cluster switch C2:
cluster::*> network interface show -role cluster (network interface show) Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home -------- ---------- ----------- -------------- -------- -------- ----- Cluster n1_clus1 up/up 10.10.0.1/24 n1 e0b false n1_clus2 up/up 10.10.0.2/24 n1 e0b true n1_clus3 up/up 10.10.0.3/24 n1 e0c true n1_clus4 up/up 10.10.0.4/24 n1 e0c false n2_clus1 up/up 10.10.0.5/24 n2 e0b false n2_clus2 up/up 10.10.0.6/24 n2 e0b true n2_clus3 up/up 10.10.0.7/24 n2 e0c true n2_clus4 up/up 10.10.0.8/24 n2 e0c false 8 entries were displayed. -
Shut down the node ports that are connected to CL1 on all of the nodes:
The following example shows specific ports being shut down on nodes n1 and n2:
cluster::*> network port modify -node n1 -port e0a -up-admin false cluster::*> network port modify -node n1 -port e0d -up-admin false cluster::*> network port modify -node n2 -port e0a -up-admin false cluster::*> network port modify -node n2 -port e0d -up-admin false
Shut down the ISL ports 24, 31, and 32 on the active 3232C switch C2.
Show example
The following example shows ISLs 24, 31, and 32 being shut down on the active 3232C switch C2:
C2# configure C2(config)# interface ethernet 1/24/1-4 C2(config-if-range)# shutdown C2(config-if-range)# exit C2(config)# interface ethernet 1/31-32 C2(config-if-range)# shutdown C2(config-if-range)# exit C2(config)# exit C2#
Remove the cables that are attached to the CN1610 switch CL1 on all of the nodes.
Using the appropriate cabling, you must reconnect the disconnected ports on all the nodes to the Nexus 3232C switch C1.
Remove the QSFP28 cables from Nexus 3232C C2 port e1/24.
You must connect ports e1/31 and e1/32 on C1 to ports e1/31 and e1/32 on C2 using supported Cisco QSFP28 optical fiber or direct-attach cables.
Restore the configuration on port 24 and remove the temporary port-channel 2 on C2:
Show example
running-configurationfile being copied to thestartup-configurationfile:C2# configure C2(config)# no interface breakout module 1 port 24 map 10g-4x C2(config)# no interface port-channel 2 C2(config-if)# interface e1/24 C2(config-if)# description 100GbE/40GbE Node Port C2(config-if)# spanning-tree port type edge Edge port type (portfast) should only be enabled on ports connected to a single host. Connecting hubs, concentrators, switches, bridges, etc... to this interface when edge port type (portfast) is enabled, can cause temporary bridging loops. Use with CAUTION Edge Port Type (Portfast) has been configured on Ethernet 1/24 but will only have effect when the interface is in a non-trunking mode. C2(config-if)# spanning-tree bpduguard enable C2(config-if)# mtu 9216 C2(config-if-range)# exit C2(config)# exit C2# copy running-config startup-config [] 100% Copy Complete.
Bring up ISL ports 31 and 32 on C2, the active 3232C switch.
Show example
The following example shows ISLs 31 and 32 being brought upon the 3232C switch C2:
C2# configure C2(config)# interface ethernet 1/31-32 C2(config-if-range)# no shutdown C2(config-if-range)# exit C2(config)# exit C2# copy running-config startup-config [] 100% Copy Complete.
Verify that the ISL connections are
upon the 3232C switch C2.For more information on Cisco commands, see the guides listed in the Cisco Nexus 3000 Series NX-OS Command References.
Show example
The following example shows the ISL connections being verified. Ports Eth1/31 and Eth1/32 indicate
(P), meaning that both the ISL ports areupin the port-channel:C1# show port-channel summary Flags: D - Down P - Up in port-channel (members) I - Individual H - Hot-standby (LACP only) s - Suspended r - Module-removed S - Switched R - Routed U - Up (port-channel) M - Not in use. Min-links not met ------------------------------------------------------------------------------ Group Port- Type Protocol Member Ports Channel ----------------------------------------------------------------------------- 1 Po1(SU) Eth LACP Eth1/31(P) Eth1/32(P) C2# show port-channel summary Flags: D - Down P - Up in port-channel (members) I - Individual H - Hot-standby (LACP only) s - Suspended r - Module-removed S - Switched R - Routed U - Up (port-channel) M - Not in use. Min-links not met ------------------------------------------------------------------------------ Group Port- Type Protocol Member Ports Channel ------------------------------------------------------------------------------ 1 Po1(SU) Eth LACP Eth1/31(P) Eth1/32(P) -
Bring up all of the cluster interconnect ports connected to the new 3232C switch C1 on all of the nodes:
The following example shows all of the cluster interconnect ports connected to the new 3232C switch C1 being brought up:
cluster::*> network port modify -node n1 -port e0a -up-admin true cluster::*> network port modify -node n1 -port e0d -up-admin true cluster::*> network port modify -node n2 -port e0a -up-admin true cluster::*> network port modify -node n2 -port e0d -up-admin true
Verify the status of the cluster node port:
The following example shows output that verifies that the cluster interconnect ports on nodes n1 and n2 on the new 3232C switch C1 are
up:cluster::*> network port show -role cluster (network port show) Node: n1 Broadcast Speed (Mbps) Health Ignore Port IPspace Domain Link MTU Admin/Open Status Health Status ----- --------- ---------- ----- ----- ------------ -------- ------------- e0a cluster cluster up 9000 auto/10000 - e0b cluster cluster up 9000 auto/10000 - e0c cluster cluster up 9000 auto/10000 - - e0d cluster cluster up 9000 auto/10000 - - Node: n2 Broadcast Speed (Mbps) Health Ignore Port IPspace Domain Link MTU Admin/Open Status Health Status ----- --------- ---------- ----- ----- ------------ -------- ------------- e0a cluster cluster up 9000 auto/10000 - e0b cluster cluster up 9000 auto/10000 - e0c cluster cluster up 9000 auto/10000 - e0d cluster cluster up 9000 auto/10000 - 8 entries were displayed.
Step 4: Complete the procedure
Revert all of the migrated cluster interconnect LIFs that were originally connected to C1 on all of the nodes:
network interface revert -server cluster -lif lif-nameShow example
cluster::*> network interface revert -vserver cluster -lif n1_clus1 cluster::*> network interface revert -vserver cluster -lif n1_clus4 cluster::*> network interface revert -vserver cluster -lif n2_clus1 cluster::*> network interface revert -vserver cluster -lif n2_clus4
Verify that the interface is now home:
The following example shows the status of cluster interconnect interfaces is
upand "Is Home" for nodes n1 and n2:cluster::*> network interface show -role cluster (network interface show) Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home -------- ---------- ----------- -------------- -------- -------- ----- Cluster n1_clus1 up/up 10.10.0.1/24 n1 e0a true n1_clus2 up/up 10.10.0.2/24 n1 e0b true n1_clus3 up/up 10.10.0.3/24 n1 e0c true n1_clus4 up/up 10.10.0.4/24 n1 e0d true n2_clus1 up/up 10.10.0.5/24 n2 e0a true n2_clus2 up/up 10.10.0.6/24 n2 e0b true n2_clus3 up/up 10.10.0.7/24 n2 e0c true n2_clus4 up/up 10.10.0.8/24 n2 e0d true 8 entries were displayed. -
n1
n2
Host is n1
Ping status:....
RPC status:
3 paths up, 0 paths down (udp check)
Expand the cluster by adding nodes to the Nexus 3232C cluster switches.
Display the information about the devices in your configuration:
network device-discovery show -
network port show -role cluster -
network interface show -role cluster -
The following examples show nodes n3 and n4 with 40 GbE cluster ports connected to ports e1/7 and e1/8, respectively, on both the Nexus 3232C cluster switches. Both nodes are joined to the cluster. The 40 GbE cluster interconnect ports used are e4a and e4e.
cluster::*> network device-discovery show Local Discovered Node Port Device Interface Platform ------ ------ ------------ --------------- ------------- n1 /cdp e0a C1 Ethernet1/1/1 N3K-C3232C e0b C2 Ethernet1/1/1 N3K-C3232C e0c C2 Ethernet1/1/2 N3K-C3232C e0d C1 Ethernet1/1/2 N3K-C3232C n2 /cdp e0a C1 Ethernet1/1/3 N3K-C3232C e0b C2 Ethernet1/1/3 N3K-C3232C e0c C2 Ethernet1/1/4 N3K-C3232C e0d C1 Ethernet1/1/4 N3K-C3232C n3 /cdp e4a C1 Ethernet1/7 N3K-C3232C e4e C2 Ethernet1/7 N3K-C3232C n4 /cdp e4a C1 Ethernet1/8 N3K-C3232C e4e C2 Ethernet1/8 N3K-C3232C 12 entries were displayed. cluster::*> network port show -role cluster (network port show) Node: n1 Broadcast Speed (Mbps) Health Ignore Port IPspace Domain Link MTU Admin/Open Status Health Status ----- --------- ---------- ----- ----- ------------ -------- ------------- e0a cluster cluster up 9000 auto/10000 - e0b cluster cluster up 9000 auto/10000 - e0c cluster cluster up 9000 auto/10000 - - e0d cluster cluster up 9000 auto/10000 - - Node: n2 Broadcast Speed (Mbps) Health Ignore Port IPspace Domain Link MTU Admin/Open Status Health Status ----- --------- ---------- ----- ----- ------------ -------- ------------- e0a cluster cluster up 9000 auto/10000 - e0b cluster cluster up 9000 auto/10000 - e0c cluster cluster up 9000 auto/10000 - e0d cluster cluster up 9000 auto/10000 - - Node: n3 Broadcast Speed (Mbps) Health Ignore Port IPspace Domain Link MTU Admin/Open Status Health Status ----- --------- ---------- ----- ----- ------------ -------- ------------- e4a cluster cluster up 9000 auto/40000 - e4e cluster cluster up 9000 auto/40000 - - Node: n4 Broadcast Speed (Mbps) Health Ignore Port IPspace Domain Link MTU Admin/Open Status Health Status ----- --------- ---------- ----- ----- ------------ -------- ------------- e4a cluster cluster up 9000 auto/40000 - e4e cluster cluster up 9000 auto/40000 - 12 entries were displayed. cluster::*> network interface show -role cluster (network interface show) Logical Status Network Current Current Is Vserver Interface Admin/Oper Address/Mask Node Port Home -------- ---------- ----------- -------------- -------- -------- ----- Cluster n1_clus1 up/up 10.10.0.1/24 n1 e0a true n1_clus2 up/up 10.10.0.2/24 n1 e0b true n1_clus3 up/up 10.10.0.3/24 n1 e0c true n1_clus4 up/up 10.10.0.4/24 n1 e0d true n2_clus1 up/up 10.10.0.5/24 n2 e0a true n2_clus2 up/up 10.10.0.6/24 n2 e0b true n2_clus3 up/up 10.10.0.7/24 n2 e0c true n2_clus4 up/up 10.10.0.8/24 n2 e0d true n3_clus1 up/up 10.10.0.9/24 n3 e4a true n3_clus2 up/up 10.10.0.10/24 n3 e4e true n4_clus1 up/up 10.10.0.11/24 n4 e4a true n4_clus2 up/up 10.10.0.12/24 n4 e4e true 12 entries were displayed. cluster::> system cluster-switch show Switch Type Address Model --------------------------- ---------------- ------------- --------- C1 cluster-network 10.10.1.103 NX3232C Serial Number: FOX000001 Is Monitored: true Reason: Software Version: Cisco Nexus Operating System (NX-OS) Software, Version 7.0(3)I6(1) Version Source: CDP C2 cluster-network 10.10.1.104 NX3232C Serial Number: FOX000002 Is Monitored: true Reason: Software Version: Cisco Nexus Operating System (NX-OS) Software, Version 7.0(3)I6(1) Version Source: CDP CL1 cluster-network 10.10.1.101 CN1610 Serial Number: 01234567 Is Monitored: true Reason: Software Version: 1.2.0.7 Version Source: ISDP CL2 cluster-network 10.10.1.102 CN1610 Serial Number: 01234568 Is Monitored: true Reason: Software Version: 1.2.0.7 Version Source: ISDP 4 entries were displayed.
Remove the replaced CN1610 switches if they are not automatically removed:
system cluster-switch delete -device switch-nameShow example
You must delete both devices individually as shown in the following example:
cluster::> system cluster-switch delete –device CL1 cluster::> system cluster-switch delete –device CL2
Verify that the proper cluster switches are monitored:
The following example shows cluster switches C1 and C2 are being monitored:
cluster::> system cluster-switch show Switch Type Address Model --------------------------- ------------------ ---------------- --------------- C1 cluster-network 10.10.1.103 NX3232C Serial Number: FOX000001 Is Monitored: true Reason: Software Version: Cisco Nexus Operating System (NX-OS) Software, Version 7.0(3)I6(1) Version Source: CDP C2 cluster-network 10.10.1.104 NX3232C Serial Number: FOX000002 Is Monitored: true Reason: Software Version: Cisco Nexus Operating System (NX-OS) Software, Version 7.0(3)I6(1) Version Source: CDP 2 entries were displayed. -
If you suppressed automatic case creation, reenable it by invoking an AutoSupport message:
