Verifying operation after power line disruption

You can test the MetroCluster configuration's response to the failure of a PDU.

About this task

The best practice is for each power supply unit (PSU) in a component to be connected to separate power supplies. If both PSUs are connected to the same power distribution unit (PDU) and an electrical disruption occurs, the site could down or a complete shelf might become unavailable. Failure of one power line is tested to confirm that there is no cabling mismatch that could cause a service disruption.

This test should take about 15 minutes.

This test requires turning off power to all left-hand PDUs and then all right-hand PDUs on all of the racks containing the MetroCluster components.

This procedure has the following expected results:

Procedure

  1. Turn off the power of the PDUs on the left-hand side of the rack containing the MetroCluster components.
  2. Monitor the result on the console by using the system environment sensors show -state fault and storage shelf show -errors commands.
    cluster_A::> system environment sensors show -state fault
    
    Node Sensor 			State Value/Units Crit-Low Warn-Low Warn-Hi Crit-Hi
    ---- --------------------- ------ ----------- -------- -------- ------- -------
    node_A_1
    		PSU1 			fault
    							PSU_OFF
    		PSU1 Pwr In OK 	fault
    							FAULT
    node_A_2
    		PSU1 			fault
    							PSU_OFF
    		PSU1 Pwr In OK 	fault
    							FAULT
    4 entries were displayed.
    
    cluster_A::> storage shelf show -errors
        Shelf Name: 1.1
         Shelf UID: 50:0a:09:80:03:6c:44:d5
     Serial Number: SHFHU1443000059
    
    Error Type          Description
    ------------------  ---------------------------
    Power               Critical condition is detected in storage shelf power supply unit "1". The unit might fail.Reconnect PSU1
    
  3. Turn the power back on to the left-hand PDUs.
  4. Make sure that ONTAP clears the error condition.